Preface

Thank you for choosing DELTA’s high-performance VFD-M Series. The VFD-M Series is manufactured with high-quality components and materials and incorporates the latest microprocessor technology available.

Getting Started

This quick start will be helpful in the installation and parameter setting of the AC motor drives. To guarantee safe operation of the equipment, read the following safety guidelines before

connecting power to the AC motor drives. For detail information, refer to the VFD-M User Manual on the CD supplied with the drive.

台达变频器

2. A charge may still remain in the DC-link capacitors with hazardous voltages, even if the power

has been turned off. To prevent personal injury, please ensure that power has turned off before opening the AC motor drive and wait ten minutes for the capacitors to discharge to safe voltage levels.

3. Never reassemble internal components or wiring.

4. The AC motor drive may be destroyed beyond repair if incorrect cables are connected to the

input/output terminals. Never connect the AC motor drive output terminals U/T1, V/T2, and

W/T3 directly to the AC mains circuit power supply.

5. Ground the VFD-M using the ground terminal. The grounding method must comply with the laws

of the country where the AC motor drive is to be installed. Refer to the Basic Wiring Diagram. 6. VFD-M series is used only to control variable speed of 3-phase induction motors, NOT for 1-

phase motors or other purpose.

7. VFD-M series shall NOT be used for life support equipment or any life safety situation.

台达变频器

easily damage by high-pressure.

2. There are highly sensitive MOS components on the printed circuit boards. These components

are especially sensitive to static electricity. To prevent damage to these components, do not touch these components or the circuit boards with metal objects or your bare hands.

3. Only quality person is allowed to install, wire and maintain AC motor drive.

台达变频器

2. DO NOT install the AC motor drive in a place subjected to high temperature, direct sunlight,

high humidity, excessive vibration, corrosive gases or liquids, or airborne dust or metallic

particles.

3. Only use AC motor drives within specification. Failure to comply may result in fire, explosion or

electric shock.

4. To prevent personal injury, please keep children and unqualified people away from the

equipment.

5. When the motor cable between AC motor drive and motor is too long, the layer insulation of the

motor may be damaged. Please use a frequency inverter duty motor or add an AC output

reactor to prevent damage to the motor. Refer to appendix B Reactor for details.

6. The rated voltage for AC motor drive must be ≤240V for 230V models (≤120V for 115V models,

≤480V for 460V models, ≤600V for 575V models) and the mains supply current capacity must be ≤5000A RMS (≤10000A RMS for the ≥40hp (30kW) models).

Specifications

Voltage Class

115V Class

Model Number VFD-XXXM 002 004 007 Max. Applicable Motor Output (kW) 0.2 0.4 0.75 Max. Applicable Motor Output (hp) 0.25 0.5

1.0 Rated Output Capacity (kVA) 0.6 1.0

1.6

Rated Output Current (A) 1.6

2.5 4.2

Maximum Output Voltage (V) 3-Phase proportion to twice the input voltage

Output Frequency (Hz) 0.1~400 Hz

O u t p u t R a t i n g

Carrier Frequency (kHz) 1-15 Single phase

Rated Input Current (A)

6 9 16

Rated Voltage, Frequency Single phase, 100-120 VAC, 50/60Hz

Voltage Tolerance +-10% (90-132VAC)

I n p u t R a t i n g

Frequency Tolerance ±5% (47~63Hz) Cooling Method Fan Cooled

Weight (kg)

1.5

1.5

1.5

Voltage Class 230V Class

Model Number VFD-XXXM 004 007 015 022 037 055 Max. Applicable Motor Output (kW)0.4 0.75 1.5 2.2 3.7 5.5 Max. Applicable Motor Output (hp) 0.5 1.0 2.0 3.0 5.0 7.5

Rated Output Capacity (kVA) 1.0 1.9 2.7 3.8 6.5 9.5 Rated Output Current (A) 2.5 5.0 7.0 10 17 25 Maximum Output Voltage (V) 3-Phase proportional to input voltage Output Frequency (Hz) 0.1~400 Hz O u t p u t R a t i n g

