Safety Precaution (Read these precautions before use.)
also cause severe injury.
It is important to follow all precautions for personal safety.
Associated Manuals
How to obtain manuals
For product manuals or documents, consult with the Mitsubishi Electric dealer from who you purchased your product.
Manual name Manual No.Description
FX 3G /FX 3U /FX 3UC Series
User's Manual - Analog Control Edition
JY997D16701MODEL CODE:
09R619
Describes specifications for analog control and
programming method for FX 3G /FX 3U /FX 3UC Series PLC.
FX 3G /FX 3U /FX 3UC Series
Programming Manual - B a s i c & A p p l i ed Instruction Edition JY997D16601MODEL CODE:
09R517Describes PLC programming for basic/applied instructions and devices.
FX 3G Series User’s Manual - Hardware Edition JY997D31301MODEL CODE:
09R521Explains FX 3G Series PLC specifications for I/O, wiring,installation, and maintenance.FX 3U Series User’s Manual - Hardware Edition JY997D16501MODEL CODE:
09R516Explains FX 3U Series PLC specifications for I/O, wiring,installation, and maintenance.FX 3UC Series User’s Manual - Hardware Edition
JY997D28701MODEL CODE:
09R519
Explains FX 3UC Series PLC specifications for I/O, wiring,
installation, and maintenance.
Applicable standards
FX 3U -4AD-ADP units made in June, 2005 or later comply with the EC Directive (EMC
Directive) and UL standards (UL, cUL). Further information can be found in the following manual.
→ Refer to the FX 3G Series Hardware Manual (Manual No. JY997D33401)→ Refer to the FX 3U Series Hardware Manual (Manual No. JY997D18801)
→ Refer to the FX 3UC (D, DSS) Series Hardware Manual (Manual No.
JY997D28601)
→ Refer to the FX 3UC -32MT-LT-2 Hardware Manual (Manual No. JY997D31601)Regarding the standards that relate to the main unit, please refer to either the FX series product catalog or consult with your nearest Mitsubishi product provider.
Caution for EC Directive
The analog special adapters have been found to be compliant to the European standards in the aforesaid manual and directive. However, for the very best per-formance from what are in fact delicate measuring and controlled output device Mitsubishi Electric would like to make the following points;
As analog devices are sensitive by nature, their use should be considered care-fully. For users of proprietary cables (integral with sensors or actuators), these users should follow those manufacturers installation requirements.
Mitsubishi Electric recommend that shielded cables should be used. If NO other EMC protection is provided, then users may experience temporary loss or accuracy between ±10% in very heavy industrial areas.
However, Mitsubishi Electric suggest that if adequate EMC precautions are fol-lowed for the users complete control system, users should expect accuracy as specified in this manual.
?Sensitive analog cable should not be laid in the same trunking or cable conduit as high voltage cabling. Where possible users should run analog cables separately.
?Good cable shielding should be used. When terminating the shield at Earth - ensure that no earth loops are accidentally created.
?When reading analog values, EMC accuracy can be improved out by averaging the readings. This can be achieved either through functions on the analog special adapters or through a users program in the FX 3U(C) Series PLC main unit.
1.Outline
The FX 3U -4AD-ADP adapter for analog input (hereinafter called 4AD-ADP) is a special adapter to add four analog input points.
1.1Incorporated Items
Verify that the following product and items are included in the package:
1.2External Dimensions, Part Names, and Terminal Layout
[1]DIN rail mounting groove (DIN rail: DIN46277)[2]Name plate
V1+I1+
COM1V3+I3+24+24-
V2+I2+V4+I4+
COM4
COM3COM2
2.Installation
For installation/uninstallation details, refer to the following manuals:
→ Refer to the FX 3G Series User's Manual - Hardware Edition.→ Refer to the FX 3U Series User's Manual - Hardware Edition.→ Refer to the FX 3UC Series User's Manual - Hardware Edition.
2.1Connection to the FX 3U Series PLC
Procedure
1)Turn off the power.
Disconnect all the cables connected to the PLC main unit and special adapter, and
using screws.2)Install an expansion board to the main unit.
→ Refer to the FX 3U 3)Remove the special adapter connector cover on the expansion board (fig.A).
When connecting this product to another special
adapter, please replace the 'expansion board' in the above description with a 'special adapter' and perform the procedure as indicated.4)Slide the special adapter slide lock
(fig.B) of the main unit.
