fx3u-2hc使用手册

JY997D36701A

Safety Precaution (Read these precautions before use.)

This manual classifies the safety precautions into two categories:

also cause severe injury.

It is important to follow all precautions for personal safety.

Associated Manuals

How to obtain manuals

For product manuals or documents, consult with the Mitsubishi Electric dealer from who you purchased your product.

Certification of UL, cUL standards

The following product has UL and cUL certification.UL, cUL File Number:E95239Models:MELSEC FX 3U series manufactured from December 1st, 2009FX 3U -2HC

Manual name Manual No.

Description

FX 3U Series User’s Manual - Hardware Edition JY997D16501MODEL CODE: 09R516Explains the FX 3U Series PLC specifications for I/O, w iring,

installation, and maintenance.FX 3UC Series User’s Manual - Hardware Edition JY997D28701MODEL CODE: 09R519Explains the FX 3UC Series PLC specifications for I/O, w iring,

installation, and maintenance.F X 3G /F X 3U /F X 3U C Series

Programming Manual - Basic & Applied Instruction Edition

JY997D16601MODEL CODE: 09R517

D es c r ib es F X 3G /F X 3U /F X 3U C Series PLC programming for basic/

applied instructions and https://www.wendangku.net/doc/aa18116942.html,pliance with EC directive (CE Marking)

This note does not guarantee that an entire mechanical module produced in accordance with the contents of this note will comply with the following standards.

Compliance to EMC directive and LVD directive for the entire mechanical module should be checked by the user / manufacturer. For more details please contact the local Mitsubishi Electric sales site.

Requirement for Compliance with EMC directive

The following products have shown compliance through direct testing (of the identified standards below) and design analysis (through the creation of a technical construction file) to the European Directive for Electromagnetic Compatibility (2004/108/EC) when used as directed by the appropriate documentation.Attention

?This product is designed for use in industrial applications.?Manufactured by:

Mitsubishi Electric Corporation

2-7-3 Marunouchi, Chiyoda-ku, Tokyo, 100-8310 Japan ?Manufactured at:

Mitsubishi Electric Corporation Himeji Works

840 Chiyoda-machi, Himeji, Hyogo, 670-8677 Japan ?Authorized Representative in the European Community:Mitsubishi Electric Europe B.V.

Gothaer Str. 8, 40880 Ratingen, Germany Type:Programmable Controller (Open Type Equipment)Models:MELSEC FX 3U series manufactured from December 1st, 2009FX 3U -2HC

Caution for EC Directive

?Installation in Enclosure

Programmable logic controllers are open-type devices that must be installed and used within conductive control cabinets. Please use the programmable logic controller while installed within a conductive shielded control cabinet. Please secure the cabinet door to the control cabinet (for conduction). Installation within a control cabinet greatly affects the safety of the system and aids in shielding noise from the programmable logic controller.

1.Outline

1.1Outline

The hardware high-speed counter block is a 2-channel high-speed counter. It is a special function block for the FX 3U and FX 3UC series PLC.

1.2Major Features of the FX 3U -2HC

?Differential-Line-Driver (AM26C31 or equivalent) and open collector output encoders are available for the FX 3U -2HC.

?The FX 3U -2HC has two outputs per channel. When the counter value coincides with an output compare value, the appropriate output is set ON. The output transistors are individually isolated to allow either sink or source connection methods.

?Various counter modes, such as 1-phase or 2-phase, 16-bit or 32-bit modes, can be selected using commands in the sequence program. Allow the FX 3U -2HC unit to run only after setting these mode parameters.

1.3Incorporated Items

Verify that the following product and items are included in the package:

Standard

Remark

EN61131-2:2003

Programmable controllers

-Equipment requirements and tests

Compliance with all relevant aspects of the standard.EMI

?Radiated Emissions ?Conducted Emissions EMS

?Radiated electromagnetic field ?Fast Transient burst ?Electrostatic discharge ?High-energy surge

?Voltage drops and interruptions ?Conducted RF

?Power frequency magnetic field

Included Items

FX 3U -2HC

1 Unit Special unit/block No. label 1 Sheet Dust proof protection sheet 1 Sheet Manuals [Japanese version]

1 manual Manuals [English version] (This manual)

1 manual

https://www.wendangku.net/doc/aa18116942.html,

[1]

Direct mounting hole: 2 holes of 4.5 (0.18") (mounting screw: M4 screw)Used when attaching FX 3U -2HC directly.

[2]Extension cable (PLC side)

Used to connect this special function block to the FX 3U /FX 3UC main unit or an extension block.[3]CH1 connector [4]

CH2 connector

[5]

Status LED (the upper side: CH1, the lower side: CH2)POWER (Green)Power LED ON when the 5V power supply is normally supplied from the PLC.UP (Red)Up count LED The respective LED is ON according to up/down count direction of the counter.

DOWN (Red)Down count LED A (Red) A phase input LED The respective LED is ON (flicker)according to ON/OFF of A and B input.

B (Red) B phase input LED

DIS (Red)DISABLE input LED T he r espec tive LED is ON /OF F

according to ON/OFF of PRESET and

DISABLE input.PRE (Red)

PRESET input LED YH1 (Red)YH1 output LED T he r espec tive LED is ON /OF F according to status of YH1 and YH2output.

YH2 (Red)YH2 output LED

[6]Top cover

[7]Extension connector (Extension side)

Used to connect a FX 3U extension block to the right of this special function block. Remove top cover for connecting.[8]DIN rail mounting hook

[9]

DIN rail mounting groove (DIN rail: DIN46277, 35mm (1.38") width)

2.Installation, Connect to the PLC

The product is mounted by the following method. ?DIN rail mounting

?Direct mounting (mounting screw: M4 screw)

For further information on installation arrangements, refer to the following manuals.

