1769-ADN Installation Instructions

1769-IN001A-US-P - April 2000

Installation Instructions

Compact? I/O 1769-ADN DeviceNet Adapter

(Cat. No. 1769-ADN)

Inside

Compact? I/O Module Description..................................................2European Union Directive Compliance..............................................3EMC Directive....................................................................................3Low Voltage Directive.......................................................................3Module Installation...........................................................................4System Configurations......................................................................5System Assembly..............................................................................7Mounting the Adapter and I/O Modules...........................................8Replacing the 1769-ADN within a System.......................................10Field Wiring Connections..................................................................10Setting the Network Address Switches............................................12Configuring the 1769-ADN................................................................13Diagnostic Indicators.........................................................................15Specifications....................................................................................19For More Information (21)

2Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Compact? I/O Module Description

Item Description Item Description 1a Upper panel mounting tab 6a Upper DIN-rail latch 1b Lower panel mounting tab 6b Lower DIN-rail latch 2I/O diagnostic LEDs

7Write-on label (user I.D. tag)3Module door with terminal identification

label 8a DeviceNet node address rotary selection switches - Most Significant Digit (MSD)4Stationary bus connector with male pins

8b DeviceNet node address rotary selection switches - Least Significant Digit (LSD)

5

Nameplate label

9

Removable DeviceNet terminal

connector

C o m m A d IO

DIAG

C o m m A d IO

DIAG

42125

Compact? I/O 1769-ADN DeviceNet Adapter3 European Union Directive Compliance

If this product has the CE mark it is approved for installation within the European Union and EEA regions. It has been designed and tested to meet the following directives.

EMC Directive

This product is tested to meet Council Directive 89/336/EEC Electromagnetic Compatibility (EMC) and the following standards, in whole or in part, documented in a technical construction file:

?EN 50081-2EMC - Generic Emission Standard, Part 2 - Industrial Environment

?EN 50082-2EMC - Generic Immunity Standard, Part 2 - Industrial Environment

This product is intended for use in an industrial environment.

Low Voltage Directive

This product is tested to meet Council Directive 73/23/EEC Low Voltage, by applying the safety requirements of EN-61131-2 Programmable Controllers, Part 2 - Equipment Requirements and Tests.

For specific information required by EN 61131-2, see the appropriate sections in this publications, as well as the following Allen-Bradley publications:

?Industrial Automation Wiring and Grounding Guidelines for Noise Immunity, publication 1770-4.1

?Guidelines for Handling Lithium Batteries, publication AG-5.4?Automation Systems Catalog, publication B111

1769-IN001A-US-P - April 2000

4Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Module Installation

Compact I/O is suitable for use in an industrial environment when installed in accordance with these instructions. Specifically, this equipment is intended for use in clean, dry environments (Pollution degree 21) and to circuits not exceeding Over Voltage Category II 2 (IEC 60664-1).3

Prevent Electrostatic Discharge

Remove Power

1. Pollution Degree 2 is an environment where, normally, only non-conductive pollution occurs except that

occasionally a temporary conductivity caused by condensation shall be expected.

2. Over Voltage Category II is the load level section of the electrical distribution system. At this level transient

voltages are controlled and do not exceed the impulse voltage capability of the product’s insulation.3. Pollution Degree 2 and Over Voltage Category II are International Electrotechnical Commission (IEC)

designations.

!

$77(17,21 Electrostatic discharge can damage integrated circuits or semiconductors if you touch bus connector pins or the terminal block. Follow these guidelines when you handle the module:?Touch a grounded object to discharge static potential.?Wear an approved wrist-strap grounding device.?Do not touch the bus connector or connector pins.?Do not touch circuit components inside the module.?If available, use a static-safe work station.

?

When not in use, keep the module in its static-shield box.

!