When connecting this product to another special adapter, please replace the 'main unit' in the
above description with a 'special adapter' and
perform the procedure as indicated.
[3]Special adapter slide lock:
Used to connect additional special adapters onto the left side of this special adapter.
[4]Special adapter connector cover:
Remove this cover to connect additional special adapters to the left side.[5]Direct mounting hole:2 holes of φ4.5 (0.18") (mounting screw: M4 screw)
Not used when connecting to FX 3UC Series PLC.[6]POWER LED (green):
Lit while 24V DC power is supplied properly to terminals '24+' and '24-'.[7]Terminal block (European type):
Connect the analog voltage/current signal, and 24V DC power supply.[8]Special adapter connector:
Used to connect this special adapter to PLC main unit or special adapter.[9]DIN rail mounting hook [10]Special adapter fixing hook [11]Special adapter connector:
Used to connect communication or analog special adapters to the left side of the 4AD-ADP .
5)Connect the special adapter (fig.C) to the main unit as shown on the right .
6)Slide back the special adapter slide lock (fig.B) of the main unit
adapter (fig.C).
Connect all the high-speed I/O special adapters before connecting other special adapters when they are used in combination.
Do not connect a high-speed I/O special adapter on the left side of a communication or analog special adapter.
2.2Connection to the FX 3UC (D, DSS) Series PLC
Procedure
1)Turn off the power.
Disconnect all the cables connected to the PLC, and demount the PLC from the DIN rail.2)Remove the special adapter connector cover (fig.A).
3)Slide the special adapter slide lock (fig.B)of the main unit.
When connecting this product to another special adapter, please replace the 'main unit' in the above description with a 'special adapter' and perform the procedure as indicated.
4)Connect the special adapter (fig.C) to the main unit as shown on the right.
5)Slide back the special adapter slide lock (fig.B) of the main unit to fix the special adapter (fig.C).
3UC -32MT-LT(-2) Series PLC
3UC Series User's Manual - Hardware Edition.
FX 3U -4AD-ADP
USER'S MANUAL
This manual describes the part names, dimensions, mounting, and specifications of the product. Before use, read this manual and the manuals of all relevant products fully to acquire proficiency in handling and operating the product. Make sure to learn all the product information, safety information, and precautions.
Store this manual in a safe place so that it can be taken out and read whenever necessary. Always forward it to the end user.Registration:
The company and product names described in this manual are registered trademarks or the trademarks of their respective companies.Effective September 2008
Specifications are subject to change without notice.
? 2005 Mitsubishi Electric Corporation
Manual Number JY997D13901Revision G
Date
September 2008
2.4Connection to the FX3G Series PLC
3.1Applicable Cable and Terminal Tightening Torque 3.4Grounding
4.4Performance Specifications
Side
B
Side
A
Side
B
JAPANESE
ENGLISH
JY997D13901G
Safety Precaution (Read these precautions before use.)
This manual classifies the safety precautions into two categories:
also cause severe injury.
It is important to follow all precautions for personal safety.
Associated Manuals
How to obtain manuals
For product manuals or documents, consult with the Mitsubishi Electric dealer from who you purchased your product.
Manual name Manual No.Description
FX 3G /FX 3U /FX 3UC Series
User's Manual - Analog Control Edition
JY997D16701MODEL CODE:
09R619
Describes specifications for analog control and
programming method for FX 3G /FX 3U /FX 3UC Series PLC.
FX 3G /FX 3U /FX 3UC Series
Programming Manual - B a s i c & A p p l i ed Instruction Edition JY997D16601MODEL CODE:
09R517Describes PLC programming for basic/applied instructions and devices.
FX 3G Series User’s Manual - Hardware Edition JY997D31301MODEL CODE:
09R521Explains FX 3G Series PLC specifications for I/O, wiring,installation, and maintenance.FX 3U Series User’s Manual - Hardware Edition JY997D16501MODEL CODE:
09R516Explains FX 3U Series PLC specifications for I/O, wiring,installation, and maintenance.FX 3UC Series User’s Manual - Hardware Edition
JY997D28701MODEL CODE:
09R519
Explains FX 3UC Series PLC specifications for I/O, wiring,
installation, and maintenance.
Applicable standards
FX 3U -4AD-ADP units made in June, 2005 or later comply with the EC Directive (EMC
Directive) and UL standards (UL, cUL). Further information can be found in the following manual.
