屋面支撑计算书

1.参考规范

《GB 50017-2003 钢结构设计规范》

《GB 50009-2001 建筑结构荷载规范》

《CECS 102:2002 门式钢架轻型钢结构设计规程》

2.构件几何信息

计算简图如下图所示

截面特性:

支撑采用直径22张紧圆钢 A e=303.4 mm2

刚性系杆采用:

中柱Φ140x4.0电焊钢管(b类):A = 1709mm2 ;i = 48.1mm ;λ = 145.5

边柱Φ114x4.0电焊钢管(b类):A = 1382mm2 ;i = 29.9mm ;λ = 179.9

3.材料特性

材料牌号:Q235B

屈服强度f y:235.0 MPa

抗拉强度设计值f:215.0 MPa

弹性模量E:2.06x105 MPa

4.荷载信息

风荷载:基本风压W0 = 0.65 kN/m2

地面粗糙度:B类

风载体型系数μs: +1.0

高度变化系数μz: 1.0

风荷载标准值:1.05μsμz W0=1.05x1.0 x1.0 x 0.65 = 0.6825 kN/m2

风荷载设计值:1.4x0.6825=0.9555kN/m2

作用在桁架上荷载设计值:F=0.9555x6x10.2/2=29.22 kN

5.内力计算

按水平放置的桁架计算

支撑最大内力N = 57.73kN

中柱柱顶系杆内力 N = -116.89N

边柱柱顶系杆内力N= -58.45kN

支撑采用带张紧装置的圆钢,不受长细比控制。

刚性系杆为受压杆件,容许长细比为220。

6.构件验算

6.1斜支撑:

强度验算: N A

=57.72x103 /303.4=190.2 MPa < 215 MPa 满足 6.2刚性系杆:

6.2.1中柱系杆

长细比:λ = 145.5< 220 满足

轴心压杆稳定系数:?= 0.324

N A

?=116.89x103 /(0.324x1709)=210.9MPa < 215 MPa 满足 6.2.2边柱系杆

长细比:λ = 179.9< 220 满足

轴心压杆稳定系数:?= 0.225

N A

?=58.45x103 /(0.225x1382)=188.0MPa < 215 MPa 满足

梁,500×800梁木模板与支撑计算书

梁木模板与支撑计算书一、梁模板基本参数 梁截面宽度 B=500mm, 梁截面高度 H=800mm, H方向对拉螺栓1道,对拉螺栓直径14mm, 对拉螺栓在垂直于梁截面方向距离(即计算跨度)850mm。 梁模板使用的木方截面40×80mm, 梁模板截面侧面木方距离200mm。 梁底模面板厚度h=15mm,弹性模量E=6000N/mm2,抗弯强度[f]=15N/mm2。梁侧模面板厚度h=15mm,弹性模量E=6000N/mm2,抗弯强度[f]=15N/mm2。 二、梁模板荷载标准值计算 模板自重 = 0.200kN/m2; 钢筋自重 = 1.500kN/m3; 混凝土自重 = 24.000kN/m3; 施工荷载标准值 = 2.500kN/m2。

强度验算要考虑新浇混凝土侧压力和倾倒混凝土时产生的荷载设计值;挠度验算只考虑新浇混凝土侧压力产生荷载标准值。 新浇混凝土侧压力计算公式为下式中的较小值: 其中γc——混凝土的重力密度,取24.000kN/m3; t ——新浇混凝土的初凝时间,为0时(表示无资料)取200/(T+15),取3.000h; T ——混凝土的入模温度,取20.000℃; V ——混凝土的浇筑速度,取1.000m/h; H ——混凝土侧压力计算位置处至新浇混凝土顶面总高度,取1.200m; β——混凝土坍落度影响修正系数,取0.850。 根据公式计算的新浇混凝土侧压力标准值 F1=17.130kN/m2 考虑结构的重要性系数0.90,实际计算中采用新浇混凝土侧压力标准值: F1=0.90×17.140=15.426kN/m2 考虑结构的重要性系数0.90,倒混凝土时产生的荷载标准值: F2=0.90×6.000=5.400kN/m2。 三、梁底模板木楞计算 梁底木方的计算在脚手架梁底支撑计算中已经包含! 四、梁模板侧模计算 面板直接承受模板传递的荷载,应该按照均布荷载下的连续梁计算,计算如下 作用在梁侧模板的均布荷载q=(1.2×15.43+1.40×5.40)×0.80=20.857N/mm 面板的截面惯性矩I和截面抵抗矩W分别为: 本算例中,截面惯性矩I和截面抵抗矩W分别为: 截面抵抗矩 W = bh2/6 = 80.00×1.50×1.50/6 = 30.00cm3; 截面惯性矩 I = bh3/12 = 80.00×1.50×1.50×1.50/12 = 22.50cm4; 式中:b为板截面宽度,h为板截面高度。

盘扣式板模板支撑计算书

盘扣式模板支撑计算书 一、模板支架选型 由于其中模板支撑架高3.6米,为确保施工安全,编制本专项施工案。设计围包括:楼板,长*宽=8m*8m,厚0.25m。 根据本工程实际情况,结合施工单位现有施工条件,3#和4#楼地下室区域选择盘扣式钢管脚手架作为模板支架的搭设材料,进行相应的设计计算。 二、搭设案 (一)基本搭设参数 模板支架高H为3.6m,立杆步距h(上下水平杆轴线间的距离)取1.8m,立杆纵距l a取0.9m,横距l b取0.9m。立杆伸出顶层横向水平杆中心线至模板支撑点的自由长度a取0.2m。整个支架的简图如下所示。

