A New Integrated Protection Scheme for Closed loop distribution Network with Distributed Generator

A New Integrated Protection Scheme for Closed loop distribution Network with Distributed Generator
A New Integrated Protection Scheme for Closed loop distribution Network with Distributed Generator

Abstract --The paper proposes the protection schemes for closed loop distribution network with distributed generators. Generally, Most of distribution networks are operated in radial or open loop due to the security and protection limited. With the rapid

expansion of modern power systems and demand for high quality

of power supply, the closed loop operation is adopted gradually. Furthermore, with the increasing penetration of distributed generators, radial operation is not suit for improving stability of system and distributed generators. This paper investigates the protection requirements of closed loop network, and then analyzes the characteristics of conventional protection schemes

which are applied in closed loop distribution network. Taking

into distributed generators consideration, the paper proposes pilot wire instantaneous protection for closed loop network. What’s more, non-communication over-current protection is also investigated to be applied in closed loop network. The proposed protection schemes are able to significantly improve the reliability and security of closed loop distribution network with

distributed generators.

Index Terms --protection scheme, closed loop operation, distribution system, distributed generator

I. I NTRODUCTION

Y now most of power feeders in distribution network are operated in radial or open-loop. The character of open loop operation is that the feeder’s structure is a ring but one switch in the ring opens naturally, which is called tie switch. Open loop operation can be considered as one kind of radial operation because power flows on the feeders is in one direction only, which allows the use of protection system without directional discrimination. There are many strong points in open loop or radial operation such as increasing the system stability and simplifying protection schemes. In radial distribution network, time-graded over-current protection or inverse definite minimum time over-current protection (IDMT) is widely used to realize protection scheme with sensitivity and reliability [12, 15]. If fault occurs somewhere, the tripping can be made at one end (the source end) or two

This work was supported by the National Basic Research Program (973 Program) of China (No. 2009CB219704), National High-tech R&D Program (863 Program) of China (No. 2007AA05Z241) and Nature Science

Foundation of Tianjin City (NO. 08JCYBJC13500).

Bin Li is with Key Laboratory of Power System Simulation and Control of Ministry of Education, Tianjin, China (e-mail: libin_tju@https://www.wendangku.net/doc/1f10359238.html,) Xuan Yu is with Tianjin University as a postgraduate, Tianjin, China (e-mail: viocy.tju@https://www.wendangku.net/doc/1f10359238.html,)

Zhiqian Bo is with the AREVA T&D – Automation & Information System, UK (e-mail: Zhiqian.bo@https://www.wendangku.net/doc/1f10359238.html,)

ends of the protected line section for radial connected line or

open-loop systems. In the case of open-loop network, the healthy feeders can be served in another route by closing the normally open tie switch with a short interval. Radial or open loop operation has been adopted in the operation of

distribution network for many decades. With the rapid expansion of modern power systems and demand for high quality of power supply, closed loop operation is becoming a subject, which is applied in distributed network in recent years, especially for the network with presence of distributed generators (DG) [1-3]. Compared with open loop, the tie

switch is closed naturally in closed loop operation, so that fault on one section can’t cause power losses in downstream feeders. Besides decreasing power losses, closed loop operation can also keep feeders’ voltage level, and has more capacity of load rising [3]. Obviously, it is desirable to realize protection for closed

loop feeders by using simple and feasible protection scheme. However, conventional over-current protection has such

shortcomings the relay near to source has longest operating tripping time is sometimes too long to prevent excessive disturbance of the power system. The rather that DGs are also involved in this network, asking for stricter operation of relays [4]. The fault clear time will determine whether DGs loss stability or not, and the adjunction of DGs also affect power flow and complicate voltage and reactive power control, so it will affect the relay action in turn. All mentioned above decide that how to design an appropriate protection scheme for closed loop network with DGs becomes a key research topic to ensure the security of power network and exert the capacity of DGs [5-7, 13]. Although closed loop operation brings lots of advantages in improving the security and continuity of power supply, it also increases the short circuit currents and increase the voltage dips frequency and severity. The closed loop operation is more vulnerable to power system oscillation and fault enlargement. Furthermore, the more complex protection scheme must be designed to satisfy the requirements of

reliability and sensitivity, etc.

Firstly, the paper presents brief introduction on protection scheme of radial or open loop network, emphases on the coordination with the time-graded over-current protection and IDMT. Secondly, the paper investigates protection schemes for closed loop feeders, and reliability and sensitivity of protection schemes are verified according to a typical closed loop network. Thirdly, by taking into account the stability of DGs in closed loop network, protection schemes are suggested Bin Li, Member, IEEE , Xuan Yu, and Zhiqian Bo, Senior Member, IEEE

Protection Schemes for Closed Loop Distribution Network with Distributed

Generator

B

based on the analysis of different protection schemes and its investment. In addition, non-communication over-current protection is adopted in the paper to realize protection scheme for closed loop network with DGs.

II. C ONVENTIONAL P ROTECTION FOR D ISTRIBUTION F EEDERS In practice, a large portion of distribution network use time-graded over-current protection or IDMT coordination. As for radial and single breaker system, because there is only one direction current flow from terminal source to downstream, the power directional relay is not necessary. Generally, relay and recloser are located in the main upstream feeder, and time-graded over-current protection or IDMT can be used to realize the main and backup protection for feeders with high sensitivity and reliability.

For the distribution feeders as shown in Fig.1 (a), the over-current protection settings are given in Fig.1, the derivation of which is given in the reference [12]. In order to ensure the protection selectivity, the tripping time-distance characteristics of the time-graded over-current protection and IDMT are

demonstrated in Fig.1(b) and Fig.1(c) respectively.

Fig.1 Relay coordination principle

(a)Distribution network with relay units

(b)Coordination of definite time delay over-current relay

(c)Coordination of IDMT relay

As is known to all, the length of the line has a direct effect

on the setting of a relay. Primarily, relays are applied to

protect a given line segment and, in addition if possible, to

back up the relay protecting adjacent line segments. However,

in industry field of distribution network, power cable is

usually short, sometimes it is only a few kilometers or

hundreds meters. So cable impedance is much less than the

source impedance. In such a case there is very little difference

in current magnitude for a fault at one end of the line

compared to a fault at the other. Therefore, only conventional

definite time-delay over-current protection or IDMT is suit to

be used in these cases, whereas instantaneous over-current

cannot be used. Therefore, the tripping time increases as the

fault moves near to power source, and maximum the tripping

time is sometimes too long to prevent excessive disturbance of

the power system, especially for distribution network with

distributed generators, because DG may lose its stability when

the fault lasts too long.

In a radial network like Fig.1, time-delay over-current

protection as main protection is applied. While fault is close to

relay Ra will operate after a definite time, and all the feeders

include downstream bus-bars and their load, will drop out. In

order to avoid fault enlarging, loop operation is put into use,

which is divided into two models, open loop operation and

closed loop operation. Open loop operation will close the

normally opened tie switch s after relay tripping fault, and

restore the healthy buses service. Therefore, relays and

breakers should be installed in both terminals of feeders and

be directional such as Fig.2. Compared with open loop, the tie

switch is closed naturally in closed loop operation. With the

rapid expansion of modern power systems and demand for

high quality of power supply, closed loop operation is

desirable in recent years. Besides decreasing power losses,

closed loop operation can also keep feeders’ voltage level, and

has more capacity of load rising, etc.

Fig.2 loop operation in distribution network

Furthermore, with the increasing penetration of distributed

generators, radial operation is not suit for distribution network

with DGs. The presence of DGs in radial feeders leads to

unnecessary DG disconnection for faults occurring upstream

the DG connection point [13]. As shown in Fig.2, if the

network is in radial or open loop operation, DG will be

disconnected when fault occurs on upstream feeder A-B.

Obviously, it is not the best choice for exerting the maximum

role of DGs. Consequently, when DG is present, closed loop

operation is adopted in distribution network.

III. P ROTECTION S CHEME FOR C LOSED L OOP F EEDERS WITH

P RESENCE OF DISTRIBUTED GENERATORS

While upgraded from open loop to closed loop operation,

the capacities of transformers and feeders should be improved

firstly, and then, protection scheme must be upgraded in order

to ensure the reliability of power supply. According to the

different requirements for reliability and sensitivity of

protection, some practical and prospective protection schemes

are proposed. Especially for closed loop network DGs, the

characteristics of protection schemes are also discussed. A

certain applied closed loop distribution network is shown in

Fig.3.

