文档库 最新最全的文档下载
当前位置:文档库 › KYN28柜使用手册

KYN28柜使用手册

KYN28-12铠装式金属封闭开关设备安装使用与维护手册

Metal-clad enclosed Switchgear

Instruction manual

JIANGSU CHANGJIANG ELECTRIC CO., LTD., P. R. CHINA

始终安全第一

Y our safety first-always!

在开关设备安装使用前请先仔细阅读本说明书

That’s why our instruction manual begins with these recommendations

开关设备只能安装在适合于电气设备工作的户内场所。

Only install switchgear and/or switchboards in enclosed rooms suitable for electrical equipment.

确保由专职电气人员进行安装、操作和维护。

Ensure that installation,operation and maintenance are carried out by specialist electricians only.

必须保证现场电气设备的联接条件和工作规程的适用和安全性。

Comply in full with the legally recognized standards(DIN VDE/IEC),the connection conditions of the local electrical utility and the applicable safety at work regulations.

有关开关设备的一切操作,都要遵守说明书中的相应规定。

Observe the relevant information in the instruction manual for all actions involving switchgear and switchboards.

危险

Danger

要特别注意说明书中标有这个危险标志的注意事项。

Pay special attention to the hazard notes in the instruction manual marked with this warning symbol.

不要超出开关设备在正常工作条件下的技术参数里规定的负载。

Make sure that under operation condition of the switchboard the specified data are not exceeded.

说明书应放在所有与安装、操作和维护有关人员能方便地拿到的地方。

Keep the instruction manual accessible to all persons concerned with installation, operation and maintenance.

用户的专职人员应对所有影响工作安全的事项负责,并正确管理开关设备。

he user’s personnel are to act responsibly in all matters affecting safety at work and

the correct handing of the switchgear.

若对本说明书尚有疑问,我们将很乐意提供进一步的资讯。

If you have any further questions on this instruction manual, the members of our field organization will be pleased to provide the required information.

目录页码1.总则 6 1.1 概述 6 1.2 标准和规范 6 1.3 工作条件 6 1.3.1 正常工作条件7 1.3.2 工特殊工作条件7 1.3.3 注意事项8

2 技术数据8 2.1 电气参数8 2.2 耐内部故障电弧性能9 2.

3 外形尺寸和重量10

3 结构概述12 3.1 基本结构12 3.2 外壳和隔板13 3.3 开关柜内的小室13 3.

4 防止误操作的联锁/保护16

4 运输和保管20 4.1 交付条件20 4.2 包装20 4.3 运输21 4.4 交货和中间保管22

5 开关柜的现场安装24 5.1 安装现场的一般要求24 5.2 配电室平面布置基本方案24 5.3 基础25 5.3.1 以配电室地板作为基础25 5.3.2 在混凝土地坪上的基础框

26 5.4 开关柜的安装与拼接27 5.5 母线的安装联接29 5.6 电力电缆和控制电缆的联

30 5.7 接地铜排的联接31 5.8 安装工作的收尾32

目录页码6 开关柜的运行37 6.1 起动37 6.1.1 准备工作37 6.1.2 起动39 6.2 开关柜的操作40 6.2.1 断路器手车40 6.2.2 断路器42 6.2.3 接地开关43 6.2.4 电缆室门44 6.2.5 电气/机械的指示/监控44

7 维护45 7.1 概述45 7.2 检查和保养46 7.3 修理49 7.3.1 一般性修理49 7.3.2 更换元件49 7.4 备件49

版权所有,禁止将本说明书的全部或部分,以任何形式提供给第三者。公司保留对提供的数据和图解的更改权力,需更改时,不另行通知。

Contents

1

1.1 1.2 1.3 1.3.1 1.3.2 1.3.3 2

2.1 2.2 2.3

3

3.1 3.2 3.3

3.4

4

4.1 4.2 4.3 4.4

5

5.1 5.2

5.3 5.31

5.32

5.4 5.5 5.6

5.7 5.8 Summary

General

Standards and specifications

Service conditions

Normal Service conditions

Special Service conditions

Matters need attention

T echnical data

Switchgear electrical data

Received internal arc nature

Dimension and weights

Structure summary

Basic structure and variants

Enclosure and partitions

Compartments in the switchgear

panels

Interlocks/protection against

mishandling

Despatch and storage

Condition on deliver

Packaging

Transport

Delivery and intermediate storage

Assemblage of the switchgear at

site

General site requirements

Basic scheme of switching room’s

play layout.