模板底部的木,截面宽40mm,高80mm,布设间距0.2m。 (二)材料及荷载取值说明 本支撑架使用?48 *3mm钢管,钢管壁厚不得小于3mm,钢管上禁打;采用的扣件,应经试验,在螺栓拧紧扭力矩达65N·m时,不得发生破坏。 模板支架承受的荷载包括模板及支架自重、新浇混凝土自重、钢筋自重,以及施工人员及设备荷载、振捣混凝土时产生的荷载等。 三、板模板支架的强度、刚度及稳定性验算 荷载首先作用在板底模板上,按照"底模→底模木/钢管→横向水平钢管→可调托座→立杆→基础"的传力顺序,分别进行强度、刚度和稳定性验算。其中,取与底模木平行的向为纵向。 (一)板底模板的强度和刚度验算 模板按三跨连续梁计算,如图所示:

(1)荷载计算,按单位宽度折算为线荷载。此时, 模板的截面抵抗矩为:w=1000?72/6=4.82?04mm3; 模板自重标准值:x1=0.3? =0.3kN/m; 新浇混凝土自重标准值:x2=0.25?4? =6kN/m; 板中钢筋自重标准值:x3=0.25?.1? =0.275kN/m; 施工人员及设备活荷载标准值:x4=1? =1kN/m; 振捣混凝土时产生的荷载标准值:x5=2?=2kN/m。 以上1、2、3项为恒载,取分项系数1.35,4、5项为活载,取分项系数1.4,则底模的荷载设计值为: g1 =(x1+x2+x3)?.35=(0.3+6+0.275)?.35=8.876kN/m; q1 =(x4+x5)?.4=(1+2)?.4 =4.2kN/m; 对荷载分布进行最不利布置,最大弯矩取跨中弯矩和支座弯矩的较大值。 跨中最大弯矩计算简图

多高层钢结构住宅楼毕业设计计算书

多 高 层 钢 结 构 住 宅 方案设计

1、工程概况 1.1工程名称:雅居乐多高层钢结构住宅; 1.2建设地点:东莞市区某地; 1.3工程概况:场地大小为30m×30m,8~12层,建筑总高度不超过40m,室内外高差为0.3m,设计使用年限为50年; 1.4基本风压:0ω=0.8kN/m2,地面粗糙程度为C类; 1.5抗震要求:抗震设防类别为丙类,抗震设防烈度为8度,Ⅱ类场地土,设计地震分组为第一组。 2、场地土层情况 表2-1 场地土层情况 3 3.1建筑布置 3.1.1首层建筑平面图 如下图3-1所示,首层平面设计为大空间的形式,可以用此空间做为店面,即商住两用住宅。中间设计为过道、楼梯和电梯。由过道和墙把首层建筑分开为四个大空间,作为四爿店。由于商业的要求,首层平面将进行比较豪华的装修,例如钢柱将外包为方柱,而墙也做成玻璃幕墙与装饰墙混合的形式。此外,门也将用比较好看的旋转门,以吸引顾客。

图 3-1 首层建筑平面图 3.1.2标准层平面图 如下图3-2所示,标准层平面设计为商品房,以中间两墙为分隔墙,分为四户。朝北两户面积较小,内设一个客厅,四个卧室,两个卫生间,一个厨房,一个阳台(左右侧阳台以一墙分开)。而朝南两户面积较大,内设一个客厅,五个卧室,一个书房,一个厨房,两个卫生间,一个杂物间,一个独立阳台。此外,左右两户为于中间墙对称。

图 3-2 标准层平面图 3.1.3顶层平面图 如下图3-3所示,顶层设计为空旷的天台,外围有1.2m的女儿墙,屋檐外挑500mm。

图3-3 顶层平面图

3.1.4剖面图 图3-4 剖面图1

梁模板(盘扣式)计算书

梁模板(盘扣式)计算书 计算依据: 1、《混凝土结构设计规范》GB50010-2010 2、《建筑结构荷载规范》GB 50009-2012 3、《钢结构设计规范》GB 50017-2003 4、《建筑施工承插型盘扣式钢管支架安全技术规程》JGJ231-2010 一、工程属性 新浇混凝土梁名称KL27 新浇混凝土梁计算跨度(m) 7.2 混凝土梁截面尺寸(mm×mm) 550×1000 新浇混凝土结构层高(m) 4 梁侧楼板厚度(mm) 300 二、荷载设计 模板及其支架自重标准值G1k(kN/m2) 面板0.1 面板及小梁0.3 模板面板0.5 模板及其支架0.75 新浇筑混凝土自重标准值G2k(kN/m3) 24 钢筋自重标准值G3k(kN/m3) 梁 1.5 板 1.1 施工人员及设备荷载标准值Q1k 3 模板支拆环境不考虑风荷载三、模板体系设计 新浇混凝土梁支撑方式梁两侧有板,梁板立柱 不共用A 梁跨度方向立柱间距l a(mm) 900 梁底两侧立柱间距l b(mm) 1000 支撑架中间层水平杆最大竖向步距h(mm) 1500 支撑架顶层水平杆步距h'(mm) 1000 可调托座伸出顶层水平杆的悬臂长度a(mm) 200