Carrier Frequency (kHz) 1-15

Single/3-phase 3-phase

Rated Input Current (A)

6.3/2.911.5/

7.6 15.7/

8.8 27/12.5 1

9.6 28

Input Current for 1-phase Models when Using 3-phase Power

3.2 6.3 9.0 12.5 -- -- Rated Voltage, Frequency

Single/3-phase 200-240 VAC, 50/60Hz 3-phase

200-240VAC, 50/60Hz

Voltage Tolerance +-10% (180~264 VAC)

I n p u t R a t i n g Frequency Tolerance

±5% (47~63 Hz) Cooling Method Fan Cooled Weight (kg) 2.2/1.5 2.2/1.5 2.2/1.5 3.2/2.2 3.2 3.2

Voltage Class 460V Class Model Number VFD-XXXM 007 015 022 037 055 075 Max. Applicable Motor Output (kW)0.75 1.5 2.2 3.7 5.5 7.5 Max. Applicable Motor Output (hp) 1.0 2.0 3.0 5.0 7.5 10

Rated Output Capacity (kVA) 2.3 3.1 3.8 6.2 9.9 13.7 Rated Output Current (A) 3.0 4.0 5.0 8.2 13 18 Maximum Output Voltage (V) 3-phase Proportional to Input Voltage Output Frequency (Hz) 0.1~400 Hz O u t p u t R a t i n g

Carrier Frequency (kHz) 1-15

3-phase

Rated Input Current (A)

4.2

5.7

6.0 8.5 14 23

Rated Voltage, Frequency 3-phase 380~480 VAC, 50/60Hz Voltage Tolerance +-10% (342~528 VAC)

I n p u t R a t i n g Frequency Tolerance

±5% (47~63 Hz) Cooling Method Fan Cooled Weight (kg) 1.5 1.5 2.0 3.2 3.2 3.3

Voltage Class 575V Class

Model Number VFD-XXXM 007 015 022 037 055 075 Max. Applicable Motor Output (kW)0.75 1.5 2.2 3.7 5.5 7.5 Max. Applicable Motor Output (hp) 1.0 2.0 3.0 5.0 7.5 10

Rated Output Capacity (kVA) 1.7 3.0 4.2 6.6 9.9 12.2 Rated Output Current (A) 1.7 3.0 4.2 6.6 9.9 12.2 Maximum Output Voltage (V)3-phase Proportional to Input Voltage Output Frequency (Hz) 0.1~400 Hz O u t p u t R a t i n g

Carrier Frequency (kHz) 1-10

3-phase

Rated Input Current (A)

2.4 4.2 5.9 7.0 10.5 12.9

Rated Voltage, Frequency 3-phase 500~600 VAC, 50/60Hz Voltage Tolerance -15%~+10% (425~660 VAC)

I n p u t R a t i n g Frequency Tolerance

±5% (47~63 Hz) Cooling Method Fan Cooled Weight (kg)

1.5 1.5

2.0

3.2 3.2 3.3

台达变频器

台达变频器

台达变频器

台达变频器

General Specifications

Protection Functions

Self-testing, over voltage, over current, under voltage, overload, overheating,

external fault, electronic thermal, ground fault.

Display Keypads

6-key, 4-digit, 7-segment LED, 4 status LEDs, master frequency, output frequency,

output current, custom units, parameter values for setup, review and faults, RUN,

STOP, RESET, FWD/REV

Built-in Brake Chopper Built-in for all models

Protection Level IP20

Pollution Degree 2

Installation Location Altitude 1,000 m or lower, keep from corrosive gasses, liquid and dust

Ambient Temperature -10o C to 40o C (-10o C to 50o C without blind plate) Non-Condensing and not frozen Storage/Transportation

Temperature

-20o C to 60o C

Ambient Humidity Below 90% RH (non-condensing)

E

n

v

i

r

o

m

e

n

t

a

l

C

o

n

d

i

t

i

o

n

s

Vibration 9.80665m/s2 (1G) less than 20Hz, 5.88m/s2 (0.6G) at 20 to 50Hz

Approvals

Note: Do not attempt to connect a single-phase power source to a three-phase models drive. However it is acceptable to connect two wires of a three-phase power source to a single-phase drive. Basic Wiring Diagram

Users must connect wiring according to the following circuit diagram shown below.

