Model UT511 OPERATING MANUAL
TITLE PAGE
1
Introduction
Unpacking the Meter Safety Information
International Electrical Symbols Battery Saver (Sleep Mode)Battery Indication The Meter Structure Display
Key Functions
Measurement Operation A.Measuring Voltages
B.Measuring Insulation Resistance a) Continuous Measurement b) Timed Measurement
c) Polarization Index (PI) Measurement d) Compare Function
C. Low Resistance Measurement 555788910121515161718181920
2
21222222242424252526262627
TITLE PAGE
The Use of Power Adaptor Maintenance
A. General Service
B. Replacing the Battery Specifications
Safety and Compliances Physical Specifications General Specifications Feature Summary
Detailed Accuracy Specifications A. Voltage Measurement
B. Insulation Resistance Measurement
C. Low Resistance Measurement
Table Title Page
1. Unpacking Inspection
2. International Electrical Symbols
3. Battery Indication
4. Meter Front Description
5. Meter Side Description
6. Display Description
7. Key Description 5 7 8 9 10 11 12
3
Figure Title Page
1. The Meter Front Structure
2. The Meter Side Structure
3. The Display
4. Voltage Measurement
5. Insulation Resistance Measurement
6. Low Resistance Measurement
7. The Use of Power Adaptor
8. Battery Replacement 9 10 10 15 16 20 21 23
4
Introduction
Uni-Trend Model UT511 insulation resistance tester (hereafter, “the Meter”) is a handheld instrument designed primarily to make resistance/ insulation resistance measurement.
Unpacking the Meter
The Meter includes the following items:
Table 1. Unpacking Inspection
Item 1
2
3
4
5
6Description
English Operating Manual
One plug test lead to one alligator
Two plugs test lead to one
alligator
1.5V Battery (R14 or LR14)
Tool Box
Power adaptor (optionally,
available at extra cost)
Qty
1 piece
2 pieces
1 piece
8 pieces
1 piece
1 piece
In the event you find any missing or damage, please contact your dealer immediately.Safety Information
This Meter complies with the standards IEC61010 safety measurement requirement: in pollution degree 2, overvoltage category (CAT. III 600V, CAT.II 1000V) and double insulation.
CAT II: Local level, appliance, PORTABLE EQUIPMENT etc., with smaller transient voltage overvoltages than CAT. III
CAT III: Distribution level, fixed installation, with smaller transient overvoltages than CAT. IV
Use the Meter only as specified in this operating manual, otherwise the protection provided by the Meter may be impaired.
Danger identifies conditions and actions that pose hazard(s) to the user.
Warning identifies avoiding electric shock.
Caution identifies conditions and actions that may damage the Meter and carrying out accurate measurement.
5
International electrical symbols used on the Meter and Array
in this Operating Manual are explained on page 4~5.
6
7
International Electrical Symbols
International symbols on the Meter and in this manual are explained in Table 2.
Table 2. International Electrical Symbols
Battery Saver (Sleep Mode)
The Meter enters the Sleep Mode and blanks the display if there is no button press for 15 minutes. This is done to conserve battery power. The Meter comes out of Sleep Mode when ON/OFF button is pressed two times. The 15 minutes timer is disabled during any insulation resistance measurement. The time period starts immediately following any measurement.Battery Indication
There is a battery indicator shows on the display upper left hand corner. Below Table 3 is the explanation:
Table 3. Battery Indication
8
9
The Meter Structure
Below Figure 1 and Table 4 shows the Meter front structure and description
Figure 1. The Meter Front Structure
Table 4. Meter Front Description
10
Below Figure 2 and Table 5 shows the Meter side structure and description
Figure 2. The Meter Side Structure (Side View)
Table 5. Meter Side Description
1 Safety Shutter
2 Power adaptor Input Terminal
Display
Table 6 and Figure 3 describe the display.
Figure 3. Display
Table 6. Display Description
Number 1
2
3
4
5
6
7
8
9
10
11Meaning
Indicator for DC voltage
Indicator for data store full
Indicator for clearing
Indicator for AC voltage
Indicator for timer
Step symbol
Indicates selected pass/fail compare
value
Indicates for negative reading
Timer 1 symbol
Timer 2 symbol
Data store is on
Number
12
13
14
15
16
17
18
19
20
21
Meaning
Data recall is on
Indicator for polarization index
Unit symbols
The continuity buzzer is on
Compare feature pass
Analogue bar graph
Risk of electric shock
Compare feature fail
Indicator for power adaptor
Battery life indicator
11
Key Functions
Table 7. Key Description
12
13
Table 7. Key Description
14
Table 7. Key Description
Press to initiate low resistance measurement
Pres to initiate voltages measurement
Lo DVC /ACV
Emergency stop button. Press this
button when the Meter is hang and cannot turn off the power.