新浇混凝土楼板立柱间距l 'a (mm)、l ' b (mm) 1200、 1200 混凝土梁居梁底两侧立柱中的位置 居中 梁底左侧立柱距梁中心线距离(mm) 500 板底左侧立柱距梁中心线距离s 1(mm) 500 板底右侧立柱距梁中心线距离s 2(mm) 500 梁底增加立柱根数 1 梁底增加立柱布置方式 按混凝土梁梁宽均分 梁底增加立柱依次距梁底左侧立柱距离(mm) 500 梁底支撑小梁根数 8 小梁两侧悬挑长度(mm) 100,100 结构表面的要求 结构表面外露 模板及支架计算依据 《建筑施工承插盘扣式钢管支架安全技术规程》JGJ231-2010 设计简图如下: 平面图

楼梯模板支撑体系计算书

楼梯模板支撑体系计算书

————————————————————————————————作者: ————————————————————————————————日期:

楼梯模板支撑体系计算书 一、参数信息 模板支架参数 横向间距或排距(m):1.00;纵距(m):1.00;步距(m):1.0; 立杆上端伸出至模板支撑点长度(m):0.10;模板支架搭设高度(m):3.3;采用的钢管(mm):Φ48×3.0 ;板底支撑连接方式:方木支撑;立杆承重连接方式:可调顶托; 荷载参数 模板与木板自重(kN/m2):0.500;混凝土与钢筋自重(kN/m3):24.000;施工均布荷载标准值(kN/m2):2.000; 材料参数 面板采用胶合面板,厚度为15mm;板底支撑采用方木; 面板弹性模量E(N/mm2):4000;面板抗弯强度设计值(N/mm2):11.5; 木方弹性模量E(N/mm2):8000.000;木方抗弯强度设计值(N/mm2):11.000; 木方抗剪强度设计值(N/mm2):1.400;木方的间隔距离(mm):250.0; 木方的截面宽度(mm):40.00;木方的截面高度(mm):70.00;

40X70 模板支架立面图 二、模板面板计算 模板面板为受弯构件,按三跨连续梁对面板进行验算其抗弯强度和刚度模板面板的截面惯性矩I和截面抵抗矩W分别为: W=bh2/6=1000×15×15/6=37500mm3 I=bh3/12=1000×15×15×15/12=281250mm4 模板面板的按照三跨连续梁计算。

1-1 剖面图 受力分解图 1、荷载计算 静荷载为钢筋混凝土楼板和模板面板的自重(kN/m): 钢筋混凝土梯段板厚度为100mm ,踏步高度为175m m,宽度为260mm,每一梯段板的踏步数为8步。 钢筋混凝土梯段板自重为:21 ×0.175×25+0.10×25/αcos =5.104 kN / ㎡ 其中:根据图纸可得α=31° 故αcos =?31cos = 0.857 q1 = 5.104×1+0.5×1 = 5.604 kN/m; α

单层双跨重型钢结构厂房设计计算书

一.建筑设计说明 一、工程概况 1.工程名称:青岛市某重型工业厂房; 2.工程总面积:3344㎡ 3.结构形式:钢结构排架 二、建筑功能及特点 1.该拟建的建筑位于青岛市室内,设计内容:重型钢结构厂房,此建筑占 地面积3344㎡。 2.平面设计 建筑物朝向为南北向,双跨厂房,每跨跨度为21m,柱距为6m,采用柱网为21m ×6m,纵向定位轴线采用封闭式结合方式。 3.立面设计 该建筑立面为了满足采光和美观需求,设置了大面积的玻璃窗。 4.剖面设计 吊车梁轨顶标高为 6.9m,柱子高度H=6.9+3.336+0.3=10.536,取柱子高度为10.8m。 5.防火 防火等级为二级丁类,设一个防火分区,安全疏散距离满足房门只外部出口或封闭式楼梯间最大距离。 室内消火栓设在两侧纵墙处,两侧及中间各设两个消火栓,满足间距小于50m 的要求。 6.抗震 建筑的平面布置规则,建筑的质量分布和刚度变化均匀,满足抗震要求。 7.屋面 屋面形式为坡屋顶:坡屋顶排水坡度为10%,排水方式为有组织内排水。屋面做法采用《01J925-1压型钢板、夹芯板屋面及墙体建筑构造》中夹芯钢板屋面。 8.采光 采光等级为Ⅳ级,窗地比为1/6,窗户面积为1160㎡,地面面积为3344平方米,窗地比满足要求,不需开设天窗。 9.排水 排水形式为有组织内排水,排水管数目为21个。 三、设计资料 1.自然条件 2.1工程地质条件:场区地质简单,无不利工程地质现象,条件良好, 地基承载力标准值1000Kpa,为强风化花岗岩,场区内无地下水。 冻土深度为0.5m。 2.2抗震设防:6度 2.3防火等级:二级 2.4建筑物类型:丙类 2.5基本风压:W=0.6KN/㎡,主导风向:东南风