Foundation

Foundation as the floorboard of

switching room.

Foundation frame on a concrete

floor

Instalment and joint of switchgear

Instalment and joint of bus bar

Contact of power cable and

control cable.

Join of the earth bus bar

The epilogue of erecting work

Page

6

6

6

6

7

7

8

8

8

9

10

12

12

13

13

16

20

20

20

21

22

24

24

24

25

25

26

27

29

30

31

32

Contents

6

6.1

6.1.1

6.1.2

6.2

6.2.1

6.2.2

6.2.3

6.2.4

6.2.5

7

7.1

7.2

7.3

7.3.1

7.3.2

7.4

Switchgear running

Start-up

Preparation work

Start-up

Operation of the switchgear

VCB truck

VCB

Earth switch

Cable door

Electrical/mechanical

indicate/monitor

Maintenance

General

Checking and maintenance

Maintenance

Checking

Change element

Spares

*The data and illustrations

are without engagement .

Subject to change without

notice.

Page

37

37

37

39

40

40

42

43

44

44

45

45

46

49

49

49

49

We reserve all rights to this publication. Misuse, particularly including duplication and making available of this manual extracts-to third parties is prohibited. The information supplied isn’t liability,subject to approval.

1 总则

Summary

1.1 概述

General

KYN28-12铠装式金属封闭开关设备(以下简称KYN28-12开关柜)适用于三相交流50Hz、7.2~12kV单母线及单母线分段电力系统,具有“五防”功能。开关柜的可移开部分可配置真空断路器和真空接触器等元器件。

KYN28-12 metal-clad enclosed switchgear is suitable for 3-phase AC 50Hz/7.2-12kV single bus bar and single bus bar section electric power system.,with the function of “five preventions”. The removing compartment of the switchgear may be assembled with vacuum circuit breaker and vacuum contactor etc.

1.2 标准和规范

Standards and specifications

KYN28-12开关柜满足IEC298,GB3906,DL404等标准。

The switchgear complies with the standards of IEC60298,GB3906,DL404 etc.

开关柜外壳的防护等级为IP4X,当断路器室门打开、手车移开时,防护等级为IP2X。

Enclosure protection degree of switchgear is IP4X, protection degree is IP2X when the door of VCB room is open and the truck is be drew out.

在系统的安装和运行期间,要遵守所有相关的IEC规范及国家或地方相关的安全导则,还应考虑江苏长江电器股份有限公司提供的有关资料。

During the installation and running of electric system, observe all the relevant information in the IEC and the safety regulations in GB or local electrical utility, and consider the relevant information provided by JIANGSU CHANGJIANG ELECTRIC CO.,LTD.,P.R.CHINA. 1.3工作条件

Service conditions

1.3.1 正常工作条件

Normal service conditions

KYN28-12开关柜正常工作条件如下:

Normal service conditions of switchgear following:

室内环境温度:

Ambient temperature in room:

最高温度+40°C

Maximum

日平均值不大于+35°C

Maximum 24 hour average

最低温度-15°C

Minimum (according to “minus 15 indoor class”)

室内环境湿度:

Ambient humidity in room:

日平均相对湿度95%及以下

Daily average relative humidity less than 95%

月平均相对湿度90%及以下

Monthly average relative humidity less than 90%

安装场所的海拔高度1000m及以下

Height above sea level at site less than 1000m

地震烈度: 不超过8度

Earthquake intensity: less than 8 degree

没有火灾、爆炸危险,没有严重污秽及化学腐蚀的场所。

This product should not be used under conditions of fire, explosion,earthquake and chemical corrosion environments.