$77(17,21 Remove power before removing or inserting this adapter. When you remove or insert an adapter with power applied, an electrical arc may occur. An electrical arc can cause personal injury or property damage by:?sending an erroneous signal to your system’s field devices, causing unintended machine motion

?

causing an explosion in a hazardous environment

Electrical arcing causes excessive wear to contacts on both the

module and its mating connector. Worn contacts may create electrical resistance.

Compact? I/O 1769-ADN DeviceNet Adapter5 System Configurations

Configuration Rules

?The adapter must be the first and left-most module in the system (the first module of Bank 1).

?The adapter can communicate with up to 30 modules in a system.?An end cap/terminator must be on the last I/O bank.

?Each bank of I/O must have its own power supply.

? A bank of I/O can have a maximum of 16 modules with a maximum of eight on either side of the power supply, depending upon module

loading on the supply.

? A 1769 I/O power supply has limits in the amount of +5V dc and +24V dc current it can supply to the modules in its I/O bank. These limits depend on the catalog number (e.g. 1769-PA2) of the supply. A bank of modules should not exceed the current limits of the I/O bank power supply. Refer to the Compact 1769 Expansion I/O Power Supplies Installation Instructions, publication 1769-5.14.

?The maximum amount of current the system supports in one direction (either side of the power supply) is: 2A @ 5V dc, 1A @ 24V dc.

?If another bank of I/O is required due to module requirements or I/O loading, you can use a cable to link them together. You can have a maximum of three banks of I/O connected with up to two

communication cables.

?Each module type has its own distance rating (the number of modules from the power supply). Each module must be within this rating for its type.

?The adapter has a distance rating of four, therefore the adapter must be within four modules of the power supply.

?The adapter supports a total of 180 words of input data from the I/O modules.

?The adapter supports a total of 180 words of output data for the I/O modules.

?The adapter supports a total of 724 words of configuration for the I/O modules.

1769-IN001A-US-P - April 2000

6Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Example Configurations

127( I/O modules are not required between either the adapter and an end cap or between the power supply and an end cap.

Right-to-Left Cable

Right-to-Left Cable

Compact? I/O 1769-ADN DeviceNet Adapter 7

1769-IN001A-US-P - April 2000

System Assembly

The adapter can be attached to adjacent 1769 modules before or after mounting. For

mounting instructions, see “Panel Mounting” on page 8, or “DIN Rail Mounting” on page 9. To work with a system that is already mounted, see “Replacing the 1769-ADN within a System” on page 10. The Check that the bus lever of the module to the right of the 1769-ADN is in the unlocked (fully right) position.

Use the upper and lower tongue-and-groove slots (D ) to secure the modules together.

Move the module back along the tongue-and-groove slots until the bus connectors line up with each other.

Push the bus lever of the module to the right of the 1769-ADN back slightly to clear the positioning tab (E ) using your fingers or a small screwdriver.

To allow communication between the adapter and I/O modules, move the bus lever of the module to the right of the 1769-ADN fully to the left (F ) until it clicks. Make sure it is locked firmly into place.

Attach an end cap terminator () to the last I/O module in the system by using the tongue-and-groove slots as before. Lock the end cap bus terminator (H ).

Refer to the “DeviceNet Wiring” section on page 11.

!

$77(17,21 When attaching a 1769-ADN adapter, it is very important that the bus connectors are securely locked together to create a proper electrical connection.

,PSRUWDQW A 1769-ECR or 1769-ECL right or left end cap must be used to

terminate the end of the serial communication bus.

8Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Mounting the Adapter and I/O Modules

Minimum Spacing

Maintain spacing from enclosure walls, wireways, adjacent equipment, etc. Allow

Panel Mounting

Mount the adapter or module to a panel using two screws per adapter or module. Use M4 or #8 panhead screws. Mounting screws are required on every module.

Panel Mounting Using the Dimensional Template

!

$77(17,21 During panel or DIN rail mounting of all devices, be sure that all debris (metal chips, wire strands, etc.) is kept from falling into the adapter or modules. Debris that falls into the adapter or modules could cause damage on power up.