梁底模板及梁侧模板支撑架计算

梁底模板支撑架计算 计算依据《建筑施工模板安全技术规范》(JGJ162-2008)。 一、计算参数: 新浇混凝土梁名称 KL12新浇混凝土梁计算跨度(m)3.8 混凝土梁截面尺寸(mm×mm)300*700 新浇混凝土结构层高(m)5.8 梁侧楼板厚度(mm)130 二、模板体系设计 新浇混凝土梁支撑方式梁两侧有板,梁板立柱共用(A)梁跨度方向立柱间距la(mm)900 梁两侧立柱间距lb(mm)1000步距h(mm)1500 新浇混凝土楼板立柱间距l'a(mm)、l'b(mm):900、900 混凝土梁居梁两侧立柱中的位置居中 梁左侧立柱距梁中心线距离(mm)500 梁底增加立柱根数2 梁底增加立柱布置方式:按梁两侧立柱间距均分 梁底增加立柱依次距梁左侧立柱距离(mm)500 梁底支撑小梁根数4 每纵距内附加梁底支撑主梁根数0 梁底支撑小梁最大悬挑长度(mm)100 结构表面的要求结构表面隐蔽 三、面板验算 取单位宽度1000mm,按三等跨连续梁计算,计算简图如下: W=bh2/6=1000×15×15/6=37500mm3,I=bh3/12=1000×15×15×15/12=281250mm4 q1=0.9max[1.2(G1k+ (G2k+G3k)×h)+1.4Q2k,1.35(G1k+ (G2k+G3k)×h)+1.4×0.7Q2k]×b=0.9max[1.2×(0.1+(24+1.5)×1)+1.4×2,1.35×(0.1+(24+1.5)×1)+1.4×0.7×2]×1=32.868kN/m q1静=0.9×1.35×[G1k+(G2k+G3k)×h]×b=0.9×1.35×[0.1+(24+1.5)×1]×1=31.104kN/m q1活=0.9×1.4×0.7×Q2k×b=0.9×1.4×0.7×2×1=1.764kN/m q2=(G1k+ (G2k+G3k)×h)×b=[0.1+(24+1.5)×1]×1=25.6kN/m 1、强度验算 Mmax=0.1q1静L2+0.117q1活L2=0.1×31.104×0.2672+0.117×1.764×0.2672=0.236kN·m

模板支撑体系计算书

模板支撑体系计算书计算依据: 1、《建筑施工模板安全技术规》JGJ162-2008 2、《建筑施工扣件式钢管脚手架安全技术规》JGJ 130-2011 3、《混凝土结构设计规》GB 50010-2010 4、《建筑结构荷载规》GB 50009-2012 5、《钢结构设计规》GB 50017-2003 一、工程属性 二、荷载设计

三、模板体系设计 设计简图如下:

平面图

立面图 四、面板验算 面板类型覆面木胶合板面板厚度t(mm) 14 面板抗弯强度设计值[f](N/mm2) 15 面板抗剪强度设计值[τ](N/mm2) 1.5 面板弹性模量E(N/mm2) 5400 取单位宽度b=1000mm,按三等跨连续梁计算: W=bh2/6=1000×14×14/6=32666.667mm3,I=bh3/12=1000×14×14×14/12=228666.6 67mm4

q1=0.9×max[1.2(G1k+(G2k+G3k)×h)+1.4Q2k,1.35(G1k+(G2k+G3k)×h)+1.4ψc Q2k]×b=0.9×max[1.2×(0.1+(24+1.5)×0.9)+1.4×2,1.35×(0.1+(24+1.5)×0.9)+1.4×0.7×2]×1=29.77 kN/m q1静=0.9×1.35×[G1k+(G2k+G3k)×h]×b=0.9×1.35×[0.1+(24+1.5)×0.9]×1=28.006kN/m q1活=0.9×1.4×0.7×Q2k×b=0.9×1.4×0.7×2×1=1.764kN/m q2=[1×(G1k+(G2k+G3k)×h)]×b=[1×(0.1+(24+1.5)×0.9)]×1=23.05kN/m 计算简图如下: 1、强度验算 M max=0.1q1静L2+0.117q1活L2=0.1×28.006×0.12+0.117×1.764×0.12=0.03kN·m σ=M max/W=0.03×106/32666.667=0.92N/mm2≤[f]=15N/mm2 满足要求! 2、挠度验算 νmax=0.677q2L4/(100EI)=0.677×23.05×1004/(100×5400×228666.667)=0.013mm≤[ν]=L/250=100/250=0.4mm 满足要求! 3、支座反力计算 设计值(承载能力极限状态) R1=R4=0.4q1静L+0.45q1活L=0.4×28.006×0.1+0.45×1.764×0.1=1.2kN R2=R3=1.1q1静L+1.2q1活L=1.1×28.006×0.1+1.2×1.764×0.1=3.292kN

钢结构厂房设计计算书

毕业设计说明书(毕业论文) 毕业设计(论文)题目 专业:土木工程专业 学生:赵鹏 指导教师:王羡农 河北工程大学土木工程学院 2013年05月29日

摘要 本设计工程为邯郸地区一67.5米双跨钢结构。主要依据《钢结构设计规范})GB50017-2003和《门式刚架轻型房屋钢结构技术规程》GECS 102:2002等国家规范,综合考虑设计工程的规模、跨度、高度及用途,依据“适用、经济、在可能条件下注意美观”的原则,对各组成部分的选型、选材、连接和经济性作了比较,最终选用单层门式钢架的结构形式。梁、柱节点为刚性连接的门式钢架具有结构简洁、刚度良好、受力合理、使用空间大及施工方便等特点,便于工业化,商品化的制品生产,与轻型维护材料相配套的轻型钢结构框架体系己广泛应用于建筑结构中,本设计就是对轻型钢结构的实际工程进行建筑、结构设计与计算。主要对承重结构进行了内力分析和内力组合,在此基础上确定梁柱截面,对梁柱作了弯剪压计算,验算其平而内外的稳定性;梁柱均采用Q235钢,10. 9级摩擦型高强螺栓连接,局部焊接采用E43型焊条,柱脚刚性连接,梁与柱节点也刚性连接;屋面和墙面维护采用双层彩色聚苯乙烯夹芯板;另外特别注重了支撑设置、拉条设置,避免了一些常见的拉条设计错误。 关键词:轻型钢结构门式钢架内力分析双层彩色聚苯乙烯夹芯板节点