台达变频器

port, permanent damage may result. Terminal 1& 2 are the power

sources for the optional copy keypad and should not be used while

using RS-485 communication.

~10V

* If it is single phase model, please select any of the two input power

terminals in main circuit power.

* Single phase model can be input 3-phase power.

Description of Digital Keypad

The digital keypad includes two parts: Display panel and keypad. The display panel provides the parameter display and shows the operation status of the AC drive and the keypad provides programming and control interface.

台达变频器

Selects normal mode/program mode. Displays output freq., selects the parameters.

Enter Key

Press ENTER parameters or change data.

Potentiometer

How to Operate the Digital Keypad LC-M02E

台达变频器

台达变频器

GO START

台达变频器

台达变频器

To set direction

(When operation sour ce is digital keypad)

NOTE: In the selection mode, press to set the parameters.

台达变频器

台达变频器

台达变频器

ENTER Selection mode

台达变频器

台达变频器

Power Terminals

台达变频器

台达变频器

Terminal Explanations

台达变频器

Control Terminal Wiring (Factory Setting)

M0

M1M2M3M4M5GND AFM AVI +10V MCM MO1

RA RB RC

Relay contactor

Output

Factory Setting

Bias

Potentiometer

Full scale voltmeter 0 to 10 VDC

Factory setting:fault indication

Photo coupler output

Forward/Stop Reverse/Stop

Reset

Multi-step speed 1Multi-step speed 2Multi-step speed 3

ACI GND 4~20mA Wire Type: 75 C, Copper Only Torque: 4kgf-cm (3.5 in-lbf)

Wire Gauge: 24-12 AWG Wire Type: Copper Only Torque: 2kgf-cm (1.73 in-lbf)

Wire Gauge: 22-16 AWG

NPN mode without ext ernal power

N PN mode with external power

台达变频器

台达变频器

台达变频器

-f u n c t i o n I n p u t T e r m i n a l s

t i n g

n c t i o n I n p u t T e r m i n a l s

Terminal Symbol Terminal Function Factory Settings (NPN mode)

RA

Multi-Function Relay Output (N.O.) a

RA-RC

Resistive Load

5A(N.O.)/3A(N.C.) 277Vac; 5A(N.O.)/3A(N.C.) 30Vdc Refer to P45 for programming. RB Multi-Function Relay Output

(N.C.) b

RB-RC

Resistive Load

5A(N.O.)/3A(N.C.) 277Vac; 5A(N.O.)/3A(N.C.) 30Vdc

RC

Multi-function Relay Common 5A(N.O.)/3A(N.C.) 277Vac; 5A(N.O.)/3A(N.C.) 30Vdc

台达变频器

Note: Use twisted-shielded, twisted-pair or shielded-lead wires for the control signal wiring. It is recommended to run all signal wiring in a separate steel conduit. The shield wire should only be connected at the drive. Do not connect shield wire on both ends.

SUMMARY OF PARAMETER SETTINGS

a: The parameter can be set during operation

Parameter Explanation Settings Factory

Setting

Customer

a Pr.00 Source of Frequency

Command

00: Master frequency determined by

digital keypad (LC-M02E)

01: Master frequency determined by 0 to

+10 V input on AVI terminal with

jumpers

02: Master frequency determined by 4 to

20mA input on ACI terminal with

jumpers

03: Master frequency determined by RS-

485 Communication port

04: Master frequency determined by

potentiometer on digital keypad

00

a Pr.01 Source of Operation

command

00: Operation determined by digital

keypad

01: Operation determined by external

control terminals, keypad STOP is

effective

02: Operation determined by external

control terminals, keypad STOP is

ineffective

03: Operation determined by RS-485

communication port, keypad STOP is

effective

04: Operation determined by RS-485

communication port, keypad STOP is

ineffective

00

Pr.02 Stop

Method 00: Ramp stop

01: Coast Stop

00

Pr.03 Maximum Output

Frequency

50.00 to 400.0 Hz 60.00

Pr.04 Maximum Voltage

Frequency (Base

Frequency)