1.3.2特殊工作条件

Special service conditions

对特殊工作条件,必须向制造厂咨询。制造厂与用户应就特殊工作条件取得一致意见。

The manufacture must be consulted in advance about each special service condition. Special

service conditions are to be agreed on by the manufacturer and user.

●已考虑安装场所的海拔高于1000m时,空气介质强度的降低对绝缘水平的影响。

Allow for the reduction in the dielectric strength of the air when site altitude is over 1000m ●若环境温度超出极限值,在母线和分支母线的设计上加以补偿或限制载流量。在柜内

安装通风装置将有利于开关柜的散热。

If the ambient temperature is over top of the high-point, must consider equalizing or limiting current capacity for the design of main bus bar and branching bus bar. Installation the aerator is favor of rejection of heat.

1.3.3 注意事项:

Matters need attention:

若开关柜运行地区的湿度较高,温度波动速度较快且幅度较大,开关柜在这种气候环境下运行,就有凝露的危险,因此开关柜在备用和运行状态下,用户应保证加热器全天侯投入!但在大电流运行中,可以不投入。

If the humidity is higher on site, temperature fluctuations speed is rapidder and range is bigger, condensation phenomena will be appear for the switchgears running in this clime condition, so user should ensure that the heater running full time on spare and running condition! But running in high-current, the heater can stop.

2技术数据

T echnical data

2.1 开关柜电气参数

Switchgear technical data

额定电压kV 12

额定绝缘水平1min工频耐压(有效值)kV 42 雷电冲击耐压(峰值)kV 75

额定频率Hz 50

主母线额定电流 A 630,1250,1600,2000,2500,3150,4000 分支母线额定电流 A 630,1250,1600,2000,2500,3150,4000* 4秒热稳定电流(有效值)kA 16,20,25,31.5,40**

额定动稳定电流(峰值)*** kA 40,50,63,80,100

Rated voltage kV 12

Rated power-frequency withstand voltage(1min) kV 42

Rated lightening impulse withstand voltage kV 75

Rated frequency Hz 50

Rated main bus bar current A 1600,1200,2500,3150,4000

Rated branching bus bar current A 630,1250,1600,2000,2500,3150,4000* 4s Short-time withstand current(rms.)kA 16,20,25,31.5,40

Peak withstand current(peak.)kA 40,50,63,80,100,125

*需装备通风装置

with forced ventilation.

**40 kA为3秒

3 second for 40kA

***仪用互感器的短路容量应单独考虑

The short-circuit capability of transformer for measure should be considered by oneself.

2.2 耐内部故障电弧性能

Performance bearing inside fault arc

KYN28-12开关柜在设计上已考虑到开关柜内部故障电弧的问题,根据GB3906和IEC298进行了严格的试验,能有效地保证设备及操作人员的安全。

KYN28-12 has been considered with the problem of inside fault arc in switchgear on design.

It is tested strictly according to GB3906 and IEC298, thus ensure effectively the safety of equipments and operation personnel.

2.3外形尺寸和重量

Outline dimensions and weight

外形尺寸

Outline dimensions

高度a (mm)2200 宽度b (mm)

分支母线额定电流为1250A及以下,短路开断电流为31.5kA及以下800/650* 分支母线额定电流为1600A及以下,短路开断电流为40kA800 分支母线额定电流为1600A及以上1000 深度c (mm)1350/1500

Height a 2200(mm)Width b

Rated branching bus bar current up to 1250A,

Rated short-circuit breaking current(rms.) up to 31.5KA800/650*(mm)Rated branching bus bar current up to 1600A,

Rated short-circuit breaking current(rms.) up to 40KA 800 (mm) Rated branching bus bar current over 1600A,1000(mm) Depth c 1350/1500 (mm)重量800~1200kg,详细资料见表1。

*配VD4断路器可用。

Weight 800~1200kg,for table 1showing.

*Suitable for VD4 being equipped.