Generator

5000kVA

3500kVA

2500kVA 3000kVA

Fig.3 Simulated closed loop network

In this network, from the point of 110kV substation, the impedance p.u. value of power supply is X 1.max.pu =0.5808, X 1.min.pu =2.1924,

X 0.max.pu =1.008, X 0.min.pu =1.6117. The base capacity S=1000MVA, and base voltage U=115kV. All cables are 3×240mm 2, and its impedance is 0.087?/km. Other related parameters are shown in Fig.3.

Taken this closed loop network as an example, the paper investigates the protection schemes as follows.

A. Select a disconnection point in the closed loop operation If open loop operation needs to be updated to closed loop operation in certain distribution network, the economic protection scheme is to select one disconnected point in the

closed loop. As for this scheme, each feeder can be guaranteed by one terminal breaker and corresponding over-current relay.

Generally, the disconnected point should be selected at the

point, which is near to the middle point of load, such as S point in Fig.3.

In this case, only breakers CB 1, CB 2, CB 3

and CB 6, CB

7, CB 8 are needed, and conventional time-delay over-current protection can be used without directional element. In normal operation, all of loads are served by power sources in closed

loop operation. When a fault occurs in the ring, no matter

where the fault is, the over-current protection R

3

(or R 8

) should pick up and trip breaker CB 3 (or CB 8) without time

delay. Consequently, according to the protection coordination for radial feeders, the time delay of relay R 1, R 2, R 3 and R 6, R 7, R 8

are shown in Fig.4(a).

When the fault occurs at the left side of CB 3 (or CB 8) and then R 3 (or R 8) trips instantaneously (for example, f 1 or f 2 fault), on the one hand, R 6, R 7 will return and loads in the right

healthy routine can be served continuously without any power interrupt. On the other hand, R 1 and R 2

will isolate fault

according to its time coordination shown in Fig.4(a).

Obviously, no matter which fault point is, some loads in bus-B

or bus-C may lose power supply. Furthermore, if fault

f 1

occurs at the point which is near to bus-A, the fault current flow through the R 3 may be too small to enable relay to trip the fault. In the case of that, R 3 can only trip fault after R

1. Based on the Fig.4(a), the tripping time is so long that the

system stability decreases.

Fig.4 Time coordination of over-current protection

It can be seen this protection configuration is the least investment scheme. But above all, the disconnection operation doesn’t improve the security and reliability of the system. What’s more, if DG is put into use in this network, DG may be disconnected unintentionally for faults occurring upstream the DG connection point. Actually, it is desirable that DG can supply power continuously when main power supply is lost. In sum, this protection scheme is a compromise scheme with low

investment and comparatively high reliability. However, in the case that more reliability and security are required, some advanced protection schemes should be applied. B. Conventional Protection Scheme for closed loop network

1) Directional over-current protection Generally, in order to improve the reliability of power supply and ensure the selectivity of protection, conventional

over-current protection must be replaced by directional relay, such as directional over-current protection, distance protection, etc. Besides that, breakers and directional relay should be applied on both sides of feeders.

In this way, relay R 1, R 2, R 3, R 4 and R 5 compose one series of protections with anti-clockwise direction for one power supply routine, whereas R 6, R 7, R 8, R 9 and R 10 compose another series of protections for another routine. According to the time coordination of over-current protection, the time delay of the relays are shown in Fig.4(b). If fault occurs at f 2

point on feeder, the relays R 2 and R 9 can trip fault by disconnecting two terminal breakers CB 2 and CB 9. It can be seen that all of loads distributed on bus-bars will not lose its power supply in this case. Even if fault occurs at f 3 point on bus-D, the relays R 3 and R 7 will trip breakers CB 3 and CB 7 so that the faulty bus-bar is isolated. Only loads on faulty bus-bar disconnected from power supply.

In this scheme, the number of loads influenced by a fault

can be minimized. From the view of protection selectivity, this scheme is superior to scheme A described above. However, from the view of fault clearing time, this scheme has a longer tripping time for each protection, which can be derived from the comparison between Fig.4 (a) and (b). Generally, the time step coordination between two sequent relay is with 0.3, so if fault occurs at f1 point, the fault clearing time of relay R1 reaches 1.2 seconds. Obviously, the over-current based time-graded protection has such shortcomings the relay near to source has longest operating time setting, where the fault level is the highest.

Furthermore, in radial network with time-graded over-current relays, the sensitivity of sequence time-graded over-current protections is generally satisfied because the fault current increases with the fault length decreases. But it is not true for closed loop operation. For example, if f1 point is very close to bus-A, the fault current flow through relay R10 may be so small that R10 may not pick up and trip fault with zero time delay (because pick up value of R10 must be greater than the minimum distinguishable value of protection device). In this case, flowing through great fault current, it is ensured that R1 will trip fault with longest time delay (1.2s), and then R6~R10 operate in radial operation, so R10 can trip fault consequently. Obviously, the fault f1 will be cleared by two terminal circuit breakers with a long time delay, which must be longer than 1.2s. It indicates that the clearing time is too long when closed loop has more feeder sections.

However, fault clearing time is critical for stability of power system, especially for distributed generators. As analysis mentioned in section II, no matter what kind of distributed generators are, long fault clearing time may leads to prompt disconnection of inverter-based power source and synchronized generator lose its stability. Therefore, instantaneous or short time delay protections should be considered as beneficial compensation for integrated protection scheme.

2) Distance protection

Distance protection can trip fault with comparatively short time, and less affected by the operation mode. At the same time, the better coordination among different distance protections is realized. However, the length of feeders in distributed network may be very short in real power distribution system so that the sensitivity of distance protection may not be satisfied.

3) Pilot current differential protection

Since closed loop operation increases the fault current and voltage dip, instantaneous protection is desirable to ensure reliable operation. Undoubtedly, pilot current differential relay provides instantaneous protection for feeders with the highest sensitivity, reliability and selectivity. With this scheme, the protection can trip feeder fault instantaneously and loads restore from fault condition quickly. The advantages of pilot current differential protection is well known, therefore it will not be described here.

Compared to conventional over-current or distance protection, pilot current differential protection improve the distribution system reliability with the expense that communication channel and its facilities are needed.

Besides those considerations, pilot current differential relay cannot provide protection for bus-bar, with which loads and DGs are connected. And that directional over-current relay can only trip bus-bar fault with some definite time delay. Generally, the bus-bar in distribution network isn’t configured with special current differential protection. However, the fault in bus-bar is more serious than that in feeders. It leads to sharp voltage drop and huge short-circuit current. Therefore bus-bar fault clearing time cannot be longer than several hundred milliseconds if DGs are taken into consideration.

C. Proposed Novel Protection for closed loop network

1) Pilot wire instantaneous over-current protection Generally differential protection is not provided for bus-bars in distribution network. But in order to realize instantaneous protection for important bus-bar with DGs, special bus-bar differential protection can be given. Besides that, the paper propose another choice of protection scheme for bus-bar, that is, a novel pilot wire instantaneous over-current protection, which is able to trip both feeder and bus-bar faults with minimum time delay.

The principle of this pilot wire Instantaneous over-current protection is shown in Fig.5.

A B C D

(a)

(b)

E

Fig .5 Schematics of pilot wire instantaneous over-current protection

(a) Over-current protection coordination

(b) Pilot wire instantaneous protection for bus-bar and feeder

In closed loop network shown in Fig.3, all of directional protections with same protective direction can be considered as one group, such as relay R1~R5. In order to illustrate the theory of pilot wire instantaneous over-current protection, the protection coordination of relay R1~R5 can be analyzed in a simplified radial operation system, as shown in Fig.5(a). And the principle of this pilot wire Instantaneous over-current protection is shown in Fig.5(b), in which the coordination of

R3~R5 is taken as an example to illustrate the protection principle.

Except over-current protection R5 on the end feeder, the other protections operate in two executive routines after pick up. For one executive routine, each feeder protection will send trip signal with its corresponding time delay t Rn after pick up. This routine is here called routine-1. For another executive routine, the trip signal is decided by pick up condition of local protection and the blocking signal, which is sent by downstream protection based on its pick up condition. This routine is here called routine-2.