10.00 to 400.0Hz 60.00

Pr.05 Maximum Output

Voltage (Vmax)

115V/230V: 0.1 to 255.0V

460V: 0.1 to 510.0V

575V: 0.1 to 637.0V

220.0

440.0

575.0

Pr.06 Mid-point Frequency 0.10 to 400.0Hz 1.50

Pr.07 Mid-point

Voltage 115V/230V: 0.1 to 255.0V

460V: 0.1 to 510.0V

575V: 0.1 to 637.0V

10.0

20.0

26.1

Pr.08 Minimum Output Freq0.10 to 20.00Hz 1.50

Pr.09 Minimum Output

Voltage

115V/230V: 0.1 to 255.0V

460V: 0.1 to 510.0V

575V: 0.1 to 637.0V

10.0

20.0

26.1

a Pr.10 Acceleration Time 1 0.1 to 600.0 sec or 0.01 to 600.0 sec 10.0 a Pr.11 Deceleration Time 1 0.1 to 600.0 sec or 0.01 to 600.0 sec 10.0 a Pr.12 Acceleration Time 2 0.1 to 600.0 sec or 0.01 to 600.0 sec 10.0 a Pr.13 Deceleration Time 2 0.1 to 600.0 sec or 0.01 to 600.0 sec 10.0 Pr.14 Accel S-curve 00 to 07 00 a Pr.15 Jog Accel/Decel Time0.1 to 600.0 sec or 0.01 to 600.0 sec 1.0

a Pr.16 Jog Frequency 0.00 to 400.0 Hz 6.00 a Pr.17 1st Step Speed Freq. 0.00 to 400.0Hz 0.00 a Pr.18 2nd Step Speed Freq.0.00 to 400.0Hz 0.00 a Pr.19 3rd Step Speed Freq. 0.00 to 400.0Hz 0.00 a Pr.20 4th Step Speed Freq. 0.00 to 400.0Hz 0.00 a Pr.21 5th Step Speed Freq. 0.00 to 400.0Hz 0.00 a Pr.22 6th Step Speed Freq. 0.00 to 400.0Hz 0.00 a Pr.23 7th Step Speed Freq. 0.00 to 400.0Hz 0.00

Pr.24 Reserve Operation

Inhibition

00: Enable REV operation

01: Disable REV operation

00

Pr.25 Over-Voltage Stall

Prevention

00: Disable

115V/230V: 330 to 450 Vdc

460V: 660 to 900 Vdc

575V: 825 to 1025 Vdc

390

780

975

Pr.26 Over-current Stall

Prevention during

Acceleration

00: Disable

20% to 200%

150

Pr.27 Over-current Stall

Prevention during

Operation

00: Disable

20% to 200%

150

Pr.28 DC Braking Current

Level

00 to 100 % 00

Pr.29 DC Braking during

Start-up

0.0 to 5.0 sec 0.0

Pr.30 DC Braking during

Stopping

0.0 to 25.0 sec 0.0

Pr.31 Start-point for DC

Braking

0.00 to 60.00 Hz 0.00

Pr.32 Momentary Power Loss

Operation Selection

00: Stop operation after momentary

power loss

01: Continues after momentary power

loss, speed search starts with Master

Frequency

02: Continues after momentary power

loss, speed search starts with

Minimum output Frequency

00

Pr.33 Maximum Allowable

Power Loss Time

0.3 to 5.0 sec 2.0

Pr.34 Base-Block Time for

Speed Search

0.3 to 5.0 sec 0.5

Pr.35 Maximum Current

Level for Speed Search

30 to 200 % 150

Pr.36 Upper Bound of Output

Frequency

0.10 Hz to 400.0 Hz 400.0

Pr.37 Lower Bound of Output

Frequency

0.00 Hz to 400.0 Hz 0.00

Pr.38 Multi-function Input

Terminal (M0,M1)