→ Refer to the FX 3G Series Hardware Manual (Manual No. JY997D33401)→ Refer to the FX 3U Series Hardware Manual (Manual No. JY997D18801)
→ Refer to the FX 3UC (D, DSS) Series Hardware Manual (Manual No.
JY997D28601)
→ Refer to the FX 3UC -32MT-LT-2 Hardware Manual (Manual No. JY997D31601)Regarding the standards that relate to the main unit, please refer to either the FX series product catalog or consult with your nearest Mitsubishi product provider.
Caution for EC Directive
The analog special adapters have been found to be compliant to the European standards in the aforesaid manual and directive. However, for the very best per-formance from what are in fact delicate measuring and controlled output device Mitsubishi Electric would like to make the following points;
As analog devices are sensitive by nature, their use should be considered care-fully. For users of proprietary cables (integral with sensors or actuators), these users should follow those manufacturers installation requirements.
Mitsubishi Electric recommend that shielded cables should be used. If NO other EMC protection is provided, then users may experience temporary loss or accuracy between ±10% in very heavy industrial areas.
However, Mitsubishi Electric suggest that if adequate EMC precautions are fol-lowed for the users complete control system, users should expect accuracy as specified in this manual.
?Sensitive analog cable should not be laid in the same trunking or cable conduit as high voltage cabling. Where possible users should run analog cables separately.
?Good cable shielding should be used. When terminating the shield at Earth - ensure that no earth loops are accidentally created.
?When reading analog values, EMC accuracy can be improved out by averaging the readings. This can be achieved either through functions on the analog special adapters or through a users program in the FX 3U(C) Series PLC main unit.
1.Outline
The FX 3U -4AD-ADP adapter for analog input (hereinafter called 4AD-ADP) is a special adapter to add four analog input points.
1.1Incorporated Items
Verify that the following product and items are included in the package:
1.2External Dimensions, Part Names, and Terminal Layout
[1]DIN rail mounting groove (DIN rail: DIN46277)[2]Name plate
V1+I1+
COM1V3+I3+24+24-
V2+I2+V4+I4+
COM4
COM3COM2
2.Installation
For installation/uninstallation details, refer to the following manuals:
→ Refer to the FX 3G Series User's Manual - Hardware Edition.→ Refer to the FX 3U Series User's Manual - Hardware Edition.→ Refer to the FX 3UC Series User's Manual - Hardware Edition.
2.1Connection to the FX 3U Series PLC
Procedure
1)Turn off the power.
Disconnect all the cables connected to the PLC main unit and special adapter, and
using screws.2)Install an expansion board to the main unit.
→ Refer to the FX 3U 3)Remove the special adapter connector cover on the expansion board (fig.A).
When connecting this product to another special
adapter, please replace the 'expansion board' in the above description with a 'special adapter' and perform the procedure as indicated.4)Slide the special adapter slide lock
(fig.B) of the main unit.
When connecting this product to another special adapter, please replace the 'main unit' in the
above description with a 'special adapter' and
perform the procedure as indicated.
[3]Special adapter slide lock:
Used to connect additional special adapters onto the left side of this special adapter.
[4]Special adapter connector cover:
Remove this cover to connect additional special adapters to the left side.[5]Direct mounting hole:2 holes of φ4.5 (0.18") (mounting screw: M4 screw)
Not used when connecting to FX 3UC Series PLC.[6]POWER LED (green):
Lit while 24V DC power is supplied properly to terminals '24+' and '24-'.[7]Terminal block (European type):
Connect the analog voltage/current signal, and 24V DC power supply.[8]Special adapter connector:
Used to connect this special adapter to PLC main unit or special adapter.[9]DIN rail mounting hook [10]Special adapter fixing hook [11]Special adapter connector:
Used to connect communication or analog special adapters to the left side of the 4AD-ADP .
5)Connect the special adapter (fig.C) to the main unit as shown on the right .
6)Slide back the special adapter slide lock (fig.B) of the main unit
adapter (fig.C).
Connect all the high-speed I/O special adapters before connecting other special adapters when they are used in combination.
Do not connect a high-speed I/O special adapter on the left side of a communication or analog special adapter.
2.2Connection to the FX 3UC (D, DSS) Series PLC
Procedure
1)Turn off the power.
Disconnect all the cables connected to the PLC, and demount the PLC from the DIN rail.2)Remove the special adapter connector cover (fig.A).