42124

mm (in)

Hole spacing tolerance: +0.4mm (0.016in).42121

Compact? I/O 1769-ADN DeviceNet Adapter 9

1769-IN001A-US-P - April 2000

Panel Mounting Procedure Using Modules as a Template

The following procedure allows you to use the assembled adapter and modules as a template for drilling holes in the panel. If you have

sophisticated panel mounting equipment, you can use the dimensional template provided on page 8.

Due to the module mounting hole tolerance, it is important to follow these procedures:

On a clean work surface, assemble no more than three modules.

Using the assembled modules as a template, carefully mark the center of all module-mounting holes on the panel.

Return the assembled modules to the clean work surface, including any previously mounted modules.

Drill and tap the mounting holes for the recommended M4 or #8screw. Place the modules back on the panel and check for proper hole alignment.

Attach the modules to the panel using the mounting screws.

127( If mounting more modules, mount only the last one of this group and put the others aside. This reduces remounting time during drilling and tapping of the next group.

Repeat steps 1 through 6 for any remaining modules.

DIN Rail Mounting

The adapter can be mounted using the following DIN rails:?35 x 7.5mm (EN50022 - 35 x 7.5)?35 x 15mm (EN 50022 - 35 x 15)

Before mounting the module on a DIN rail, close the DIN rail latches. Press the DIN rail mounting area of the module against the DIN rail. The latches will momentarily open and lock into place.

10Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Replacing the 1769-ADN within a System

The adapter can be replaced while the system is mounted to a panel (or DIN rail).

Remove power. See important note on page 4.

Remove the DeviceNet cable from the module by removing the connector.

Remove the upper and lower mounting screws from the adapter (or open the DIN latches using a flat-blade or phillips-style screwdriver). On the right-side adjacent module, move its bus lever to the right (unlock) to disconnect it from the adapter being removed. Gently slide the disconnected adapter forward.

If you feel excessive resistance, make sure that you disconnected the adapter from the bus and that you removed both mounting screws (or opened the DIN latches).

1RWH It may be necessary to rock the module slightly from front to back to remove it, or, in a panel-mounted system, to loosen the screws of adjacent modules.

Before installing the replacement adapter, be sure that the bus lever on the right-side adjacent module is in the unlocked (fully right) position. Slide the replacement adapter into the open slot.

Connect the adapter and modules together by locking (fully left) the bus levers on the right-side adjacent module.

Replace the mounting screws (or snap the adapter onto the DIN rail). Replace the DeviceNet cable on the module by attaching the connector to the module.

Set the network address switches to the same value as the removed adapter.

Field Wiring Connections

Grounding the Adapter

This product is intended to be mounted to a well-grounded mounting surface such as a metal panel. Additional grounding connections from the adapter’s mounting tabs or DIN rail (if used), are not required unless you cannot ground the mounting surface. Refer to Industrial Automation

Compact? I/O 1769-ADN DeviceNet Adapter 11

1769-IN001A-US-P - April 2000

Wiring and Grounding Guidelines , publication 1770-4.1, for additional information.

DeviceNet Wiring

Connect the DeviceNet cable to the removable connector as shown.

Insert the removable female connector into the mating male connector on the DeviceNet adapter module.

Screw the removable connector to the adapter case with the upper and lower mounting screws. Screw torque is 5-6 in-lbs.127( DeviceNet cable colors are shown on the wiring label on the front of the adapter.

,PSRUWDQW If the 1769-ADN is the last device connected to the DeviceNet

network trunkline, be sure to add the termination resistor (Allen-Bradley part number 1485A-C2 or a 120? 5% or > ?W resistor) across the Blue (CAN Low) and White (CAN High) wires.