Abstract This project in handan area is a 67.5m double-span steel structure. The project designed strictly complies with the relavant stipulations of the "CODE FOR DESIGN OF STEEL STRUCTURES (GF50017-2003)" and "TECHNICAL SPECIFICATION FOR STEEL STRUCTURE OF LIGHT WEIGHT BUILDINGS WITH GABLED FRAMES (CECS 102:2002)", and some others. Synthesize the scale of the consideration design engineering and across a principle for span and use, according as" applying, economy, under the possible term attention beautifully", Connecting method, structure type and material of each part which consist of a light-weight steel villa are analysed, then choose the construction form that use single layer a type steel. The beam, pillar node is a light steel construction frame system that rigid and copular a type steel a ware for having construction Simple, just degree goodly, suffering dint reasonablely, using space bigly and starting construction convenience etc. characteristics, and easy to industrialisation, commercializing produce, thinking with light maintenance material the kit the already extensive applying in the building construction inside, this design is to proceeds the building, construction design to the structural and actual engineering in light steel and calculation. The tractate includes the internal force analyzes and combines, based on these analyses; we can choose the section of beam and calumniation. Next, checking computatians of stability calculatian of the plane structure. The steel beam and column employs Q235 carbon structural steel. Connection bolts are high strength bolt of friction type with behavioral grade 10.9. Common bolts are rough type made by Q235-B.F steel. Rod for manual welding usually adopts E43..Rigid connections apply to the column leg and the connection of column and beam adopts hinged connection. The metope and roofage adopts the Bauble-decked colored polystyrene clamps the circuit board. otherwise, it is analysed that the forced state of the bracing system for a steel factor building under wind land, and the design of a bracing truss for a building with larger width. Avoid some errors in the design of brace, tension rod, and tension rod jpints. Keywords:Lightweight steel structures; gabled frame; the internal force analyzes; The double-decked colored polystyrene clamps the circuit board;joint

梁模板支架计算示例

梁模板碗扣钢管高支撑架计算书 计算依据《建筑施工碗扣式钢管脚手架安全技术规范》(JGJ166-2008)。 计算参数: 模板支架搭设高度为7.0m , 梁截面 B ×D=1000mm ×1000mm ,立杆的纵距(跨度方向) l=0.60m ,立杆的步距 h=1.20m , 梁底增加3道承重立杆。 面板厚度18mm ,剪切强度1.4N/mm 2,抗弯强度15.0N/mm 2,弹性模量6000.0N/mm 4。 木方100×100mm ,剪切强度1.3N/mm 2,抗弯强度13.0N/mm 2,弹性模量9500.0N/mm 4。 梁底支撑木方长度 1.50m 。 梁顶托采用双钢管48×3.25mm 。 梁底按照均匀布置承重杆3根计算。 模板自重0.50kN/m 2,混凝土钢筋自重25.00kN/m 3,施工活荷载5.00kN/m 2。 梁两侧的楼板厚度0.20m ,梁两侧的楼板计算长度3.00m 。 地基承载力标准值230kN/m 2,基础底面扩展面积0.250m 2,地基承载力调整系数1.00。 扣件计算折减系数取1.00。 700 图1 梁模板支撑架立面简图 计算中考虑梁两侧部分楼板混凝土荷载以集中力方式向下传递。 集中力大小为 F = 1.20×25.000×0.200×3.000×0.600=10.800kN 。

采用的钢管类型为48×3.25。 一、模板面板计算 面板为受弯结构,需要验算其抗弯强度和刚度。模板面板的按照三跨连续梁计算。 静荷载标准值 q1 = 25.000×1.000×1.000+0.500×1.000=25.500kN/m 活荷载标准值 q2 = (4.000+1.000)×1.000=5.000kN/m 面板的截面惯性矩I和截面抵抗矩W分别为: 本算例中,截面惯性矩I和截面抵抗矩W分别为: W = 100.00×1.80×1.80/6 = 54.00cm3; I = 100.00×1.80×1.80×1.80/12 = 48.60cm4; (1)抗弯强度计算 f = M / W < [f] 其中 f ——面板的抗弯强度计算值(N/mm2); M ——面板的最大弯距(N.mm); W ——面板的净截面抵抗矩; [f] ——面板的抗弯强度设计值,取15.00N/mm2; M = 0.100ql2 其中 q ——荷载设计值(kN/m); 经计算得到 M = 0.100×(1.20×25.500+1.4×5.000)×0.600× 0.600=1.354kN.m 经计算得到面板抗弯强度计算值 f = 1.354×1000× 1000/54000=25.067N/mm2 面板的抗弯强度验算 f > [f],不满足要求! (2)抗剪计算 [可以不计算] T = 3Q/2bh < [T] 其中最大剪力 Q=0.600×(1.20×25.500+1.4×5.000)×0.600=13.536kN 截面抗剪强度计算值 T=3×13536.0/(2×1000.000× 18.000)=1.128N/mm2 截面抗剪强度设计值 [T]=1.40N/mm2 抗剪强度验算 T < [T],满足要求! (3)挠度计算

梁模板支撑计算

梁模板(扣件钢管架)计算书梁段:L16a。 一、参数信息 1.模板支撑及构造参数 梁截面宽度B(m): 0.4m; 梁截面高度D(m): 1m; 混凝土板厚度(mm): 120mm; 立杆纵距(沿梁跨度方向间距)La(m): 0.8m; 立杆上端伸出至模板支撑点长度a(m): 0.1m; 脚手架步距(m): 1.2m; 梁支撑架搭设高度H(m):12.6m;