→ Refer to the FX 3U Series User's Manual - Hardware Edition.→ Refer to the FX 3UC Series User's Manual - Hardware Edition.

2.1.1DIN Rail Mounting

The product can be mounted on a DIN rail (DIN46277, 35mm (1.38") width).

1)Fit the upper edge of the DIN rail mounting groove (fig. A) onto the DIN rail.

2)Press the product against the DIN rail. -An interval space of 1 to 2 mm (0.04" to 0.08") between each unit is necessary.

2.1.2Direct Mounting (mounting screw: M4 screw)

The product can be installed directly with screws.

Refer to the External Dimensions (section 1.4) for the product’s mounting hole pitch information.

An interval space between each unit of 1 to 2 mm (0.04" to 0.08") is necessary.

2.2Connection to the PLC

A maximum of eight *1 FX 3U -2HC(s) are connectable with the main unit or the right side of the powered extension unit/block. A unit number of No.0 to No.7 is assigned based on the order in which special function units/blocks are attached to the main unit.

For connection to an FX 3UC Series PLC or FX 2NC Series PLC extension block, an FX 2NC -CNV-IF or FX 3UC -1PS-5V is required.

*1Up to seven special function units/blocks in total can be connected to the

FX 3UC -32MT-LT(-2) PLC. Unit numbers assigned to special function units/blocks begins with No.1.

For further information on installation arrangements, refer to the following manuals.

→ Refer to the FX 3U Series User's Manual - Hardware Edition.→ Refer to the FX 3UC Series User's Manual - Hardware Edition.

FX 3U -2HC

USER’S MANUAL

This manual describes the part names, dimensions, mounting, wiring, and specifications of the product. Before use, read this manual and the manuals of all relevant products fully to acquire proficiency in handling and operating the product. Make sure to learn all the product information, safety information, and precautions.

Store this manual in a safe place so that it can be taken out and read whenever necessary. Always forward it to the end user.Registration:

The company and product names described in this manual are registered trademarks or the trademarks of their respective companies.Effective December 2009

Specifications are subject to change without notice.

? 2009 Mitsubishi Electric Corporation

Manual Number JY997D36701Revision A

Date

December 2009

3.2.2

PNP output encoders

3.2.5YH1, YH2 output wiring [Source wiring]

4.4Applicable PLC

5.Buffer Memories (BFM)

5.1Buffer memory List

Note:

1)When writing to BFM #0 (CH1 counter mode), BFM #1 to #27 and #29 bit1 to 6 will be initialized. When writing to BFM #40 (CH2 counter mode), BFM #41to #67 and #29 bit10 to 15 will be initialized.

When setting the counter mode, use a TOP (pulsed) instruction, or M8002(initial pulse) to drive the TO instruction. (The continuous operation type cannot be used.)

2)Read/Write of 16 bit data

When using a positive value between K32,768 and K65,535 with 16 bit counters, read/writes of data, such as the current value, ring length, preset data, YH1/YH2 compare value, maximum count value and the minimum count value should use the 32-bit forms of FROM/TO instructions ((D)FROM, (D) TO).

3)Read/write of 32 bit data

The usage of a 32-bit FROM/TO instruction is recommended.

In the event that a 16-bit FROM/TO instruction is used, the following cases need to be considered.

?If the writing order is low word first and then high word, the 32 bit data will be written normally. Data becomes valid after both low and high words are written.

?In the event that data is not written in the order low word first and then high word, the error bit b7 of BFM #29 turns ON.

5.2Details of buffer memories

5.2.1

Counter mode [BFM #0 (CH1), #40 (CH2)]

The counter mode is shown in the upper right table. (Default value: K0)

BFM #Description

Default

BFM Access CH1CH2BFM #0

BFM #40

Counter mode

(Setting range: K0 to K11)

K0

R/W

BFM #1BFM #41DOWN/UP command

(1-phase 1-input mode [S/W UP/

DOWN] only)K0R/W BFM #2BFM #42Ring length

Lower K65536R/W BFM #3BFM #43

Upper

R/W BFM #4

BFM #44Command

K0R/W B F M #5~ #9BFM #45

~ #49Not used

-

-BFM #10BFM #50Preset data

Lower K0

R/W BFM #11BFM #51Upper R/W BFM #12BFM #52YH1 compare value Lower K32767

R/W BFM #13BFM #53Upper R/W BFM #14BFM #54YH2 compare value Lower K32767

R/W BFM #15BFM #55

Upper

R/W

BFM #16~ #19BFM #56

~ #59Not used

--BFM #20BFM #60Counter current value

Lower K0

R/W BFM #21BFM #61Upper R/W BFM #22BFM #62Maximum count value Lower K0

R/W BFM #23BFM #63Upper R/W

BFM #24BFM #64Minimum count value Lower K0R/W BFM #25BFM #65

Upper

R/W BFM #26BFM #66Compare results -R BFM #27BFM #67

Terminal status -R BFM #28Not used --BFM #29Error status

-R BFM #30Model identification code: K4020K4020R BFM #31 ~ 39Not used --BFM #68 ~ 32767

Not used

-

-Note:

When writing to BFM #0 (CH1 counter mode), BFM #1 to #27 and #29 bit1 to 6 will be initialized. When writing to BFM #40 (CH2 counter mode), BFM #41 to #67 and #29bit10 to 15 will be initialized. Please perform the setting of other BFM(s) after the setting of the counter mode (BFM #0, #40).

When setting the counter mode, use a TOP (pulsed) instruction, or M8002 (initial pulse) to drive the TO instruction. (The continuous operation type cannot be used.)