00: M0: FWD/STOP, M1: REV/STOP

01: M0: RUN/STOP, M1: REV/FWD

02: M0, M1, M2: 3-wire operation control

mode

00

Pr.39 Pr.40 Pr.41 Pr.42 Multi-function Input

Terminal (M2)

Multi-function Input

Terminal (M3)

Multi-function Input

Terminal (M4)

Multi-function Input

Terminal (M5)

00: No Function

01: Output OFF (N.O.) (enabled when

running)

02: Output OFF (N.C.) (enabled when

running)

03: External Fault (normally open) N.O.

04: External Fault (normally close) N.C

05: RESET

06: Multi-Step Speed Command 1

07: Multi-Step Speed Command 2

08: Multi-Step Speed Command 3

09: Jog Operation

10: Accel/Decel Speed Inhibit

11: First or Second Accel/Decel Time

12: Base-block (B.B.) (N.O)

13: Base-block (B.B.) (N.C)

14: Increase Master Frequency

15: Decrease Master Frequency

16: Run PLC Program

17: Pause PLC

18: Counter Trigger Signal

19: Counter Reset

20: No function

21: RESET command (N.C)

22: Control source: External Terminal

23: Control source: Keypad

24: Control source: Communication

25: Parameter Lock (Write disable, Read

is always 0)

26: PID Disable (N.O.)

27: PID Disable (N.C.)

28: Second Source for Frequency

Command

29: Forward (contact is open) / Reverse

(contact is close)

30: One-Shot PLC Run

31: Index input signal

32: Counter Incremented by Drive Output

Frequency

05

06

07

08

a Pr.43 Analog

Output

Signal 00: Analog Frequency Meter (0 to

Maximum Output Frequency)

01: Analog Current Meter (0 to 250% of

the rated AC drive current)

02: Feedback signal (0 - 100%)

03: Output power (0 - 100%)

00

a Pr.44 Analog Output Gain 00 to 200 % 100

Pr.45 Pr.46 Multi-Function Output

Terminal 1

(Photocoupler output)

Multi-function Output

Terminal 2

(Relay Output)

00: AC Drive Operational

01: Maximum Output Frequency Attained

02: Zero Speed

03: Over-Torque Detection

04: Base-Block (B.B) Indication

05: Low Voltage Indication

06: AC Drive Operation Mode

07: Fault Indication

08: Desired Frequency Attained

09: PLC Program Running

10: PLC Program Step Completed

11: PLC Program Completed

12: PLC Operation Paused

13: Top Count Value Attained

14: Preliminary Counter Value Attained

15: Warning (PID feedback loss,

communication error)

16: Below the Desired Frequency

17: PID supervision

18: Over Voltage supervision

19: Over Heat supervision

20: Over Current stall supervision

21: Over Voltage stall supervision

22: Forward command

23: Reverse command

24: Zero Speed (Includes Drive Stop)

00

07

a Pr.47 Desired Frequency

Attained

0.00 to 400.0 Hz 0.00

a Pr.48 Adjust Bias of External

Input Frequency

0.00 to 200.0% 0.00

a Pr.49 Potentiometer Bias

Polarity

00: Positive Bias

01: Negative Bias

00

a Pr.50 Potentiometer

Frequency Gain

0.10 to 200.0% 100.0

Pr.51 Potentiometer Reverse

Motion Enable

00: Reverse Motion Disabled in negative

bias

01: Reverse Motion Enabled in negative

bias

00

a Pr.52 Motor Rated Current 30.0% FLA to 120.0% FLA FLA

a Pr.53 Motor No-Load Current00%FLA to 99%FLA 0.4* FLA

a Pr.54 Torque Compensation00 to 10 00 a Pr.55 Slip Compensation 0.00 to 10.00 0.00 Pr.56 Reserved

Pr.57 AC Drive Rated Current Display (unit: 0.1A) ##.#

Pr.58 Electronic Thermal

Overload Relay

00: Standard Motor (self cool motor)

01: Inverter Motor (auxiliary cool fan on

motor)

02: Inactive

02

a Pr.59 Electronic Thermal

Motor Overload

30 to 300 sec 60

Pr.60 Over-Torque Detection

Mode

00: Over-Torque Detection Disable

01: Enabled during constant speed

operation until the allowable time for

detection (Pr.62) elapses.