3)Slide the special adapter slide lock (fig.B)of the main unit.
When connecting this product to another special adapter, please replace the 'main unit' in the above description with a 'special adapter' and perform the procedure as indicated.
4)Connect the special adapter (fig.C) to the main unit as shown on the right.
5)Slide back the special adapter slide lock (fig.B) of the main unit to fix the special adapter (fig.C).
3UC -32MT-LT(-2) Series PLC
3UC Series User's Manual - Hardware Edition.
2.4
Connection to the FX 3G Series PLC
Procedure
1)Turn off the power.
Disconnect all the cables connected to the PLC, and demount the PLC from the DIN rail.
2)following manual:
→ 3)4)adapter.
indicated.5)Connect the special adapter (fig.B) to the connector
conversion on the right 6)Slide back the
special adapter
slide lock (fig.A) of the connector
conversion
adapter to fix the
special adapter
(fig.B). 3.Wiring
3.1Applicable Cable and Terminal Tightening Torque
3.1.1
Terminal block (European type)
1)Wire size
Wiring to analog device should use 20-22 AWG wire.
*1Use 2-core shielded twisted pair cable for the analog input lines, and separate
the analog input lines from other power lines or inductive lines.*2Make sure to short-circuit the 'V +' and 'I +' terminals when current is input.
( : input channel number)*324V DC service power supply of the FX 3G /FX 3U Series PLC can also be used.
3.4Grounding
Grounding should be performed as stated below.?The grounding resistance should be 100? or less.
?Independent grounding should be performed for best results.
When independent grounding is not performed, perform "shared grounding"of the following figure.
→ For details, refer to the FX 3G Series User's
Manual - Hardware Edition.
→ For details, refer to the FX 3U Series User's
Manual - Hardware Edition.
→ For details, refer to the FX 3UC Series User's
Manual - Hardware Edition.
?The grounding wire size should be AWG 22-20 (0.3-0.5 mm 2).
?The grounding point should be close to the PLC, and all grounding wire should be as short as possible.
4.Specifications
4.1Applicable PLC
The version number can be checked by monitoring D8001 as the last three digits indicate it.
4.2General Specifications
For the general specifications, refer to the manual of the PLC main unit.
The items other than the following are equivalent to those of the PLC main unit.
4.3Power Supply Specifications
STARTUP AND MAINTENANCE PRECAUTIONS
?Do not disassemble or modify the PLC.
Doing so may cause fire, equipment failures, or malfunctions.* For repair, contact your local Mitsubishi Electric distributor.?Do not drop the product or exert strong impact to it.Doing so may cause damage.DISPOSAL PRECAUTIONS
?Please contact a certified electronic waste disposal company for the environmentally safe recycling and disposal of your device.TRANSPORT AND
STORAGE PRECAUTIONS
?The product is a precision instrument. During transportation, avoid any impacts. Failure to do so may cause failures in the product. After transportation, verify the operations of the product.
Model name Applicability
FX 3U Series PLC
Ver. 2.20 or later (from first production)
FX 3UC Series PLC Ver. 1.20 or later (from the production manufactured in May,2004 with SER No. 45****)
FX 3G Series PLC
Ver. 1.00 or later (from first production)
Item
Specification
Dielectric withstand
voltage
500V AC for one minute
Conforming to JEM-1021Between all terminals and ground terminal of PLC
main unit Insulation resistance 5M ? or more by 500V DC megger Item
Specification
A/D conversion circuit driving power 24V DC +20%/-15%, 40mA for 24V DC
Connect a 24V DC power supply to the terminal block.Interface driving power
5V DC, 15mA
5V DC power is supplied from the internal power supply of main unit.
4.4Performance Specifications
FX 3U -4AD-ADP
USER'S MANUAL
This manual describes the part names, dimensions, mounting, and specifications of the product. Before use, read this manual and the manuals of all relevant products fully to acquire proficiency in handling and operating the product. Make sure to learn all the product information, safety information, and precautions.
Store this manual in a safe place so that it can be taken out and read whenever necessary. Always forward it to the end user.Registration:
The company and product names described in this manual are registered trademarks or the trademarks of their respective companies.Effective September 2008
Specifications are subject to change without notice.
? 2005 Mitsubishi Electric Corporation
Manual Number JY997D13901Revision G
Date
September 2008