梁两侧立柱间距(m): 0.8m; 承重架支设: 多根承重立杆,钢管支撑垂直梁截面; 立杆横向间距或排距Lb(m): 0.6m; 采用的钢管类型为Φ48×3.50; 扣件连接方式: 单扣件,考虑扣件质量及保养情况,取扣件抗滑承载力折减系数: 0.8; 2.荷载参数 模板自重(kN/m2): 0.35kN/m2; 钢筋自重(kN/m3): 1.5kN/m3; 施工均布荷载标准值(kN/m2): 2.5kN/m2; 新浇混凝土侧压力标准值(kN/m2): 18kN/m2; 倾倒混凝土侧压力(kN/m2): 2kN/m2; 振捣混凝土荷载标准值(kN/m2): 2kN/m2; 3.材料参数 木材品种:杉木; 木材弹性模量E(N/mm2):10000N/mm2; 木材抗弯强度设计值fm(N/mm2):16N/mm2; 木材抗剪强度设计值fv(N/mm2):1.7N/mm2; 面板类型:胶合面板; 钢材弹性模量E(N/mm2):210000; 钢材抗弯强度设计值fm(N/mm2):205N/mm2; 面板弹性模量E(N/mm2):9500N/mm2; 面板抗弯强度设计值fm(N/mm2):13N/mm2; 4.梁底模板参数 梁底纵向支撑根数:2; 面板厚度(mm):12mm;

24.4m模板支撑计算书

碗扣钢管楼板模板支架计算书 依据规范: 《建筑施工碗扣式钢管脚手架安全技术规范》JGJ166-2008 《建筑施工模板安全技术规范》JGJ 162-2008 《建筑结构荷载规范》GB50009-2012 《钢结构设计规范》GB50017-2003 《混凝土结构设计规范》GB50010-2010 《建筑地基基础设计规范》GB50007-2011 《建筑施工木脚手架安全技术规范》JGJ 164-2008 计算参数: 钢管强度为205.0 N/mm2,钢管强度折减系数取1.00。 模板支架搭设高度为24.4m, 立杆的纵距 b=0.60m,立杆的横距 l=0.90m,立杆的步距 h=1.20m。 面板厚度14mm,剪切强度1.4N/mm2,抗弯强度15.0N/mm2,弹性模量6000.0N/mm2。内龙骨采用50.×100.mm木方,间距200mm, 木方剪切强度1.3N/mm2,抗弯强度16.0N/mm2,弹性模量9000.0N/mm2。 梁顶托采用85.×85.mm木方。 模板自重0.20kN/m2,混凝土钢筋自重25.10kN/m3。 倾倒混凝土荷载标准值0.00kN/m2,施工均布荷载标准值2.50kN/m2。

图1 楼板支撑架立面简图 图2 楼板支撑架荷载计算单元 采用的钢管类型为φ48×2.8。 钢管惯性矩计算采用 I=π(D4-d4)/64,抵抗距计算采用 W=π(D4-d4)/32D。 一、模板面板计算 面板为受弯结构,需要验算其抗弯强度和刚度。模板面板的按照三跨连续梁计算。静荷载标准值 q1 = 25.100×0.300×0.600+0.200×0.600=4.638kN/m

某多高层钢结构住宅毕业设计含计算书、建筑结构设计图

雅居乐 多高层钢结构住宅方案设计

1.工程概况 工程名称:雅居乐多高层钢结构住宅; 建设地点:东莞市区某地; 工程概况:场地大小为30m×30m,8~12层,建筑总高度不超过40m,室内外高差为0.3m,设计使用年限为50年; 基本风压:0ω=0.8kN/m2,地面粗糙程度为C类; 抗震要求:抗震设防类别为丙类,抗震设防烈度为8度,Ⅱ类场地土,设计地震分组为第一组。 场地土层情况: 表2-1 场地土层情况 2.建筑与结构布置 3.1.建筑布置 3.1.1.首层建筑平面图 如下图3-1所示,首层平面设计为大空间的形式,可以用此空间做为店面,即商住两用住宅。中间设计为过道、楼梯和电梯。由过道和墙把首层建筑分开为四个大空间,作为四爿店。由于商业的要求,首层平面将进行比较豪华的装修,例如钢柱将外包为方柱,而墙也做成玻璃幕墙与装饰墙混合的形式。此外,门也将用比较好看的旋转门,以吸引顾客。

图3-1 首层建筑平面图 3.1.2.标准层平面图 如下图3-2所示,标准层平面设计为商品房,以中间两墙为分隔墙,分为四户。朝北两户面积较小,内设一个客厅,四个卧室,两个卫生间,一个厨房,一个阳台(左右侧阳台以一墙分开)。而朝南两户面积较大,内设一个客厅,五个卧室,一个书房,一个厨房,两个卫生间,一个杂物间,一个独立阳台。此外,左右两户为于中间墙对称。

