变压器日常维护参考说明

变压器安全和顺利的运行主要依靠定期和仔细的监测和维护工作。维护工作通常由操作人员执行。监测和维护必须在变压器断电和接地时进行。

Safety operation of transformer depends on regular monitor and maintenance. Maintenance work is usually performed by the operator. Monitoring and maintenance must be carried out in the transformer outages and grounded.

1、变压器油箱和储油柜

Tank and conservator

1.1检查油温Check oil temperature

对油温进行读数,然后记下来。判断油或绕组温度是否因变压器长期过负荷或不充分的冷却受到影响,并采取纠正措施。

Record readings of oil temperature. Decide if oil or winding temperature is affect or not due to long time overload or insufficient cooling and take corrective actions.

1.2检查吸湿器Check breather

为了确保储油柜不受潮,当上面一层蓝色材料厚度减少至大约7cm时,必须更换干燥剂(硅胶颗粒)。

In order to ensure that the conservator is not exposed to moisture, dryer (silicon particles) should be changed when the thickness of above blue material is reduced to 7cm.

1.3检查油位Check oil level

通过观察透明玻璃管或油位指示计检查储油柜或其它容器的油位。油位必须符合指示计上指示的温度。如果油位太低,必须排除导致油损耗的故障,注入新的合格油,需使用的油牌号见油的检验证明和铭牌。

Check oil level of conservator or other container by transparent glass or oil level indicator. Oil level should be according to the temperature indicated. If oil level is too low, failures should be found and fill new oil. The Type of oil needed see Oil Inspection Record and nameplate.

1.4检查法兰连接和焊接是否漏油Check flange connection and welding for oil leakage

所有的法兰、密封和焊接都须检查是否漏油。如果发现泄漏,必须及时再次拧紧螺钉,替换密封件或焊接进行弥补。焊接只能由有经验的焊工进行。必须遵守所有有关的事故预防规章,特别是油浸变的防火措施。

All flanges, seals and weldings should be checked for oil leakage. If find leak, must tighten bolts again, change sealing gaskets or weld. Weld should be done by experienced weldor. Must comply with all relevant accident prevention regulations, especially fire preventions of oil immersed transformer. 1.5检查油漆,清洁表面Check painting, clean surface

如果及时修整(损坏的)面漆,那么不必进行整体的重新涂漆。操作指导:使用浸有溶剂的布或蒸汽喷射鼓风机清洁涂漆表面。必须完全清除泥浆、油和油脂。轻轻磨旧漆,去掉将要脱落的部分。用金属丝刷子刷生锈的部分,直至发亮。

然后去了锈的部分涂两层底漆,最后在底漆上涂上面漆。如果旧漆是极易损坏的且已不牢固粘敷在金属表面,必须通过人工打磨或借助于去漆器完全去掉这层旧漆。然后涂上完整的面漆。

It is unnecessary to overall repaint the transformer if repair (damaged) finish timely.

Operation guide: clean surface by using cloth immersed with solvent or steam injection blower. Completely clear away mud, oil and grease. Gently worn old paint, and remove the shedding part. Using a wire brush to brush the rust part, until shiny. Paint two layers of primer on cleaned part and paint finish on primer. If the old paint is easily damaged and firmly stick on the metal surface, old paint should be completely removed by polish or special device and then paint finish.

1.6检查接地系统(保护接地)check earthing system (protective earthing)

为了防止悬浮带电,危及人员安全,变压器油箱和冷却系统必须通过一根足够截面的接地导线接地。同时为了避免环流,要选择一点接地。检查接地螺栓是否拧紧,必要时再次拧紧。

In order to prevent the suspension of charged, endanger personnel security, transformer oil tank and the cooling system must be enough through a cross section of grounding conductor. In order to avoid the circulation at the same time, choose to one-point earthing. Check the earthing bolts are tight, if necessary, to tighten again.

1.7取油样(用于油分析)oil sample (for analysis)

采油样的目的是为了测量击穿电压和检查液体绝缘的化学和物理特性。变压器运行前、运行了很长时间或者为防止击穿应对油采油样。建议采油样最长间隔期5年。油样阀位于“顶部”或“中部”,采油样用于气体分析。油样阀位于“底部”,采油样用于其它分析。

The aim of oil sample is to measure breakdown voltage and to check chemical and physical characteristics of liquid insulation. Oil sample should be taken before transformer running, or running for a long time or in order to prevent breakdown. Proposed max. Interval of taking oil sample is 5 years. Oil sample from oil sample valve on "top" or "middle" part is used for gas analysis; oil sample from oil sample valve on "bottom" is used for other analysis.

2、有载调压开关On load tap changer

2.1读出电动驱动机构上的计数器显示的动作次数

Read action times display on counter of motor drive mechanism

转换开关的动作次数必须记录下来。

Record action times of tap changer.

2.2切换所有分接,以清洁选择器触头

Switch all the taps to clean contacts of selector

如果调压开关一年内操作次数小于3000次或者不是在全分接范围内移动,变压器断电情况下应切换所有分接大约10次,以清洁触头。

If operation times of tap changer is less than 3000 or not move in full range, all taps should be

2.3检查保护继电器Check protective relay

检查有载调压开关的保护继电器,按下试验按钮进行试验。这时变压器断路器应跳闸。然后将按钮逆时针方向旋转90度重新设置。

Check protective relay of OLTC. Push the test button to do the test. On this condition, transformer breaker should trip. And then, spin button counter-clockwise rotation 90 degrees to re-set.

2.4检查外部轴系和法兰漏油

Check external shafting and flanges for oil leakage

退出联轴器、中心轴和与橡胶套筒连-。检查入口处轴承是否漏油,去盖后检查内表面是否腐蚀。检查开关头部法兰和入口轴承是否漏油。Exit universal joint (connect to coupling, central shaft and rubber muff-joint) to necessary position. Check bearing on entrance for oil leakage and internal surface for corrosion after removing the cover. Check flanges on tap changer head and bearing on entrance for oil leakage.

2.5检查电动驱动机构check motor drive

以下各项需检查:Following items should be checked:

l外壳的防腐蚀涂层anti-corrosion coating of enclosure

l门密封垫和锁Door sealing gasket and lock

l清洁外壳通风孔Clean air vent in enclosure

l加热(自动调温器在20℃操作),照明Heating (operate thermostat under 20℃), lighting l端子安装的紧密度Tightness of terminals installed

l就地的和远方的逐级控制Local and remote step by step control

限位开关,电动的和机械的检查Check limit switch, electric and mechanical

l触点排和位置指示计Contact row and position indicator

l必要时,清洁电动驱动If necessary, clean motor drive

l如果电动驱动是安装在振动强烈的地方,应检查所有的螺栓否拧紧,并再一次拧紧。If motor drive is installed on strong vibration place, all bolts should be checked and tightened again.

2.6有载调压开关—检修On-load tap changer -- repair

有载调压开关的检修只能由有经验的人员或专业人员进行。

Repair of on-load tap changer should be done only by skilled or professional staff

3、无励磁调压开关off-circuit tap changer

注意:无励磁调压开关只能在断电的情况下操作。

3.1切换所有分接,以清洁开关触头Switch all the taps to clean contacts of selector

铜触头浸于油中时,会失去光泽。这种锈蚀层可能会导致触头温度升高。所以无励磁调压开关一年至少一次切换所有分接头。以清洁触头(变压器断电时)。

Copper contacts will be corroded in oil and corrosion layer may cause high temperature of contacts. So, all taps should be switched at least once a year to clean contacts (when the transformer is interruption of power supply.

3.2检查联锁check interlock

端部位置是机械固定的。当到达端部位置时,开关只能向反方向转动。

The end position is mechanically fixed. When reach end position, the switch can only rotate in opposite direction.

4、控制箱和端子箱Cable box and terminal box

l检查控制箱的加热和照明Check heating and lighting in control box

对加热进行控制,使自动温度调节器至大约20℃。检查是否正确运行。必须检查橡胶密封件预防内部腐蚀。必须清洁控制箱的通气孔。控制箱内的继电器、电流接触器等必须进行检查,必要时进行替换。同时必须检查控制箱的照明情况。Control heating, and set automatic thermostat to 20℃. Check whether correct running. Must check rubber sealing gaskets to prevent internal corrosion. Muse clean air vent of control box. Check relay, and contactor in the control box and change it if needed. At the same time, check lighting in control box.

5、套管Bushing

l必须检查套管的油位Must check oil level of bushing

l必须检查套管的密封和清洁瓷瓶部分。Must check bushing sealing and clean porcelain part.

6、电缆盒(油,空气,气体或物质浸渍绝缘)

Cable Box (oil, air, gas or impregnated insulation

电缆盒,包括安装架和电缆套筒,必须检查是否有泄漏。

Check cable box, including erection fixture and cable bush for leakage.

7、电流互感器Current Transformer

内置式电流互感器必须与测量仪器连接或予短接。必要时,清洁互感器接线端子。

Built-in current transformer must be connected with measuring apparatus or short circuit. If needed, clean connector of current transformer.

8、监测设备Monitor Equipment

8.1检查气体继电器Check gas relay

报警和跳闸浮子是机械动作。断路器闭合时检查报警状况(气体报警)。如果报警浮子动作,报警信号必须到达控制室,但是断路器必须没有跳闸。如果跳闸浮子动作,断路器必须跳闸且发电机必须被断电。检查控制室内的信号。Alarm and trip float is mechanical movement. Check alarm (gas alarm) when breaker is closed. If alarm float works, alarm signal must reach control room and breaker must be no trip. If trip float works, breaker must be tripped and the generator must be interrupted. Check signals in control room.

