CSM_K3GN_DS_E_3_1
1/32 DIN Digital Panel Meter
K3GN
1/32 DIN Digital Panel Meter for Downsizing Equipment and Control Panels
?Compact size: 48 x 24 x 83 (W x H x D).
?Multi-input compatible: DC voltage/current, rotary pulse.?T wo display colors (switchable): green/red.?Selectable outputs.
?CE marking and UL/CSA approval.
?Splash-proof construction (NEMA4X: equivalent to IP66).
Refer to Safety Precautions for All Digital Panel Meters
.
Model Number Structure
■Model Number Legend
1.Input Type ND:DC voltage/current, NPN PD:DC voltage/current, PNP
2.Output Type C: 2 relay contact outputs (SPST -NO)
C-FLK: 2 relay contact outputs (SPST -NO) and RS-485C-L1: 2 relay contact outputs (SPST -NO) and DC current (0 to 20 mA, 4 to 20 mA)C-L2: 2 relay contact outputs (SPST -NO) and DC voltage (0 to 5 V , 1 to 5 V , 0 to 10 V)T1: 3 transistor outputs (NPN open collector)
T1-FLK: 3 transistor outputs (NPN open collector) and RS-485T1-L1: 3 transistor outputs (NPN open collector) and DC current (0 to 20 mA, 4 to 20 mA)T1-L2: 3 transistor outputs (NPN open collector) and DC voltage (0 to 5 V, 1 to 5 V , 0 to 10 V)T2: 3 transistor outputs (PNP open collector)
T2-FLK: 3 transistor outputs (PNP open collector) and RS-4853.
Option None:None -400:Normally energized relays 4.Supply Voltage 24 VDC: 24 VDC
K3GN
Ordering Information
■List of Models
Note:Refer to page 5 for information on models with normally energized relays.
Specifications
■Ratings
Note:1. A control power supply capacity greater than the rated capacity is required when the Digital Panel Meter is turned ON. Do not forget to
take this into consideration when using several Digital Panel Meters. When power is supplied, all indicators will light and outputs will be OFF . When using startup compensation time operation, the display will read “00000” and all outputs will be OFF .2.Enabled only when using DC voltage/current input. (Min.time for control signal input: 80 ms)
Supply voltage Input type
Output type
Model
Judgement output
Data transmission output
24 VDC
DC voltage, DC current, or NPN input 2 relay contact outputs (SPST -NO)
None K3GN-NDC 24 VDC RS-485
K3GN-NDC-FLK 24 VDC DC current (0 to 20 mA, 4 to 20 mA)K3GN-NDC-L1 24 VDC DC voltage (0 to 5 V , 1 to 5 V , 0 to 10 V)
K3GN-NDC-L2 24 VDC 2 relay contact outputs
(SPST -NO)
Normally energized relays (See note.)
None K3GN-NDC-400 24 VDC RS-485
K3GN-NDC-FLK-400 24 VDC DC current (0 to 20 mA, 4 to 20 mA)K3GN-NDC-L1-400 24 VDC DC voltage (0 to 5 V , 1 to 5 V , 0 to 10 V)
K3GN-NDC-L2-400 24 VDC 3 transistor outputs (NPN open collector)
None K3GN-NDT1 24 VDC RS-485
K3GN-NDT1-FLK 24 VDC DC current (0 to 20 mA, 4 to 20 mA)K3GN-NDT1-L1 24 VDC DC voltage (0 to 5 V , 1 to 5 V , 0 to 10 V)
K3GN-NDT1-L2 24 VDC DC voltage, DC current, or PNP input 2 relay contact outputs (SPST -NO)
None K3GN-PDC 24 VDC RS-485
K3GN-PDC-FLK 24 VDC 3 transistor outputs (PNP open collector)
None
K3GN-PDT2 24 VDC RS-485
K3GN-PDT2-FLK 24 VDC
Item
K3GN-ND
With DC voltage, DC current, and NPN input K3GN-PD
With DC voltage, DC current, and PNP input
Supply voltage
24 VDC
Operating voltage range
85% to 110% of the rated supply voltage
Power consumption (at max. load) (See note 1.) 2.5 W max. (at max. DC load with all indicators lit)Input signal DC voltage, DC current, no-voltage contact, open collector DC voltage/current input
A/D conversion Double integral method Pulse signal input
Pulse measurement method
Periodic measurement method External power supply None
Control input
Present value hold or forced zero (selectable) (See note 2.)
Outputs (Outputs depend on the model.)
Relay contact output 1 A, 30 VDC (resistive load), mechanical life: 50,000,000 operations min., electrical life: 100,000 operations min.