02: Enabled during constant speed

operation and halted after detection.

03: Enabled during acceleration until the

allowable time for detection (Pr.62)

elapses.

04: Enabled during acceleration and

halted after detection.

00

Pr.61 Over-Torque Detection

Level 30 to 200 % 150

Pr.62 Over-Torque Detection

Time

0.0 to 10.0 seconds 0.1

Pr.63 Loss of ACI (4-20mA) 00: Decelerate to 0 Hz

01: Stop immediately and display "EF"

02: Continue operation by last frequency

command

00

a Pr.64 User Defined Function

for Display

00: Display AC drive output Frequency

(Hz)

01: Display User-defined output

Frequency (H*Pr.65)

02: Output Voltage (E)

03: DC Bus Voltage (u_)

04: PV (i)

05: Display the value of internal counter

(c)

06: Display the setting frequency (F or

o=%)

07: Display the parameter setting (Pr.00)

08: Reserved

09: Output Current (A)

10: Display program operation (0.xxx),

Fwd, or Rev

06

a Pr.65 Coefficient K 0.01 to 160.0 1.00

a Pr.66 Communication

Frequency

0.00 to 400.0 Hz 0.00

Pr.67 Skip Frequency 1 0.00 to 400.0 Hz 0.00 Pr.68 Skip Frequency 2 0.00 to 400.0 Hz 0.00 Pr.69 Skip Frequency 3 0.00 to 400.0 Hz 0.00 Pr.70 Skip Frequency Band 0.00 to 20.00 Hz 0.00

01 to 15

The factory setting of VFD075M43A is 10.15

Pr.71 PWM Carrier

Frequency

575V series: 01 to 10 6

Pr.72 Auto Restart Attempts

after Fault

00 to 10 00

Pr.73 Present Fault Record 00

Pr.74 Second Most Recent

Fault Record

00

Pr.75 Third Most Recent

Fault Record

00: No fault occurred

01: Over-current (oc)

02: Over-voltage (ov)

03: Overheat (oH)

04: Overload (oL)

05: Overload 1 (oL1)

06: External Fault (EF)

07: CPU failure 1 (CF1)

08: CPU failure 3 (CF3)

09: Hardware Protection Failure (HPF)

10: Over-current during acceleration (oca)

11: Over-current during deceleration

(ocd)

12: Over-current during steady state

operation (ocn)

13: Ground fault or fuse failure(GFF)

14: Low Voltage (not record)

15: 3 Phase Input Power Loss

16: EPROM failure (CF2)

17: External interrupt allowance(bb)

18: Overload (oL2)

19: Auto Adjustable accel/decel failure

(CFA)

20: CPU self detection failure (codE)