8.2检查有载调压开关继电器Check on-load tap changer

检查保护设备,运行情况应与相关规定的相同。有载调压开关的保护设备运行时,检查断路跳闸、发电机断电和控制室的信号输入状况。有载调压开关的保护继电器一动作,变压器必须被切断。保护继电器仅作报警信号的布置是不允许的。

Protective device and running condition should be same to relative rules. When protective device of OLTC is running, check trip, generator outage and signal input in control room. Once protective relay of OLTC works, the transformer must be cut off. The arrangement of protective relay only as alarm signal is not allowed.

8.3检查远方温度计Check remote thermometer

记下温度设定值并注明油或绕组温度是否测量过。如果不确定是否测量过,可用(水银)温度计(温度计座中)测量油面温度,然后两个温度进行对比。必要时必须再次校准温度计。

Record set value of temperature and indicate whether oil or winding temperature measured. If not sure whether temperature measured, thermometer (mercury) (in thermometer pocket) can be used to measure top oil temperature and two values are compared. If necessary, re-calibrate thermometer.

8.4检查温度监测器Check temperature monitor

记下温度值。触头是否动作可听声音。请参阅“可调的温度监测器”。Record temperature value. Listen to check if contacts work. See " Adjustable temperature monitor"

8.5检查信号温度计Check signal thermometer

检查信号温度计是否正确运行。

Check signal thermometer is running correctly.

8.6检查油位监视器Check oil level monitor

操作信号触点可检查油位监视器是否正确运行。

Operate signal contact to check if oil level monitor work correctly.

8.7压力释放阀Pressure relief valve

发送跳闸信号给断路器的触点必须检查运行状况。检查之后,必须将触点设置至运行位置。

Check the contact of sending trip signal to breaker. After check, set contact to running position.

《变压器常见故障原因及处理表》Transformer General Fault Diagnosis Reference Table

序号

NO.

项目Items 故障现象F aults Phenomenon可能的原因Possible Reasons 补救措施Measures of Remediation

1 变压器油温

Oil Temperature

变压器油温升过高

Oil temperature rise is too high

2 变压器绕组油温

Winding Temperature

变压器绕组温升过高

Winding temperature rise is too

high

-油位计指示异常

Oil level indicator indicate abnormally

-冷却系统工作不正常。

Cooling system work abnormally

-变压器过载Transformer overload

-变压器室通风差。

V entilation of transformer room is not

well.

-变压器内部有短路或局部过热现象

There is short circuit or local overheating

phenomenon in the transformer interior.

-检查温度计,将此温度计与其它温度计对

比。

Check the thermometer and compares to others.

-是否切断风扇或者关闭冷却设备阀门。

Whether cut fans or close the valves of cooling

equipment.

--检查冷却设备控制装置。

Check the control device of cooling equipment.

-变压器减载检查。

Check transformer deloading

-改善变压器室通风条件。

Improve the ventilation of transformer room.

-取油样化验进行判断。

Analysis of oil sample for judging.

温度指示不准Indicate incorrectly -温度计温包漏液。

Leakage of thermometer bulb

-温度计座内未加油。

No oil in the thermometer socket.

-绕组温度计变流器不匹配。

Winding thermometer converter is

mismatching.

-变流器与绕组温度计及互感器接线不

正确或虚接。

Connection of converter, winding

thermometer and CT are not correct or.

virtual joint.

-用手拨动过温度计指针。

Thermometer pointer is turned by hand.

-更换温度计。

Change the thermometer.

-补加变压器油。

Refill transformer oil.

-调节变流器档位。

Regulate the converter tap position.

-检查接线是否正确,重新接线。

Check the connection, if not correct, rewiring.

-重新校正温度计或更换温度计。

Re-Calibrate or changer the thermometer.

3 变压器温度计

Thermometer

变压器本体温度计与后台数

显温度指示不一致

Transformer body thermometer

and background digital display

-温度计接线错误。

Thermometer connection is error.

-温度计输出信号不正确。

Output signal of transformer is incorrect.

-检查温度计接线并更正。Check and make

corrections to the connection of thermometer.

-测量温度输出信号,检查接线情况,如接线

无异常,更换温度计

Measure temperature output signal, check the

connecting condition if that is normal, change

-数显仪与温度计不匹配。Mismatching of digital display instrument and thermometer. the thermometer.

-检查温度计与数显仪型号并更正。

Check and make corrections to the type of thermometer and digital display instrument.

温度计高温报警

High temperature alarm of thermometer. -油温高high oil temperature

-温度计报警、跳闸接点整定值不正确。

Thermometer alarm、set value of trip

contact is incorrect.

-温度计本身或后台线路故障

Fault in the thermometer own or

background line.

-检查油温高原因,参考项1。

Check the reason of high oil temperature,

reference item 1.

-检查温度计并重新整定。

Check and reset the thermometer.

-检查线路故障并修复。

Check and repair the fault of circuit.

4 变压器油位

Oil level of

transformer

油位过低(低油位报警)

Oil level is too low(Low oil

level alarm).

-漏油。Leakage

-油温偏低。Oil temperature is low.

-油位计指示异常。

Indicate abnormally of oil level indicator.

-油位计本身或后台线路故障。

Fault in the oil level indicator own or

background line.

-检查是否有漏油,补油。

Check if there is leakage, add oil.

-检查油位是否符合油温油位曲线。

Check the oil level whether accord with oil

temperature oil level curve.

-检查油位计。Check the oil level indicator.

-检查线路故障并修复。

Check and repair the fault of circuit.

油位过高(高油位报警)Oil level is too high(High oil level alarm). -安装期间注油过高。Oil-filling is too

high during installation.

-油温偏高。Oil temperature is too high.

-假油位。False oil level.

-油位计指示异常。

Indicate abnormally of oil level indicator.

-油位计本身或后台线路故障。

Fault in the oil level indicator own or

background line.

-放油至符合油温油位曲线。

Dumping oil to the level according with the Oil

temperature level curve.

-检查油温偏高原因,参考项1。

Check the reason of high oil temperature,

reference item 1.

-充气定位。Inflatable positioning.

-检查油位计。Check oil level indicator.

-检查线路故障并修复。Check and repair the

fault of circuit.

5 变压器声音

Transformer sound

有异响、声音过大(注:大幅

度的负载变动,如大设备启

动,电弧炉炼钢,晶闸管整流

器等负载,由于高次谐波很

大,也会产生异常声响,属于

正常情况)There is abnormal

sound、the sound is too

loud(Note: Large load change,

eg. The load of big equipment

-过负载运行会使变压器发生很高且较

重的嗡嗡声

Overload running will make transformer

produce loud and heavy sound.

-电源频率波动较大造成变压器外部附

件及散热器振动

Power frequency wave bigger, cause

external accessories and radiators shake.

-变压器内部紧固件松动而发出强烈而

-需适当降低负载

Should reduce load properly.

-需检查调整输入电源

Should check and adjust input power.

-需停电吊检(注意区分是否变压器外部附件

松动发出的声响)Should untanking inspection

without electricity.(Note the sound if come from

external accessories which become flexible).

-需停电吊检(注意区分是否外部线路发出的

starting, electric arc furnace steelmaking, silicon controlled rectifier, due to the high order harmonic is very big, also can produce abnormal sound. Those are normal condition.)不均匀的噪声。

Transformer send out a strong and

nonuniform sound due to the internal

fastener become flexible.

-变压器内部接触不良或绝缘有击穿产

生噼啪的放电现象

Transformer internal poor contact or

insulation have breakdown produce the

discharge phenomenon.

-外部接地不良或某些金属部位未接

地,产生静电放电

Bad grounding in external or some metal

parts are ungrounded cause electrostatic

discharge.

声响)

Should untanking inspection without electricity.

Note the sound if come from external wires).

-检修接地部位

Check and repair grounding part.

-焊接部位渗漏油Leakage in the welding parts.

-焊接部位存在砂眼、气孔

There are sand holes, air holes in the

welding parts.

-带油补焊Repair welding with oil.

-专用密封胶补漏Special sealant mend

6 变压器密封性

Sealing of transformer

-法兰密封部位渗漏油

Leakage in the sealing parts of

-密封处螺栓松动

Looseness of bolts in sealing parts.

-重新紧固螺栓Retighten bolts.

-消除或减小外力,并重新紧固Eliminate or

flange.-密封部位受外力影响

Sealing parts are influenced by external

force.

-密封胶垫安装不到位

Sealing gaskets installation is below

standard.

-密封面不平整

Sealing surface out-of-flatness

-密封胶垫材质缺陷

Sealing gaskets’ material are defective reduce external forces and retighten.

-重新安装胶垫Reinstall sealing gaskets. -处理密封面后重新安装

Deal with and reinstall sealing surface.

-更换密封胶垫

Change sealing gaskets.

7

变压器油

Transformer oil -变压器油耐压降低

Transformer oil withstand

voltage to reduce.

-变压器油微水超标。

Oil moisture content exceed

standard.

-变压器油色谱异常Oil

chromatographic abnormality.

-变压器运行时间很长。Transformer

long time running.

-变压器油受潮Transformer oil have

got damp.

-变压器内部存在放电

Discharge in the transformer internal.

-滤油处理Filter oil

-检修渗漏部位。

Check and repair leakage parts.

-需停电检修。Power failure repair.

-风扇停转 Fan stalling

8

变压器冷却系统

Transformer cooling system

-风扇过热 Fan overheating.

