Monitoring Relays

Product Description

?TRMS 3-phase over and under voltage,

phase sequence and phase loss monitoring relays ?Detect when all 3 phases are present and have the

correct phase sequence (except for N versions)

?Available versions (W4) supplied between phase and

neutral

?Detect if all the 3-phase-phase or phase-neutral volt-ages are within the set limits

?Upper and lower limits separately adjustable ?Measure on own power supply

?Selection of measuring range by DIP-switches ?Adjustable voltage on relative scale ?Adjustable delay function (0.1 to 30 s)?Output: 8 A SPDT relay N.E.

?For mounting on DIN-rail in accordance with

DIN/EN 50 022 (DPB01) or plug-in module (PPB01)

?22.5 mm Euronorm housing (DPB01) or 36 mm plug-in module (PPB01)

?LED indication for relay, alarm and power supply ON

Type Selection

Mounting Phase sequence Output Supply:

Supply:

Supply:

detection 208 to 240 VAC 380 to 415 VAC 380 to 480 VAC DIN-rail yes SPDT DPB 01 C M23DPB 01 C M48 W4DPB 01 C M48Plug-in yes SPDT PPB 01 C M23PPB 01 C M48 W4Plug-in yes SPDT PPB 01 C M48

DIN-rail no SPDT DPB 01 C M23 N DPB 01 C M48 N W4DPB 01 C M48 N

Plug-in no SPDT PPB 01 C M23 N

PPB 01 C M48 N W4Plug-in

no

SPDT

PPB 01 C M48 N

True RMS 3-Phase, 3-Phase+N, Multi-function Types DPB01, PPB01

Input Specifications

3-phase or 3-phase+neutral line voltage monitoring relay for phase sequence, phase loss, over and under voltage (separately adjustable set

points) with built-in time delay function.

Supply ranges from 208 to 480 VAC covered by two multivoltage relays.

DPB01PPB01

DPB01, PPB01

Mode of Operation

Connected to the 3 phases (and neutral) D

B01 and P P B01 operate when all 3phases are present at the same time, the phase sequence is correct (not N versions) and the phase-phase (or phase-neutral)voltage levels are within set limits.

If one or more phase-phase or phase-neutral voltages exceeds the upper set level or drops below the lower set level, the red LED starts

flashing 2 Hz and the output relay releases after the set time period. In any case if phase-neutral measurement is selected both phase-phase and phase-neutral voltages are monitored. If the phase sequence is wrong or one phase is lost,the output relay releases immediately.

Only 200 ms delay occurs.The failure is indicated by the red LED flashing 5 Hz during the alarm condition.

Example 1

(mains network monitoring)The relay monitors over and under voltage, phase loss and correct phase sequence.

In case of N versions, the relay monitors over and under voltage.

Example 2

(load monitoring)

The relay releases in case of interruption of one or more phases, when one or more voltages drop below the lower set level or exceed the upper set level.

Output Specifications

DPB01, PPB01

Adjust the input range set-ting the DIP switches 3 and 4as shown below.

Select the desired function setting the DIP switches 1and 2 as shown below.

To access the DIP swiches open the grey plastic cover as shown below

Selection of level and time delay:

Upper knob:

Setting of lower level on rel-ative scale.

Centre knob:

Setting of upper level on rel-ative scale.

Lower knob:

Setting of delay on alarm time on absolute scale (0.1to 30 s).

Function/Range/Level and Time Delay Setting

Operation Diagrams

(*) N versions don’t detect incorrect phase sequence.

Wiring Diagrams

Dimensions

Note

When DPB01 or PPB01 is used with phase indicator lamps (see examples in the following diagrams), the lamp H1 or H2might be dimly lit when there is a phase loss in L1 or L2. This might happen if the lamps used are the typical low power indi-cator lamps, and there are no other loads present.

This fact can be avoided by using W4 models. Note that the neutral must be always connected to the device.H1

H1

DPB01, PPB01