C o m m A IO

DIAG

DeviceNet Connector

42123

Connect To BLK Wire -V BLU Wire

CAN Low

Bare Drain WHT CAN High RED +V

BLK

42122

12Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Setting the Network Address Switches

Set the network address with the two rotary switches. Use a small, slotted screwdriver to set the switches. The switch labeled MSD (Most Significant Digit) sets the 10s while the switch labeled LSD (Least Significant Digit) sets the 1s.

Valid network addresses are 00 through 63. Switch settings from 00 to 63 select network addresses 00 to 63. Switch settings from 64 to 99 instruct the adapter to use the software programmed value for the network address.The software programmed value is set via RSNetworx TM for DeviceNet TM and stored in non-volatile memory on the 1769-ADN. The initial, 127( The baud rate for the adapter is set by way of the module’s automatic “auto baud” function at power-up.

Use the removable, write-on label to mark your I.D. tag, etc. with

permanent ink. Your markings are visible when the module door is closed.

C o m m A IO

DIAG

Network Address Switches

42127

Compact? I/O 1769-ADN DeviceNet Adapter 13

1769-IN001A-US-P - April 2000

Configuring the 1769-ADN

The 1769-ADN must be configured with RSNetworx for DeviceNet. This configuration tool allows you to identify all of the devices (I/O modules, power supplies, expansion cables, end caps) and their locations in your 1769 system. The 1769-ADN must have the I/O configuration loaded into its’ memory to perform the network communication function.

The 1769-ADN will not accept I/O connections if the programmed system configuration does not match the actual system configuration. The

1769-ADN retains the programmed system configuration in non-volatile memory so it can compare it with the actual system configuration on power-up. For more information, refer to the Compact? I/O 1769-ADN DeviceNet Adapter User Manual , publication 1769-UM001A-US-P.

I/O Memory Mapping

Output Data

This is the I/O data the DeviceNet master sends to the 1769-ADN. All outputs are in words. For more information, refer to the Compact? I/O 1769-ADN DeviceNet Adapter User Manual publication 1769-UM001A-US-P.

W o r d

Bit Position

15

14

13

12

11

10

9

87

6

5

4

3

2

1

0Output data for slot 1*

1“““

n

Output data for slot 30*

* = The amount of output data for each module is based on the configuration of each I/O module done

as part of the 1769-ADN configuration. Note that if an I/O module is configured to have 0 words of output data, then there are no output data words for that module in the 1769-ADN’s output image.

14Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Input Data

This is the I/O data the 1769-ADN sends to the DeviceNet master. All inputs are in words. For more information, refer to the Compact? I/O 1769-ADN DeviceNet Adapter User Manual , publication 1769-UM001A-US-P.

W o r d

Bit Position

151413

12

11

10

9

8765432100V16V15V14V13V12V11V10

V9

V8

V7

V6

V5

V4

V3

V2

V1

1X

NS

V30V29V28V27V26V25V24V23V22V21V20V19V18V17

2Input data for slot 1*

3“““

n

Input data for slot 30*

* = The amount of input data for each module is based on the configuration of each I/O module done as part of the

1769-ADN configuration. Note that if an I/O module is configured to have 0 words of input data, then there are no input data words for that module in the 1769-ADN’s input image.V1 =Data invalid from slot 1V2 =Data invalid from slot 2V3 =Data invalid from slot 3...

V30 =Data invalid from slot 30

where 1 = data invalid or a module error is detected; 0 = data valid, no module error NS =Node address switch changed

where 1 = node address switch changed since power-up X =Reserved

Compact? I/O 1769-ADN DeviceNet Adapter15

Module Status Indicator

IO DIAG

42128

1769-IN001A-US-P - April 2000

16Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

LED Indication

Meaning

Module Status (MS)

OFF No power

Flashing GRN/OFF On-line but configuration missing

Solid GRN Device operational

Flashing RED/OFF

Recoverable fault

?configuration incorrect

?duplicate mac id (node address) check failed ?node address switch changed ?main program checksum failed ?