-控制箱故障Control box fault

-风机故障 Fan fault

-检修控制箱,参考项11

Check control box, reference item 11. -检修风机 Examine and repair fan.

9

压力释放装置(阀)

Pressure relief device (valve)

-压力释放阀发生报警跳闸故障pressure relief valve occur alarm and trip

-压力释放阀喷油 oil injection -压力释放阀误报警(本身或后台线路故障)。False alarm(itself or background line fault)

-储油柜管道关闭或堵塞。Oil conservator channel close or jam -油箱内出现短路现象。Inner tank occur

-检查压力阀本身及后台线路电气连接。 Check connection of itself or background

line

-检查管道,并开启管道阀门。Check channel,

open channel vavle

-需停电检修power off and check 10

套管端子接线片

Lug plate of bushing terminal

-连接部件变色

Interconnecting pieces

change

color

接触不好。Bad contact 清洁连接面,拧紧螺栓。

Clean joint face, tighten bolt.

11 控制箱 Control box -不能正常启、停风机。 Start, stop fan abnormally -控制箱内电器件烧损。 -控制箱内接线不正确。

-控制箱内温湿控、相序继电器等电器件整定值不正确。

-检查烧损原因并更换电器件。

-参照控制箱图纸检查接线情况,并整改。 -参照控制箱组件说明书重新进行整定。

12接地连接

Earthing 接地线中断

ground wire discontinuous

接地电流过大earthing

current is too high

由于外部短路产生很大的短路电流。

Great short circuit current caused by external

short circuit

多点接地形成环流。

Multiple points earthing form circulation

清洁触点,拧紧螺栓,检查电气间隙。打开

电流环。足够截面一点接地。

Clean contact, tighten bolt, and check electric

clearance open current loop One point earthing

13气体继电器

Gas relay 气体继电器报警

alarm

-空气积聚

accumulation of air

-气体继电器本身或后台线路故障导致

误报警

Gas line fault lead to false alarm relay itself or

the background

-由于内部故障产生气体。

The production of gas due to internal fault

-剧烈的振动。

Severe vibration

可以暂时继续运行,为分析故障应进行以下

试验和检查。

Continue run. Following tests should be done to

analyse failures.

1.检查油位、管道和阀门位置。

1.Check oil level, pipe and valve position.

2.检查电气连接。

2.Check electrical connection

3.检查气体继电器报警跳闸机械机构。

3.Check trip mechanism of gas relay

4.把故障发生5小时内产生的部分气体放入

一个玻璃容器,并进行分析。

4.Gather some gas produced in 5 hours after failure

in a glass container and be analysed.

5.从油箱中部取油样,做油色谱分析。

6.拆开所有套管连接,并做以下试验:

Take apart all bushing connection and do

following tests:

6.1测量绝缘电阻。

6.2测量变比。

6.3测量直阻。

measure winding resistance by DC method

6.4施加低电压测量空载电流。

measure no load current by applying low voltage

7、将试验结果同试验报告进行对比。当没有发现故障或故障已消除时,接通变压器重新投入运行。Compare test result with test report. When there is no fault or fault has been eliminated, put transformer into use again.

气体继电器跳闸trip -内部闪络产生剧烈涌流。

the production of inrush current due to inner

flashover

-由于内部故障产生剧烈气体。

The production of gas due to internal fault

-剧烈的振动。severe vibration

-故障跳闸。fault trip

-保持跳闸状态。根据如上1到7的描述进行

试验和测量。

keep trip state. Do the tests and measurement as per

above 1 to 7 items.

-当没有发现故障或故障已消除时,接通变压

器重新投入运行。

When there is no fault or fault has been eliminated,

put transformer into use again.

14开关气体继电器

Gas relay for OLTC 气体继电器报警

Gas relay alarm

-气体继电器本身或后台线路故障导致

误报警。itself or background line

Fault lead to false alarm

-由于开关切换频繁,内部故障产生气

体。Because changer switch

frequently, internal fault

-安装阶段注油后排气不彻底。Remove

gas is not completely after

oiling at the installation stage

-检查气体继电器及其线路。

Check gas relay and its circuit

-排除气体,建议取消轻瓦斯报警信号。

Remove gas, it was suggested cancel the

light gas alarm singal

-排气。Remove gas

气体继电器跳闸

Gas relay trip

-内部闪络产生剧烈涌流。Severe flow

by inner flashover

-剧烈的振动。Severe shake

-故障跳闸。Fault trip

-保持跳闸状态,进行以下检查:

Maintain trip,check as below:

1、检查油位、管道和阀门位置。

Check oil level, channel and valve

2、检查电气连接。

Check electrical connection

3、检查气体继电器报警跳闸机械机构。

Check alarm and trip mechanism of gas

relay

4、对开关进行吊检 check tap changer

-当没有发现故障或故障已消除时,接通变压器重新投入运行。

Connect and operate again if there is no fault or fault clearance.

15有载开关电动机构

OLTC electric

mechanism 驱动不能电气操作

Drive can't be electrical

operated

电气接线错误或连接点松动;

Electric connection fault or

connection point loose

见其操作手册

Refer to operation manual

16

无励磁开关

non-excited tap 不能运行couldn't working

变压器没有电压 no voltage

驱动装置有故障。Driving device is

fault

连接不好。Connection is not well

-修理手动驱动装置。

Repair manual driving drive

-无载开关每年一次触点滑动操作。

No-load tap changer is contactor slide

per year.

17开关的压力冲击保护

Pressure impact

protection of

switch 由于膜盘提升而跳闸

trip due to lifting of membranous

disk

开关产生故障致隔膜破裂和产生冲击

涌流。

Film rupture and inrush current caused by

switch failure

保持跳闸状态,检查跳闸机械机构。拆下并

检查开关,如果没有发现故障,重新设置跳

闸机械机构,并使变压器重新投入运行。

Keep trip state, and check trip mechanism. Remove

and check switch. If failure is found, reset trip

mechanism and put transformer into use again.

18 变比试验

Voltage ratio test 结果异常

Abnormal result

-测试接线错误。

Wiring error

-变压器外部接线影响。

External wiring effect

-外部设备影响。

External equipment effect

-测试电压不稳。

Test voltage instability

-剩磁影响。

Remanence effect

-三相独立无载开关不在同一分接位

置。

Three phase separate off circuit

tap changer not on the same tap

position

-变压器本体问题

The problem of the transformer

-更正接线,重新测试。

Correct wiring, retest

-拆除变压器所有套管外部连接。

Demolish all the outside connection of the

bushing

-关闭变压器附近大功率、强磁场设备。

Turn off the large power and high magnetic

fields equipment near by the transformer

-使用稳定电源测试。

Use the stabilized power supply

-消除剩磁,重新测试。

Eliminate remanence, retest

-检查开关位置,重新测试。

Check the tap location, retest

-条件允许,进行低电压空载试验进一步核实。

由生产厂家技术人员综合分析。

Condition allowed, carry on the low voltage off

load test to check it. Comprehensive analyze by

the TWTB engineer

19 直流电阻试验

DC resistance test 结果异常

Fault

-测试接线接触不良。

Wiring bad contact

-分接开关长时间不切换形成氧化膜。

Oxidation film is formed due to

non-changing the tap changer for a

long time

-三相独立无载开关不在同一分接位

置。

Three phase separate off circuit

tap changer not on the same tap

position

-变压器本体问题

The problem of the transformer

-检查接线,清洁接触面。

Check the wiring, clean the contact surface

-反复切换分接开关,破除氧化膜重新测试。

Change the tap changer repeatedly to explode

the oxidation film, and retest

-检查开关位置,重新测试。

Check the tap location, retest

-由生产厂家技术人员综合分析。

Comprehensive analyze by the TWTB engineer

20 绝缘电阻试验

Insulation

resistance test 绝缘电阻低

Low insulation resistance

-变压器套管污秽影响。

Effect of the duty bushing

-测试环境温、湿度影响。

The effect of the environment

temperature and humidity

-清洁套管,重新测试。

Clean the bushing, retest

-在环境温度10-40℃,干燥环境下测量(一般

要求湿度<70%)。

Test under 10-40℃, humidity<70%

-变压器油质劣化。

Transformer oil deterioration -变压器器身受潮。

Transformer body damp -滤油后,重新测量。

filter oil, retest

-热油循环或联系生产厂家结合现场情况综合判断。

Hot oiling or contact the manufacture to compressive analyze according to the site condition

21 变压器差动

Transformer

differential 差动动作

Differential action

-接线错误

Wiring fault

-整定值过小

Setting value is too low

-电流互感器故障

CT fault

-变压器本体问题

The problem of the transformer

检查接线,排除问题后重新送电。

Check the wiring, deliver current again after

removing the faults

调整整定值,重新送电。

Adjust the setting value, deliver current again

检查互感器,故障消除检查无误后,重新送

电。

Check the CT, deliver current again after

removing the faults

变压器本体问题需进行以下工作:

If it is the problem of the transformer, the

following should be done:

变压器日常维护和故障处理

变压器日常维护和故障处理 【摘要】随着社会的不断发展和进步,电力变压器所承载的工作任务和工作量在不断的提高。在这种情况下,我们需要对变压器实行状态检修,通过相关技术的作用,帮助变压器提高自身所具有的性能,并且在日后的工作当中,能够更好的为居民服务。本文分析了平时的维护和故障处理,避免事故的发生。 【关键词】变压器;日常维护;故障;处理 电能是人们生活和工作中不可缺少的能源,随着经济的快速发展,人们对电能的需求量也在增多,为了更好地保证电力系统的稳定运行,对电气设备进行日常的维护是非常重要的,在电力系统中变压器的作用非常大,其出现故障对电力系统的影响非常大,因此,一定要对其常见的故障进行分析,这样才能保证故障处理的及时性。 一、变压器的故障处理 1.1铁芯故障 铁芯故障在变压器故障中不常出现,但是一旦出现后果是非常严重的,铁芯故障主要是由于铁芯柱的螺杆或者是铁轮的绝缘损坏而导致的,会导致螺杆和铁芯之间出现绝缘损坏,会出现环流局部过热的情况,甚至会导致铁芯出现局部熔毁的情况。也可能会导致铁芯的迭片出现短路的情况,绝缘层出现损坏,使得变压器的空载损失出现增大。在变压器出现故障以后,在确定是否是铁芯故障的时候可以采用吊芯检查的方式。先要对各相绕组的直流电阻进行测量,出现差别较大的情况,就说明是绕组故障,然后对铁芯的外观进行检查,可以对直流电压进行测量,如果出现的损坏不大,那么就可以在损坏处涂漆进行处理。 1.2电缆安装不良引发的故障 夏季电力系统的负荷通常是较大的,这个时候变压器的负荷也相对较大,在这种情况下,电流会出现过大的情况,这样非常容易出现过大电流导致引线烧伤,导致变压器内的油出现分解,在油中的总烃会出现超标。出现这种故障主要是由于不均匀的磁场作用下,变压器在运行过程中出现了振动的情况,使得绝缘层出现了破损。在进行电缆安装的时候,要检查安装的是否到位,在确定了不相连以后可以用万用表进行测试[1]。 1.3绕组故障 绕组故障通常有匝间短路、绕组接地、相间短路、断线以及接头开焊几种。导致绕组故障的原因也是非常多的,在制造或者检修的时候,出现了局部绝缘受到损害;变压器在运行中出现散热不良或者是长期处在过载;绕组内出现杂物;运行温度过高导致绝缘老化;绕组制造工艺不良,在压制过程中出现压制不紧,

干式变压器日常运行及检测维护事项【新版】

干式变压器日常运行及检测维护事项 干式变压器在电力系统中有着最核心的地位,电力系统能安全运行的关键部位,若干式变压器发生故障,会导致电力的供应发生中断,甚至会引发火灾等一系列安全事故,将会对社会生活以及经济的发展造成重大的损失。所以,加强干式变压器的运行前检查及运行时的故障分析处理,才能够保障电力系统安全、可靠运行。 一、干式变压器运行前的检查 1. 检查所有紧固件、连接件是否有松动现象并进行彻底紧固,紧固铜螺母时,扭矩不能过大,以免造成滑丝。 2. 检查配套零部件是否重新安装妥当;检查变压器本体内是否有异物,重点确认变压器风道内、高压绕组的表面及下垫块的凸台处。 3.检查风机、温控装置、外壳的门控装置、行程开关及其他辅助器件能否正常运行。 二、干式变压器运行前的试验项目

1.测量三相绕组所有分接头位置的直流电阻和电压比,并进行联结组别的判定。 2.检查变压器壳体与铁芯是否已永久性接地。 3.绕组绝缘电阻测试。 4.铁芯绝缘电阻的测试。 5.外施工频耐压试验。 6.有载调压变压器应根据有载调压分接开关使用说明书做投入运行前的必要检查和试验。 三、干式变压器运行注意事项 1.变压器投运前,应根据电力网电压测试值,按其铭牌和分接指示牌将其分接片(对有载调压变压器将有载分接开关)调到合适的位置。如变压器输出电压偏高,在确保高压一次侧断电的情况下,将分接头的连接片往上(1档方向)调;如变压器输出电压偏低,在确保高压一次侧断电的情况下,将

分接头的连接片往下(5档方向)调。如为升压变压器,则正好与上述相反。 2. 变压器投运前,应检查和确认变压器及其保护装置是否具备带电运行条件。一般送电3次,第一次送电间隔时间不少于10Min,其余送电间隔时间不少于5 Min,送电前检查项目: 1)螺栓紧固情况和铁芯上是否有金属异物; 2)绝缘距离是否符合送电标准; 3)电器功能是否运行正常; 4)连线是否正确; 5)摇各部件绝缘是否符合送电标准; 6)器身有无凝露现象; 7)外壳有无可使小动物进入的漏洞(特别是电缆进线部位);

计算机硬件常见故障排除及解决方法

计算机硬件常见故障排除及解决方法 1.CPU常见故障排除 常见的CPU故障大致有以下几种:散热故障、重启故障、黑屏故障及超频故障。由于CPU 本身出现故障的几率非常小,所以大部分故障都是因为用户粗心大意造成的。 1.CPU针脚接触不良导致电脑无法启动 2.CPU高温引起的死机或重启(风扇及硅胶或本身损坏) 3.CPU超屏引起显示器黑屏 4.夏日里灰尘引发的死机故障 2.主板常见故障排除 电脑主板产生故障的原因,一般有三个方面:一是元器件质量引起的故障。这种故障在一些劣质的板子上比较常见,主是指主板的某个元器件因本身质量问题而损坏,导致主板的某部分功能无法正常使用,系统无法正常启动,自检过程中报错等现象。 1.电容爆奖在一些劣质主板上是常有的事情 2.是环境引发的故障。因外界环境引起的故障,一般是指人们在未知的情况下或不可预测、不可抗拒的情况下引起的。如雷击、市电供电不稳定,它可能会直接损坏主板,这种情况下人们一般都没有办法预防;外界环境引起的另外一种情况,就是因温度、湿度和灰尘等引起的故障。这种情况表现出来的症状有:经常死机、重启或有时能开机有时又不能开机等,从而造成机器的性能不稳定。 3.人为故障。有些朋友,电脑操作方面的知识懂得较少,在操作时不注意操作规范及安全,这样对电脑的有些部件将会造成损伤。如带电插拔设备及板卡,安装设备及板卡时用力过度,造成设备接口、芯片和板卡等损伤或变形,从而引发故障。 4.开机无显示的故障处理。一般认为,开机无显示故障是硬件引起,这种看法有一定的片面性。在检修这类故障的时候,我们一般还是应该先从软故障的角度入手解决问题。开机时,若电源指示灯没有亮,一般应该怀疑外接电源没有接好或电源有问题。若开机电源指示灯亮但无显示,这种情况一般应按以下的顺序去排查故障: 一是通过主板的跳线(一般在CMOS的电池旁边)清除主板上CMOS原有的设置再开机。 二是重新安装CPU后再开机。 三将电脑硬件组成最小系统后再开机。 经过以上三个步骤后,若开机还是没有显示,这时可以在最小系统中拔掉内存。若开机报警,则说明主板应该没有太大的问题。故障的怀疑重点应该放在其他设备上。若在拔掉内存后开机不报警,一般来说,故障可能出在主板上。维修或更换 开机有显示但自检无法通过的故障处理。开机有显示但自检无法通过,这类故障一般都会有错误提示信息。我们在排除这类故障时,主要是根据该提示信息,找出故障点。但这类故障一般是因为主板的某个部件损坏引起,多数应该属于硬故障,但也不排除软故障引起的可能。针对软故障的排查,我们可以依照以下的顺序进行: ①.主板温控失常引发主板“假死” 故障分析:由于现在CPU发热量非常大,所以许多主板都提供了严格的温度监控和保护装置。一般CPU温度过高,或主板上的温度监控系统出现故障,主板就会自动进入保护状态。拒绝加电启动,或报警提示。上述例子就是由于主板温度监控线脱落,导致主板自动进入保护状态,拒绝加电。所以当你的主板无法正常启动或报警时,先检查下主板的温度监控装置

变压器维护内容

变压器的检修按其检修工作性质可分为大修和小修,小修一般至少每年一次,对安装在特别污秽区的变压器可另行规定;大修一般5~10年检修一次,对变压器一直在正常负荷下运行时,考虑每10年大修一次。 1、变压器小修内容和要求1)消除巡视中发现的一切缺陷。 2)测定线圈的绝缘电阻值,应满足绝缘要求。找绝缘标准是多少 3)清扫瓷套管和外壳,发现瓷套管破裂或胶垫老化者应更换,漏油者应拧紧螺丝或更换胶垫。 4)拧紧引出线的接头,如发现烧伤,应用砂布擦光后接好。5)缺油时应补油,并清除油