For example, if fault f5 occurs on the end section of power supply feeder, all relay R1~R5 can detect the fault and pick up. However, R5 will trip the fault f5 instantaneously. At the same time, as a blocking signal, the pick up signal of relay R5 is sent through a wire cable to the upstream protection R4. Obviously, the executive routine-2 of protection R4 is blocked, and R4 can only trip fault with definite time delay t R4. However, after R5 trips and then CB5 disconnection, fault f5 will be isolated and all other over-current relays R1~R4 will return. Of course, if relay R5 refuse to trip fault f5 because some unexpected reasons, relay R4 can trip the fault by executive routine-1 with time delay t R4. It can be noticed that the coordination of relay R4 and R5 is ensured with high reliability.

If fault f4 occurs on the DE feeder or bus-E, R1~R4 detect fault and pick up, but relay R5 will not pick up because fault is located in the reverse direction. Therefore, the blocking signal from R5 is zero, so the executive routine-2 of relay R4 is enabled. R4 pick up signal can be passed through “AND” gate. After a short time delay tε, the tripping signal will be sent to CB4 directly. It should be noted that tε is only a fixed short time delay, which is used to ensure the transferring time delay of blocking signal from downstream relay. Obviously, in this way, relay R4 can clear faults of DE feeder or bus-E with a very short time delay tε, not comparatively long time delay t R4. Of course, if relay R4 refuse to clear faults of DE feeder or bus-E, relay R3 will operate as a backup protection with original time of R3 and R4.

With same operation logic, the relay R1~R3 can also clear faults of local feeder and remote bus-bar with a short time delay tε. Therefore, the continuity of power supply, stability of distribution system and DGs are all improved with high reliability. At present, this blocking function in conventional over-current or IDMT protection has been developed. What’s more, the pilot wire instantaneous over-current protection has been applied successfully on providing instantaneous protection for feeder and bus-bar.

In this protection scheme, wire cable act as a type of communication channel, but sometimes it cannot be supplied. Therefore, it would be beneficial if the speed of response of the over-current based protection scheme could be substantially increased without the need for communication link.

2) Non-communication directional over-current protection Recently, the concept of non-communication protection has attracted the interests of both academics and manufactures. Based on the concept, a number new protection schemes for distribution systems have been proposed to accelerate the speed of response of the over-current protection [8-11, 14]. Here non-communication over-current protection is considered to be applied in closed loop network shown in Fig.3. The relays are arranged into two groups. The conventional time setting over-current protection group includes R4, R5 and R9, R10. Obviously, It is easily noticed from Fig.4(b) that these relays are set faster operating time. The accelerated operation group consists of the relays R1, R2, R6 and R7 which are set slower operating time in the conventional scheme. The target of the protection technique is to improve the respond speed of the accelerated operation group.

With reference to Fig.3, for a fault f1 occurring on cable section AB, the directional relays R1 and R6~R10 may detect the fault since the fault is in the forward direction to these relays. The relay R10 that has the fastest time setting will operate first to open its associated circuit breaker CB10. After the opening of the circuit breaker CB10, the fault is isolated from cable section BC, CD, DE and EA, and their associated relay R6~R9 will restrain from operation. However, the opening of the circuit breaker CB10 does not clear the fault on the section AB. As long as R1 detect the opening of the circuit breaker CB10, it means that the fault is on the protected cable section AB, and then relay R1 will accelerated trip breaker CB1. The detection of the circuit breaker operation takes only a few power frequency cycles; therefore, the operation speed of the relay R1 can be significantly accelerated. In this way, relay R2, R6 and R7 can be accelerated when fault occurs on its associated feeder.

In sum, the relay makes tripping decision based on detecting the breaker operation to determine whether the system is in a balanced operation or not. The system unbalance ratio and the super-imposed signals are used to detect the remote breaker operation, from which whether an unbalanced fault is on the protected section can be derived [14]. However, these proposed methods can only be used to determine whether remote breaker opens or not when an unbalanced fault occurs. Particularly, as for closed loop operation, the fault current flowing through local relay will increase when the remote breaker of the line is disconnected. For example, after R10 trips fault f1, the fault current flowing through R1 will increase definitely. Therefore, by detecting the variation of fault current, no matter what kind of fault is, remote breaker operation can be estimated.

Therefore, it is feasible and economic for closed loop network to use non-communication over-current protection to ensure the stability of system and distributed generators.

IV. C ONCLUSION

This paper proposes a series of protection schemes for closed loop distribution network based on the different protection requirements. These protection schemes vary from fault clear effect, investment to impact on distributed generators. Considering the continuity of power supply and stability of system and distributed generators, a novel pilot wire instantaneous protection is implemented in this paper.

Besides that, the paper also discusses the application and its improvement of non-communication over-current protection in closed loop network with distributed generators.

V. R EFERENCES

Periodicals:

[1]Tsai-Hsiang Chen, Wei-Tzer Huang, Jyh-Cherng, et al, "Feasibility

Study of Upgrading Primary Feeders From Radial and Open-Loop to Normally Closed-Loop Arrangement", Power Systems, IEEE Transactions on, vol.19, No.3, pp.1308-1316, Aug. 2004.

[2]W. T. Huang and T. H. Chen, "Assessment of upgrading existing

primary feeders from radial to normally closed loop arrangement,"

Transmission and Distribution Conference and Exhibition 2002: Asia Pacific. IEEE/PES, vol. 3, pp. 2123-2128, 2002.

[3] F. A. Viawan and D. Karlsson, "Voltage and Reactive Power Control in

Closed Loop Feeders with Distributed Generation", Power Tech, 2007 IEEE Lausanne, pp. 549-554, 2007.

[4]S. K. Salman and I. M. Rida, "Investigating the impact of embedded

generation on relay settings of utilities electrical feeders," Power Delivery, IEEE Transactions on, vol. 16, pp. 246-251, 2001.

[5]S. M. Brahma, A. A. Girgis, "Development of Adaptive Protection

Scheme for Distribution Systems with High Penetration of Distributed Generation", Power Delivery, IEEE Transactions on, vol.19, No.1, pp.

56-63, Jan. 2004.

[6]S. K. Salman and S. F. Tan, "Comparative Study of Protection

Requirements of Active Distribution Networks Using Radial and Ring Operations," Power Tech, 2007 IEEE Lausanne, pp. 1182-1186, 2007. [7] F. A. Viawan and D. Karlsson, "Various Protection Schemes for Closed

Loop Feeders with Synchronous Machine Based Distributed Generation and Their Impacts on Reliability," Power Tech, 2007 IEEE Lausanne,

pp. 1170-1175, 2007.

[8]Z Q Bo, "A New Non-communication Protection Technique for

Transmission Lines", Power Delivery, IEEE Transactions on, vol.13, No.4, pp. 1073 – 1078, Oct. 1998.

[9]S X Shi, X Z Dong, J Z Liu, Z Q Bo, “Research on Non-communication

Protection for Distribution Systems”, Journal of Power System Automation, 25(6), pp. 31-34, Oct. 2001 .

[10]J K Liu, X Z Dong, Z Q Bo, “Studies of Non-Communication Protection

of Distribution Systems with Tapped-off-loads”, Journal of Power System Automation, 27(1): pp. 37-41, 2003.

[11]J K Liu, X Z Dong, Z Q Bo, “Implementation of A Non-Communication

Protection of Distribution System with Tapped-off-loads”, Journal of Power System Automation, 27(23): pp. 41-44, 2003.

Books:

[12]Stanley H. Horowitz, Arun G. Phadke, Power System Relaying,

Chichester, West Sussex: John Wiley & Sons Ltd, 2008.

[13]Nick Jenkins, Ron Allan, Peter Crossley, et al, Embeded Generation,

The Institution of Electrical Engineers, 2000.

Papers from Conference Proceedings (Published):

[14]Z Q Bo, X Z Dong, B R J Caunce, et al, "Scheme of Accelerated

Overcurrent Protection for Distribution Systems with IDMT Coordination", in 2006 China International Conference on Electricity Distribution, pp. 1654-1659.

Standards:

[15]Guide on security and stability for power system, CSIC-DL 755-2001,

2001.

VI. B IOGRAPHIES

Bin Li obtained the B.Sc, M.Sc and Ph.D degrees from Tianjin University in 1999, 2002 and 2005 respectively. He was academic visitor of the University of Manchester, U.K. in 2006. And he worked in the design and application of protection relays and phasor measurement unit as a research fellow, in AREVA Company U.K. from 2008 to 2009. Now he is associated professor of the School of Electrical Engineering and its Automation, Tianjin University, Tianjin, China. His main research field is involved in the protection and control of distributed generation.Xuan Yu obtained her B.Sc degree from Tianjin University in 2008. Now she is the postgraduate in Tianjin University.