表1 安装要求的尺寸及柜体重量

柜内设备型式移开式移开式移开式

柜深 c 柜宽 b 距墙距离mm

mm

mm

1500

650

800

1500

800

1000

1500

1000

1200

走廊宽度* mm 1000 1100 1200 安装通道(室内通道要求)

宽度

长度(深)门框要求宽度

高度mm

mm

mm

mm

1000

1500

800

2200

1000

1500

1000

2200

1200

1500

1200

2200

重量(近似值)地坪承重

kg

kg/m2

800

1000

850

1000

1200

1000

List 1 Dimension and weight for switchgear installation

Mode of device in switchgear Removing

type

Removing

type

Removing

type

depth c Width b Distance to wall mm

mm

mm

1500

650

50

1500

800

50

1500

1000

50

The width of Passage * mm 1000 1100 1200 Assemble walkway

Demand of passage indoor

Width

Length(Depth)Demands of door frame Width

Height** mm

mm

mm

mm

1000

1500

800

2000

1000

1500

1000

2200

1200

1500

1200

2200

Mass(approximation)Weight terrace beared

kg

kg/m2

800

1000

850

1000

1200

1000

*取决于最大柜宽

Depend on the most width of the switchgear.

3 开关柜结构概述

Structure general of switchgear

3.1基本结构(图3/1)

Basic structure(Figure3/1)

开关柜由固定的柜体和真空断路器手车组成,这是它的基本结构。开关柜及安装的电气元件见图3/1。进线柜或出线柜是基本柜方案,并有派生方案,如母线分段柜或计量柜等。此外,尚有配置固定式负荷开关、真空接触器手车、隔离手车等方案。开关柜靠墙或面对面安装。结构细节和柜内安装设备,可见订货文件。

The basic structure of switchgear panel comprises the panel itself a removing part. The panel and main components can see in figure 3/1.Incoming-line panel or outgoing-line panel are diagram of basic switchgear panel,there are other derivative diagram,for example ,contact panel or metering panel .in addition,There are so many diagram of the switchgear panel with stationary type load switch、(SF6)VCB truck、VC truck、Disconnect truck. The panel has two maintenance modes. That is single-face maintenance and double-face maintenance. The detail of structure and main components, can reference order document.

3.2外壳和隔板

Enclosure and clapboard

开关柜的外壳和隔板由优质钢板制成,具有很强的抗氧化、耐腐蚀功能,且刚度和机械强度比普通低碳钢板高。三个高压室的顶部都装有压力释放板。出现内部故障时,高压室内气压升高,由于柜门已可靠密封,高压气体将冲开压力释放板释放出来。相邻的开关柜由各自的侧板隔开,拼柜后仍有空气缓冲层,可以防止开关柜被故障电弧贯穿熔化。低压室D 装配成独立隔室,与高压区域分隔开。隔板将断路器室B和电缆室C隔开,即使断路器手车移开(此时活门会自动关闭),也能防止操作者触及母线室A和电缆室C内的带电部分。卸下紧固螺栓就可移开水平隔板,便于电缆密封终端的安装。

The enclosure and clapboard of the switchgears is made up from high quality steel, have very strong function to resistant oxidation and corrosion, and its rigidity and mechanical robustness is higher than common low-carbon steel board. Have been installed release of pressure plate on the top of three high-pressure chambers. When appear internal fault electric arc, air pressure heightens in high-pressure chamber, because that the doors of switchgear is already airtight coating, the pressure gas will clash out the release of pressure plat. Adjacent switchgears are isolated by its self side board, after putting the switchgears together, air buffer layer exist yet, it may prevent the switchgears from pronging and melted by electric arc. Low-voltage vault D is separate room with high-pressure area. Clapboard space isolate the VCB vault B with cable vault C, even if VCB. truck is moved(here the valve is closed self-motion),can prevent the operator from touching the electrification parts of bus bar vault A and cable vault C. releasing the tighten bolt, the level clapboard is removed, convenient for installation of cable seal terminal.

