Universal Measuring Device
UMG96S
Operating instructions
Brief instructions see last page
low rate/supply
L1-N / L1-L2L2-N / L2-L3L3-N / L3-L1
Programming mode Sum measurement L - L
Password
Voltage transformer Current transformer Output 1Output 2
D o k N r . 1.028.027.d F i r m w a r e R e l. 1.09
Janitza electronics GmbH Vor dem Polstück 1D-35633 Lahnau
Support Tel. (0 64 41) 9642-22Fax (0 64 41) 9642-30e-mail: info@janitza.de
Internet: http://www.janitza.de
high rate/Con-sumption
A r t .N r .: 33.03.046
Page 2Contents
Meaning of the symbols4 Hints for usage4 Receipt control4 Contents of delivery5 Accessories possible5 Hints for maintenance6 Repairing and calibration6
Face plate6
Battery6
Waste management6 Service6 Product description7 Intended use7 Functional description8 Voltage versions9 Device versions10 Installation18 Mounting18 Measurement and operation voltage18 Current measurement19 Sum current measurement19 Serial interfaces20 Inputs and outputs20 Connection22 Putting into service24 Insert device24
Connect measur. and operating voltage24
Connect measurement current25
Check phase assignment25
Check current direction25
Check measurement25
Check single phase power25
Check sum power25 Removal of errors26 Error messages28 Warnings29 Heavy errors29 Exceeding of measuring range29 Usage and display30 Indication mode30 Programming mode30 Key functions31Parameters and meas. values32 Parameter indication at UMG96S32
Measured value indication at UMG96S32 Program parameters33 Mean values34
Averaging time current (Adr.057)34
Averaging time power (Adr.058)34
Averaging time voltage (Adr.073)34
Minimum and maximum values34
Net frequency (Adr.063)35
Real energy35
Current transformer (Addr. 600)36
Voltage transformer (Addr. 602)37
Harmonics (Addr.221)38
Measured value rotation39
Measured value indications42
Indication profile (Addr. 060)42
Indication profile (Addr. 604)43
User password (Addr.011)44
Delete energy (Addr.009)44
Field rotation (Addr. 277)45
LCD Contrast (Addr. 012)45
Time detection46
Serial number (Addr. 911)46
Software Release (Addr. 913)47
Hardware expansion (Addr. 914)47 Serial interfaces48 Interface selection (Addr. 062)48
Modem operation (Addr. 070)48 MODBUS RTU49 Realized functions49 RS232 interface50 Fieldbus (RS485)52 Profibus DP54 Profibus profiles56 Inputs and outputs60 Pulse output62
Pulse valence63
Digital output66 Limit supervision68 Analog output70
Digital input72 Memory74 Data memory (Option)74
Data memory (056)74
Page 3
Tables
76
Parameter list
77Measured value list
80Measured value displays, overview 86Indication range and accuracy 90Safety regulations
91Requirements of electromagnetical compatibility
91
Technical data
92
Ambient conditions 92Connectable wires 92Inputs and outputs 92Measurement 93Serial interfaces 93Dimension sketch 94Connection diagrams
95
Brief instructions
96
Change current transformer 96Call up measured values
96
Issue note
22.04.2003 First edition.08.11.2004 Completions.02.08.2005 Completions.08.10.2007 Profibus profiles.
11.01.2008 Page 56, Profibus profiles.16.04.2009 Completions.
All rights reserved. No part of this manual may be reproduced or duplicated without the written permission of the author. Any contraventions are punishable and will be prosecuted with all legal means.
No liability can be taken for the faultless condi-tion of the manual or damage caused by the use of it. As failures cannot be avoided completely,we shall be very grateful for any advice. We will try to remove any failures as soon as possible.The mentioned software and hardware descriptions are registered trademarks in the most cases and are subjected to the regulations by law. All registered trademarks are property of the corresponding companies and are fully recognized by us.
Page 4
Receipt control
In order to ensure a perfect and safe use of the device, a proper transport, expert storage, erec-tion and mounting and careful usage and main-tenance are required. When it may be sup-posed, that a safe operation is no longer possi-ble, the device has to be put out of service and be protected against unintentional putting into service.
A safe operation can no longer be assumed,when the device
? shows visible damage,
? does not work in spite of intact net supply,? has been exposed to disadvantageous condi-tions for a longer time (e.g. storage out of the allowed climate without adaption to the room climate, dew etc.) or transport use (e.g. falling from great height, even without visible damage).
Please test the contents of delivery for comple-tion, before starting the installation of the device.All delivered options are listed on the delivery papers.
Hints for usage
This device may be put into service and used by qualified personnel according to the safety regulations and instructions only. Please mind the additional legal and safety regulations for the respective application.