Zhiqian Bo received his BSc degree from the Northeastern University, China in 1982 and PhD degree from the Queen’s University of Belfast, UK in 1988 respectively. From 1989 to 1997, he worked at the Power System Group at the University of Bath. Presently, he is with AREVA T&D and responsible for new technology developments. His main research interests are power system protection and control.

高中语文说课稿子实用模板(共5篇)

篇一:高中语文说课模板通稿 各位评委老师:大家好,我是几号考生,我今天说课的题目是《》。下面,我将会从说教材、说教法、说学法、说教学过程等部分来进行我的说课。 一、说教材 教材简析:本篇课文是人教版高中语文课本必修几第几册第几单元第几课的课文,是一篇什么体裁的文章。文章主要叙述的容是什么,表现了作者什么样的思想感情。本篇课文具有什么样的地位,和什么特色。学习教材的目的是为了让学生能够触类旁通,举一反三,能将知识由课向课外延伸。通过对本篇课文学习,能够更好的培养学生的鉴赏能力和归纳总结能力。 教学目标: (一)诗歌:根据教学大纲的要求,诗歌教学要以诵读为主,在诵读中使学生领悟诗的思想感情,鉴赏文学作品能够感受形象,品味语言。同时,本篇诗歌通过典型意象创造出优美的意境,巧妙的将诗人的情感融入其中。确立教学目标如下: 我的知识目标是:品味诗的意象美,领悟诗的意境,体会诗人的真情。 能力目标是:培养学生鉴赏诗歌的能力。 德育目标是:体悟作者情怀,引发共鸣,逐渐养成良好的审美情趣,培养审美能力。 本节课的教学重点是:领反复诵读,鉴赏诗歌意象,体会诗歌的意境美,体悟诗情,获得情感体验。教学难点是:把握诗歌的思想感情,以及意象的体味与把握。 (二)文言文:根据教学大纲的要求,文言文教学要求培养学生阅读浅显文言文的能力,把握文章的思想容,积累语言知识。同时本课情节、结构、语言等的特点,确立教学目标如下: 知识与能力目标:了解作者的基本常识;理解文中所出现的生僻词以及意义特殊的词语;把握文中的主要思想感情,初步鉴赏文中的形象与个性。 过程与方法:通过诵读质疑、自主探究、合作解决,培养学生借助注释和工具书阅读浅显文言文,理解重点词句的含义以及初步的研究分析能力并积累文言文实词、虚词和句式,培养学生的自学能力和翻译能力。情感态度与价值观目标:理解作者在作品中所流露出的情感,培养正确的审美观/价值观/人生观。 我确定以上的三个目标是体现新课标所提倡的“知识与能力、过程与方法、情感与态度”并重的教学理念。教学重点:诵读课文,在把握文意的基础上理解词句,积累一些文言实词、虚词和句式。 教学难点:掌握文章的写作风格和特点;深入分析文章涵,并作出评价,激发学生的学习兴趣。 (三)现代文:新课标强调了要全面提升高中学生的语文素养,初步形成正确的人生观、世界观、价值观,并学会收集判断、处理信息,具有人文素养、创新精神与实践能力。同时本篇课文,感情真挚,感悟深刻,具有典型的人文性,结合本单元的教学目标以及本篇课文在语言,结构设置等方面的特点,确立本课的教学目标如下: 知识能力目标:领悟本文的写作手法,揣摩语言,体会语言的感情和特色,学习作者运用语言的技巧。同时学习本文对比喻、拟人等修辞手法的运用。 过程与方法目标:在教师恰当的提升引导下,培养学生“自主、合作、探究”的学习方式,并掌握一定的赏析语言的能力与方法。 情感与态度目标:理解作者在作品中所流露出的情感,培养正确的审美观/价值观/人生观。 我确定以上的三个目标是体现新课标所提倡的“知识与能力、过程与方法、情感与态度”并重的教学理念。我的教学重点是:理清本篇文章的思路,领会课文的思想感情。教学难点

【精品】校企合作方案

深化校企合作工作攻坚方案 (讨论稿) 为落实《国家中长期教育改革和发展规划纲要(2010—2020年)》文件中关于“大力推行职业教育实行工学结合、校企合作、顶岗实习的人才培养模式”的精神,依据教育部《中等职业教育改革创新行动计划(2010-2012年)》之教产合作与校企一体办学推进计划,围绕职业教育服务区域经济发展的要求和河南省产业发展的新形势,我校在现有校企合作基础上,将全方位、深层次地推进校企合作,并以此为契机,深化改革,充实内涵,着力提升学校招生就业、专业教学、行业培训等方面工作水平,实现学校与企业“合作多赢"的目标,特制订如下校企合作工作攻坚方案: 一、校企合作的指导思想 以科学发展观统领工作全局,围绕中原经济区建设,面向电子信息产业、先进制造业和现代服务业领域,按照“以服务为宗旨,以就业为导向,走产学结合发展道路”的办学要求,以专业及课程建设、建立实训基地、开展技能培训与鉴定、打造“双师型”队伍、加强订单培养、优化招生就业体系等为载体,畅通校企沟通渠道,搭建校企合作平台,努力实现学校各专业与产业、企业、岗位对接,专业课程内容与职业标准对接,教学过程与生产过程对接,学历证书与职业资格证书对接,为学校人才培养提供全方位有效服务,促进学校办学水平不断提升。

二、校企合作的基本思路 立足学校现有的校企合作项目,立足中原经济区建设需求,以我校强项专业为基础,面向本省、珠三角及港澳等地区拓展定单式培养的校企合作关系;以信息产业、行业和省内知名企业为依托,坚持资源共享、优势互补、共同培养、互利共赢的原则,瞄准新设备、新工艺、新技术、新材料,选择生产设备先进、核心技术处于同行业领先水平的企业作为合作对象,创建校内外实训实习基地;积极寻求企业在资金、设备和师资的投入,积极拓展企业在职职工的培训,变招工为招生,把学校办成大企(行)业的技能型人才培养基地;积极拓展学校办学模式创新,加大引企入校、引校入企的工作力度,逐步由人才输出到产品输出,建立起校企紧密型战略合作关系。 三、校企合作的主要内容 1、人才培养模式的合作:根据企业需求,校企双方共同拟定人才培养计划和方案,并制定切实可行的教学计划和理论、实践教学大纲,学校在遵循基本教育规律的前提下,按企业的要求订单式培养人才,企业为人才培养“埋单”。 其表现形式包括:“订单式”人才培养模式、“2+1”人才培养模式、“学工交替”人才培养模式以及以产品项目为基础的全方位合作教育模式等.学校“汉恩班"、“中兴班”便是成功的例子,其特点在于

2课下作业三十二

课下作业(三十二) 、选择题 1.哲学基本问题又称哲学的根本问题、哲学的最高问题。这一问题包括( ) ①物质和意识的辩证关系问题 ②思维和存在何者是本原的问题 ③思维和存在有没有同一性的问题 ④唯物主义和唯心主义关系问题 A .①② B .②③ C .③④ D .①③ 解析:选 B 。哲学基本问题包括两个方面的内容:一是思维和存在何者是本原的问题;二是思维和存在有没有同一性的问题,②③入选。 2. 唯物主义是哲学上两个敌对的基本派别之一,是同唯心主义相对立的思想体系。划分唯物 主义和唯心主义的唯一标准是( ) A .物质和意识的关系问题 B .客观与主观的关系问题 C .思维和存在何者是本原的问题 D ?思维和存在有没有同一性的问题 解析:选C。对思维和存在何者是本原问题的不同回答,是划分唯物主义和唯心主义的唯一 标准, C 入选。 3. “二月春分八月秋分昼夜不长不短;三年一闰五年再闰阴阳无差无错。”这副对联从一个侧面反映了( ) ①思维和存在具有同一性 ②认识与自然的吻合具有必然性 ③认识以实证和猜测为基础 ④意识活动具有主动创造性 A .①③ B .②④ C .①④ D .②③ 解析:选C o材料反映人们可以认识和把握自然界的运动规律,说明思维和存在具有同一性 反映了意识活动具有主动创造性,①④符合题意;认识与自然的吻合不具有必然性,②错误;实践是认识的基础,③错误。 4 .(2019河南中原名校联考)“为天地立心,为生民立命,为往圣继绝学,为万世开太平”是北宋张载的名言。由于其言简意宏,一直被人们传颂不衰。下列观点符合“为天地立心”的