枕集泥器中的水和污垢。6)检查呼吸器和出气瓣是否堵塞,并清除污垢。 7)检查变压器瓦斯保护引出线是否侵蚀,若侵蚀应更换处理。8)检查各部位的油截门是否堵塞。 9)跌开式熔断器保护的变压器应检查熔丝管和一、二次熔丝是否完好正常。10)检查变压器的接地良好,地线是否腐蚀,腐蚀严重时应更换。2、变压器大修的步骤和内容 1)大修前的准备:将运行中记录下来的缺陷到现场进行核对,制定消除缺陷的对策,对检修中需用的设备、材料和工具应预先列出清单,并到现场检查环境和用具是否齐全。 2)放油、打开变压器顶盖、吊器身、检查线圈和铁芯。3)检修铁芯、线圈、分接开关和引出线。 4)检修顶盖、油枕、防爆管、散热器、油截门、吸湿器和套管等。5)检修冷却装置和油再生装置。 6)清扫壳体,必要时重新油漆。7)检修控制测量仪表、信号和保护装置。8)滤油或换油。9)必要时干燥绝缘。10)装配变压器。 11)按试验规程规定的项目进行测量和试验。12)试验合格后将变压器重新投入运行。3、变压器大修的要求 1)为防止器身吊出后,绕组在空气中暴露的时间过长受潮,应避免在阴天吊芯,在相对湿度不大于65%空气中不超过16小时,在相对湿度不大于75%空气中不超过12小时。 2)对于运行时间较长的变压器(如超过20年运行的变压器),在吊芯时应重点检查绕组的绝缘是否老化。 3)变压器线圈间隔衬垫应牢固线圈不能有松动、变形或位移,高低压绕组应对称无油粘物。4)分接开关接点应牢固,绝缘纸板和胶管应完整无损。 5)查对电压转换开关的接点、压紧螺丝、转动部分的转轴与顶盖上的标示字样应一致。6)铁芯不能有松动,铁芯与线圈间的油道应畅通。 7)穿芯螺栓的绝缘电阻,应用1000V摇表测定10KV以下变压器绝缘电阻不应低于2MΩ,35KV变压器不应低于5 MΩ。 8)瓦斯继电器的二次回路绝缘电阻应合格、接线正确,瓦斯继电器内部浮筒及水银接点完整。 9)充油套管内的油应保持在规定的指示线上。 配电变压器检查和常见故障分析王纪昌晋高峰配电变压器是一种静止的电气设备,在输电、配电系统中起到了改变电压和传输功率的作用。因此,作为维修电工应对变压器进行维护和定期检查,以便发现故障,及时处理。一、配电变压器的维护检查变压器维护检查的内容如下:1.检查运行中的变压器声响是否正常变压器运行中声响是均匀而轻微的“嗡嗡”声,这是在交变磁通作用下,铁芯和线圈振动造成的,若变压器内有各种缺陷或故障,会引起异常声响,其声响如下:(1)声音增大并比正常时沉重,这是变压器负荷电流大,过负荷的情况。(2)声音中杂有尖锐声,声调变高,这是电源电压过高、铁芯过饱和的情况。(3)声音增大并有明显杂音,这是铁芯未夹紧,片间有振动的情况。2.检查变压器的油位及油的颜色是否正常,是否有渗漏油现象油位应在油表刻度的1/4~3/4以内。油面过低,应检查是否漏油,若漏油应停电修理。若不漏油,则应加油至规定油面。加油时,应注意油表刻度上标出的温度值,根据当时的气温,把油加至适当油位。对油质的检查,通过观察油的颜色来进行。新油浅黄色,运行一段时间后变为浅红色。发生老化、氧化较严重的油为暗红色。经短路、绝缘击穿的油中含有碳质,油色发黑。3.检查变压器运行温度是否超过规定变压器运行中温度升高主要由本身发热造成的,一般说,变压器负载越重,线圈中流过的工作电流越大,发热量越大,运行温度越高。其温度越高,使绝缘老化加剧,寿命减

干式变压器日常检查维护作业规定(新版)

( 安全管理 ) 单位:_________________________ 姓名:_________________________ 日期:_________________________ 精品文档 / Word文档 / 文字可改 干式变压器日常检查维护作业 规定(新版) Safety management is an important part of production management. Safety and production are in the implementation process

干式变压器日常检查维护作业规定(新版) 1适用范围 1.1本规定适用于容量为6300KVA及以下,电压为35KV及以下的干式变压器日常检查维护作业及安全操作规范。 1.2适用人员:已经过培训并取得有效电工证操作手、修理工和专业维修保养作业人员。 2规范性引用文件 GB1094.11-2007干式电力变压器 GB/T10228-1997干式电力变压器技术参数和要求 3现场责任 3.1电工(修理工)是执行本规定的第一责任人。 3.2电工(修理工)对设备安全操作及日常检查维护的全面性、故障或故障隐患报告的及时性以及发现与处理故障或故障隐患后所采取措施的及时有效性负有责任。在日常检查维护、操作过程中发

现设备存在故障或故障隐患,应及时报分公司设备主管。 3.3分公司设备主管对故障处理、故障信息及时上报负有责任。在接到电工(修理工)上报的故障或故障隐患后,分公司设备主管应根据故障性质及时采取有效防范和修复措施,防止故障进一步扩大,对不能处理的故障或故障隐患,应及时上报分公司主管领导。 3.4分公司主管领导对设备主管上报的故障或故障隐患处理的组织和最终结果负有责任。在接到设备主管报告的设备故障信息后,应根据故障性质采取及时有效的防范措施,并积极组织故障修复,不得强令设备带病运转。 3.5分公司电工(修理工)应对故障维修的质量、二级保养作业的全面性、对号率负责。否则,因维修质量或保养不到位造成设备非正常损坏、磨损或机械事故的,电工(修理工)应承担相应的责任。 3.6分公司设备主管应至少每周对整个分公司设备进行一次巡检,对电工(修理工)依据本规定进行的安全使用及日常检查维护作业情况进行检查并在《日常检查维护记录表》上签字确认。

10KV电力变压器的日常维护与检修

10KV电力变压器的日常维护与检修 来源:中国变压器交易网10KV电力变压器在各大行业使用范围越来越广,所以电力变压器的可靠性、保证性、维修性也显得尤其重要,10KV电力变压器一旦出现问题将直接影响到本身的性能以及其他 电力设备运行的安全可靠性,那么我们如何正确地做好10KV电力变压器日常维护与检修呢? 一、加强10KV电力变压器的定期检查 (1)定期检查瓷套管及绝缘子的清洁度,及时清扫黏附在表面的灰尘,清除裸露导体的氧化膜或者是锈迹。 (2)变压器运行中会产生震动,影响紧固件,所以要在运行一段时间后停电进行紧固件的维护,保证电气连接的紧固可靠。 (3)定期检查分接开关。并检验触头的紧固、转动灵活性及接触的定位。 (4)在油浸式变压器中,要检查器身有无渗漏、生锈、污垢淤积以及任何限制油自由流动的机械损伤。 (5)定期检查油浸式电力变压器的绝缘油够不够,干式电力变压器的风机的运转、温控器的显示正不正常。 (6)调压变压器的分接开关的定期检查包括绝缘油的检查和开关的吊心检查,检查周期可按DL/T574-95规定进行。分接开关中的绝缘油在多次切换后颜色变黑,耐压下降,一般在耐压值降低到20kV-25kV时应更换新油。分接开关应根据切换次数或使用时间定期吊心检查,主要检查快速机构和触头的磨损情况以及储能弹簧、触头压力弹簧等部件的疲劳情况。 二、加强10KV电力变压器日常巡视检查 (1)日常巡视每天应至少一次,夜间巡视每周应至少一次。 (2)下列情况应增加巡视检查次数:首次投运或检修、改造后投运72h内;气象突变(如雷雨、大风、大雾、大雪、冰雹、寒潮等)时;高温季节、高峰用电期间;变压器过负荷运行时。 (3)10KV电力变压器日常巡视检查应包括以下内容:油温应正常,应无渗油、漏油,储油柜油位计油位应正常;电力变压器音响应正常;散热器各部位手感温度应相近,散热附件工作应正常;吸湿器应完好,吸附剂应干燥;引线接头、电缆、母线应无发热迹象;压力释放器、安全气道及防爆膜应完好无损;分接开关的分接位置及电源指示应正常;气体继电器内应无气体;各控制箱和二次端子箱应关严,无受潮;干式变压器的外表应无积污,风机运

