include a recessed mounting option, interchangeable ion, thermal detectors, a vari-

ety of mounting bases, and a full line of optional accessories.

Ionization.All 400 Series ionization smoke detectors include a specially designed dual

source, dual unipolar detector chamber design which will sense the presence of smoke

particles produced by fast combustion as well as slow smoldering fires. This chamber

exhibits increased stability, significantly reduces nuisance alarms, and provides better

performance at higher air velocities.

Thermal.The 400 Series thermal rate-of-rise with fixed heat detector contains a

unique dual thermistor heat sensing circuit to provide maximum performance and

solid state reliability. The Model 5451 is designed to initiate an alarm at 135°F and

to respond to a temperature increase in excess of 15° per minute. This enables the

heat detector to communicate an alarm to the central control panel prior to reaching

the static set point for these high rates of rise, providing a timely response to both

rapid and slow temperature increases. This model should be used in applications

where rapid response is desired and where rapid temperature increases would only be

caused by a fire emergency.

SSV120-6

Wide variety of mounting bases with

built-in shorting spring

Detector head plugs easily into base

Built-in test switch

Field sensitivity metering of detector to

meet the requirements of NFPA 72

Built-in tamper-resistant feature

SEMS screws for easy wiring

Optional recessed mounting

Removable cover and insect screen for

field cleaning

元器件交易网https://www.wendangku.net/doc/9f16785135.html,

Mounting Base Selection Guide Base Model

Loop Current

Alarm

Nominal Current Draw Number Version Type Limit Resistor Contact Type Voltage on Alarm (mA)B401B UL/ULC 2-wire* No — 12/24VDC?? 10–100**B401BR UL/ULC 2-wire* Yes — 24VDC 10–62B402B UL/ULC 4-wire Yes Form A&C 24VDC 14–39B404B UL/ULC 4-wire Yes Form A&C+A 120VAC

75 mA AC Max

Supervisory B406B UL/ULC/EN-54 2-wire* No Form C 24VDC 12–100**B401? UL/EN-54 2-wire* No — 12/24VDC?? 10–100**B401R?

EN-54

2-wire*

Yes

24VDC

10–62

*Functionality contingent on panel compatibility. **Must be limited by control panel.

Operating Voltage/Alarm Current: Mounting base dependent (see chart on page 2)Standby Current:Ion:

120 μA maximum Thermal:

100 μA maximum Sensitivity:

1.9% + ±6%/ft. Ion Weight:1451:

0.5 lb. (227 gm) 5451:

0.3 lb. (136 gm)

Size:

3.2”/8.1 cm height

4.0”/10.2 cm diameter, unflanged base

6.2”/15.7 cm diameter, flanged base

Construction:

Flame retardant Noryl plastic Operating Temperature:1451: 32°F to 120°F (0°C to 49°C) 5451: 32°F to 100°F (0°C to 38°C)Alarm Point, Thermal:

135°F (57.2°C) or 15°F/min. rate of rise

Humidity Range:

10 – 93% RH non-condensing Air Velocity Rating:

Ionization: 1200 fpm maximum Smoke Detector Spacing:

For ion detectors on smooth ceilings (as defined in NFPA 72), spacing of 30 feet (900 sq. ft.) may be used as a guide. For thermal detectors on smooth ceilings (as defined in NFPA 72), spacing of 50 feet (2500 sq. ft.) may be used. Other spacing may be used depending on ceiling height, high air movements, and other conditions or response requirements.

Specifications

Junction Box Selection Guide* Single

Gang 3.5” Octagon 4” Octagon 4” Square 50 mm 60 mm 75 mm B401/B401R No No No No Yes Yes No B401B/BR

Yes

Yes Yes Yes No No No B402B/B406B Yes Yes Yes Yes Yes Yes Yes B404B

No

No

Yes

Yes

No

No

No

* Box depth contingent on base and wire size.

Refer to National Electrical Code of local applicable codes for appropriate recommendations.

Relay Contact Ratings: Resistive or Inductive (60% power factor) load. Form A: 2.0A at 30 VAC/DC

Form C: 0.6A at 110VDC, 2.0A at 30VDC 1.0A at 125VAC, 2.0A at 30VAC

?Flangeless base

?? Although B401B and B401 bases are capable of operating at 12 and 24 VDC, they cannot be used with the 5451 in 12 V applications.

R E S I S T O R

120 VAC

120 VAC

EOL

RESISTOR

B401 Series

B402B

B406B

Ordering Information

Part No. Description

1451 Ionization detector. Must be mounted to one of the B40X series bases listed in Mounting Base Guide.

1451A Same as above, Canadian model

5451 Fixed heat detector with rate-of-rise. Alarm point at 57.2°C (135°F). Must be mounted to one of the 400

Series Bases listed in Mounting Base Guide.

Accessories Description

RA400Z Remote annunciator for 2- or 4-wire systems, 3–32V. Use with ion and photo plug-in detectors.

Fits standard U.S. single gang electrical box.

B401BH Sounder base with B401. Requires an external 24 VDC power supply.

Mounts to 4” square electrical box (11/2” minimum depth).

MOD400R Detector sensitivity test tool. (See below.) Use with most analog or digital multimeters.

Satisfies requirement of NFPA 72 for sensitivity testing. (See below.)

RMK400 Recessed mounting kit for use with B401 or B401R mounting bases only. (See below.)

SMK400 Surface mounting kit provides for entry of surface wiring conduit.

For use with B401 or B401R mounting bases only.

EOLR-1 End of line relay for power supervision, 12/24 VDC, 4-wire only.

RS14 Replacement insect screen for 1451.

DUST45 Replacement protective dust cover for plug-in 400 Series.

CRT400 Cover removal tool for 1451.

M02-04-01 Test magnet.

M02-09-00 Test magnet with 32 inch telescoping handle.

XR5 Detector removal tool. Allows installation and/or removal of ion, photo,

and thermal detector heads from base in high ceiling installations.

XP-4 Extension pole for XR5. Comes in three 5 ft. sections.

The MOD400R Field Sensitivity Test Module can be used with

any standard DC voltmeter or multimeter to check the sensitivity

range of System Sensor’s detectors (satisfies NFPA 72 require-

ment for sensitivity testing).

System Sensor’s Recessed Mounting Kit, RMK400, provides

a simple installation solution where applications demand a

lower profile smoke detector and reduces the depth of any

400 Series plug-in detector by almost an inch. A special

metal mounting bracket secures the kit and the base to

the junction box and ceiling panel. (For use with B401 and

B401R bases only.)

System Sensor Sales and Service

System Sensor Headquarters

3825 Ohio Avenue

St. Charles, IL 60174

Ph: 800/SENSOR2

Fx: 630/377-6495

https://www.wendangku.net/doc/9f16785135.html,

System Sensor Canada

Ph: 905.812.0767

Fx: 905.812.0771

System Sensor Europe

Ph: 44.1403.891920

Fx: 44.1403.891921

System Sensor in China

Ph: 86.29.8832.0119

Fx: 86.29.8832.5119

System Sensor in Singapore

Ph: 65.6273.2230

Fx: 65.6273.2610

System Sensor – Far East

Ph: 85.22.191.9003

Fx: 85.22.736.6580

System Sensor – Australia

Ph: 613.54.281.142

Fx: 613.54.281.172

System Sensor – India

Ph: 91.124.237.1770 x.2700

Fx: 91.124.237.3118

System Sensor – Russia

Ph: 70.95.937.7982

Fx: 70.95.937.7983

? 2005 System Sensor. The company reserves the right to change product specifications without notice. A05-0205-005?3/05?#1427

相关文档