1)16/32-bit counter modes a)32-bit counter modes

Modes: K0, K2, K4, K6, K8, K10

A 32-bit binary counter which executes UP/DOWN counting will change from the lower limit value to the upper limit value or the upper limit value to the lower limit value when overflow occurs. Both the upper and lower limit values are fixed values: the upper limit value is +2,147,483,647, and the lower limit value is -2,147,483,648.b)16-bit counter modes

Modes: K1, K3, K5, K7, K9, K11

A 16-bit binary counter handles only positive values from 0 to 65,535. Changes to zero from the upper limit value or to the upper limit value from zero when overflow occurs;the upper limit value is determined by BFMs #3 and #2 (CH1), #43 and #42 (CH2).3)2-phase counter [2 edge-count] (K2, K3)4)2-phase counter [4 edge-count] (K4, K5)

5)1-phase 2-input counter (K6, K7)

Count modes

32 bits 16 bits Reference 2-phase input (phase difference pulse)

1 edge count K0K11), 2)

2 edge count K2K31), 3)4 edge count

K4K51), 4)1-phase 2-input (add/subtract pulse)K6K71), 5)1-phase 1-input

Hardware UP/DOWN K8K91), 6)Software UP/DOWN

K10

K11

1), 7)

7)5.2.2

DOWN/UP command [BFM #1 (CH1), #41 (CH2)]

When using the 1-phase 1-input counter [Software UP/DOWN] (counter mode: K10,K11), set the count direction by the current value of BFM #1 or BFM #41. (Default value: K0)

→ For the operation, refer to the Subsection 5.2.1 7)5.2.3

Ring length [BFM #3, #2 (CH1), #43, #42 (CH2)]

When setting the upper limit value of the 16 bit counters, the setting range is K2 to K65536. (Default value: K65536)

Please use the DTO instruction and write data as 32 bit data.

When ring length K100 is specified, the current value of the counter is changed as 5.2.4Command [BFM #4 (CH1), #44 (CH2)]

*1When b0 is set to ON and the DISABLE input terminal to OFF, the counter is

permitted to start counting input pulses.*2Unless b1 is set to ON, YH1 (compared output) does not turn ON.*3Unless b2 is set to ON, YH2 (compared output) does not turn ON.

*4When b3=ON, YH2 output is reset if YH1 output is set, and YH1 output is reset if

YH2 output is set. When b3=OFF, YH1 and YH2 output act independently, and do not reset each other.

The mutual reset action becomes valid only when both the YH1 comparison

output and the YH2 comparison output are permitted (b1, b2=ON).*5When b4=OFF, the preset function using the PRESET input terminal is disabled.*6When bit 5 is set to ON, the counter will be stopped and reset and the outputs

YH1 and YH2 will be switched OFF when the PLC is set from RUN to STOP .*7When bit 8 in BFM #4 is set to ON, the error flags bit 1 to 6 in BFM #29 will be

reset. The shared error flags (bit 7 and bit 8) will also be reset if no error on the other counter channel requires them to remain ON. When bit 8 in BFM #44 is set to ON, the error flags bit 10 to 15 in BFM #29 will be reset. The shared error flags (bit 7 and bit 8) will also be reset if no error on the other counter channel requires them to remain ON. After clearing BFM #29 error flags this flag will be reset automatically.*8b9 to b12 can perform a forced set of the YH1 output or the YH2 output, and

reset.

The output is not changed when the forced set and reset are performed

simultaneously.

Count Direction Setting Value

Up count K0Down count

K1

Bit No.

Setting Value

OFF (0)ON (1)b0*1Count prohibit

Count permit

b1*2YH1 compared output prohibit YH1 compared output permit b2*3YH2 compared output prohibit YH2 compared output permit

b3*4

YH1/YH2 independent action

Mutual reset action b4*5Preset prohibit

Preset permit

b5*6

No action if PLC is set from RUN

to STOP

(FX 2N -1HC compatibility mode)

Counter is stopped and reset if PLC is set from RUN to STOP

b6, b7Not used

b8*7No action Error flag reset b9*8

No action YH1 output reset b10*8No action YH2 output reset b11*8No action YH1 output set b12*8No action

YH2 output set

b13 ~ b15

Not used

5.2.5Preset data [BFM #11, #10 (CH1), #51, #50 (CH2)]

When BFM #4, #44 b4 is ON and the PRESET input is switched from OFF to ON,preset data is stored in BFM #21, #20 (CH1) #61, #60 (CH2) (counter current value).

5.2.6

YH1 compare value [BFM #13, #12 (CH1), #53, #52 (CH2)], YH2 compare value [BFM #15, #14 (CH1), #55, #54 (CH2)]

?The comparison set value for the output currently written here and the present value of the counter are measured, and when the comparison result is equal,the YH1 output or the YH2 output is set to ON within 30 μs.

?Output occurs when the current value becomes equal to the compare value but only if b1 and b2 of BFM #4, #44 are ON. Once an output is set, it remains ON 5.2.7Counter current value [BFM #21, #20 (CH1), #61, #60 (CH2)]

The current value of the counter can be read by the PLC. It will not be an accurate value during high-speed operations because of the communication delay. The current value of the counter can be forcibly changed by writing a 32-bit value into the appropriate BFMs from the PLC.

5.2.8

Maximum count value [BFM #23, #22 (CH1), #63, #62 (CH2)],Minimum count value [BFM #25, # 24 (CH1), #65, #64 (CH2)]

These BFM store the maximum and minimum value reached by the counter. If the power is turned off, the stored data is cleared. Any value written to maximum and minimum count value in 16 bit counter mode which is exceeding the valid range (0 <= value < ring length) will be automatically adjusted. Values < 0 will be adjusted to 0, values >= ring length will be adjusted to "ring length" - 1.