干式变压器日常维护须知建议

部分检 查 维护和保养检查铁心及夹件等表面及缝隙间是否有积灰及异物。 用清洁的压缩空气或氧气吹扫铁芯、夹件表面和各缝隙;并除去异物。检查变压器铁芯表面涂层是否损坏。 铁芯和夹件表面涂层如有破损,采用同色油漆(丙烯酸油漆)修补。检查变压器铁芯是否接地良好,是否一点接地。如发现铁心接地螺栓松动,需用扳手拧紧;铁心不得多点接地。 检查夹件紧固程度,检查拉板螺栓、夹件螺栓、穿芯螺杆是否松动。 对夹件螺栓,拉板螺栓、车架连接螺栓进行复紧。绕组清洁,表面无灰尘杂质;绕组无变形、倾斜、位移,绝缘无破损、变色及放电痕迹,表面凝露后干燥处理试验合格。干式变压器日常运行维护建议须知 一:干式变压器定期检查 铁心(变压器长期运行后,线圈表面容易积累灰尘,正常情况下这些灰尘不会影 响变压器的正常运行。但较大的污秽度将降低变压器抗过电压能力,建议每年进行一次灰尘清理工作。)用清洁的压缩空气或氧气吹扫线圈表面、线圈高、低压绕组间风道无被杂物堵塞现象,高、低压绕组风道畅通,无杂物积存。 检查引线绝缘完好,无变形、变脆,引线无断股情况,接头表面平整、清洁、光滑无毛刺,并不得有其它杂质;引线及接头处无过热现象,引线固定牢靠。绝缘子固定应牢靠,表面清洁,无爬电和碳化现象;如发现绝缘变形变脆等现象需及时更换。检查浇注型绕组和相间连接线有无积尘,有无龟裂、变色、放电等现象,绝缘电阻是否正常。 如发现放电现象及绝缘异常等现象需由专业人员进行进一步检测及处理。检查各绝缘件,检查紧固件、连接件。 表面有无爬电痕迹和炭化现象,绝缘无损坏。紧固件、连接件不松动,螺栓齐全紧固,松动螺栓进行紧固。检查变压器线圈支撑(上下垫块)是否有位移、松动现象。用扳手锁紧线圈垫块上的顶紧螺栓。 电气联接电气联接处应保证一定的接触压力方可保证导电良好,用户应定 期检查:低压引出线与联接母排,高压端子与高压电缆接线鼻的联接。检查调压分接开关触点有无过热变色、接触不良或锈蚀等现象。 对于电气联接处的紧固螺栓,推荐使用扭距扳手进行复紧。 温控器在可能的情况下应经常监视温控仪工作情况,如发现无显示、显 示缺字、闪烁、字符错乱,用户首先应关闭温控仪,然后重新开 机,一般情况下故障可消除,如故障仍然存在,请立即通知厂方。 擦拭温控仪灰尘,重新紧固温控仪控制回路的连接螺丝。 线圈内部、线圈与铁芯之间的灰尘和异物(注意:不可用潮湿的物体擦拭变压器本体,以免降低绝缘水平)。发现线圈表面凝露,需干燥处理。风机检查所有配备的风机是否同时开启或停止。如有部分风机不运 转,首先检查风机电源连线是否断路,如连接线正常,请通知厂家。风机运转状态下,应无异响、异常震动、异味。如有异常响声,请首先排除风机出风口有无异物落下。排除异物后,仍存在 上述情况,请与厂家联系。 紧固风机电源联接螺丝,紧固风机固定螺栓。用清洁的压缩空气或氧气吹扫风机各部分。 外壳 检查变压器外罩、铭牌是否完好。完毕后检查变压器内有无遗留工具,关上变压器外罩门并琐好。序号 1 2.干式变压器从制造到投入运行的时间不能相隔太长,以免绝缘受潮,更不能遭受雨淋,否则需重新干燥处理; 检 查 有无异常声音、振动。3.变压器在维护过程中绝对禁止脚踩风机攀升; 4.变压器维护必须由专业人员进行操作。 注意事项二:干式变压器投入运行后的检查 1.维护是必须断开变压器高低压两侧电网; 2 3GB 1094.2 电力变压器 第2部分:温升GB 1094.5 电力变压器 第5部分:承受短路的能力GB T 10228 干式电力变压器技术参数和要求DLT 1102-2009 配电变压器运行规程 注意:以上建议仅供贵方参考;干式变压器具体日常维护及定期维护须按国家标 准及供电局所规定的规程进行。引 用 规 范 GB 1094.1 电力变压器 第1部分:总则 GB 1094.3 电力变压器 第3部分:绝缘水平、绝缘试验和外绝缘空气间隙 GB 1094.11 电力变压器 第11部分:干式电力变压器 DL T 572 电力变压器运行规程有无由于局部过热、有害气体腐蚀等使绝缘表面出现爬电痕迹和炭化现象等造成的变色。变压器所在房屋或柜内的温度是否特别高,其通风、换气是否正常,变压器的风冷装置是否正常运转。

干式变压器的维护保养

干式变压的维护保养 环氧浇注干式变压器具有难燃、自熄、耐潮、机械强度高、体积小、重量轻、承受短路能力强等多种优点,得到了广泛应用。但是干式变压器也存在一些缺点,比如在通风不畅的情况下,其散热性能不如油浸式变压器好等。根据我公司使用干式变压器多年的实践经验,对干式变压器的运行维护总结几点心得,供参考。 1、定期做好清扫工作 如发现有过多的灰尘聚集,则必须立即清除,以保证空气流通。在积尘较大的场所,干式变压器至少每半年在清扫一次。对于通风道里的灰尘。应使用吸尘器或压缩空气来进行清除。如果不及时清除将影响变压器的散热,还将导致变压器绝缘降低甚至造成绝缘击穿。例如我公司220kV位庄变压站35kV站用变在一次停电试验中。使用2500V光欧表测量干式变压器铁心绝缘电阻,其铁心绝缘电阻降低至3MΩ,比上次试验数据100MΩ降低很多,其主要原因就是变压器通风道中的灰尘没有清扫干净,清扫处理后铁心绝缘电阻上升至100M Ω。2、加强通风设备的运行维护,保证变压器通风流畅 确保通风设备正常,主要是确保风机的正常运转。如所带负荷很小,并证明变压器确实没有特别过热点(这可用红外线测温仪和本身自配的温控器检测),可以减少运转的风机,但必须保证有风机正常运行,因为干式变压器一旦发生热损坏,将严重损坏内部绕组,其后果不堪设想。一般散发1kW损耗的热量,应该的4 m3/min的通风量。对无外壳的变压器应在周围安装隔离遮拦。变压器室的门、通风孔都要有防止雨雪和飞鸟、蛇等小动物进入的措施。 3、加强温度的监控 平常要加强对温控器的观察,看显示的三相温度是否平衡,某一相的温度显示值是否有突变现象。目前温控器与变压器内部热敏电阻(测温度)之间的接头采用的是针式插头,一旦接触不良,就会导致温控器误判断。但如果加强监视,就会发现温控器的不正常工作状态,提前采取措施,避免故障的发生。对于大容量变压器和重要场所的变压器,在订货时可以要求变压器生产厂家每相多安装一只热敏电阻,实现对温控器的双重化配置,这样就可以很好在避免此类故障的发生。 4、积极开展去潮去湿工作,保证其干燥程度 在某些比较潮湿的地方(如雨水较多、阴暗地方),若启用已停运的干式变压器,则要检查是否有异常潮湿。如有,要启动热风对其表面进行干燥处理,以防绝缘击穿。对氧浇注干式变压器而言,这种表面潮湿并不影响绕组内部的绝缘,因此,处理后就可投入运行。一旦变压器投入运行,其损耗产生的热量,将会使绝缘电阻恢复正常。 5、认真检查紧固件、连接件是否松动,保障干式变压器的机械强度 变压器在长期运行过程中,由于外界知路等原因,不可避免地出现端头受力、振动引起的紧固件、连接件松动现象。发生上述现象,就有可能产生过热点。为此,在高低压端头及所有可能产生过热的地方都要设置示温蜡片,定期观察,并结合清扫、预防性试验,紧固端头和连接件。 6、积极开展除锈工作,防止铁心锈蚀 干式变压器的铁心都是暴露在空气中,极易锈蚀。如果发生大面积铁心锈蚀,就会使变压器的损耗增加、效率下降,甚至直接影响变压器的寿命。所以要定期除锈防锈,避免铁心锈蚀。 另外,目前生产的干式变压器耐压水平较油浸式变压器低,因此要加强对避雷器的配置和维护检测。避雷器以选氧化锌避雷器为佳。高压侧应由电缆进线,不宜直接与架空线路相连接。

最常见的电脑故障以及解决方法500例

电脑出现的故障原因扑朔迷离,让人难以捉摸。并且由于Windows操作系统的组件相对复杂,电脑一旦出现故障,对于普通用户来说,想要准确地找出其故障的原因几乎是不可能的。那么是否是说我们如果遇到电脑故障的时候,就完全束手无策了呢?其实并非如此,使电脑产生故障的原因虽然有很多,但是,只要我们细心观察,认真总结,我们还是可以掌握一些电脑故障的规律和处理办法的。在本期的小册子中,我们就将一些最为常见也是最为典型的电脑故障的诊断、维护方法展示给你,通过它,你就会发现——解决电脑故障方法就在你的身边,简单,但有效! 一、主板 主板是整个电脑的关键部件,在电脑起着至关重要的作用。如果主板产生故障将会影响到整个PC机系统的工作。下面,我们就一起来看看主板在使用过程中最常见的故障有哪些。 常见故障一:开机无显示 电脑开机无显示,首先我们要检查的就是是BIOS。主板的BIOS中储存着重要的硬件数据,同时BIOS也是主板中比较脆弱的部分,极易受到破坏,一旦受损就会导致系统无法运行,出现此类故障一般是因为主板BIOS被CIH病毒破坏造成(当然也不排除主板本身故障导致系统无法运行。)。一般BIOS被病毒破坏后硬盘里的数据将全部丢失,所以我们可以通过检测硬盘数据是否完好来判断BIOS是否被破坏,如果硬盘数据完好无损,那么还有三种原因会造成开机无显示的现象: 1. 因为主板扩展槽或扩展卡有问题,导致插上诸如声卡等扩展卡后主板没有响应而无显示。 2. 免跳线主板在CMOS里设置的CPU频率不对,也可能会引发不显示故障,对此,只要清除CMOS即可予以解决。清除CMOS的跳线一般在主板的锂电池附近,其默认位置一般为1、2短路,只要将其改跳为2、3短路几秒种即可解决问题,对于以前的老主板如若用户找不到该跳线,只要将电池取下,待开机显示进入CMOS设置后再关机,将电池上上去亦达到CMOS放电之目的。 3. 主板无法识别内存、内存损坏或者内存不匹配也会导致开机无显示的故障。某些老的主板比较挑剔内存,一旦插上主板无法识别的内存,主板就无法启动,甚至某些主板不给你任何故障提示(鸣叫)。当然也有的时候为了扩充内存以提高系统性能,结果插上不同品牌、类型的内存同样会导致此类故障的出现,因此在检修时,应多加注意。 对于主板BIOS被破坏的故障,我们可以插上ISA显卡看有无显示(如有提示,可按提示步骤操作即可。),倘若没有开机画面,你可以自己做一张自动更新BIOS的软盘,重新刷新BIOS,但有的主板BIOS被破坏后,软驱根本就不工作,此时,可尝试用热插拔法加以解决(我曾经尝试过,只要BIOS相同,在同级别的主板中都可以成功烧录。)。但采用热插拔除需要相同的BIOS外还可能会导致主板部分元件损坏,所以可靠的方法是用写码器将BIOS更新文件写入BIOS里面(可找有此服务的电脑商解决比较安全)。 常见故障二:CMOS设置不能保存 此类故障一般是由于主板电池电压不足造成,对此予以更换即可,但有的主板电池更换后同样不能解决问题,此时有两种可能: 1. 主板电路问题,对此要找专业人员维修; 2. 主板CMOS跳线问题,有时候因为错误的将主板上的CMOS跳线设为清除选项,或者设置成外接电池,使得CMOS数据无法保存。 常见故障三:在Windows下安装主板驱动程序后出现死机或光驱读盘速度变慢的现象 在一些杂牌主板上有时会出现此类现象,将主板驱动程序装完后,重新启动计算机不能以正常模式进入Windows 98桌面,而且该驱动程序在Windows 98下不能被卸载。如果出现这种情况,建议找到最新的驱动重新安装,问题一般都能够解决,如果实在不行,就只能重新安装系统。 常见故障四:安装Windows或启动Windows时鼠标不可用 出现此类故障的软件原因一般是由于CMOS设置错误引起的。在CMOS设置的电源管理栏有一项modem use IRQ项目,他的选项分别为3、4、5......、NA,一般它的默认选项为3,将其设置为3以外的中断项即可。 常见故障五:电脑频繁死机,在进行CMOS设置时也会出现死机现象 在CMOS里发生死机现象,一般为主板或CPU有问题,如若按下法不能解决故障,那就只有更换主板或CPU了。