configured I/O size too large

Solid RED

Unrecoverable fault

?terminator/end cap missing

?connector/cable between modules missing/not connected ?bad configuration memory ?

watchdog tripped Network Status (NS)

OFF No power or no network access Flashing GRN/OFF On-line but not connected Solid GRN On-line and connected Flashing RED/OFF Connection time-out Solid RED Critical network failure

I/O Status (IO)

OFF No power or outputs off

Flashing GRN/OFF Idle/program mode - one or more I/O modules in Idle Mode

Solid GRN Device operational - all I/O modules in Run Mode Flashing RED/OFF Recoverable fault - one or more I/O modules may be in

Fault Mode Solid RED

Unrecoverable fault - one or more I/O modules may be in

Fault Mode

Compact? I/O 1769-ADN DeviceNet Adapter 17

1769-IN001A-US-P - April 2000

Diagnostic Status (DIAG)

OFF No power or no diagnostics running

Flashing Amber Main Program detected an error - number of flashes indicates

the error Flashing RED/OFF

Diagnostics found error - number of flashes indicates which test

failed

?One flash - RAM test failed ?Two flashes - Boot program checksum failed ?Three flashes - Main program checksum failed ?Four flashes - Configuration checksum failed ?Five flashes - Access to program or configuration failed

LED Indication

Meaning

18Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Hazardous Location Considerations

This equipment is suitable for use in Class I, Division 2, Groups A, B, C, D or non-hazardous locations only. The following ATTENTION statement applies to use in hazardous locations.

Environnements dangereux

Cet équipement est concu pour être utilisé dans des engironnements de Classe 1, Division 2, Groupes A, B, C, D ou non dangereux. La mise en garde suivante s’applique à une utilisation dans des environnements dangereux.

!

:$51,1* EXPLOSION HAZARD

?Substitution of components may impair suitability for Class I, Division 2.

?Do not replace components or disconnect equipment unless power has been switched off.

?Do not connect or disconnect components unless power has been switched off.

?This product must be installed in an enclosure.

?All wiring must comply with N.E.C. article 501-4(b).

!

$9(57,66(0(17 DANGER D’EXPLOSION

?La substitution de composants peut rendre cet équipement impropre à une utilisation en environnement de Classe 1, Division 2.

?Ne pas remplacer de composants ou d éconnecter l’équipement sans s’être assur é que l’alimentation est coup ée.

?Ne pas connecter ou d éconnecter des composants sans s’être assur é que l’alimentation est coup ée.

?Ce produit doit être install é dans une armoire.

Compact? I/O 1769-ADN DeviceNet Adapter19

Specifications

General Specifications

Class I, Division 2, Hazardous Location, Groups A, B, C, D

The adapter has passed testing at the following levels:

1. Conducted immunity frequency range may be 150 kHz to 30 MHz if the Radiated Immunity frequency

range is 30 MHz to 1000 MHz.

1769-IN001A-US-P - April 2000

20Compact? I/O 1769-ADN DeviceNet Adapter

1769-IN001A-US-P - April 2000

Input/Output Specifications

Specification Value

Bus Current Draw (Maximum)

450mA at 5V dc (2.25W)

Heat Dissipation 4.7W maximum I/O Capacity 30 modules Communication Rate

125k bit/s 250k bit/s 500k bit/s Indicators

Module status- red/grn Network status- red/grn I/O status- red/grn Diagnostic status- red/grn

DeviceNet Power Requirements

24V dc (+4%) @ 90mA maximum, N.E.C. Class 2DeviceNet Cable Allen-Bradley part no. 1485C-P1-Cxxx. Refer to publication

DN-2.5 for more information.Power Supply Distance Rating

4

(The adapter may not be more than 4 modules away from the

power supply.)

Isolation Voltage Verified by one of the following qualification tests:

710V dc, 1 minute

Vendor I.D. Code 1Product Type Code 12Product Code

69