3.3开关柜内的小室

Compartments in switchgear

断路器室(见附图3/1,3/3,3/5,3/6)

VCB vault (figure 3/1,3/3,3/5,3/6 showing)

断路器手车装在有导轨的断路器室B内,可在运行、试验/隔离两个不同位置之间移动。当手车从运行位置向试验/隔离位置移动时,活门会自动盖住静触头,反向运行则打开。手车能在开关柜门关闭的情况下操作,通过门上的观察窗可以看到手车的位置、手车上的ON (断路器合闸)/OFF(断路器分闸)按钮、合分闸状态指示器和储能/释放状况指示器。

VCB truck is installed in VCB vault B with track, may move in the middle of the position to service and test/disconnected. While the truck move from service position to test/disconnected position, the valve can cover un-move contact in self-motion, open when moving reverse. The truck can be operated when the truck vault door is closed, while you can watch the position of the truck, on (VCB tripping)/off(VCB closing) push knob in the truck, close and open indicator and charging/releasing indicator by inspection window.

断路器手车

VCB truck

手车可采用手动进行移动。框架由合金钢板拼装而成,上面装断路器和其他设备。具有弹簧触头系统的触臂装在断路器的极柱上,当手车插入到运行位置时起电气联接作用。手车于开关柜之间的信号、保护和控制线,用一个控制线插头联接。手车刚插入开关柜就固定在试验/隔离位置,同时也可靠地联接到开关柜的接地系统。手车的所在位置,能通过观察窗或装在低压室面板上的手车电气位置指示器看到。

除真空断路器外,手车可配真空接触器、隔离装置和计量设备等。

The truck can be moved by manual. The structure of the truck is made of the steel, the VCB and other equipments are installed on top of it. The arm of spring bush is installed on the pillar of the VCB,When the truck is pushed on the service position, it has the effect of electrical interlocking. The signal 、protection、control line between the truck and the switchgear is connection with the pin of control line. The truck is fixed on the test position as soon as it is pushed into the switchgear, and be connection to the earth system of the switchgear. The position of truck will be seen by the lamp that is installed on the looking window or the panel of low-voltage.

Beside the VCB, the Truck can be equipped the vacuum contactor 、isolated device and the measuring equipment.

母线室

Bus bar compartment

母线从一个开关柜引至另一个开关柜,通过分支母线和套管固定。矩形的分支母线直接用螺栓联接到主母线上,不需任何联接夹。所有母线和分支母线都用热缩套管覆盖。套管板和套管将柜与柜之间的母线隔离起来,并有支撑作用。对电动应力大的开关柜,一般需要这种支持。

The bus bar from one switchgear to the other switchgear is fixed with the bushing and the ramus bus .The ramus bus is connection to the main bus with the bolt, it needn’t any clip. All bus and the ramus bus are covered with pyrocondensation bushing. The panel of bushing and bushing are isolated between the switchgear and the switchgear. And it has the effect on supporting.

电缆室(图3/1)

Cable compartment(drawing 3/1)

电流互感器和接地开关装在电缆室后部。电缆室也可安装避雷器。当电缆室门打开后,有足够的空间供施工人员进入柜内安装电缆(最多可并接6根)。盖在电缆入口处的底板可采用非导磁的不锈钢板,是开缝的,可拆卸的,便于现场施工。底板中穿越一、二次电缆的变径密封圈开孔应与所装电缆相适应,以防小动物进入。

对于湿度较大的电缆沟,建议用防火泥、环氧树脂将开关柜进行密封。

CT and earth switch are installed on the back of the Cable Compartment. The Surge arrester is also installed on the Cable Compartment. When the truck and the horizontal panel are moved .There is enough room so that the worker install the cables (the most is 6).The bottom of panel that lie on the incoming of cable in made of the stainless steel panel,It is uncork, disassembly so that working on the local. The airplane of panel where is together secondary cable make sure as same as the installed cable prevent the small animal being into it.

For the cable trench in humidity,It is suggested that the switchgear is airproofed with fireproofing mud and epoxide resin.

低压室(图3/1、3/2)

Low-voltage compartment (figure 3/1、3/2)

开关柜的二次元件装在低压室内及门上。控制线线槽空间宽裕,并有盖板,左侧线槽

用来引入和引出柜间连线,右侧线槽用来敷设开关柜内部连线。低压室侧板上有控制线穿越孔,以便控制电源的联接。

Low-voltage components of switchgear are installed in low-voltage compartment and on door. Control wiring trunking has ample space and cover board. Nearside wiring trunking is used to introduce and educe the wiring between switchgears, starboard wiring trunking is used to lay intramural wiring in switchgear. Traversing hole for control wiring on side board in low-voltage compartment is used to connect with control power supply.