Qualified personnel are persons, familiar with erection, mounting, putting into service and us-age of the product and having the qualifications such as:
? education or instruction / entitlement to switch,release, ground or characterize current circuits and devices according to the standards of safety techniques.
? education or instruction in care and usage of suitable safety equipment according to the standards of safety techniques.
?
Attention!
If the instrument is not used according to the operating instructions, a safe use can-not be granted, and certain danger can be effected by the instrument.
?
?Beware dangerous electrical voltage.
This symbol shall warn you about possi-ble danger, that can occur while mount-ing, putting into service or the use of this instrument.
Meaning of the symbols
The symbols, that were used in this manual have the following meaning:
Page 5
This manual also describes options,which have not been delivered and,hence, do not belong to the contents of delivery.
?
Part no. see delivery note.
Contents of delivery
Accessories possible
All delivered options and versions are described on the delivery papers.?
Page 6Service
If you have problems, which are not described in this manual, please ask our technical support. For further handling of your questions, please have the following on hand:
- Device description (see type plate),
- Serial number (see type plate),
- Software Release,
- Measurement and auxiliary voltage and
- Exact description of the problem.
Y ou can contact us:
Monday to Thursday
between 07:00h and 15:00h
and Friday
between 07:00h and 12:00h
Janitza electronic GmbH
Vor dem Polstück 1
D-35633 Lahnau
Support:Tel.(0 64 41) 9642-22
Fax(0 64 41) 9642-30
e-mail: info@janitza.de
Hints for maintenance
Before delivery the device is tested in various safety checks and marked with a seal. If the device is opened, these checks must be re-peated.
There is no guarantee for devices, which are opened out of the manufacturing works. Repairing and calibration
Maintenance and calibration can only be carried out at manufacturer's end.
Face plate
The cleaning of the front foil must be done with a soft cloth using a common cleansing agent. Acid or acidic agents may not be used for clean-ing.
Battery
On the additional PC B 1 (option), there is a Lithium battery. The life expectance of the bat-tery at storage temperature +45°C is a minimum of 5 years. The typical life expectance is between 8 and 10 years.
If the battery voltage is too low after net return, the display shows the warning "Err 320".
For safety reasons, the battery should be ex-changed in the manufacturing works only! Waste management
The UMG96S can be disposed and recycled as electronical waste according to the legal regu-lations. Please note, that the input Lithium bat-tery must be disposed separately.
Page 7
Product description
Intended use
The UMG96S has been designed for a fixed in-stallation in panels, measuring voltage, current,power etc. in low voltage switchgear. The meas-urement is laid out for three phase systems with neutral conductor (TN and TT networks).
The UMG96S gets its operating voltage from the measuring voltage and can be delivered for operating voltage of 150V and 300V . The 300V standard version, measurement and operation voltage (50Hz/60Hz) up to 300VAC against ground and 520VAC phase to phase can be connected directly. The 150V special version,measurement and operating voltage (50Hz/60Hz) up to 150VAC against ground and 240VAC phase to phase can be connected di-rectly.
The measurement and operational voltage must be connected to the UMG96S via a separation (circuit breaker or power switch) and a fuse (2-10A) within the installation. The separation (circuit breaker or power switch) must be near to the instrument and easy to reach.
The connection of the measurement and oper-ating voltage is carried out on the backside of the UMG96S via touch proof spring terminal. To the current inputs, either .../5A or .../1A trans-formers can be connected.
Attention!
Measurement in systems with pulse load is not possible, because no continuous scanning of the measuring signals is car-ried out.
?Attention!
The inputs, outputs and serial interfaces must be shielded.
?
Attention!
The connection of the neutral conductor N is absolutely neccessary.
?
Page 8
Functional description
The three phase electronic measuring system detects and digitizes the true rms values of al-ternating voltage and current in 50/60Hz net-works.
The operating voltage of the UMG96S is taken from the measuring voltage L1-N, L2-N and L3-N. Devices for the measurement in 230V/400V networks, at least one phase must be within the rated range. Instruments for measurement in 58V/100V or 63V/110V networks, at least two phases must be within the rated voltage range.Either .../5A or .../1A transformers can be con-nected to the current inputs. In networks with 150VAC against ground, currents up to 5A can be connected directly to the UMG96S.
Each second, one sample measurement is car-ried out at all current and voltage inputs. Volt-age interruptions longer than one second are safely recognized. For each sample, 6 periods are scanned. From these values, the inserted microprocessor calculates the electrical quanti-ties. The measured values can be indicated in the measured value displays. The energy and minimum and maximum values as well as the programming data are stored every 5 minutes in a none volatile memory (EEPROM).