5.2.9

Compare results [BFM #26 (CH1), #66 (CH2)]

5.2.10Terminal status [BFM #27 (CH1), #67 (CH2)]

5.2.11Error status [BFM #29]

Bit No.Target output OFF (0)

ON (1)

b0YH1

Compare value ≤ current value Compare value > current value b1Compare value ≠ current value Compare value = current value b2Compare value ≥ current value Compare value < current value b3YH2

Compare value ≤ current value Compare value > current value

b4Compare value ≠ current value Compare value = current value b5

Compare value ≥ current value Compare value < current value

b6 ~ b15

Not used

Bit N0.Signal Name OFF (0)ON (1)b0PRESET input OFF ON b1DISABLE input OFF ON b2YH1 output OFF ON b3YH2 output

OFF ON

b4 ~ b15

Not used

Bit N0.Error Status

b0

Set when any of b1 to b15 is ON.

b1

Set when the value of the ring length is written incorrectly. (CH1)

?Outside of K2 to K65,536?Written while CH1 is in 32-bit counter mode ?Ring length changed while counter running

b2

Set when the preset value is written incorrectly. (CH1)Value is other than "K0 to ring length-1" for 16-bit counters.

JY997D36701A

Safety Precaution (Read these precautions before use.)

This manual classifies the safety precautions into two categories:

also cause severe injury.

It is important to follow all precautions for personal safety.

Associated Manuals

How to obtain manuals

For product manuals or documents, consult with the Mitsubishi Electric dealer from who you purchased your product.

Certification of UL, cUL standards

The following product has UL and cUL certification.UL, cUL File Number:E95239Models:MELSEC FX 3U series manufactured from December 1st, 2009FX 3U -2HC

Manual name Manual No.

Description

FX 3U Series User’s Manual - Hardware Edition JY997D16501MODEL CODE: 09R516Explains the FX 3U Series PLC specifications for I/O, w iring,

installation, and maintenance.FX 3UC Series User’s Manual - Hardware Edition JY997D28701MODEL CODE: 09R519Explains the FX 3UC Series PLC specifications for I/O, w iring,

installation, and maintenance.F X 3G /F X 3U /F X 3U C Series

Programming Manual - Basic & Applied Instruction Edition

JY997D16601MODEL CODE: 09R517

D es c r ib es F X 3G /F X 3U /F X 3U C Series PLC programming for basic/

applied instructions and https://www.wendangku.net/doc/aa18116942.html,pliance with EC directive (CE Marking)

This note does not guarantee that an entire mechanical module produced in accordance with the contents of this note will comply with the following standards.

Compliance to EMC directive and LVD directive for the entire mechanical module should be checked by the user / manufacturer. For more details please contact the local Mitsubishi Electric sales site.

Requirement for Compliance with EMC directive

The following products have shown compliance through direct testing (of the identified standards below) and design analysis (through the creation of a technical construction file) to the European Directive for Electromagnetic Compatibility (2004/108/EC) when used as directed by the appropriate documentation.Attention

?This product is designed for use in industrial applications.?Manufactured by:

Mitsubishi Electric Corporation

2-7-3 Marunouchi, Chiyoda-ku, Tokyo, 100-8310 Japan ?Manufactured at:

Mitsubishi Electric Corporation Himeji Works

840 Chiyoda-machi, Himeji, Hyogo, 670-8677 Japan ?Authorized Representative in the European Community:Mitsubishi Electric Europe B.V.

Gothaer Str. 8, 40880 Ratingen, Germany Type:Programmable Controller (Open Type Equipment)Models:MELSEC FX 3U series manufactured from December 1st, 2009FX 3U -2HC

Caution for EC Directive

?Installation in Enclosure

Programmable logic controllers are open-type devices that must be installed and used within conductive control cabinets. Please use the programmable logic controller while installed within a conductive shielded control cabinet. Please secure the cabinet door to the control cabinet (for conduction). Installation within a control cabinet greatly affects the safety of the system and aids in shielding noise from the programmable logic controller.

1.Outline

1.1Outline

The hardware high-speed counter block is a 2-channel high-speed counter. It is a special function block for the FX 3U and FX 3UC series PLC.

1.2Major Features of the FX 3U -2HC

?Differential-Line-Driver (AM26C31 or equivalent) and open collector output encoders are available for the FX 3U -2HC.

?The FX 3U -2HC has two outputs per channel. When the counter value coincides with an output compare value, the appropriate output is set ON. The output transistors are individually isolated to allow either sink or source connection methods.

?Various counter modes, such as 1-phase or 2-phase, 16-bit or 32-bit modes, can be selected using commands in the sequence program. Allow the FX 3U -2HC unit to run only after setting these mode parameters.

1.3Incorporated Items

Verify that the following product and items are included in the package:

Standard

Remark

EN61131-2:2003

Programmable controllers

-Equipment requirements and tests

Compliance with all relevant aspects of the standard.EMI

?Radiated Emissions ?Conducted Emissions EMS

?Radiated electromagnetic field ?Fast Transient burst ?Electrostatic discharge ?High-energy surge

?Voltage drops and interruptions ?Conducted RF

?Power frequency magnetic field

Included Items

FX 3U -2HC

1 Unit Special unit/block No. label 1 Sheet Dust proof protection sheet 1 Sheet Manuals [Japanese version]

1 manual Manuals [English version] (This manual)

1 manual

https://www.wendangku.net/doc/aa18116942.html,

[1]

Direct mounting hole: 2 holes of 4.5 (0.18") (mounting screw: M4 screw)Used when attaching FX 3U -2HC directly.