3.4防止误操作的联锁/保护

Interlocks/protections for preventing mishandling

具备一系列的联锁装置,从根本上防止出现危险局面和可能引起严重后果的误操作,因此有效地保护了操作人员和开关柜。联锁装置地功能如下:

A series of interlocks are provided to prevent mishandling, thus protecting both personnel and switchgear itself. The function of interlocks is following:

断路器和接地开关在分闸位置时,手车能从试验/隔离位置移动到运行位置。在这种分闸状态下,反向移动也行(机械联锁)。

VCB and earth switch in the OPEN position, you can move the truck from the test/disconnected position to service position. On this state, it is be able to move reversely yet(electric interlock).

手车已完全处于试验或运行位置时,断路器才能合闸(机械和电气联锁)。

Only the truck quite in the test or service position, VCB can be closed (machine and electric interlock).

手车在试验或运行位置而没有控制电压时,断路器不能合闸,仅能手动分闸(电气联锁)。

The truck is in the test or service position, but no given control voltage, VCB is not closed, only manual open (electric interlock).

手车在运行位置时,控制线插头被锁定,不能拔出。

The truck in the service position, control wiring plug have been locked, don’t be pull out.

手车在试验/隔离位置或移开时,接地开关才能合闸(机械联锁)。

Only the truck have been in the test/disconnected position or moved out, the earth switch is permitted to be closed (machine interlock).

接地开关关合时,手车不能从试验/隔离位置移向运行位置(机械联锁)。

When earth switch has been closed, the truck don ’t move from the test/disconnected position to service position (machine interlock).

可在手车和/或接地开关操动机构上安装附加联锁装置,如闭锁电磁铁,用户在订货时

应提出要求。

Some additive interlocks can be assembled on the truck and/or earth switch operating mechanism, as case electromagnet, user should provide the required information when ordering.

隔室:Compartment

A

母线室

Bus

bar

compartment C

电缆室

Cable compartment

B

断路器室 Truck compartment

D

Low-voltage compartment

主要部件:Master parts 1 母线 Bus bar 2 绝缘子 Insulator 3 静触头 Fixed contact 4 触头盒 Bush 5

电流互感器 Current

transformer 6

接地开关 Earth switch

7 电缆终端 Cable terminal 8 避雷器 Arrester 9

零序电流互感器 Zero -sequence current

10

断路器手车 VCB truck

10.1

滑动把手 Slip handle

10.2 锁键(联到滑动把手) Lock key (link to sliding handle )

11

控制和保护单元 Control and protection unit 12

穿墙套管 W all bushing

图3/1:KYN28-12进线或出线柜基本结构剖面图

Figure3/1:Basic structural sectional view of incoming line or outgoing line 主要附件:Master accessories

13 丝杆机构操作孔

Operation hole of screw machine 14 电缆夹

Cable grip

15.1 电缆密封圈Cable lock-ring 15.2 连接板Connection board

16 接地排Earth bus 17 二次插头Control wiring plug

17.1 联锁杆Interlock lever 18 压力释放板Pressure-relief plate

19 起吊耳Flying rings 20 运输小车Transport cart

20.1 锁杆Lock bar 20.2 调节轮Regulating wheel 20.3 导向杆Guide bar

图3/2低压室内部视图,端子排座可向上旋转以便辅助开关的安装,控制线的布线和接线Figure 3/2 Intramural view in low-pressure chamber. In order to install auxiliary switch, control

wiring and connection, the terminal foundation can be circumrotated upwards.

Figure 3/3 Door of the VCB truck compartment is opened, the truck in the test position

图3/4 断路器手车在向运行位置插入

Figure 3/4 Insert the VCB truck to service position

图3/5 断路器手车 Figure 3/5 VCB truck

21 活门 V alve 10.3

梅花触头Contactor 4 触头盒 Bush 10.4 触臂 Contact arm

10

断路器手车 VCB truck

相关文档