The IEEE Reliability Test System

1System Description

The24bus system[1]is illustrated in Figure1.The slack bus of the system is node13.

Figure1:24-bus power system–IEEE One Area RTS-96

1.1Unit Data

Tables1-3present the generating units’data of the power system.The generating units o?er a single block of energy,up and down reserve capacity.Table1provides the technical data of generating units,Table2categorizes the units in di?erent types and Table3provides the costs and initial state of the generating units at the beginning of the scheduling horizon.The data is based on[1],[2],[3].

Table1:Technical Data of Generating Units

Unit Node P max P min R+R?RU RD UT DT

MW MW MW MW MW/min MW/min h h Unit181840010000 6.67 6.6711

Unit212140010000 6.67 6.6711

Unit1115230.440402284

Unit2215230.440402284

Unit15b1515554.2530303388

Unit161615554.2530303388

Unit23a23310108.560603388

Unit23b2335014040404488

Unit773507570707788

Unit1313591206.85180180331210

Unit15a15601260601142

Unit2222300300005500

Table2:Unit Type

Unit T ype Unit(s)

Nuclear1821

Coal/Stream12151623a

Coal/3Stream23b

Oil/Stream71315

Hydro22

Table3:Costs and Initial State of Generating Units

Unit C C u C d C su P ini U ini T ini

$/MWh$/MW$/MW$MW0/1h

Unit18 5.47000320150

Unit21 5.47000320116

Unit113.3215141430.4121.6122

Unit213.3215141430.4121.6122

Unit15b10.52161431200-2

Unit1610.521614312124110

Unit23a10.521716624248110

Unit23b10.8916142298280150

Unit720.70109172500-2

Unit1320.93873056.700-1

Unit15a26.117543700-1

Unit220.00000240124

A positive T ini shows the time periods that the generating unit has been online at the beginning of scheduling horizon.A negative one shows the time periods that the generating unit has been o?ine at the beginning of scheduling horizon.

1.2Load Data

In Figure2,the load pro?le is illustrated.Table4provides the total system demand per hour and Table5presents the node location of the loads,as well as load at each node as a percentage of the total system demand.The load data is based on[2].

Figure2:System Demand Pro?le

Table4:Load Pro?le

Hour System Demand Hour System Demand

MW MW

11598.252132266.178

21502.834142266.178

31431.270152218.469

41407.416162218.469

51407.416172361.596

61431.270182385.450

71765.233192385.450

82051.487202290.032

92266.178212170.760

102290.032221979.924

112290.032231741.379

122266.178241502.834

Table5:Node Location and Distribution of the Total System Demand

Load Node%of system load Load Node%of system load

Load11 3.8Load1010 6.8

Load22 3.4Load13139.3

Load33 6.3Load1414 6.8

Load44 2.6Load151511.1

Load55 2.5Load1616 3.5

Load66 4.8Load181811.7

Load77 4.4Load1919 6.4

Load886Load2020 4.5

Load99 6.1

1.3Transmission Lines

The transmission lines data is given in Table6.The lines are characterized by the nodes that are connected,as well as the reactance and the capacity of each line.The data is based on[2].

Table6:Reactance and Capacity of Transmission Lines

F rom T o Reactance Capacity F rom T o Reactance Capacity

p.u.MVA p.u.MVA

120.014617511130.0488500

130.225317511140.0426500

150.090735012130.0488500

240.135617512230.0985500

260.20517513230.0884500

390.127117514160.0594500

3240.08440015160.0172500

490.11117515210.02491000

5100.0943*******.0529500

6100.064217516170.0263500

780.065235016190.0234500

890.176217517180.0143500

8100.176217517220.1069500

9110.08440018210.01321000

9120.08440019200.02031000

10110.08440020230.01121000

10120.08440021220.0692500

2Implementation Including Wind Power Production

It is recommended to include six wind farms at di?erent locations throughout the grid.It is proposed to locate the wind farms at3,5,7,16,21and23nodes.In this case,the capacity on the transmission lines connecting the node pairs(15,21),(14,16)and(13,23)is reduced to400MW,250MW and 250MW,respectively.This is done in order to introduce bottlenecks in the transmission system.

References

[1]C.Grigg,P.Wong,P.Albrecht,R.Allan,M.Bhavaraju,R.Billinton,Q.Chen,C.Fong,S.

Haddad,S.Kuruganty,et al.The IEEE Reliability Test System1996.A report prepared by the reliability test system task force of the application of probability methods subcommittee.IEEE Transactions on Power Systems,14(3):1010-1020,1999.

[2]A.J.Conejo,M.Carrion,J.M.Morales.Decision Making under Uncertainty in Electricity

Markets.Springer US,2010.

[3]F.Bou?ard,F.D.Galiana,A.J.Conejo.Market-Clearing with Stochastic Security Part II:

Case Studies.IEEE Transactions on Power Systems,20(4):1827-1835,2005. Nomenclature

C Production cost

C d Downward reserve cost

C su Start up cost

C u Upward reserve cost

DT Minimum down time of each generating unit

P ini Power output of each generating unit at time0

P max Maximum output power of each generating unit

P min Minimum output power of each generating unit

R+Maximum reserve capacity of up regulation of each generating unit

R?Minimum reserve capacity of up regulation of each generating unit

RD Ramp down rate of each generating unit

RU Ramp up rate of each generating unit

T ini Number of hours of which the generating unit was in/out at the beginning of planning horizon U ini Stating whether the unit is online/o?ine at time0

UT Minimum up time of each generating unit