图 3-2 标准层平面图 3.1.3.顶层平面图 如下图3-2所示,顶层设计为空旷的天台,外围有1.2m的女儿墙,屋檐外挑500mm。

图3-3 顶层平面图3.1.4.剖面图

图3-4 剖面图1

梁木模板与支撑计算书

梁木模板与支撑计算书(1500×300) 3.1 梁模板基本参数 梁截面宽度 B=300mm, 梁截面高度 H=1500mm, H方向对拉螺栓2道,对拉螺栓直径20mm, 对拉螺栓在垂直于梁截面方向距离(即计算跨度)600mm。 梁模板使用的方木截面80×100mm, 梁模板截面底部方木距离300mm,梁模板截面侧面方木距离300mm。 梁底模面板厚度h=18mm,弹性模量E=6000N/mm2,抗弯强度[f]=15N/mm2。 梁侧模面板厚度h=18mm,弹性模量E=6000N/mm2,抗弯强度[f]=15N/mm2。 3.2 梁模板荷载标准值计算 模板自重 = 0.340kN/m2; 钢筋自重 = 1.500kN/m3; 混凝土自重 = 24.000kN/m3; 施工荷载标准值 = 2.500kN/m2。 强度验算要考虑新浇混凝土侧压力和倾倒混凝土时产生的荷载;挠度验算只考虑新浇混凝土侧压力。 新浇混凝土侧压力计算公式为下式中的较小值: 其中——混凝土的重力密度,取24.000kN/m3; t ——新浇混凝土的初凝时间,为0时(表示无资料)取200/(T+15),取4.000h; T ——混凝土的入模温度,取20.000℃; V ——混凝土的浇筑速度,取2.500m/h;

H ——混凝土侧压力计算位置处至新浇混凝土顶面总高度,取1.200m; 1——外加剂影响修正系数,取1.000; 2——混凝土坍落度影响修正系数,取0.850。 根据公式计算的新浇混凝土侧压力标准值 F1=28.380kN/m2 实际计算中采用新浇混凝土侧压力标准值 F1=28.380kN/m2 倒混凝土时产生的荷载标准值 F2= 6.000kN/m2。 3.3 梁模板底模计算 本算例中,面板的截面惯性矩I和截面抵抗矩W分别为: W = 30.00×1.80×1.80/6 = 16.20cm3; I = 30.00×1.80×1.80×1.80/12 = 14.58cm4; 梁底模板面板按照三跨度连续梁计算,计算简图如下 q 梁底模面板计算简图 1.强度计算 强度计算公式要求: = M/W < [f] 其中——梁底模板的强度计算值(N/mm2); M ——计算的最大弯矩 (kN.m); q ——作用在梁底模板的均布荷载(kN/m); q=1.2×[0.34×0.30+24.00×0.30×1.50+1.50×0.30×1.50] +1.4×2.50×0.30=14.94kN/m 最大弯矩计算公式如下: M=-0.10×14.942×0.3002=-0.134kN.m =0.134×106/16200.0=8.301N/mm2 梁底模面板计算强度小于15.00N/mm2,满足要求! 2.抗剪计算 最大剪力的计算公式如下: Q = 0.6ql 截面抗剪强度必须满足: T = 3Q/2bh < [T]

梁、板木模板及支撑计算书

梁、板木模板及支撑计算书

楼板模板扣件钢管高支撑架计算书 高支撑架的计算参照《建筑施工扣件式钢管脚手架安全技术规范》( JGJ130-2001) 本计算书还参照《施工技术》2002.3.《扣件式钢管模板高支撑架设计和使用安全》。 模板支架搭设高度为8.05米, 搭设尺寸为:立杆的纵距 b=0.80米,立杆的横距1=0.80米,立杆的步距h=1.50米 k b L 采用的钢管类型为'-48X 3.5。 、模板面板计算 面板为受弯结构,需要验算其抗弯强度和刚度。模板面板的按照三跨连续梁计算 ■5 5 匚 纵向钢昔 僑向钢背 板底方木 图楼板支撑架立面简图 图楼板支撑架立杆稳定性荷载计算单元

静荷载标准值q1 = 25.000 X 0.120 X 1.000+0.350 X 1.000=3.350kN/m 活荷载标准值q2 = (2.000+1.000) X 1.000=3.000kN/m 面板的截面惯性矩I和截面抵抗矩V分别为: 本算例中,截面惯性矩I和截面抵抗矩V分别为: W = 100.00 X 1.80 X 1.80/6 = 54.00cm 3; I = 100.00 X 1.80 X 1.80 X 1.80/12 = 48.60cm 4; (1) 强度计算 f = M / W < [f] 其中f ――面板的强度计算值(N/mm2); M ---- 面板的最大弯距(N.mm); W——面板的净截面抵抗矩; [f] ―― 面板的强度设计值,取15.00N/mm2; M = 0.100ql 2 其中q ---- 荷载设计值(kN/m); 经计算得到M = 0.100 X (1.2 X 3.350+1.4 X 3.000) X 0.450 X 0.450=0.166kN.m 经计算得到面板强度计算值f = 0.166 X 1000X 1000/54000=3.083N/mm2 面板的强度验算f < [f], 满足要求! (2)抗剪计算 T = 3Q/2bh < [T] 其中最大剪力Q=0.600 X (1.2 X 3.350+1.4 X 3.000) X 0.450=2.219kN 截面抗剪强度计算值T=3 X 2219.0/(2 X 1000.000 X 18.000)=0.185N/mm2 截面抗剪强度设计值[T]=1.40N/mm 2 抗剪强度验算T < [T],满足要求! (3)挠度计算