变压器的日常运行维护

变压器的日常运行维护 对运行中的变压器要按规定进行巡视检查,监视运行情况,严格掌握运行标准,保证安全运行。 1、运行标准 (1)允许温度根据新厂目前投入运行的一台1600KV A干式变压器这两年运行情况来看,夏季最高负荷时:电流在2100安培时,温度在105度左右,变压器运行正常,而干式变压器允许温度 一般不宜超过110度,最高不得超过120度。 (2)允许负荷变压器运行中的负荷应该在额定容量一下,也就是变压器的视在功率。变压器一般不应超过额定容量运行,但允许 正常过负荷运行,过负荷运行时不能超过变压器容量的10%,而且要注意温升。 (3)变压器三相不平衡负荷当三相不平衡时应该监视最大一相的电流,当发现三相电流严重不平衡时应及时进行调节单相用电 设备负荷的平均分配。 (4)允许波动电压变压器电源电压一般不得超过额定值的5%,也就是10KV线路电压不得超过10.5KV,不得低于9.5KV。 2、变压器维护 (1)值班人员应该根据电压表、电流表、温度表指示,监视变压器的运行负荷情况,发现异常情况及时上报。 (2)夏季负荷高峰时期要加强对变压器负荷电流、温度的巡视监测,经常查看冷却风扇的运行情况,发现异常及时解决处理。

(3)监视运行中的声音是否正常。 (4)定期查看变压器引线接头、电缆、母线等处有无过热氧化腐蚀。(5)每年遇到外网停电时,要对变压器室内顶部和底部循环风口进行吸尘,保证风口的畅通。用抹布擦拭绕组浇注体外表灰尘,且查看绕组浇注体有无裂纹和表面过热损坏。查看变压器绕组的底角固定螺丝有无松动。 (6)正常运行时尽量避免打开变压器室的前后门,防止小动物(如小鸟、老鼠等)进入变压器室造成事故。 (7)经常打扫变压器室周围环境卫生,不得放置任何物体在变压器周围。 (8)经常查看变压器室下方的电缆沟里是否有积水,造成变压器运行环境潮湿,发现后及时处理,避免变压器绕组吸潮。

干式变压器检修维护手册

中广核太阳能光伏电站干式变压器 检修维护手册 一、干式变压器的作用及意义 干式变压器是光伏电站中重要的电气设备,光伏方阵中的干式变压器在电站发电期间,它将逆变器所发交流电升压为一定电压等级的交流电,送至电站汇集升压站;而在逆变器待机状态下,它将电网与逆变器进行有效的电气连接,为逆变器检测电网信号(部分干变作为逆变器电源),提供有效介质途径。 此外,电站站用变压器绝大多数也采用干式变压器,为电站生产、生活用电提供可靠的电源保障,因此保障干式变压器安全、稳定、可靠运行是光伏电站运维的一项重要任务。 二、干式变压器的结构及技术参数 公司大多投产及新建电站的干式变压器多为明珠电气及特变电工生产,具体结构可参考如下结构图。

以青铜峡光伏电站为例,干变主要技术参数如下表所示。 该型号干变过负荷能力如下表所示:

环境温度为20℃时过负荷能力曲线如下: 三、干式变压器投运前的运维 1、干变投运前的本体检查 检查所有紧固件、连接件是否松动,并重新紧固一边。 检查运输时拆下的零部件是否重新安装妥当(对照干变安装手册及施工图),并检查变压器是否有异物存在,特别是变压器底部冷却器及下垫块。 检查风机、温度控制器、温度显示仪及其他附件能否正常运行工作(特别是温控器接线勿在干变本体缠绕)。 检查干变本机、附件及箱体清洁无杂物。 2、干变投运前的试验 测量所有分接下的电压比,连接组别。最大电压比误差应小于0.5%。 线圈绝缘电阻的测试:一般情况下(温度20~40℃,湿度90%),高压对低压及地≥300MΩ,低压对高压及地≥100MΩ(2500V兆欧表测量)。但是如果变压器遭受异常潮湿发生凝露现象,则无论其绝缘电阻如何,在其进行耐压试验

(推荐)变压器的日常巡视规定

变压器的日常巡视应符合下列规定 1、日常巡视每天应至少一次,夜间巡视每周应至少一次。 2、下列情况应增加巡视检查次数: 1)、首次投运或检修、改造后投运72h内。 2)、气象突变(如雷云、大风、大雾、大雪、冰雹、寒潮等)时。 3)、高温季节、高峰负载期间。 4)、变压器过载运行时。 3、变压器日常巡视检查应包括以下内容: 1)、油温应正常,应无渗油、漏油,储油柜油位应与温度相对应。 2)、套管油位应正常,套管外部应无破损裂纹、无严重油污、无放电痕迹及其它异常现象。 3)、变压器音响应正常。 4)、散热器各部位手感温度应相近,散热附件工作应正常。 5)、吸湿器应完好,吸附剂应干燥。 6)、引线接头、电缆、母线应无发热迹象。 7)、压力释放器、安全气道及防爆膜应完好无损。 8)、分接开关的分接位置及电源指示应正常。 9)、气体继电器内应无气体。 10)、各控制箱和二次端子箱应关严,无受潮。 11)、干式变压器的外表应无积污。

12)、变压器室不漏水,门、窗、照明应完好,通风良好,温度正常。 如何做好配电变压器的巡视检查 配电变压器在运行中常常会因运行维护不当造成设备事故,如果运行人员定期通过看、听、闻手段对设备进行巡视检查,可以及时发现设备的缺陷,从而把设备故障处理在萌芽状态,避免出现设备事故。 1、看,主要为观察配电变压器外观 1)、看油位计:油位应在油标刻度的1/4~3/4以内(气温高时,油面在上限侧;气温低时,油面在下限侧)。油面过低,应检查是否漏油。若漏油应停电检修,若不漏油应加油至规定油位。加油时,应注意油标刻度上标出的温度值,根据当时气温,把油加至适当位置。 2)、看配变套管:看套管表面是否清洁,有无裂纹、碰伤和放电痕迹。表面清洁是套管保持绝缘强度的先决条件。当套管表面沉积有灰尘、煤灰及盐雾时,遇到阴雨天或雾天,便会沾上水分容易引起套管的闪络放电,因此应定期予以清扫。套管由于碰撞或放电等原因产生裂纹伤痕,也会使绝缘强度下降,造成放电。因此对有裂纹或碰伤的套管应及时更换。 3)、看配变箱体外表:主要看配变运行中是否渗漏油。一是由于配变箱体的焊接缺陷造成油渗漏,可采取环氧树脂粘合剂堵塞。二是由于长期运行造成密封垫圈老化,引起渗漏,应更换密封垫圈。特别是低压侧出线套管,往往由于接线端接触不良、过负荷等原因造成过热,使密封垫变质,起不到密封作用,导致漏油。

常见问题及解决方法

重庆电子招投标常见问题

目录 一、常见问题说明 (3) 二、投标人注意事项 (6) 1、投标函 (6) 2、导入word目录乱的问题 (6) 3、资格标制作 (7) 4、技术标 (7) 5、填报“清单数据”中分部分项清单综合单价与综合合价 (7) 5、填报措施项目费 (9) 6、填报主要材料 (9) 三、招标人注意事项 (10) 1、填写项目基本信息 (10) 2、模版的应用 (10) 3、清单数据 (10) 4、添加补遗、答疑或者最高限价文件 (12) 五、标盾使用说明 (12) 六、开标 (13)

一、常见问题说明 《金润电子标书生成器》软件需安装在Windows Xp系统上,暂不支持Vista和Win7系统,安装时不能插入任何加密锁,同时关闭所有杀毒软件和防火墙 1、安装了“重庆电子标书生成器(重庆)”,导入标书一闪而过,却没有导入任何文件? 答:金润电子标书生成器没有正确安装,若安装正常可在“打印机和传真”看到“金润电子标书生成器”的虚拟打印机,如下图: 解决方法:A:运行以下命令安装打印机不包含引号 “C:\WINDOWS\system32\BJPrinter\PrinterSet.exe”,点击“安装打印机”,如(图一)。此后如弹出提示框都选择继续、信任、通过等按钮,如(图二):倘若被阻止则程序安装不完整,电子标书生成器软件无法正常使用。 图一图二 或者 B:卸载金润电子标书生成器并且重新安装。 2、安装了“重庆电子标书生成器(重庆)”,却无法双击打开或者报错? 答:金润软件相关程序可能被防火墙或者杀毒软件默认阻止了。 解决方法:查看杀毒防护软件,在阻止列表将其设为信任,以360安全卫士为例