[2]Extension cable (PLC side)

Used to connect this special function block to the FX 3U /FX 3UC main unit or an extension block.[3]CH1 connector [4]

CH2 connector

[5]

Status LED (the upper side: CH1, the lower side: CH2)POWER (Green)Power LED ON when the 5V power supply is normally supplied from the PLC.UP (Red)Up count LED The respective LED is ON according to up/down count direction of the counter.

DOWN (Red)Down count LED A (Red) A phase input LED The respective LED is ON (flicker)according to ON/OFF of A and B input.

B (Red) B phase input LED

DIS (Red)DISABLE input LED T he r espec tive LED is ON /OF F

according to ON/OFF of PRESET and

DISABLE input.PRE (Red)

PRESET input LED YH1 (Red)YH1 output LED T he r espec tive LED is ON /OF F according to status of YH1 and YH2output.

YH2 (Red)YH2 output LED

[6]Top cover

[7]Extension connector (Extension side)

Used to connect a FX 3U extension block to the right of this special function block. Remove top cover for connecting.[8]DIN rail mounting hook

[9]

DIN rail mounting groove (DIN rail: DIN46277, 35mm (1.38") width)

2.Installation, Connect to the PLC

The product is mounted by the following method. ?DIN rail mounting

?Direct mounting (mounting screw: M4 screw)

For further information on installation arrangements, refer to the following manuals.

→ Refer to the FX 3U Series User's Manual - Hardware Edition.→ Refer to the FX 3UC Series User's Manual - Hardware Edition.

2.1.1DIN Rail Mounting

The product can be mounted on a DIN rail (DIN46277, 35mm (1.38") width).

1)Fit the upper edge of the DIN rail mounting groove (fig. A) onto the DIN rail.

2)Press the product against the DIN rail. -An interval space of 1 to 2 mm (0.04" to 0.08") between each unit is necessary.

2.1.2Direct Mounting (mounting screw: M4 screw)

The product can be installed directly with screws.

Refer to the External Dimensions (section 1.4) for the product’s mounting hole pitch information.

An interval space between each unit of 1 to 2 mm (0.04" to 0.08") is necessary.

2.2Connection to the PLC

A maximum of eight *1 FX 3U -2HC(s) are connectable with the main unit or the right side of the powered extension unit/block. A unit number of No.0 to No.7 is assigned based on the order in which special function units/blocks are attached to the main unit.

For connection to an FX 3UC Series PLC or FX 2NC Series PLC extension block, an FX 2NC -CNV-IF or FX 3UC -1PS-5V is required.

*1Up to seven special function units/blocks in total can be connected to the

FX 3UC -32MT-LT(-2) PLC. Unit numbers assigned to special function units/blocks begins with No.1.

For further information on installation arrangements, refer to the following manuals.

→ Refer to the FX 3U Series User's Manual - Hardware Edition.→ Refer to the FX 3UC Series User's Manual - Hardware Edition.

3.1Connection to input/output connector

The input and output connectors conform to the MIL-C-83503.

→ For the input and output connectors pin assignment, refer to section 1.4.1)Compliant connectors (commercially available connectors)

Use a 40-pin (1-key) socket connector conforming to MIL-C-83503.

Confirm in advance that the connectors do not interfere with other parts including connector covers.

2)Connectors for user-made input/output cables (available from Mitsubishi)Users should provide electric wires and a pressure bonding tool.3.2Wiring

Note:

Make sure to properly wire in accordance with the encoder output specifications. Incorrect wiring may cause accidents or damage to the product.

3.2.1

NPN output encoders

WIRING

PRECAUTIONS

?When drilling screw holes or wiring, make sure cutting or wire debris does not enter the ventilation slits.

Failure to do so may cause fire, equipment failures or malfunctions.

?Make sure to observe the following precautions in order to prevent any damage to the machinery or accidents due to abnormal data written to the PLC under the influence of noise:

1)Do not bundle the main circuit line together with or lay it close to the main circuit, high-voltage line or load line. Otherwise, noise disturbance and/or surge induction are likely to take place. As a guideline, lay the control line at least 100mm (3.94") or more away from the main circuit or high-voltage lines.2)Ground the shield wire or shield of the shielded cable at two points; on the PLC and the device on other end. However, do not use common grounding with heavy electrical systems.

Model name and composition of input/

output connector Applicable electric wire (UL-1061 are recommended)

and tool Our model name Details of part (made by DDK Ltd.)Electric wire size Pressure bonding tool (made by DDK

Ltd.)

FX-I/O-CON2-S for bulk wire (2-piece set)Housing:HU-400S2-001Solderless contact:HU-411S

AWG22(0.3mm 2)357J-5538

FX-I/O-CON2-SA for bulk wire (2-piece set)

Housing:HU-400S2-001Solderless contact:HU-411SA

AWG20(0.5mm 2)

357J-13963

3.2.2

PNP output encoders

3.2.3Differential-Line-Driver output encoders

When applying the Differential-Line-Driver encoder (AM26C31 or equivalent) to the FX 3U -2HC, connect the encoder output with the 5V DC terminal as shown in the figure below.

Caution

A protection fuse should be inserted at the output.

Use a load power supply capacity that is at least 2 times larger than the total rated fuse capacity.

Caution

A protection fuse should be inserted at the output.

Use a load power supply capacity that is at least 2 times larger than the total rated fuse capacity.

3.3Grounding

Grounding should be performed as stated below.?The grounding resistance should be 100Ω or less.

?Independent grounding should be performed for best results.

When independent grounding is not performed, perform "shared grounding"of the following figure.