E-STOP
Measurement Operation
Below section explains how to make measurements.
A. Measuring Voltages Figure 4. Voltages Measurement l Special care should be taken when measuring high voltage.
Caution
Warning
l To avoid harms to you or damages to the Meter, please do not attempt to measure voltages higher than 1000V DC or 750V AC, although readings may be obtained.
To measure voltages, set up the Meter as Figure 4 and do the following:
Press DCV or ACV button to select DC voltage or AC voltage measurement
Insert the red test lead into the V terminal and the black test lead into the COM terminal.
Connect the red and black alligator clip to the circuit to be measured.
During measurement, when the red test lead is
negative voltage, then “-“ shows on the display. 1.
2.
3.
4.
Black
Red
15
16
l When voltage measurement has been completed, disconnect the connection between the testing leads and the circuit under test and remove testing leads away from the input terminals of the Meter.
Note
B. Measuring Insulation Resistance
Figure 5. Insulation Resistance Measurement
Red
Black
l l l l l l 17
When performing insulation resistance tests,
remove all power from the circuit to be measured and discharge all the power.
Do not short circuit two test leads under high
voltage status.
Do not measure insulation resistance after high
voltage output.
Do not measure over 10 seconds when:
100V measure resistance lower than 500k 250V measure resistance lower than 1M 500V measure resistance lower than 2M 1000V measure resistance lower than 5M When the measurement is completed, don’t
touch the circuit as the circuit has already stored capacitance which may cause electric shock.Don’t touch the test leads even after it has been
removed from the circuit until voltages are all released.
Caution
To measure insulation resistance, set up the Meter as Figure 5 and do the following:
1.2.3.4.5.Press HO button to select insulation resistance measurement.
Press and button to select voltages of 100V,250V, 500V or 1000V.
Insert the red test lead into the LINE terminal and the black test lead into EARTH terminal.
Connect the red and black alligator clip to the circuit to be measured, positive voltage output from LINE terminal.
Choose below insulation resistance measurement mode.l l Press TIME button to select continuous
measurement mode, there is no timer icon on the LCD.
Press and hold TEST button for 1 second to
carry out continuous measurement. Output insulation resistance testing voltage, TEST button light up,
Press TEST button to close the insulation resistance
measurement voltage when measurement is
completed. TEST
The LCD shows the current insulation resistance
measurement value.
Press TIME button to select timed measurement
mode, the LCD displays TIME 1
Press , and STEP buttons to set the time
(00:05~29:30).
Then press and hold TEST button for 1 second to
carry out timed measurement. TIME 1
displayed and blinked on the LCD on every 0.5
seconds.
When the set time is reached, the insulation
resistance measurement voltage will be closed and
the measurement will be automatically stopped.
The LCD displays the insulation resistance reading.
l
l
l
l
Press TIME button to select timed measurement
mode, the LCD displays TIME 1
Press , and STEP buttons to set the time
(00:05~29:30).
Press TIME button again. TIME 2, PI
appear on the LCD.
Press , and STEP buttons to set the time
(00:10~30:00).
Then press and hold TEST button for 1 second to
carry out timed measurement.
TIME 1
LCD on every 0.5 seconds before TIME 1 set time
is reached.
TIME 2
LCD on every 0.5 seconds before TIME 2 set time
is reached.
When the two set time are reached, the insulation
resistance measurement voltage will be closed and
the measurement will be automatically stopped.
The LCD displays the polarization index reading.
l
l
l
l
l
l
l
l
18
19
Press , to set through the polarization index,
TIME 2 insulation resistance reading and TIME 2insulation resistance reading.
l Information:
PI = 3 minutes ~10 minutes reading / 30 second ~1minutes reading
PI Standard 4 or more The best 4~2Good
2.0~1.0Warning
1.0 or less Bad
Press COMP button to select compare feature.
COMP symbol displays on the LCD.
Press , and STEP buttons to set the compare
value. The minimum value is 1M The maximum value is the maximum tested voltage allowable measurement value.
Press and hold TEST button for 1 second to carry
out the measurement.
The NG symbol will display if the insulation resistance
value is smaller than resistance value. Otherwise GOOD symbol will be displayed.
l l l l