00

Pr.76 Parameter Lock and

Configuration

00: All parameters can be set/read

01: All parameters are read-only

02-08: Reserved

09: Resets all parameters to 50Hz factory

defaults

10: Resets all parameters to 60Hz factory

defaults

00

Pr.77 Time for Auto Reset the

Restart Times in

Abnormality

0.1 to 6000.0 sec 60.0

Pr.78 PLC Operation Mode 00: Disable PLC operation

01: Execute one program cycle

02: Continuously execute program cycles

03: Execute one program cycle step by

step

04: Continuously execute one program

cycle step by step

00

Pr.79 PLC FWD/REV Motion00 to 127 00

Pr.80 Identity Code of the AC

Motor Drive

Read only ##

Pr.81 Time Duration of 1st

Step Speed

00 to 9999 sec 00

Pr.82 Time Duration of 2nd

Step Speed

00 to 9999 sec 00

Pr.83 Time Duration of 3rd

Step Speed

00 to 9999 sec 00

Pr.84 Time Duration of 4th

Step Speed

00 to 9999 sec 00

Pr.85 Time Duration of 5th

Step Speed

00 to 9999 sec 00

Pr.86 Time Duration of 6th

Step Speed

00 to 9999 sec 00

Pr.87 Time Duration of 7th

Step Speed

00 to 9999 sec 00

Pr.88 Communication

Address

01 to 254 01

Pr.89 Transmission

Speed 00: 4800 bps

01: 9600 bps

02: 19200 bps

03: 38400 bps

01

Pr.90 Transmission Fault

Treatment

00: Warn and Continue Operating

01: Warn and RAMP to Stop

02: Warn and COAST to Stop

03: Keep Operation without Warning

03

Pr.91 Time Out Detection 0.0: Disable

0.1 to 120.0 sec

0.0

Pr.92 Communication

Protocol

00: MODBUS ASCII mode, <7,N,2>

01: MODBUS ASCII mode, <7,E,1>

02: MODBUS ASCII mode, <7,O,1>

03: MODBUS RTU mode, <8,N,2>

04: MODBUS RTU mode, <8,E,1>

05: MODBUS RTU mode, <8,O,1>

00

Pr.93 Accel 1 to Accel 2

Frequency Transition

0.01 to 400.0

0.00: Disable

0.00

Pr.94 Decel 1 to Decel 2

Frequency Transition

0.01 to 400.0

0.00: Disable

0.00

Pr.95 Auto Energy Saving 00: Disable auto energy saving

01: Enable auto energy saving

00

Pr.96 Counter Countdown

Complete

00 to 9999 00

Pr.97 Preset counter

countdown

00 to 9999 00

Pr.98 Total Time Count from

Power On (Days)

00 to 65535 days

Read

Only

Pr.99 Total Time Count from

Power On (Minutes)

00 to 1440 minutes

Read

Only

Pr.100 Software

Version ##

Pr.101 Auto Adjustable

Accel/Decel

00: Linear Accel/Decel

01: Auto Accel, Linear Decel

02: Linear Accel, Auto Decel

03: Auto Accel/Decel

04: Linear Accel/Decel Stall Prevention

during Deceleration

00

Pr.102 Auto Voltage

Regulation (AVR)

00: AVR function enabled

01: AVR function disabled

02: AVR function disabled when stops

03: AVR function disabled when decel

00

Pr.103 Auto tune Motor

Parameters

00: Disable

01: Auto tune for R1

02: Auto tune for R1 + No Load testing

00

Pr.104 R1

value 00 to 65535 mΩ00

Pr.105 Control

Mode 00: V/F Control

01: Sensor-less Control

00

Pr.106 Rated Slip 0.00 to 10.00 Hz 3.00 Pr.107 Vector Voltage Filter 5 to 9999 (per 2ms) 10

Pr.108 Vector Slip

Compensation Filter

25 to 9999 (per 2ms) 50

Pr.109 Selection for Zero

Speed Control

00: No output

01: Control by DC voltage

00

Pr.110 Voltage of Zero Speed

Control

to 20.0 % of Max. output voltage (Pr.05) 5.0

Pr.111 Decel S-curve 00 to 07 00

Pr.112 External Terminal

Scanning Time

01 to 20 01

Pr.113 Restart Method after

Fault (oc, ov, BB)

00: None speed search

01: Continue operation after fault speed

search from speed reference

02: Continue operation after fault speed

search from Minimum speed

01

Pr.114 Cooling Fan Control 00: Fan Off when the drive stop after 1

Min.