The scanning frequency for all measuring inputs is calculated from the net frequency of phase L1. For a net frequency of 50Hz, the scanning frequency is 2.5kHz and for a net frequency of 60Hz, the scanning frequency is 3.0kHz. If voltage in L1 is smaller than 50V , the UMG96S uses the last measured net frequency for the calculation of the scanning frequency.
Diagr. Generation of the operating voltage,300V standard version.
Diagr. Generation of the operating voltage,150V special version.
Page 9
Voltage versions
The UMG96S takes the measurement voltage as operating voltage and can be delivered in the versions 150V and 300V . The delivered version is indicated on the type plate of UMG96S.Please ensure, that the local net conditions match the numbers on type plate before con-nection.
300V standard version
In 300V standard version , the UMG96S can measure voltage up to 300VAC against ground.At leats one phase (L) of the UMG96S and the neutral N must be connected and the connected voltage must be within the measurement and operation voltage range.
The measurement and operation voltage range of devices without additional PCB and for devices with additional PCB 1 (analogue output)are:
Measuring range L-N : 50 .. 300V AC Measuring range L-L : 87 .. 520V AC Operating voltage range L-N : 85 .. 300V AC The measurement and operating voltage range for devices with additional PCB 2 (Profibus) are:Measuring range L-N : 50 .. 300V AC Measuring range L-L : 87 .. 520V AC Operating voltage range L-N :140.. 300V AC
150V special version
In 150V special version, the UMG96S can measure voltage up to 300VAC against ground.At least 2 phases (L) of the UMG96S must be connected, and the connected voltage must be within the measurement and operation voltage range.
Measuring range L-N : 25 .. 140V AC Measuring range L-L
: 40 .. 260V AC Operating voltage range L-L
: 85 .. 260V AC
Attention!
Voltage, which is above the allowed range can damage the device.
?
The operating voltage for the unit is taken from the outer conductors.?
Page 10
Device versions
The UMG96S can be delivered in different ver-sions. The customer can assign a function to the clamps 11, 12 and 13 of UMG96S.Version 1
Version 1 contains the following functional groups:
RS485 (MODBUS RTU) Input/Output
Pulse output 1 (Wp=real energy)Pulse output 2 (Wq=reactive energy)Digital output 1
Digital output 2
UMG96S
Basic PCB
R S 485
Current measurement 1514131211
10
8
791324
6
5 I / O
Measurement and operating voltage
Art.Nr.52.13.00152.13.00252.13.00352.13.004
Page 11
Version 2
Version 2 contains the following functional groups:
RS232 (MODBUS RTU) RS485 (MODBUS RTU) Input/Output
Pulse output 1 (Wp=real energy)Pulse output 2 (Wq=reactive energy)Digital output 1
Digital output 2
UMG96S
Basic PCB
RS232
R S 485
Current measurement
1514131211
10
8
791
324
6
5 I / O
Measurement and operating voltage
Art.Nr.52.13.00552.13.00652.13.00752.13.008
Page 12
Version 3
Version 3 contains the following functional groups:
RS232 (MODBUS RTU) RS485 (MODBUS RTU) Input/Output
Pulse output 1 (Wp=real energy)Pulse output 2 (Wq=reactive energy)Digital output 1Digital output 2Clock with battery
Data memory
UMG96S
Basic PCB
Page 13
Version 4
Version 4 contains the following functional groups:
RS232 (MODBUS RTU) RS485 (MODBUS RTU) Input/Output
Pulse output 1 (Wp=real energy)Pulse output 2 (Wq=reactive energy)Digital output 1Digital output 2Analog output 1
Analog output 2
UMG96S
Basic PCB
Page 14
Version 5
Version 5 contains the following functional groups:
RS232 (MODBUS RTU) RS485 (MODBUS RTU) Input/Output
Pulse output 1 (Wp=real energy)Pulse output 2 (Wq=reactive energy)Digital output 1Digital output 2Analog output 1Analog output 2
Clock with battery
Data memory
UMG96S
Basic PCB
Page 15
Version 6
Version 6 contains the following functional groups:
RS232 (MODBUS RTU) RS485 (MODBUS RTU) Input/Output
Pulse output 1 (Wp=real energy)Pulse output 2 (Wq=reactive energy)Digital output 1Digital output 2Digital input 1Digital input 2
UMG96S
Page 16
Version 7
Version 7 contains the following functional groups:
RS232 (MODBUS RTU) RS485 (MODBUS RTU) Profibus DP Input/Output
Pulse output 1 (Wp=real energy)Pulse output 2 (Wq=reactive energy)Digital output 1Digital output 2Digital input 1Digital input 2
UMG96S
Page 17
Page 18
Installation
Mounting
The UMG96S is designed for a fix installation in low and medium voltage systems. The mount-ing position is random.