→ For details, refer to the FX 3U Series User's Manual - Hardware Edition.→ For details, refer to the FX 3UC Series User's Manual - Hardware Edition.

?The grounding wire size should be AWG 22-20 (0.3-0.5 mm ).

?The grounding point should be close to the PLC, and all grounding wires should be as short as possible.

4.Specifications

4.1General Specifications

The general specifications are equivalent to the PLC main unit.

(For general specifications, refer to the manual of the PLC main unit.)

Caution

When a dielectric withstand test of this product is performed, ground all terminals of this product and the PLC unit.

4.2Power Supply Specifications

Item

Specifications

Units driving power 5V DC, 245mA (Internal power supply from main unit or extension power supply unit)

Allowable instantaneous power failure time

Operation can be continued upon occurrence of instantaneous power failure for 1 ms or less.

4.4Applicable PLC

The version number can be checked by reading the last three digits of device D8001.

*1An FX 2NC -CNV-IF or FX 3UC -1PS-5V is necessary to connect the FX 3U -2HC with the FX 3UC PLC.

Model name Applicability

FX 3U Series PLC Ver. 2.20 and later FX 3UC Series PLC *1

Ver. 2.20 and later

FX 3U -2HC

USER’S MANUAL

This manual describes the part names, dimensions, mounting, wiring, and specifications of the product. Before use, read this manual and the manuals of all relevant products fully to acquire proficiency in handling and operating the product. Make sure to learn all the product information, safety information, and precautions.

Store this manual in a safe place so that it can be taken out and read whenever necessary. Always forward it to the end user.Registration:

The company and product names described in this manual are registered trademarks or the trademarks of their respective companies.Effective December 2009

Specifications are subject to change without notice.

? 2009 Mitsubishi Electric Corporation

Manual Number JY997D36701Revision A

Date

December 2009

5.Buffer Memories (BFM)

5.1Buffer memory List

Note:

1)When writing to BFM #0 (CH1 counter mode), BFM #1 to #27 and #29 bit1 to 6 will be initialized. When writing to BFM #40 (CH2 counter mode), BFM #41to #67 and #29 bit10 to 15 will be initialized.

When setting the counter mode, use a TOP (pulsed) instruction, or M8002(initial pulse) to drive the TO instruction. (The continuous operation type cannot be used.)

2)Read/Write of 16 bit data

When using a positive value between K32,768 and K65,535 with 16 bit counters, read/writes of data, such as the current value, ring length, preset data, YH1/YH2 compare value, maximum count value and the minimum count value should use the 32-bit forms of FROM/TO instructions ((D)FROM, (D) TO).

3)Read/write of 32 bit data

The usage of a 32-bit FROM/TO instruction is recommended.

In the event that a 16-bit FROM/TO instruction is used, the following cases need to be considered.

?If the writing order is low word first and then high word, the 32 bit data will be written normally. Data becomes valid after both low and high words are written.

?In the event that data is not written in the order low word first and then high word, the error bit b7 of BFM #29 turns ON.

5.2Details of buffer memories

5.2.1

Counter mode [BFM #0 (CH1), #40 (CH2)]

The counter mode is shown in the upper right table. (Default value: K0)

BFM #Description

Default

BFM Access CH1CH2BFM #0

BFM #40

Counter mode

(Setting range: K0 to K11)

K0

R/W

BFM #1BFM #41DOWN/UP command

(1-phase 1-input mode [S/W UP/

DOWN] only)K0R/W BFM #2BFM #42Ring length

Lower K65536R/W BFM #3BFM #43

Upper

R/W BFM #4

BFM #44Command

K0R/W B F M #5~ #9BFM #45

~ #49Not used

-

-BFM #10BFM #50Preset data

Lower K0

R/W BFM #11BFM #51Upper R/W BFM #12BFM #52YH1 compare value Lower K32767

R/W BFM #13BFM #53Upper R/W BFM #14BFM #54YH2 compare value Lower K32767

R/W BFM #15BFM #55

Upper

R/W

BFM #16~ #19BFM #56

~ #59Not used

--BFM #20BFM #60Counter current value

Lower K0

R/W BFM #21BFM #61Upper R/W BFM #22BFM #62Maximum count value Lower K0

R/W BFM #23BFM #63Upper R/W

BFM #24BFM #64Minimum count value Lower K0R/W BFM #25BFM #65

Upper

R/W BFM #26BFM #66Compare results -R BFM #27BFM #67

Terminal status -R BFM #28Not used --BFM #29Error status

-R BFM #30Model identification code: K4020K4020R BFM #31 ~ 39Not used --BFM #68 ~ 32767

Not used

-

-Note:

When writing to BFM #0 (CH1 counter mode), BFM #1 to #27 and #29 bit1 to 6 will be initialized. When writing to BFM #40 (CH2 counter mode), BFM #41 to #67 and #29bit10 to 15 will be initialized. Please perform the setting of other BFM(s) after the setting of the counter mode (BFM #0, #40).

When setting the counter mode, use a TOP (pulsed) instruction, or M8002 (initial pulse) to drive the TO instruction. (The continuous operation type cannot be used.)