是( ) ①形存则神存,形谢则神灭②吾心即是宇宙,宇宙即是吾心 ③思维着的精神是地球上最 美的花朵④“天不生仲尼,万古长如夜” A .①② B .①③ C .③④ D .②④ 解析:选C。“为天地立心”的意思是为天地确立一种核心价值理念,强调精神的作用,③ ④强调思维着的精神的作用,符合题意;①强调物质决定意识,②片面夸大意识的作用,均不合题意。 5.有位生物学学者认为,唯有生物学才能带领人类探究物种本源、生从何来死往何方等问题,他确信构成生物的眼见为实的物质比辩证唯物主义判断猜想的物质还正确。这种认识( ) ①没弄清辩证唯物主义的物质概念与构成生物的物质之间的关系 ②坚持了唯物主义根本方向,但属于古代朴素唯物主义的思想 ③犯了近代形而上学唯物主义错误,具有机械性、形而上学性 ④是在自然科学基础上对辩证唯物主义和历史唯物主义的发展 A .①② B .①③ C .②③ D .③④ 解析:选B。材料中的生物学学者没有看到哲学对具体科学的意义,认为哲学中的物质是猜 想的,没有看到哲学中的物质与自然科学中的物质是共性与个性的关系,因而具有机械性、 形而上学性,①③正确,②④错误。 6.18世纪法国哲学家丹尼斯狄德罗认为:“自然界由数目无穷、性质不同的异质元素构成。” 这种观点( ) ①承认世界的物质性,但把物质归结为自然科学意义上的元素②建立在自然科学成就的基 础上,丰富和发展了唯物主义③坚持物质第一性,但对物质的认识没有科学依据④认为世界是物质的,正确揭示了物质世界的基本规律 A .①② B .③④ C .①③ D .②④ 解析:选A。“狄德罗认为:‘自然界由数目无穷、性质不同的异质元素构成。'” 这种观点承认世界的物质性,但把物质归结为自然科学意义上的元素,①正确;狄德罗生活在18世纪,其观点建立在自然科学成就的基础上,丰富和发展了唯物主义,属于近代形而上学唯物主义,②入选;③④ 说法错误。 7 ?“宇宙创造过程中,上帝没有位置……没有必要借助上帝来为宇宙按下启动键”。这是斯

课后巩固作业(十九) 3.2.1

温馨提示: 此套题为Word版,请按住Ctrl,滑动鼠标滚轴,调节合适的观看比例,答案解析附后。 课后巩固作业(十九) (30分钟50分) 一、选择题(每题4分,共16分) 1.下列试验中,是古典概型的是( ) (A)发射一颗卫星能否成功 (B)从高一(18)班60名同学中任选一人测量其身高 (C)抛掷一枚骰子,出现1点或2点 (D)射击选手射击一次,恰中靶心 2.(2011·温州高一检测)抛掷两个骰子,则两个骰子点数之和大于4的概率为 ( ) (A)13 18 (B)8 9 (C)7 12 (D)5 6 3.从{1,2,3,4,5}中随机选取一个数为a,从{1,2,3}中随机选取一个数为b,则 b>a的概率是( ) (A)4 5 (B)3 5 (C) 2 5 (D)1 5 4.用1,2,3,4这四个数字,组成比2 000大且无重复数字的四位数的概率是 ( ) (A)1 4 (B)1 2 (C)3 4 (D)1 3 二、填空题(每题4分,共8分) 5.(2011·江苏高考)从1,2,3,4这四个数中一次随机取两个数,则其中一个

数是另一个的两倍的概率是_____. 6.(2011·永定高二检测)扔两枚骰子出现的点数为m,n,以(m,n)为坐标的点出现在x2+y2=16内的概率为_____. 三、解答题(每题8分,共16分) 7.一个袋中装有四个形状大小完全相同的球,球的编号分别为1,2,3,4. (1)从袋中随机抽取两个球,求取出的球的编号之和不大于4的概率; (2)先从袋中随机取一个球,该球的编号为m,将球放回袋中,然后再从袋中随机取一个球,该球的编号为n,求n

公司治理和提名委员会职权范围

公司名称认证认证之认可证书编号(CC)状态暂停/撤销日期上海英达宝塑料有限公司ISO 9001:2008UKAS3234撤销14/9/2018 东莞丽适内衣有限公司SA8000:2014SAAS5845撤销8/9/2018 东莞市源康毛绒玩具有限公司SA8000:2014SAAS6229撤销26/4/2018 东莞雅隽纸品有限公司SA8000:2014SAAS6349暂停29/11/2018 中交一航局第五工程有限公司ISO 9001:2008HKCAS,UKAS6035撤销24/5/2018 中交一航局第五工程有限公司QSPSC:2014UKAS6035撤销24/5/2018 中国电信股份有限公司TL-V 6.0/5.0CNAS2861撤销28/3/2019 中国移动通信集团四川有限公司ISO 9001:20085969撤销29/4/2018 中国移动通信集团广东有限公司TL-V 5.5/5.0CNAS3117撤销1/1/2018 中国移动通信集团福建有限公司厦门分公司ISO 14001:2004CNAS3810撤销24/2/2018 中山市海荣金属制品有限公司ISO 9001:2008UKAS3312撤销20/6/2018 伟信(天津)工程咨询有限公司ISO 9001:2008CNAS5110撤销14/9/2018 佛山市高明南越钢结构制造有限公司ISO 9001:2008HKCAS6238撤销7/1/2018 佳达电子塑胶(深圳)有限公司ISO 9001:2008CNAS,HKCAS,UKAS3474撤销14/9/2018 南京智达康无线通信科技股份有限公司TL-HS 5.5/5.0CNAS5203撤销14/9/2018 厦门华润燃气有限公司OHSAS18001:20076059撤销15/2/2019 嘉实多(深圳)有限公司ISO 9001:2008CNAS,UKAS1506撤销29/6/2018 嘉实多(深圳)有限公司ISO 14001:2004CNAS,UKAS2168撤销29/6/2018 嘉实多(深圳)有限公司ISO 9001:20085982撤销29/6/2018 天津美罗钢格板有限公司ISO 9001:2015CNAS,HKCAS,UKAS5577撤销9/7/2018 奥仕达电器(深圳)有限公司ISO 14001:2004CNAS,HKCAS5518撤销14/9/2018 广东中奥物业管理有限公司ISO 9001:20085972撤销27/5/2018 广东中奥物业管理有限公司ISO 14001:20045973撤销27/5/2018 广东中奥物业管理有限公司OHSAS18001:20075974撤销27/5/2018 广东恒泰钢结构有限公司ISO 9001:2008HKCAS,UKAS6135撤销18/3/2018 广州同略信息科技有限公司SA8000:2014SAAS6092撤销17/8/2018 广州哲品家居用品有限公司SA8000:2014SAAS6547撤销22/2/2019 广州方盈珠宝首饰有限公司第一分厂SA8000:2014SAAS6329撤销10/3/2018 广州美罗钢格板有限公司ISO 9001:2008CNAS,HKCAS,UKAS1583撤销27/8/2018 广州莱佛士物业服务有限公司ISO 9001:2008CNAS,HKCAS,UKAS3845撤销29/3/2018 广州誉川兴业鞋业有限公司SA8000:2014SAAS6109撤销20/4/2018 张家港保税区舒尔玆金属贸易有限公司ISO 9001:2008UKAS5471撤销4/1/2018 惠州宏丰手袋实业有限公司SA8000:2014SAAS5278撤销4/3/2019 无锡德思普科技有限公司SA8000:2014SAAS6108撤销31/3/2019 正东钢铁结构(深圳)有限公司ISO 9001:2015CNAS,HKCAS,UKAS2531撤销28/8/2018 比优特(苏州)塑胶科技有限公司SA8000:2014SAAS6093撤销28/2/2019

人教版高中语文说课稿合集(必修一至必修五)139页)