01: AC Drive Runs and Fan On, AC Drive

Stops and Fan Off

02: Always Run

03: Reserved

02

Pr.115 PID Set Point Selection 00: Disable

01: Keypad (based on Pr.00 setting)

02: AVI (external 0-10V)

03: ACI (external 4-20mA)

04: PID set point (Pr.125)

00

Pr.116 PID Feedback Terminal

Selection

00: Input positive PID feedback, PV from

AVI (0 to 10V)

01: Input negative PID feedback, PV from

AVI (0 to 10V)

02: Input positive PID feedback, PV from

ACI (4 to 20mA)

03: Input negative PID feedback, PV from

ACI (4 to 20mA)

00

Pr.117 Proportional Gain (P) 0.0 to 10.0 1.0

Pr.118 Integral Time (I) 0.00: Disable

0.01 to 100.0 sec

1.00

Pr.119 Differential Time (D) 0.00 to 1.00 sec 0.00

Pr.120 Integration’s Upper

Bound Frequency

00 to 100 % 100 %

Pr.121 One-Time Delay 0.0 to 2.5 sec 0.0

Pr.122 PID Frequency Output

Command Limit

00 to 110 % 100

Pr.123 Feedback Signal

Detection Time

0.0: Disable

0.1 to 3600 sec

60.0

Pr.124 Feedback Signal Fault

Treatment

00: Warning and RAMP to stop

01: Warning and keep operating

00

Pr.125 Source of PID Set Point0.00 to 400.0Hz 0.00 Pr.126 PID Offset Level 1.0 to 50.0 % 10.0

Pr.127 Detection Time of PID

Offset

0.1 to 300.0 sec 5.0

Pr.128 Minimum Reference

Value

0.0 to 10.0 V 0.0

Pr.129 Maximum Reference

Value

0.0 to 10.0 V 10.0

Pr.130 Invert Reference Signal

AVI (0-10V)

00: Not inverted

01: Inverted

00

Pr.131 Minimum Reference

Value (4-20mA)

0.0 to 20.0mA 4.0

Pr.132 Maximum Reference

Value (4-20mA)

0.0 to 20.0mA 20.0

Pr.133 Invert Reference Signal

(4-20mA)

00: Not inverted

01: Inverted

00

Pr.134 Analog Input Delay

Filter for Set Point

00 to 9999 (per 2ms) 50

Pr.135 Analog Input Delay

Filter for Feedback

Signal

00 to 9999 (per 2ms) 5

Pr.136 Sleep Period 0.0 to 6550.0 sec 0.0 Pr.137 Sleep Frequency 0.00 to 400.0 Hz 0.00 Pr.138 Wake Up Frequency 0.00 to 400.0 Hz 0.00

Pr.139 Treatment for Counter

Attained

00: Continue operation

01: Stop Immediately and display E.F.

00

Pr.140 External Up/Down

Selection

00: Fixed Mode (keypad)

01: By Accel or Decel Time

02: Reserved

00

Pr.141 Save Frequency Set

Point

00: Not Save

01: Save

01

Pr.142 Second Source of

Frequency Command

00: Keypad Up/Down

01: AVI (0-10V)

02: ACI (4-20mA)

03: Communication

04: Keypad potentiometer

00

115V/230V 370-450 Vdc 380.0

460V 740-900 Vdc 760.0

Pr.143 Software Braking Level

575V 925-1075

Vdc 950.0

Pr.144 Total operation time

(Day)

Read Only

Pr.145 Total operation time

(Minutes)

Read Only

Pr.146 Line

start

Lockout 00: Disable

01: Enable

00

Pr.147 Decimal Number of

Accel / Decel Time

00: One decimal

01: Two decimals

00

Pr.148 Number of Motor Poles02 to 20 04

Pr.149 Gear Ratio for Simple

Index Function

4 to 1000 200

Pr.150 Index Angle for Simple

Index Function

00.0 to 360.0 180.0

Pr.151 Deceleration Time for

Simple Index Function

0.00 to 100.00 sec 0.00

Pr.152 Skip Frequency Width0.00 to 400.0Hz 0.00 Pr.153 Bias Frequency Width0.00 to 400.0Hz 0.00 Pr.154 Reserved

a Pr.155 Compensation

Coefficient for Motor

Instability

0.0: Disable

0.1 to 5.0 (recommended setting d2.0)

0.0

a Pr.156 Communication

Response Delay Time

0 to 200 (x500us) 0

a Pr.157 Communication Mode

Selection

0: Delta ASCII

1: Modbus

1