1)16/32-bit counter modes a)32-bit counter modes

Modes: K0, K2, K4, K6, K8, K10

A 32-bit binary counter which executes UP/DOWN counting will change from the lower limit value to the upper limit value or the upper limit value to the lower limit value when overflow occurs. Both the upper and lower limit values are fixed values: the upper limit value is +2,147,483,647, and the lower limit value is -2,147,483,648.b)16-bit counter modes

Modes: K1, K3, K5, K7, K9, K11

A 16-bit binary counter handles only positive values from 0 to 65,535. Changes to zero from the upper limit value or to the upper limit value from zero when overflow occurs;the upper limit value is determined by BFMs #3 and #2 (CH1), #43 and #42 (CH2).3)2-phase counter [2 edge-count] (K2, K3)4)2-phase counter [4 edge-count] (K4, K5)

5)1-phase 2-input counter (K6, K7)

Count modes

32 bits 16 bits Reference 2-phase input (phase difference pulse)

1 edge count K0K11), 2)

2 edge count K2K31), 3)4 edge count

K4K51), 4)1-phase 2-input (add/subtract pulse)K6K71), 5)1-phase 1-input

Hardware UP/DOWN K8K91), 6)Software UP/DOWN

K10

K11

1), 7)

7)5.2.2

DOWN/UP command [BFM #1 (CH1), #41 (CH2)]

When using the 1-phase 1-input counter [Software UP/DOWN] (counter mode: K10,K11), set the count direction by the current value of BFM #1 or BFM #41. (Default value: K0)

→ For the operation, refer to the Subsection 5.2.1 7)5.2.3

Ring length [BFM #3, #2 (CH1), #43, #42 (CH2)]

When setting the upper limit value of the 16 bit counters, the setting range is K2 to K65536. (Default value: K65536)

Please use the DTO instruction and write data as 32 bit data.

When ring length K100 is specified, the current value of the counter is changed as 5.2.4Command [BFM #4 (CH1), #44 (CH2)]

*1When b0 is set to ON and the DISABLE input terminal to OFF, the counter is

permitted to start counting input pulses.*2Unless b1 is set to ON, YH1 (compared output) does not turn ON.*3Unless b2 is set to ON, YH2 (compared output) does not turn ON.

*4When b3=ON, YH2 output is reset if YH1 output is set, and YH1 output is reset if

YH2 output is set. When b3=OFF, YH1 and YH2 output act independently, and do not reset each other.

The mutual reset action becomes valid only when both the YH1 comparison

output and the YH2 comparison output are permitted (b1, b2=ON).*5When b4=OFF, the preset function using the PRESET input terminal is disabled.*6When bit 5 is set to ON, the counter will be stopped and reset and the outputs

YH1 and YH2 will be switched OFF when the PLC is set from RUN to STOP .*7When bit 8 in BFM #4 is set to ON, the error flags bit 1 to 6 in BFM #29 will be

reset. The shared error flags (bit 7 and bit 8) will also be reset if no error on the other counter channel requires them to remain ON. When bit 8 in BFM #44 is set to ON, the error flags bit 10 to 15 in BFM #29 will be reset. The shared error flags (bit 7 and bit 8) will also be reset if no error on the other counter channel requires them to remain ON. After clearing BFM #29 error flags this flag will be reset automatically.*8b9 to b12 can perform a forced set of the YH1 output or the YH2 output, and

reset.

The output is not changed when the forced set and reset are performed simultaneously.

Count Direction Setting Value

Up count K0Down count

K1

Bit No.

Setting Value

OFF (0)ON (1)b0*1Count prohibit

Count permit

b1*2YH1 compared output prohibit YH1 compared output permit b2*3YH2 compared output prohibit YH2 compared output permit

b3*4

YH1/YH2 independent action

Mutual reset action b4*5Preset prohibit

Preset permit

b5*6

No action if PLC is set from RUN

to STOP

(FX 2N -1HC compatibility mode)

Counter is stopped and reset if PLC is set from RUN to STOP

b6, b7Not used

b8*7No action Error flag reset b9*8

No action YH1 output reset b10*8No action YH2 output reset b11*8No action YH1 output set b12*8No action

YH2 output set

b13 ~ b15

Not used

5.2.5Preset data [BFM #11, #10 (CH1), #51, #50 (CH2)]

When BFM #4, #44 b4 is ON and the PRESET input is switched from OFF to ON,preset data is stored in BFM #21, #20 (CH1) #61, #60 (CH2) (counter current value).

5.2.6

YH1 compare value [BFM #13, #12 (CH1), #53, #52 (CH2)], YH2 compare value [BFM #15, #14 (CH1), #55, #54 (CH2)]

?The comparison set value for the output currently written here and the present value of the counter are measured, and when the comparison result is equal,the YH1 output or the YH2 output is set to ON within 30 μs.

?Output occurs when the current value becomes equal to the compare value but only if b1 and b2 of BFM #4, #44 are ON. Once an output is set, it remains ON 5.2.7Counter current value [BFM #21, #20 (CH1), #61, #60 (CH2)]

The current value of the counter can be read by the PLC. It will not be an accurate value during high-speed operations because of the communication delay. The current value of the counter can be forcibly changed by writing a 32-bit value into the appropriate BFMs from the PLC.

5.2.8

Maximum count value [BFM #23, #22 (CH1), #63, #62 (CH2)],Minimum count value [BFM #25, # 24 (CH1), #65, #64 (CH2)]

These BFM store the maximum and minimum value reached by the counter. If the power is turned off, the stored data is cleared. Any value written to maximum and minimum count value in 16 bit counter mode which is exceeding the valid range (0 <= value < ring length) will be automatically adjusted. Values < 0 will be adjusted to 0, values >= ring length will be adjusted to "ring length" - 1.