目录 1、《荷塘月色》说课稿 (3) 2、《故都的秋》说课稿1 (6) 2、《故都的秋》说课稿2 (8) 3、《囚绿记》说课稿 (11) 4、诗经两首《氓》说课稿 (12) 5、《离骚》说课稿 (15) 6、孔雀东南飞说课稿 (17) 7《涉江采芙蓉》说课稿一. (18) 7、短歌行说课稿 (19) 8、归园田居其一说课稿 (20) 9、兰亭集序》说课 (23) 10、赤壁赋说课稿 (24) 11、《游褒禅山记》说课稿(2则) (26) 12、就任北京大学校长之演说 (30) 13、我有一个梦想说课稿 (35) 14、《在马克思墓前的讲话》说课稿 (38) 15、林黛玉进贾府说课稿 (39) 16、《祝福》说课稿 (43) 17、《老人与海》说课稿 (45) 18蜀道难说课稿 (46) 19、《秋兴八首》(其一)教案 (48) 20、杜甫诗三首》说课稿 (49) 21、琵琶行说课稿 (51) 22、李商隐诗2首 (53) 23、《寡人之于国也》说课稿 (55) 24、《劝学》说课稿 (58) 24《劝学》创新课说课稿 (59) 25、过秦论说课稿 (61) 26、师说》说课稿 (63) 27、动物游戏之谜 (65) 27-1动物游戏之谜 (67) 28、《宇宙的边疆》 (69) 13-1、宇宙的边疆 (70) 29、一名物理学家的教育历程》说课稿 (71) 30、《窦娥冤》说课稿 (75) 30-1、《窦娥冤》说课稿 (76) 30-2《窦娥冤》说课稿 (77) 31、《雷雨》说课稿 (79) 32、《哈姆雷特》说课稿 (81) 33、《望海潮》说课稿 (82) 34、《雨霖铃》说课稿 (83) 35、《苏轼词两首》说课稿 (84) 36、《念奴娇赤壁怀古》说课稿 (86) 37、《水龙吟》教案 (89)

人教版二年级下册语文每课作业完整版

人教版二年级下册语文 每课作业 HEN system office room 【HEN16H-HENS2AHENS8Q8-HENH1688】

1、找春天 一、看拼音写词语。 tuō xiàjiědònɡxī shuǐmián yī tàn tóu yáo tóu?yě huā duǒcánɡ 二、按课文内容填空。 1、春天来了!我们几个孩子,_______棉袄,________家门,________田野,去_______春天。春天像个___________,遮遮掩掩,躲躲藏藏。我们________地找啊,找啊。 2、春天来了!我们______到了她,我们______到了她,我们______到了她,我们______到了她。她在柳枝上_________,在风筝尾巴上_________;她在喜鹊、杜鹃__________,在桃花、杏花__________…… 三、填空。 藏藏丁丁遮遮 慌慌清清摇摇 四、照样子写词语。 遮掩遮遮掩掩认真 开心() ()() 五、在正确读音下面画横线。 1、我家院子里有几(jǐ jī)只小鸡,这些小鸡真可爱! 2、我家的客厅里的茶几(jǐ jī)上有两杯水。 ★照样子,写句子。 小草从地下探出头来,那是春天的眉毛吧? ,是 2、古诗两首 一、看拼音写词语。 Wèi lái zhuī gǎn shūdiàn kūhuáng

guāng róng yěcài zhù sù gāo shāo 二、抄写古诗《草》 题目: 作者:三、比一比,组词语。 未()烧()枯()徐() 末()浇()姑()除() ★这两首诗都是描写季景色的。 ★《草》是朝大诗人写的,诗中“, 。”句最为有名,它描写了草顽强的生命力。诗中还有一对反义词,分别是________和________。★《宿新市徐公店》描写了种景物,分别是 。诗中最有意思的一句 是、 。 3、笋芽儿 一、拼一拼,写一写。 shì jiè sǔn yá hūhuàn shān gāng hōng dòng 二、读一读,并照样子,写一写。 啊,多么明亮、多么美丽的世界呀! 三、按课文内容填空。 1、笋芽儿被叫醒了。她()眼睛,()懒腰,()四周一片漆黑,撒娇地说:“是谁在叫我呀” 2、春雨姑娘()着她,()着她。太阳公公()着她,()着她。笋芽儿脱下一件件衣服,长成了一株()的竹子。她站在山冈上,()地喊着:“我长大啦!”四、比一比,再组词。 岗()界()笋()牙()喊 ()呼() 刚()介()笛()芽()减 ()乎()

统编版三年级语文下册20.肥皂泡课后练习题作业(有答案)

部编版三年级语文下册同步练习 20. 肥皂泡 一、看拼音写词语。 féi zào cháng láng mù wǎn tòu míng jiāo ruǎn yǎng tóu yí chuàn fēi yuè yīng ér xī wàng 二、给下列加点字选择正确的读音,打“√”。 1、几个同学散.(sǎn sàn)漫得在操场上散.(sǎn sàn)步。 2、若用扇.(shān shàn)子在下面轻轻地扇.(shān shàn)送,有时它能飞得很高很高。 三、比一比,再组词。 皂()透()婴()娇()希() 泉()诱()耍()骄()杀() 四、照样子,完成练习。 例:无声地散裂无声地()无声地() 例:轻轻地扇轻轻地()轻轻地() 例:颤巍巍(ABB式)()()()() 五、我会查字典,给加点字选择正确的解释。 “仰”字按部首查字法应先查()部,再查()画。按音序查字法应先查大写字母(),再查音节()。“仰”字在字典里的解释有:①脸向上,与“俯”相对;②敬慕;③依赖;给下列加点字选择正确的解释,填序号。 仰.起头()久仰.大名()仰.仗() 六、择合适的词语填空。(填序号) ①颤巍巍②软悠悠③轻飘飘④慢腾腾 1.不知为什么,我这几天头晕眼花,走起路来感觉________的。 2.轻轻地一提,那轻圆的球儿便从管上落了下来,_______地在空中飘游。 3.他做事总是像老牛拉破车,_______的。

4.有时吹得太大了,扇得太急了,这脆薄的球,会扯成长圆的形式,______的,光影零乱。 七、按要求完成句子练习。 1. 把句子写具体。 ①薄球就散裂了。___________________________________________________________ ②浮光在球面上乱转。______________________________________________________ 2.我把用剩的碎肥皂放在一只小木碗里。(改为“被”字句) ____________________________________________________________________________ 3.小时候,我喜欢玩吹泡泡、滚铁环、西瓜等游戏。(修改病句) ___________________________________________________________________________ 七、阅读课文片段,完成练习 方法是把用剩的碎肥皂放在一只小木碗里,加上点水,(),使它融化,然后 ..用一 支竹笔的套管,蘸上那黏稠的肥皂水,()地吹起,吹起一个()的网球大小 的泡儿,再.()地一提,那轻圆的球儿,便从管上落了下来,()地在空中飘游。若用扇子在下面()地扇送,有时它能飞得很高很高。 1.根据课文内容填空。 2.这是写()肥皂泡和()肥皂泡的过程。 3.用“”画出做肥皂水方法的句子。 4.用“先……然后……再……”说一说吹肥皂泡的过程。 . 八、快乐阅读。 种一片树叶 冰心 埋下一片树叶,固执地相信它终会长成一棵参天大树。这便是儿时最美的梦。 我4岁那年的秋天,枯黄的叶子从高高的树枝上飘落,正在院中玩耍的我俯身拾起一片, 觉得很美。玩赏了半天,我忽发一个奇怪的想法:这个曾经是树伯伯身上一部分的叶,把它 种进土里之后,必定可以长出一棵同样的大树! 于是我捡了许多片叶子,虔诚地跪在地上挖了个小坑,把树叶全埋到了土里。就像妈妈 生下了我,我也会渐渐长大—样,我坚定地相信我的梦马上可以实现。 我天天蹲在种树叶的地方等待我的大树,直到大雪纷飞。我想叶子大概怕冷,所以不敢 出来,等明年开春,一定会长得更好!我依旧固执地坚守着自己的梦,直到燕子衔泥,杨树吐