钢结构桁架设计计算书概况

renchunmin 一、设计计算资料 1. 办公室平面尺寸为18m×66m ,柱距8m ,跨度为32m ,柱网采用封闭结合。火灾危险性:戊类,火灾等级:二级,设计使用年限:50年。 2. 屋面采用长尺复合屋面板,板厚50mm ,檩距不大于1800mm 。檩条采用冷弯薄壁卷边槽钢C200×70×20×2.5,屋面坡度i =l /20~l /8。 3. 钢屋架简支在钢筋混凝土柱顶上,柱顶标高9.800m ,柱上端设有钢筋混凝土连系梁。上柱截面为600mm×600mm ,所用混凝土强度等级为C30,轴心抗压强度设计值f c =1 4.3N /mm 2。 抗风柱的柱距为6m ,上端与屋架上弦用板铰连接。 4. 钢材用 Q235-B ,焊条用 E43系列型。 5. 屋架采用平坡梯形屋架,无天窗,外形尺寸如下图所示。 6. 该办公楼建于苏州大生公司所 属区内。 7. 屋盖荷载标准值: (l) 屋面活荷载 0.50 kN /m 2 (2) 基本雪压 s 0 0.40 kN /m 2 (3) 基本风压 w 0 0.45 kN /m 2 (4) 复合屋面板自重 0.15 kN /m 2 (5) 檩条自重 查型钢表 (6) 屋架及支撑自重 0.12+0. 01l kN /m 2 8. 运输单元最大尺寸长度为9m ,高度为0.55m 。 二、屋架几何尺寸的确定 1.屋架杆件几何长度 屋架的计算跨度mm L l 17700300180003000=-=-=,端部高度取mm H 15000=跨中高度为mm 1943H ,5.194220 217700 150020==?+ =+=取mm L i H H 。跨中起拱高度为60mm (L/500)。梯形钢屋架形式和几何尺寸如图1所示。

梁支撑计算

梁支撑计算 公司标准化编码 [QQX96QT-XQQB89Q8-NQQJ6Q8-MQM9N]

梁模板(扣件钢管架)计算书梁段:L16a。 一、参数信息 1.模板支撑及构造参数 梁截面宽度 B(m): ; 梁截面高度 D(m): 1m;

混凝土板厚度(mm): 120mm; 立杆纵距(沿梁跨度方向间距)La(m): ; 立杆上端伸出至模板支撑点长度a(m): ; 脚手架步距(m): ; 梁支撑架搭设高度H(m):; 梁两侧立柱间距(m): ; 承重架支设: 多根承重立杆,钢管支撑垂直梁截面; 立杆横向间距或排距Lb(m): ; 采用的钢管类型为Φ48×; 扣件连接方式: 单扣件,考虑扣件质量及保养情况,取扣件抗滑承载力折减系数: ; 2.荷载参数 模板自重(kN/m2): m2; 钢筋自重(kN/m3): m3; 施工均布荷载标准值(kN/m2): m2; 新浇混凝土侧压力标准值(kN/m2): 18kN/m2;

倾倒混凝土侧压力(kN/m2): 2kN/m2; 振捣混凝土荷载标准值(kN/m2): 2kN/m2; 3.材料参数 木材品种:杉木; 木材弹性模量E(N/mm2):10000N/mm2; 木材抗弯强度设计值fm(N/mm2):16N/mm2; 木材抗剪强度设计值fv(N/mm2):mm2; 面板类型:胶合面板; 钢材弹性模量E(N/mm2):210000; 钢材抗弯强度设计值fm(N/mm2):205N/mm2; 面板弹性模量E(N/mm2):9500N/mm2; 面板抗弯强度设计值fm(N/mm2):13N/mm2; 4.梁底模板参数 梁底纵向支撑根数:2; 面板厚度(mm):12mm;

现浇混凝土模板的支撑设计计算书

模板的支撑设计计算书 ●本工程的模板均采用胶合板模板,木方背楞,钢管扣件支撑,配合采用 对拉螺栓。

施工荷载 1.4×2500=3500N/m 2 钢筋自重荷载 1.2×1100=1320N/m 2 振捣荷载 1.4×2000=2800 N/m 2 合计: 15480 N/m 2 mm q bh f l bh W m 80148 .156181********* 12 22=****=*≤ (2)按剪应力验算 mm q bhf l f bh ql bh V ql V v v 201648 .1533.118100043443232/1max =****=≤≤== =τ (3)按挠度验算

mm q EI l l EI ql 487200 632.0100200 100632.034=??=< ?=ω 现浇板木胶合板模板跨度(即70×100mm 木方背楞间距)取400mm. 4) 70×100mm 木方背楞受力验算 70×100mm 木方背楞搁置在钢管大横杆上,现进行木方背楞受力验算。 (1)按抗弯强度验算 上式中q ’=15480×0.4=6.192N/mm (2))按剪应力验算 (3 根据以上计算,胶合板木方70×100mm 背楞跨度可取1200mm 。 但模板下钢管扣件支撑,每一扣件抗滑能力约为6500N ,而其上荷载为15480N/m 2,可知如支撑立杆间距布置为600mm×600mm,则扣件承受

的力为15480×0.6×0.6=5.57KN<6.5KN,可满足要求。 则木方背楞下,φ48×3.5钢管大横楞及φ48×3.5立杆间距取@600mm ,也即,木方背楞的实际跨度为600mm ,现进行大横杆及立杆验算。 5) 木方背楞下φ48×3.5钢管大横杆受力验算 作用于钢管横楞上的集中荷载为F=q ×0.6×0.4=4.39KN 则按单跨梁,最大弯距可能为: m KN Fl M ?=?== 439.04 6.039.44max (2) 按挠度验算 mm mm F EI l l EI Fl 6008364390400121867101.24820048400 4853<=????=≤≤ =ω 6) 钢管支撑立杆受力验算。 支撑立杆步距1800m ,采用φ48×3.5钢管对接连接: 立杆最大受力F=15480×0.6×0.6=5573N<扣件的抗滑能力值 2 2/205/01.36489 316.05573316 .0,1488 .151800 3.1mm N mm N A N i l <=?=?===?= ?= ?σ?μλ则查表 150mm 厚及其以下模板支撑设计

相关文档