5.2.9

Compare results [BFM #26 (CH1), #66 (CH2)]

5.2.10Terminal status [BFM #27 (CH1), #67 (CH2)]

5.2.11Error status [BFM #29]

Bit No.Target output OFF (0)

ON (1)

b0YH1

Compare value ≤ current value Compare value > current value b1Compare value ≠ current value Compare value = current value b2Compare value ≥ current value Compare value < current value b3YH2

Compare value ≤ current value Compare value > current value

b4Compare value ≠ current value Compare value = current value b5

Compare value ≥ current value Compare value < current value

b6 ~ b15

Not used

Bit N0.Signal Name OFF (0)ON (1)b0PRESET input OFF ON b1DISABLE input OFF ON b2YH1 output OFF ON b3YH2 output

OFF ON

b4 ~ b15

Not used

Bit N0.Error Status

b0

Set when any of b1 to b15 is ON.

b1

Set when the value of the ring length is written incorrectly. (CH1)

?Outside of K2 to K65,536?Written while CH1 is in 32-bit counter mode ?Ring length changed while counter running

b2

Set when the preset value is written incorrectly. (CH1)Value is other than "K0 to ring

length-1" for 16-bit counters.

*1In the following case, BFM #29 b7 turns on.?write in a BFM that is not used ?writing to read only BFMs

?

accessing 32 bit BFMs using the FROM/TO command in the wrong order

Error status in the FX 3U -2HC can be checked by reading the contents of b0 to b15of BFM #29 to auxiliary relays of the PLC.

The error flag of b1 to b8 is reset-table with ON of BFM #4 b8. The error flag of b7,b8 and b10 to b15 is resettable with ON of BFM #44 b8. The error flags in BFM #29 can also be reset by writing 0 to it. The Hardware error flag (bit 9 of BFM #29)can not be cleared.

5.2.12Model identification code [BFM #30]

This BFM stores the identification number for the FX 3U -2HC.The identification number for the FX 3U -2HC unit is K4020.

By reading this identification number, the user may create built-in checking routines to check whether the physical position of the FX 3U -2HC matches that of the software.

6.Example Program

The ON/OFF status of M10 to M25 is written in BFM #4 (CH1) of special function block No.2 by the following program, and b0 to b15 actions. Among these, b0 to b4 are always ON as controlled by M10-M14.

Furthermore, b8 (M18), b9 (M19), and b10 (M20) are controlled by input X004 of unit. Other instructions to read the current value of the counter, status etc. can be

Bit N0.Error Status

b3Set when the compare value is written

incorrectly. (CH1)

Value is other than "K0 to ring length-1" for 16-bit

counters.b4Set when the current value is written incorrectly. (CH1)

b5Set when the counter overflows the upper

limit. (CH1)

When the upper or lower limit is exceeded on a 32-bit counter.b6Set when the counter underflows the lower limit. (CH1)

b7Set when the FROM/TO command is used incorrectly.*1b8Set when the counter mode (BFM #0,

#40) is written incorrectly.

Except K0 to K11

b9

Hardware error (UP , DOWN LED turn ON)

b10

Set when the value of the ring length is

written incorrectly. (CH2)

?Outside of K2 to K65,536?Written while CH2 is in

32-bit counter mode

?Ring length changed while counter running b11Set when the preset value is written incorrectly. (CH2)

Value is other than "K0 to

ring length-1" for 16-bit

counters.

b12Set when the compare value is written

incorrectly. (CH2)

b13Set when the current value is written incorrectly. (CH2)

b14Set when the counter overflows the upper

limit. (CH2)

When the upper or lower limit is exceeded on a 32-bit counter.b15Set when the counter underflows the lower limit. (CH2)

Error status in the FX 3U -2HC can be checked by reading the contents of b0 to b15 of BFM #29 to auxiliary relays of the PLC. These error flags are resettable BFM #4, #44 b8.

7.Preliminary checks

1)Check that the I/O wiring and extension cable of the FX 3U -2HC are properly connected.

2)The FX 3U -2HC occupies 8 points of I/O on the FX 3U , FX 3UC expansion bus. The 8 points can be allocated from either inputs or outputs.

5V DC 245mA power is supplied from the main or extension power supply units for the FX 3U -2HC. Check that there is no power overload from this and other extension blocks.

3)The counter works correctly only when data such as the counter mode (set with a pulse command), the TO command, the compare value, etc. are appropriately specified. Remember to initialize the count (BFM #4, #44 b0), preset (BFM #4,#44 b4), and output (BFM #4, #44 b2, b1) prohibits. The YH1/YH2 outputs are reset during start.Note:

Inputting pulses higher than the maximum frequency may cause miscounting in the FX 3U -2HC or a FROM/TO error in the PLC main unit.

8.Diagnostics

1)The following LEDs on the main panel of the FX 3U -2HC may help you to troubleshoot the unit.a)

A, B:

Goes on/off as A, B input turn ON/OFF. It can be checked by rotating the encoder slowly.b)UP , DOWN:

Lights up to indicate whether the counter is going up (UP) or down (DOWN).c)PRE, DIS:

The appropriate LED lights up when the PRESET (PRE) terminal or the DISABLE (DIS) terminal is ON.d)YH1, YH2:

The appropriate LED lights up when YH1/YH2 output is turned on.

2)You can check the error status by reading the content of BFM #29 to the PLC.

→ For error contents, refer to the Subsection 5.2.11

STARTUP AND MAINTE-NANCE PRECAUTIONS

?Do not disassemble or modify the PLC.

Doing so may cause fire, equipment failures, or malfunctions.*For repair, contact your local Mitsubishi Electric distributor.?Do not drop the product or exert strong impact to it.Doing so may cause damage.DISPOSAL PRECAUTIONS

?Please contact a certified electronic waste disposal company for the environmentally safe recycling and disposal of your device.TRANSPORT AND STOR-AGE PRECAUTIONS

?The product is a precision instrument. During transportation, avoid any impacts. Failure to do so may cause failures in the product.

After transportation, verify the operations of the product.9.Reference (CH1 System Block Diagram)