华为企业人力资源研究

标杆企业人力资源研究提纲 (供参考,根据你能够收集到信息整理) 1.企业概况 1.1企业概况华为技术有限公司,简称华为,是中国一家生产销售通信设备的民营公 司,总部位于广东省深圳市。华为于1987年注册成立,产品主要涉及通信网络中的交换网络、传输网络、无线及有线固定接入网络和数据通信网络及无线终端产品,为世界各地通信运营商及专业网络拥有者提供硬件设备、软件、服务和解决方案。 华为技术有限公司是一家总部位于中国广东深圳市的生产销售电信设备的员工持股的民营科技公司,总裁任正非,董事长孙亚芳。它1988年成立的时候,是个只有两万元注册资本、20个员工,唯一的资源是人的头脑的默默无名的小公司。20世纪末,旋风一样席卷了国内市场,研发投入与回报间的漫长周期带来了巨大的风险,但他每次都能披荆斩棘,昂首阔步的走下去。可是行业的冬天给这位领军者造成了巨大的伤害,但他没有倒下去,押上命运的决心,把上亿资金、上千人员投入了新的项目。2002年,它拥有员工22000多人,2003年销售额达到317亿元。到今天,它是行业内的领军者,在国内市场占领了巨大的份额,并已经展开国际发展的征程。这个时候,世界第一的思科已紧张地盯着它的主要竞争对手。 1.2发展历程、阶段 1988年成立于深圳的华为公司是一家通讯设备供应商。其营业范围包括交换、传输、无线和数据通信类电信产品。在通讯设备领域为世界各地的客户提供网络设备、服务和解决方案。 1988-1997年,“农村包围城市”零起步的华为无论是资金还是竞争实力都无法与对手在大、中城市参与竞争。但华为公司的创始人看到:县城以及农村更广阔的市场是国外厂商尚未涉足的领域,这为华为带来了机会。华为认为:以农村为突破口有两个非常明显的好处:首先,小县城和农村发展通讯设备行业门槛低,承受风险小。其次,农村对于产品的技术和质量要求不高,也不是很关注品牌,而是更加注重实用。 1989 自主开发PBX。1992年,华为开始研发并推出农村数字交换解决方案。农村包围城市的战役正式打响。很快,华为培养起一支精良的营销队伍,成长起来一个研发团队。在1995年,公司销售额达15亿人民币。随着自有资金实力不断增强,华为发动城市战的资本逐渐积累完成。至此华为正式将市场目标转移到中国主要城市。1994 推出C&C08 数字程控交换机。 1995 成立知识产权部。成立北京研发中心。 1996 推出综合业务接入网和光网络SDH设备。与香港和记黄埔签订合同,为其提供固定网络解决方案。成立上海研发中心。

人教版职高语文基础模块上册教案

《永远的校园》 教学目的: 1.了解北大,走近北大,感受北大,思考北大 2. 借助演讲、辩论等形式培养学生思辨说理的能力 3.对比谢冕心中的北大与现实中北大的差异,并揣摩这种差异的根源,从而树立正确的大学观、人生观 教学难点: 如何看待理想中北大与现实中北大的差异 教法与学法: 1.课型:讲读课、公开课、研讨课、活动课 2.教法:质疑、讨论、辩论 3.教具及能力培养方向:多媒体课件(包括图片、音频、视频及文字材料);培养学生思辨能力 课时安排:2课时(第一课时主要诵读文章,感知大意;第二课时主要展开拓展、延伸的活动) 教学过程: 一、新课导入 2003年2月25日,在首都北京发生了二起震惊中外的爆炸案,先后发生在清华大学的荷园餐厅和北京大学的农园餐厅,虽然比不上恐怖份子驾机撞毁世贸大楼那样引人注目,但在很少发生恐怖流血冲突的中国大陆来说,这的确也算得上是惊天动地的事情了,最引人深

思的是:恐怖份子为什么要选择清华和北大进行作案呢?案情侦破之后,答案浮出水面,而这个答案竟让人哭笑不得,因为犯罪谷子声称:“制造爆炸案的目的是为了出名。” 对于这起事件,我不想多作分析了,我只是想说:为什么炸清华、北大就能出名呢?那是因为这两所大学太有名了,本身就是名望的象征。我们这就容易理解了:为什么从古至今那些杀人的罪犯很少留下姓名,而刺客荆轲的故事却被广为传诵,不仅仅是因为荆轲的大义凛然、高风亮节,还因为他刺杀的对象是权倾天下、赫赫有名的秦王。 的确,清华、北大太有名气了,不仅是每一位莘莘学子梦寐以求的地方,就连没有丁点儿文化常识的人可能也会对他们肃然起敬。江泽民同志作为一国主席,日理万机,我不知道他曾去过哪些大学,但我知道北大他是去过的,就在北大建校一百周年的校庆典礼上,还作了热情扬溢的讲话,因此,才有了我们课本上这篇文章。 大凡有名望的人、事、物都难得一见:比如卢浮宫珍藏的那些传世珍品;比如我们的局长、县长、市长或者更高的官员。于是我们容易对那些有名望的东西产生神秘感,认为他们与众不同,认为他们超凡脱俗,认为他们高不可攀,或许真的如此,或许未必竟然。那么,今天,我们就一起走进北大著名学者、中国当代著名诗歌理论家、朦胧诗派的倡导者谢冕先生用他的眼、他的手、他的心为我们搭建的北大校园,去感受北大的那一份脱俗和平凡吧! 二、感受北大

必修2 Unit 1 课下作业(一~三)

必修2 Unit 1 课下作业(一~三) 课下作业(一)考点过关针对练 Ⅰ.单词拼写 1.Jim insisted that the book Mr.Black referred to was worth (值得的) reading. 2.She took one look at the horse and her heart sank (下沉). 3.It was not until he removed (摘掉) his sunglasses that I recognized him. 4.I'll be waiting for you at the entrance (入口) to Guangzhou station. 5.The coal industry is now barely half its former (以前的) size. 6.The door opened and in came a troop of children in all sorts of fancy (奇特的) dresses. 7.Some animals are hunted illegally, so they become rare (珍贵的;稀有的). 8.To make my room look nicer, I had the walls decorated (装饰) with paper cuts last year. Ⅱ.语境语法填空 1.?Having_removed (remove) from his hometown to the city, Zhang Qiang didn't know what ?to_do (do) at first.Under the guidance of his friend Li Ping, he made ?a fortune by doing business.He launched a campaign which ?was_designed (design) to help those in need in return ?for the society.He has done so much for the poor in his community that we can't think ?highly (high) of him enough. 2.As is known to all, cultural relics belong ?to human beings rather than individuals, so they are well worth ?protecting (protect).However, some people are in search ?of them and take possession of them illegally.Some of them have been damaged while only a few survive.Therefore, every one of us should make all efforts to protect them from ?being_destroyed (destroy).There is no doubt ?that it is our duty to protect cultural relics. 3.The old piano I bought years ago took up too much room, so ?by the light of the room, I ?took (take) it apart.I sold it to a waste recycling center at a low price. Ⅲ.语境改错 1.文中共有3处错误,每句中最多有两处,请找出并改正。 After removed dirt from the vase, the expert was amazed to find that it survived the Tang Dynasty.The vase was so amazingly designed that it was very worth buying at such a reasonable price. 答案:第一句:removed→removing; survived后加from 第二句:very→well 2.文中共有3处错误,每句中最多有两处,请找出并改正。

H3C

华为 华为技术有限公司 Huawei Technologies Co., Ltd. 公司 类型 民营企业 成立1987年 代表人物总裁:任正非董事长:孙亚芳 总部中国深圳市龙岗区坂田华为基地 邮政 编码 518129 电话 号码 +86 755 2878-0808 标语口号丰富人们的沟通与生活(Enrich life through communication) 业务 地区 全球 产业无线电,微电子,通讯 产品接入设备,骨干路由器,无线基站和交换设备,语音视频设备 服务企业网,国家级骨干网,光纤网络设计,建设 年营 业额 ▲284亿美元(2010年)

税后 盈余 ▲36.8亿美元(2010年) 员工 人数 110,000(2010年12月) 主要部门移动、宽带、IP、光网络、电信增值业务和终端 网址https://www.wendangku.net/doc/1f10359238.html,

华为研发大楼(深圳)