Transistor output
Max. load voltage: 24 VDC, Max. load current: 50 mA, Leakage current: 100 μ A https://www.wendangku.net/doc/866371530.html,munications output RS-485 (2-wire, half-duplex)
Linear output
DC current (0 to 20 mA DC, 4 to 20 mA: Load: 500 ? max., Resolution: Approx. 10,000)
DC voltage (0 to 5 VDC, 1 to 5 VDC, 0 to 10 VDC: Load: 5k ? min., Resolution: Approx. 10,000)
---Display Negative LCD (backlit LCD) display
7-segment digital display, character height: 7.0 mm, and single illuminated display
Main functions Scaling, prescaling, teaching, average processing, forced zero, display color selection, output type selection, key protection, startup compensation timer, hysteresis Ambient temperature Operating: ?10°C to 55°C (with no condensation or icing)Storage: ?25°C to 65°C (with no condensation or icing)Ambient humidity Operating: 25% to 85%Altitude 2,000 m max.
Accessories
Rubber packing, fixture, operation manual
K3GN
■Characteristics
■Input Ranges: Measurement Range and Accuracy
Note:The shaded ranges indicate default settings.
Item
K3GN-ND
With DC voltage, DC current, and NPN input
K3GN-PD
With DC voltage, DC current, and PNP input
Input signal
DC voltage/current (4 to 20 mA, 1 to 5 V , ±5 V , ±10 V)
No-voltage contact (30 Hz max. with ON/OFF pulse width of 16 ms min.)Open collector (5 kHz max. with ON/OFF pulse width of 90 μs min.)Displayable range 5 digits (-19999 to 99999)Sampling period 250 ms
Display refresh period Sampling period: 250 ms (at 4 Hz min.), 250 × Number of averaging times (ms) (with average processing selected), Input pulse cycle (at less than 4 Hz): Input pulse cycle × Number of averaging times
Comparative output response
time
(transistor outputs)
750 ms max. (transistor output)
(The time required for the judgment output to be output if the input signal rapidly changes from 15% to 95% or from 95% to 15%.)Linear output response time
750 ms max. (The time required for the analog output to be output if the output signal rapidly changes from 15% to 95% or from 95% to 15%.)
---Insulation resistance 20 M ? min. (at 500 VDC) between external terminal and case.Insulation provided between inputs, outputs, and power supply.Dielectric strength 1,000 VAC for 1 min between external terminal and case.
Noise immunity ±480 V on power supply terminals in normal mode, ±1,500 V in common mode, ±1 μs, or 100 ns for square-wave noise with 1 ns Vibration resistance Vibration frequency: 10 to 55 Hz, Acceleration: 50 m/s 2 for 10 min each in X, Y , and Z directions Shock resistance Models with transistor outputs: 150 m/s 2 three times each in 3 axes, 6 directions Models with contact outputs: 100 m/s 2 three times each in 3 axes, 6 directions Weight Approx. 100 g (Main Unit only)
Degree of protection
Front panel NEMA4X for indoor use (equivalent to IP66), Rear case IP20
Terminals
IP00 and finger protection (VDE0106/100)
Memory protection Non-volatile memory (EEPROM) (possible to rewrite 100,000 times) Approved standards UL508, CSA C22.2 No. 142EMC
(EMI)
EN 61326Industry Emission Enclosure:EN55011 Group 1 class A (EMS)
EN 61326Industry Immunity ESD:
EN 61000-4-2: 4 kV (contact discharge)
8 kV (air discharge)
Immunity RF-interference:EN 61000-4-3:10 V/m (amplitude-modulated,
80 MHz to 1 GHz)
Immunity Fast Transient Noise:EN 61000-4-4: 2 kV (power line)Immunity Burst Noise: 1 kV line to line (I/O signal line)Immunity Surge:EN 61000-4-5: 2 kV line to ground (power line)Immunity Conducted Disturbance EN 61000-4-6: 3 V (0.15 to 80 MHz) Immunity Power Frequency Magnetic EN 61000-4-8:30 A/m (50 Hz) continuous time
Input type
in-t
Analog
analg
Pulse
pulse
Remote
rmt
DC current input
DC voltage input
Rotary pulse
Analog range
range
4 to 20 mA
4-20
Analog range
range
1 to 5 V
1-5±5 V 5
±10 V
10
Pulse frequency
p-fre
30 Hz 30
5 kHz
5k
Range of display
from :9999 to 99999 using communications.
Connection terminal E -F
Connection
terminal D -E
Connection terminal
B -C
Input
impedance
60 ?