Measurement and operation voltage
The UMG96S gets its operating voltage from the measuring voltage. The measurement is designed for three phase systems with neutral conductor (TN and TT networks). The measure-ment and operational voltage must be con-nected to the UMG96S via a separation (circuit breaker or power switch) and a fuse (2-10A)within the installation. The connection of the measurement and operating voltage is carried out on the backside of the UMG96S via touch proof spring terminal.
300V standard version
At least one phase (L) of the UMG96S and the neutral N must be connected and the connected voltage must be within the measurement and operation voltage range.
The measurement and operation voltage range of devices without additional PCB and for devices with additional PCB 1 (analogue output)are:
L-N 85 .. 300V L-L 148 .. 520V
The measurement and operating voltage range for devices with additional PC B 2(Profibus) are:
L-N 140 .. 300V L-L 242 .. 520V 150V special version
At least 2 phases (L) of the UMG96S must be connected, and the connected voltage must be within the measurement and operation voltage range.
The measurement and operating voltage range is:
L-N 50 .. 150V L-L 85 .. 260V
Attention!
Before connecting voltage, the device should be deposited in the preposed in-stallation room for at least 2 hours, in order to create a temperature equaliza-tion and avoid humidity or dew within the instrument.
?
Attention!
The limits, mentioned under "technical data" may not be exceeded, even not during checking or putting into service of UMG96S.
?- The used cables must be suitable for a rated voltage of 300VAC against ground.
- The measurement and operating voltage must be protected by a fuse. The fuse must be in the range of 2A to 10A .
- Please provide a circuit breaker or power switch for the operating voltage.
- The switch must be near the UMG96S and easy to reach.
- The switch must be marked as a separation for this instrument.
Page 19
Sum current measurement
If the current measurement is carried out via two current transformers and a sum current trans-former, the total transformer ratio must be programmed at UMG96S.
Example: Sum current transformer
A current measurement is carried out via one ct with a ratio of 1000/5A and one ct with a ratio of 1000/5A. The current measurement is carried out via a sum current transformer 5+5/5A.
The UMG96S must be programmed as follows:Primary current: 1000A + 1000A = 2000A Secondary current: 5A
Verbraucher 1
Consumer 1
Verbraucher 1 Consumer 1Einspeisung 1 Supply 1
Einspeisung 1 Supply 1
UMG96S
L l K k
L l K k
AK AL K l k l
BK Bl
Current measurement
The current measurement is carried out via cur-rent transformers of either ../5A or ../1A. If the current must be measured by an Amperemeter additionally, it must be connected in series to the UMG96S.
In networks with voltage up to 150VAC against ground, currents up to 5A can be connected di-rectly to the UMG96S.
L l K k A
l k
UMG96S
Verbraucher Consumer
Einspeisung Supply
Attention!
The secondary connections of the current transformer must be short-circuited, be-fore the wires that lead to the device are interrupted!
If a testing switch is available, which short-circuits the secondaries of the cts automatically, it is sufficient to set it into position "check", provided that the short-circuiters have been checked before.
?
Page 20
Serial interfaces
Depending on the version the UMG96S may have up to three serial interfaces. The serial in-terfaces are not separated galvanically.
The RS232 and RS485 cannot be operated at the same time!
If both interfaces are connected, the device rec-ognizes by the signal level, if an instrument is connected to the RS232. The data transmission is carried out via RS232 only.
If no device is recognized at RS232, data trans-mission is active on RS485 interface.
?Inputs and outputs
The UMG96S offers the possibility of assigning different functions to the outputs of the different versions (options).
Terminal 12, for example, can have the function "pulse output" and terminal 13 can have the function "digital input". Please note, that both circuits have a common supply +24VDC, termi-nal 11.
Only one function can be assigned to each ter-minal 12 and 13.
12
13
11
Input/Output 2
Pulse output Wq (003 =0)Digital output
(003 = 1)
Analog output(003 = 2)Digital input
(003 = 3,5)
Profibus-Remote (003 = 4)
Input/Output 1
Pulse output Wp (002 =0)Digital output
(002 = 1)
Analog output (002 = 2)Digital input
(002 = 3,5)
Profibus-Remote (002 = 4)Attention!
Real energy Wp is firmly assigned to puls output 1.
Reactive energy Wq is firmly assigned to puls output 2.
?
Diagr.: UMG 96S with one analogue and one digital output as pulse output for real energy.
The cable for serial data transmission must be performed in a shielded way, if the cable length is more but 30m or the cable leaves a building.