变压器的日常维护

变压器的日常维护 3.1 安装及运行。 (1)变压器的安装地点应与其设计和建造的标准相适应。若置于户外,应确定该变压器适于户外运行。 (2)保护变压器不受雷击及外部损坏危险。(3)确保负荷在变压器的设计允许范围之内。严防出现小马拉大车的现象。(4)在油冷变压器中需要仔细地监视顶层油温。(5)平时在运行操作中,应严格按照运行操作规程执行,严防出现误操作。(6)在操作变压器的解、并运行过程中,一定要按变压器解、并列的“三要素”进行,严防出现操作过电压。(7)平时应对变压器进行经常检查和巡视,发现问题应及时处理。 3.2 对油的检验。 变压器油的介电强度随着其中水分的增加而急剧下降。油中万分之一的水份就可使其介电强度降低近一半。除小型配电变压器外所有变压器的油样应经常作击穿试验,以确保正确地检测水分并通过过滤将其去除。应进行油中故障气体的分析。应用变压器油中8 种故障气体在线监测仪,连续测定随着变压器中故障的发展而溶解于油中气体的含量,通过对气体类别及含量的分析则可确定故障的类型。每年都应作油的物理性能试验以确定其绝缘性能,试验包括介质的击穿强度、酸度、界面张力等等。 3.3 经常维护。 (1)保持瓷套管及绝缘子的清洁。(2)保证电气连接的紧固可靠。(3)定期检查分接开关。并检验触头的紧固、灼伤、疤痕、转动灵活性及接触的定位。(4)在油冷却系统中,检查散热器有无渗漏、生锈、污垢淤积以及任何限制油自由流动的机械损伤。(5)每年检验避雷器接地的可靠性。接地必须可靠,而引线应尽可能短。旱季应检测接地电阻,其值不应超过4Ω。(6)每三年应对变压器线圈、套管以及避雷器进行介损的检测。 4 结论 变压器是电网中的重要设备之一。虽配有避雷器、差动、接地等多重保护,但由于内部结构杂、电场及热场不均等诸多因素,维护不当事故仍然会发生。经常对设备进行检测,并加强日常的维护和保养,会对电力设备起到极其重要的作用,从而使电力供应更加安全可靠。 此文章来源:中国电器交易网

干式变压器日常检查维护作业规定.docx

干式变压器日常检查维护作业规定 1 适用范围 1.1 本规定适用于容量为6300KVA及以下,电压为35KV及以下的干式变压器日常检查维护作业及安全操作规范。 1.2 适用人员:已经过培训并取得有效电工证操作手、修理工和专业维修保养作业人员。 2 规范性引用文件 GB1094.11-2007 干式电力变压器 GB/T10228-1997 干式电力变压器技术参数和要求 3 现场责任 3.1 电工(修理工)是执行本规定的第一责任人。 3.2 电工(修理工)对设备安全操作及日常检查维护的全面性、故障或故障隐患报告的及时性以及发现与处理故障或故障隐患后所采取措施的及时有效性负有责任。在日常检查维护、操作过程中发现设备存在故障或故障隐患,应及时报分公司设备主管。 3.3 分公司设备主管对故障处理、故障信息及时上报负有责任。在接到电工(修理工)上报的故障或故障隐患后,分公司设备主管应根据故障性质及时采取有效防范和修复措施,防止故障进一步扩大,对不能处理的故障或故障隐患,应及时上报分公司主管领导。 3.4 分公司主管领导对设备主管上报的故障或故障隐患处理的组织和最终结果负有责任。在接到设备主管报告的设备故障信息后,应根据故障性质采取及时有效的防范措施,并积极组织故障修复,不得强令

设备带病运转。 3.5 分公司电工(修理工)应对故障维修的质量、二级保养作业的全面性、对号率负责。否则,因维修质量或保养不到位造成设备非正常损坏、磨损或机械事故的,电工(修理工)应承担相应的责任。 3.6 分公司设备主管应至少每周对整个分公司设备进行一次巡检,对电工(修理工)依据本规定进行的安全使用及日常检查维护作业情况进行检查并在《日常检查维护记录表》上签字确认。 3.7 公司设备与物资管理部应至少每半年对所管辖设备进行一次巡检,对电工(修理工)依据本规定进行的安全使用及日常检查维护作业情况进行检查。 3.8 电工(修理工)在日常检查维护、操作过程中发现设备存在安全隐患,应及时报分公司设备主管。分公司设备主管在接到报告的设备安全隐患信息后,根据设备安全隐患性质采取及时有效的防范措施,并积极组织排除安全隐患,如隐患性质为重大安全隐患的须报现场安全员统一处理。 4 本规定执行要求 4.1 本规定及所附《日常检查维护记录表》应随机携带,用完后交分公司设备主管保管存档,上级部门检查时提供查阅。分公司设备主管每月将设备使用及检查维护情况上报公司设备与物资管理部。 4.2 本规定所要求的日常检查维护项目,由电工(修理工)在当日设备作业前进行逐项检查和维护。当日设备不运转,可不进行检查和维护作业。分公司停工期间进行的设备检查和维护作业,也应按本规定

浅谈变压器的瓦斯保护及其日常维护注意事项(标准版)

Safety is the goal, prevention is the means, and achieving or realizing the goal of safety is the basic connotation of safety prevention. (安全管理) 单位:___________________ 姓名:___________________ 日期:___________________ 浅谈变压器的瓦斯保护及其日常维护注意事项(标准版)

浅谈变压器的瓦斯保护及其日常维护注意事 项(标准版) 导语:做好准备和保护,以应付攻击或者避免受害,从而使被保护对象处于没有危险、不受侵害、不出现事故的安全状态。显而易见,安全是目的,防范是手段,通过防范的手段达到或实现安全的目的,就是安全防范的基本内涵。 变压器是用来改变交流电压大小的电气设备,在电力系统和供用电系统中占有极其重要的地位。目前在我国电力系统中大量普及使用油浸式变压器,保护变压器的安全运行也自然成为供电部门的重点工作,而瓦斯保护就是确保油浸式变压器安全运行的有效技术措施之一。瓦斯保护的主要优点是动作迅速、灵敏度高、安装接线简单、能反映油箱内部发生的各种故障。在我局的安装规程中规定“800KVA及以上油浸式变压器必须设有瓦斯保护”。 一、瓦斯保护的基本工作原理 (1)瓦斯保护的基本工作原理 当在变压器油箱内部发生故障(包括轻微的匝间短路和绝缘破坏引起的经电弧电阻的接地短路)时,由于故障点电流和电弧的作用,将使变压器油(通常为25#绝缘油)及其它绝缘材料因局部受热而分解产生气体,因气体比较轻,它们将从油箱流向油枕的上部。当故障严

干式变压器运行维护保养规范

干式变压器运行维护保养规范

1.检查与准备 1.1根据维护保养需要下达ERP工单后开始相关工作。 1.2上报调度人员并填写PPS维检修作业计划,经同意后开展相关工作。 1.3工器具及备品备件 序号名称规格型号数量备注一工器具 1红外线测温仪UT302C1台 2钳形万用表FLUKE3171块 3电工组合工具成套1套 二材料 1绝缘胶带1卷 2抹布若干 3硅胶变色硅胶1瓶 4保险根据需要若干 三安全防护器具 1手提干粉式灭火器1具 2安全警戒带1卷 3急救药箱1套 4绝缘手套1套 5电工安全帽1个 表1工器具及备品备件 2.操作 2.1日常巡视检查 2.1.1检查变压器的各温度表计指示正常,风机运转正常。 变压器运行温度达到以100o C,风机起动;运行温度达到80o C时,停止风机;变压器的运行温度达到130o C时,输出报警信号;运行温度达到155o C,输出跳闸信号。常巡视检查中,必须注意观察温控器的变化,且保持有较畅通的风道,加强

空气介质的流通,若发现某一相温度显示值变化显著,与其它两相相差较大,说明干式变压器温升不正常。 2.1.2绝缘阻值 值班人员应经常注意干式变压器浇注树脂及支撑线圈的垫块是否有变色和开裂现象,变压器运行若干年(建议五年)后进行绝缘电阻(阻值≥2M?/Km,若低于这个阻值则不能运行)的测试来判断变压器能否运行,一般无需进行其它测试。 2.1.3辨别声音 巡检中要仔细辨别变压器发出的声音,干式变压器正常运行发出连续均匀的"嗡嗡"声,如果发出以下声音则说明变压器出现了问题。 2.2变压器的清扫(春检期间) 2.2.1工作地点范围设置遮拦(警戒带)、四周悬挂警示牌,防止非工作人员进入; 2.2.2戴绝缘手套使用验电器检验确定无电压,装设接地线; 2.2.3对变压器高、低压端逐相进行充分放电; 2.2.4擦拭母线上的灰尘及瓷瓶上的污渍; 2.2.5清扫风机外壳,确定壳体内外无异物; 2.2.6对锈蚀部位进行除锈、刷漆处理; 2.2.7完成清扫后,恢复现场。