Input
impedance
1 M ? min.
------Measurement accuracy ±0.1% full scale ± one digit max. (at 23±3°C)
±0.1% full scale ± one digit max. (at 23±5°C)
±0.1% full scale ± one digit max. (at 23±5°C)
---
Current range
(mA)
20.004.000.00
Voltage
range (V)10.00
5.0000.000
?5.000?10.00
Frequency
range
(Hz)
5000400030002000
10000.0
5.500
0.000
5.500
?5.500
22.00
0.00
11.00
?11.00
30.000.05
5000
0.05
K3GN
■Input/Output Ratings
Relay Contact Output
(Incorporating G6K Relays)
Transistor Output
Communications Specifications
Linear Output
Item
Resistive load (cos φ = 1)Rated load
1 A at 30 VDC
Rated through current 1 A max. (at COM terminal)Max. contact voltage 60 VDC
Max. contact current 1 A (at COM terminal)Max. switching capacity 30 VA Min. permissible load (P level, reference value)10 mV , 10 μA
Mechanical life
50,000,000 operations min. (at a switching frequency of 36,000 operations/hr)
Electrical life (at an ambient
temperature of 23°C)
100,000 operations min. (at the rated load with a switching frequency of 1,800 operations/hr)
Rated load voltage 24 VDC Max. load current 50 mA Leakage current
100 μA max.
Item
RS-485
Communications method 2-wire, half-duplex Synchronization method Start-stop synchronization Baud rate
1,200/2,400/4,800/9,600/19,200bps Transmission code
ASCII
Commu-nications Reading/Writing to the K3GN Read/write comparative set values, read/write scaling values, enable/
disable the writing of data through
communications, forced-zero control, and other data.
Item
0 to 20mA
4 to 20mA
0 to 5 V 1 to 5 V 0 to 10V
Permissible load impedance 500 ? max. 5 k ? min.
Resolution Approx. 10,000Output error
±0.5% full scale
±0.5 full scale.
±0.15 V at 1 V or less (no output for 0 or less)
K3GN
Nomenclature
Name
Functions
1. Main display Displays process values, parameters, and set values.
2. Status indicators
OUT1Lit when output 1 is ON.OUT2Lit when output 2 is ON.
SV Lit when a set value is being displayed or changed.
T
Lit when the teaching function is enabled. Flashes when the K3GN is in teaching operation.
Lit when a calibration value is being displayed during user calibration. Flashes while reading a calibra-tion value.
ZERO Lit while the forced-zero function is activated.HOLD Lit when HOLD input is ON.
CMW
Lit when communications writing is “enabled” and is out when it is “disabled.”3. Level indicator Displays the current level that the K3GN is in. (See below for details.)4. Level Key Used to change the level.
5. Mode Key Used to allow the Main display to indicate parameters sequentially.
6. Shift Key Used to enable that set value to be changed. When changing a set value, this key is used to move along the digits.
7. Up/Zero Key
Used to change a set value. Used to set or clear a forced-zero function when a measurement value is being displayed. 1. Main display
2. Status indicators
3. Level indicator
4. Level key
2. Status indicators
7. Up/Zero key
6. Shift key 5. Mode key
Level indicator
Level
p
Protect Not lit
Operation a Adjustment s Initial setting
c Communications setting f Advance
d function setting u
User calibration
Models with Normally Energized Relays K3GN-NDC-@-400 24 VDC
?The drive operation for the output relay is reversed in these models.?Relay contacts can be made open (i.e., OFF) when comparative set values are being judged. This is effective when constructing systems that take failsafe measures into consideration.
List of Models
Models with Normally Energized Relays
K3GN-NDC-400 24 VDC K3GN-NDC-FLK-400 24 VDC K3GN-NDC-L1-400 24 VDC K3GN-NDC-L2-400 24 VDC
Relation between Output Type and Relay
Output Operation
K3GN
Connections
■Terminal Arrangement
Terminal No.
Name
Description
A -
B Operation power
Connect the operation power supply.
C -B Event input or pulse/contact input
Operates as follows depending on parameter setting:
?Holds process value.
?Calibrate the process value to zero and clear the forced-zero function.?Pulse or contact input.
C -A
D ,F -
E Analog input Connect the voltage or current analog input.G -H
Communications RS-485 communications terminals.Linear output
0 to 20 mA DC, 4 to 20 mA DC 0 to 5 VDC, 1 to 5 VDC, 0 to 10 VDC I ,K -L Outputs
Outputs relay or transistor outputs. There is also a PASS output for models with transistor outputs.
I ,J ,K -L
Output terminals
Input terminals
NC NC
u t o n s
K3GN ■Block Diagram
■Input Circuits
Analog Input (DC Voltage/Current) Use terminal 5 for analog common.