大学里的H3C无线网络硬件

华为朗新科技有限责任公司(下面简称:合资公司),总部所在地北京,由朗新董事长徐长军任合资公司的董事长。合资公司立足原朗新在中国电信、中国联通市场的现有产品和应用经验,结合华为的销售与服务网络及资金优势,加大投入,进一步为中国电信和中国联通客户提供更优质的解决方案和服务,构建有竞争力的全业务融合运营支撑系统。 [编辑]员工待遇 华为员工等级分23级,一般技术工从13级开始,13级以下一般是秘书等岗位。待遇包括基本工资+奖金,部分优秀员有配股,可分红。对新人建立了导师制度,使新员工能尽快适应公司。对老员工还有在职培训。龙岗基地有可容纳3000人的百草园员工公寓群。基地内部外部都有接送巴士。 [编辑]争议 2003年时,思科控告华为窃取其路由器程式码,华为同意从市场上撤回路由器并修改程式码后,思科随后便取消控告。 2004年芝加哥贸易展上,一位华为员工因拍摄竞争对手的产品而被捕。 2007年秋,华为鼓励7000多名工作满8年的老员工辞职后再竞聘上岗,外界普遍认为是为了规避即将于2008年施行的《劳动合同法》,而华为内部人士表示这是为了企业的活力。[2] 2008年,摩托罗拉控告五位离职员工,指称他们携带商业机密,投效与华为订有经销协议的Lemko Corp.。2010年,摩托罗拉提出修正控告,向美国联邦芝加哥地方法院控告华为自2001年开始透过摩托罗拉内部员工窃取商业机密。但华为董事长任正非声明这项指控毫无根据。 2011年3月4日,华盛顿以国家安全为由阻止华为收购3Leaf公司,理由如下[3]: 1.华为总裁任正非参加中国共产党超过3分之1个世纪。 2.任正非为长期活跃的中国共产党重量级成员。 3.任正非以上校军衔离开解放军立即创建华为,资金来源不明。 4.华为创业早期合约全部为解放军控制的中资驻港企业,政府背景明显。 5.中国军方长期无偿向华为提供关键技术,华为与解放军签署多项现存长期合作项目,军方背景明显。 6.华为长期策划及从事与盗取知识产权相关的商业犯罪,商业道德败坏。 7.华为有向包括萨达姆侯赛因、伊朗、塔利班提供服务的长期历史。 8.华为在收购3Leaf以前曾经策划及参与盗取3Leaf知识产权的商业犯罪。 9.中国多家国家银行在华为成立后的24年当中向华为提供“无限制的融资”,政府背景明显。

高中语文《鸿门宴》说课稿模板

高中语文新课程标准教材 语文教案( 2019 — 2020学年度第二学期 ) 学校: 年级: 任课教师: 说课稿 / 高中说课稿 / 高中说课稿范文 编订:XX文讯教育机构

高中语文《鸿门宴》说课稿模板 教材简介:本教材主要用途为通过学习语文的内容,培养学生的阅读能力、交流能力,学习语文是为了更好的学习和工作,为了满足人类发展和实现自我价值的需要,本说课稿资料适用于高中语文科目, 学习后学生能得到全面的发展和提高。本内容是按照教材的内容进行的编写,可以放心修改调整或直接进行教学使用。 各位评委,各位同仁: 大家好!今天我说课的题目是《鸿门宴》。下面我将从:教材、教法、学法、课时安排、教学过程五个方面来进行我的说课。 一、说教材 1、教材简析及该课所处的地位作用: 《鸿门宴》是人教版新教材高一年级《语文》必修1第二单元 第6课,节选自《史记》。所选情节描写的是刘邦、项羽在推翻秦王朝后,为争夺天下而进行的一场惊心动魄的政治斗争。鸿门宴是项羽在新丰鸿门设下的一个富有杀机的宴会,是刘、项之间政治矛盾由潜滋暗长到公开化的表现,是长达五年的楚汉相争的序幕,名为宴会,实则是一场激烈的政治斗争。作者以娴熟的艺术技巧,生动地刻画了不同性格的人物形象,描绘了众多富有戏剧性的令人难忘的场面,情节波澜起伏,扣人心弦。鸿门宴一文充分展示了刘、项之间不可调和的矛盾,并预示了胜负的必然结局。因此具有很高的史学价值和

文学价值。如何通过本课激起学生学习的兴趣,树立学生学好文言文的信心和领悟我国传统文化的精髓,这是一个关键所在。 2、教学目标: 高中语文教学大纲对文言文学习的要求是:诵读古典诗词和浅易文言文,背诵一定数量的名篇。掌握文中常见的文言实词、虚词和句式,能理解词句含义,读懂课文,学习用现代观念审视作品的内容和思想倾向。 根据课文特点,结合大纲要求,我确立了如下教学目标:(课件展示) 板书一二三 (1)知识和能力目标:一个巨匠,一部巨著:了解作家作品及相关史实,积累文言词句知识,学习创造性阅读。 (2)过程和方法目标:两个英雄,两种性格:利用人物个性化语言,分析人物性格,学习作者运用对照的方法和在矛盾斗争中描写人物的方法,学习一分为二地评论历史人物,树立正确的读史观。 (3)情感和价值目标:三种认知态度: ①学以致用的态度,感受司马迁隐忍发愤的著书精神,从容应对学习生活中的各种困难和挫折 ②领悟态度:分析项羽悲剧的原因,到底“败”在哪里?领悟良好的性格决定一生的命运

matlab课下作业

MATLAB 作业 1.构造矩阵A =[?718?3],B =[4257],C =[59 62 ] (1)试将A ·*B 与A*B 的结果相加,并找出相加后新矩阵中绝对值大于10的元素。 (2)组合成一个4×3的矩阵,第一列为按列顺序排列的A 矩阵元素,第二列为按列顺序排列的B 矩阵元素,第三列为按列顺序排列的C 矩阵元素。 解答: (1) 在matlab 上的程序如下: >> A=[-7,1;8,-3]; >> B=[4,2;5,7]; >> C=[5,9;6,2]; >> A.*B ans = -28 2 40 -21 >> A*B ans = -23 -7 17 -5 >> D=A.*B+A*B D = -51 -5 57 -26 >> D(find(D<-10|D>10)) ans = -51 57 -26 (2) 在matlab 上的程序如下: >> A=[-7,1;8,-3]; >> B=[4,2;5,7]; >> C=[5,9;6,2]; >> D=[A(:),B(:),C(:)] D = -7 4 5 8 5 6 1 2 9 -3 7 2 2、求解以下方程组的解(一组解即可)。

{4x +6y +3z =132x +3y +4z =9 解答: 在matlab 上的程序如下: >> A=[4,2;6,3;3,4]; >> A=A'; >> B=[13;9]; >> x=A\B x = 0 1.6667 1.0000 3、使用spdinag(B,d,m,n)命令创建4阶稀疏矩阵A,求其秩,并将A 转换为全矩阵C (其中矩阵B=[1;2;3;4],d=1)。 解答: 在matlab 上的程序如下: >> B=[1;2;3;4]; >> A=spdiags(B,1,4,4) A = (1,2) 2 (2,3) 3 (3,4) 4 >> sprank(A) ans = 3 >> full(A) ans = 0 2 0 0 0 0 3 0 0 0 0 4 0 0 0 0 4、求函数f (t )=1?12.5e ?t sin(2t +3.4)在t>0区间内的所有零点。 解答: 在matlab 上的程序如下: >> f=@(t)(1-12.5*exp(-t)*sin(2*t+3.4)); >> fplot(f,[0,10]); >> a=fzero(f,1) a = 1.6583 >> b=fzero(f,2) b = 1.6583 >> c=fzero(f,3) c =

(完整word版)二年级下册语文作业设计1-20课

1、让我们荡起双桨 一、基础擂台赛 1、照样子做一做 京(凉)(凉风) (惊)(惊吓) ()()()()()()良西果 ()()()()()()2、选字填空 做作 工()()工()事()业 课棵 ()桌一()()本几()树 3、句式仿写 例:水中鱼儿望着我们,悄悄地听我们愉快歌唱。 4、在括号里填上合适的词。 美丽的()幸福的()()地飘荡 凉爽的()亲爱的()()地听 二、作业超市 选择你喜欢的题目做一做! 1、课文回放 “红领巾迎着太阳”一句中的“红领巾”指____________________________。 2、记录生活试着写几句描写我们课外生活的话,用上“欢乐、伙伴、愉快、尽情”等课文中的词语,相信你一定会写得很精彩。

2、友谊桥 一、基础擂台赛 1、填空 傲慢的近义词是()它的反义词是() 他傲慢地说:“()。” 2、短文共有()个自然段。从第一自然段至第六自然段描写蜡笔娃娃的________,第7、8自然段描写蜡笔娃娃共同。 3、短文说蜡笔娃娃画的彩虹是他们架起的友谊桥,为什么?选择正确的答案打“√”。 (1)彩虹像一座弯弯的小桥,太美丽。() (2)彩虹是蜡笔娃娃团结协作,共同画的,彩虹的样子也像桥,表现了他们之间的友谊。() 二、读下面一段话,完成练习。 看,蓝蓝的天上挂着红太阳,阳光下的青山格外美丽;小溪像白色的飘带,溪边花红柳绿;山下是一望无际的麦田,麦田里翻滚着金色的麦浪…… 1、找出这段话中描写颜色的词语,用“△”做上记号。 2、背诵这段话,看谁背得又快又准确。 3、“一望无际”是说麦田,跟“格外”意思相近的词语有、。 4、你见过小溪吗?学着课文中的方法写一写,它还像什么? 5、(选做题)认真读上面一段文字,边读边想,把想到的画面画下来。

相关文档