Comparative Output
Contact Output
Transistor Output Pulse Input/ Event Input (HOLD/ZERO)?If analog input is selected, 2 and 3 will be the event inputs. Select Hold/Zero with event input allocation.
?Use terminal 2 for the common terminal.
?Use the NPN open collector or the no-voltage contacts for the control input.
NPN Input
PNP Input
K3GN Linear Output
with L1 and L2 are connected internally.
Depending on how the common is wired for externally
connected devices, unwanted current paths for the linear
output signal in the circuit may prevent the output signal from
being output.
When connecting an external device, externally connect a relay
to the transistor output or provide another means of insulation.
K3GN
Operating Procedures
■Initial Setting Flowchart
Input Type
Note:The default value is analg : Analog input.
Analog Input Type
K3GN-ND @
Note:The default value is 4-20: 4 to 20 mA input range.
K3GN-NL @ (with Microvoltage Input)
Note:The default value is 199.9: ±199.9 mV input range.
Pulse Frequency
Note:The default value is 5k : 5 kHz input range.
Setting Scaling
Analog Input Signal
(Refer to page 10 if a pulse input is selected.)
?The scaling will be displayed on a line connecting two points by setting Display 1 for Input 1 and Display 2 for Input 2.
The position of the decimal point can be set as desired. If the decimal point is to be displayed, it is necessary to consider the number of digits to be displayed past the decimal point when setting the scaling display value.
Note: When pulse input is used, the base point is the 0 point, so the settings are only the input value and the display value.
Input type Parameter
Function
Analog
analg Selects the DC voltage/current signal input.Pulse pulse Selects the pulse input signal.
Remote
rmt
Displays the communications remote data from the Programmable Controller.
Input specification Parameter
Setting range
4 to 20 mA 4-20Values from ?19999 to 99999 can be displayed with scaling.The position of the decimal point can be set as desired.
1 to 5 V
1-5±5 V 5±10 V
10
Input specification Parameter
Setting range
±199.9 mV 199.9Values from ?19999 to 99999 can be displayed with scaling. The position of the decimal point can be set as desired.
±19.99 mV
19.99
Input specification Parameter
Setting range
0.05 Hz to 30.00 Hz 30Values from ?19999 to 99999 can be displayed with scaling. The position of the decimal point can be set as desired.
0 Hz to 5 kHz
5k
Instead of setting by inputting with the Shift Key and Up Key, current measurement values van be input as scaling input values for teaching. This is useful for making settings while checking the operation status of the K3GN.
For details on the operating procedures, refer to the K3GN Digital Panel Meter Manual (Cat. No. N102).
K3GN
?If the K3GN is used with a pulse signal input, the display value will be the input frequency if scaling is not performed.
Display the rate of rotation or the speed of a device or machine to which the K3GN is mounted by converting using scaling.
The relation between input f (Hz) and display D is expressed in the form D = f x a (factor). The value depends on the display unit. The formula will be comprised as follows:
Display using rpm: D = f x 1/N x 60, N = Number of pulses per rotation, f = Input pulse frequency (Hz) (i.e., number of pulses in one second)Display using m/min: D = f x π d x 1/N x 60, π d = Circumference length (m) per rotation
Output 1 Type
Note:The default value is hi : Upper limit.Prescaling Example
To display the rotational speed of a device that outputs five pulses per rotation:
D = f × 1/5 × 60, and,
If f=1, D = 12, so
The setting will be completed by inputting inp :1 and dsp :12.
Output 2 Type
Note:The default setting is lo : Lower limit.
The output operations can be selected separately for OUT1 and OUT2. Output type Parameter
Function
Upper limit
hi Output turns ON if the
measurement value ≥ comparative set value 1.
Lower limit lo Output turns ON if the
measurement value ≤ comparative set value 1.
Upper and lower limits
hi-lo
The comparative upper-limit set value and comparative lower-limit set value can be set separately and expressed high and low.Output turns ON if the
measurement value ≥ comparative upper-limit set value 1 or if the measurement value is ≤
comparative lower-limit set value 1.
Output type Parameter
Function
Upper limit
hi Output turns ON if the
measurement value ≥
comparative set value 2.
Lower limit
lo Output turns ON if the
measurement value ≤ comparative set value 2.
Upper and lower limit
hi-lo
The comparative upper-limit set value and comparative lower-limit set value can be set separately and expressed high and low.Output turns ON if the
measurement value ≥ comparative upper-limit set value 2 or if the measurement value is ≤
comparative lower-limit set value 2.
Upper Limit
Lower Limit
Upper and Lower Limits
Upper Limit 2-stage Output
Threshold Output
Combination of Upper Limit and Upper/