1.设计任务:为一酒店设置空调系统

2.冷负荷计算

2.1冷负荷计算依据

2.1.1外墙和屋面温差传热的冷负荷计算

外墙和屋面瞬变传热形成的冷负荷Qc1可按下式计算:Qc1=KFΔtτ-ε

式中 k——传热系数,w/(m2﹒℃)见课本附录2-9;

F——计算面积,m2;

τ——计算时刻;

τ-ε——温度波的作用时刻,即温度波作用于外墙或屋面外侧的时刻;

Δtτ-ε——作用时刻下,通过外墙或屋面的冷负荷计算温差,简称负荷温差,℃,对于常用外墙查课本附录2-10;对于屋面可查课本附录2-11。

2.1.2外窗温差传热冷负荷的计算

通过外窗温差传热形成的冷负荷Qc2,用下式计算:Qc2= KFΔtτ

式中Δtτ——计算时刻下的负荷温差,℃,见课本附录2-12;

K——传热系数,双层窗可取2.9,单层窗可取5.8,w/(m2﹒℃);

F——传热面积,m2;

2.1.3外窗太阳辐射的冷负荷计算

透过外窗的太阳辐射形成的冷负荷Qf=XgXdCnCsFJj﹒τ

式中Xg——窗的有效面积系数,单层钢窗0.85,双层钢窗0.75;单层木窗0.7,双层木窗0.6;Xd——地点修正系数,见课本附录2-13;

Jj﹒τ——计算时刻时,透过单位窗口面积的太阳总辐射形成的冷负荷,简称负荷强度,w/ m2,见课本附录2-13。

2.1.4——内围护结构的传热冷负荷计算

内围护结构传热的冷负荷,可按邻室的状况分别以如下方法进行计算:

2.1.4.1当邻室为通风良好的非空调房间时,通过内窗的温差传热负荷,

可按式QKFΔtτ进行计算。

2.1.4.2当邻室为通风良好的非空调房间时,通过内墙和楼板的温差传热负荷可按式Qc2= KFΔtτ进行计算,此时负荷温差Δtτ-ε及其平均值Δtpj,应按课本附录2-10中零朝向的数据采用。

2.1.4.3当邻室有一定发热量是,通过空调房间内窗、隔墙、楼板或内门等内围护结构的温差传热负荷,可按下式计算:Qc3=KF(twp+Δtls-tn)

式中Qc3——稳态冷负荷,下同,w;

Twp——夏季空气调节室外计算日平均温度,℃;

tn——夏季空气调节室内计算温度,℃;

Δtls——邻室温升,℃,可根据邻室散热强度,按表2-14采用;

2.1.5人体散热的冷负荷计算

由人体散热形成的冷负荷Qr1=φnq1Xτ-T。式中φ——群集系数,见表2-15

n——计算时刻空调房间内的总人数;

q1——一名成年男子小时显热散热量,见课本表2-16,W

T——人员进入空调房间的时刻;

τ-T——从人员进入房间时刻算起到计算时刻的时间,h;

Xτ-T——τ-T时间人体显热散热量的冷负荷系数,见课本附录2-16。

2.1.6照明灯具散热的冷负荷计算

镇流器装在空调房间内的荧光灯散热:

Qd=1200n1NXτ-T

n1——同时使用系数,一般为0.5~0.8;

N——照明设备的安装功率,KW;

Xτ-T——τ-T

时间照明散热的冷负荷系数,见课本附录2-15;

τ-T——从开灯时刻算起到计算时刻的时间,h;

2.1.7设备散热的冷负荷计算

此次设计的时餐厅和办公室可认为无设备散热

2.1.8食物散热冷负荷的计算

计算餐厅冷负荷时,必须要将食物的散热量计入。但食物的显热散热形成的冷负荷很难准确计算,可按每位就餐顾客9W急性估算。

2.1.9人体散湿量

计算公式:D1=0.001φng

式中D1——散湿量kg/h;

G——一名成年男子小时散热量,见课本表2-16,g/h

2.1.10 人体散湿形成的潜热冷负荷Qr2,W,可按下式计算:Qr2=φnq2

式中 q2——一名成年男子小时潜热散热量,见课本表2-16,W;

φ——群集系数,见表2-15;

n——计算时刻空调房间内的总人数;

2.1.11食物散湿量。计算公式:D2=0.012φn

式中 n——就餐总人数。

2.1.12食物散湿量形成的潜热冷负荷Qss,W,可按下式计算:Qss=688D

2.2取管理办公室3做具体的冷负荷计算:

2.2.1北外墙冷负荷

从课本附录2-9中查得,k=1.49w/㎡﹒k。衰减系数β=0.15,衰减度ν=38.6,延迟时间ε=12.7h。从附录2-10查得作用时刻τ-ε时的北京北向外墙负荷温差的逐时值Δtτ-ε,按式CLQτ=kFΔtτ-ε算出北外墙的逐时冷负荷,计算结果列于表1-1中。

2.2.2北外窗冷负荷

2.2.2.1瞬变传热得热形成冷负荷,有附录2-1中查得各计算时刻的负荷温差Δtτ,计算结果列于表1-2

2.2.2.2日射得热形成冷负荷:由附录2-13查得各计算时刻的负荷强度Jj﹒τ,窗面积4.8㎡,窗的有效面积系数Xg=0.85,得点修正系数Xd=1,窗户内遮阳系数Cn=0.5(浅色),按式CLQj﹒τ=XgXdCnCsFJj ﹒τ,玻璃取5mm厚的普通玻璃Cs=1。计算结果列于表1-3。

2.2.3西内墙冷负荷(钢筋混凝土剪力墙350mm)邻室为通风良好的空调房间,由附录2-9种查得,k=2.3w/㎡﹒k,β=0.18,ε=10.7h。从附录2-10查得扰量作用时刻τ-ε时的北京西内墙负荷温差的逐时值Δtτ-ε,按式CLQτ=kFΔtτ-ε算出西内墙的逐时冷负荷,计算结果列于表1-4。

2.2.4南内墙冷负荷,邻室为通风良好的空调房间,从课本附录2-9中查得,k=1.49w/㎡﹒k。衰减系数β=0.15,衰减度ν=38.6,延迟时间ε=12.7h。从附录2-10查得作用时刻τ-ε时的北京北向外墙负荷温差的逐时值Δtτ-ε,按式CLQτ=kFΔtτ-ε算出北外墙的逐时冷负荷,计算结果列于表1-5中。

2.2.5将前面各项冷负荷值汇总于表1-6,由计算可知,最大的围护结构冷负荷出现在14:00时,其值为607 w。各项冷负荷中,以窗的日射得热冷负荷最大。

2.2.6照明得热(两个荧光灯)镇流器装在空调房间内,求下午14时的冷负荷。从上午9时到下午17时,连续使用8小时。查附录2-15,开灯后小时数τ-T=14-9=5 h,连续开灯时间17-9=8 h,则负荷系数Xτ-T=0.79,照明冷负荷Qd=1200n1NXτ-T=1200×0.7×0.04×0.79×4=106 w。

n1——同时使用系数,一半为0.5~0.8

N——照明设备安装功率,kw

Xτ-T——τ-T时间照明散热的冷负荷系数

2.2.7人体散热冷负荷(下午14时按静坐),潜热冷负荷Qr2=φnq2=45 w

显热冷负荷Qr1=φnq1 Xτ-T=1×1×63×0.84=52.92 w

φ——群集系数,见表2-15,取1

n——计算时间空调房间内总人数,1人。

q1——一名成年男子小时显热散热量,见课本表2-16。

T——人员进入空调房间的时刻

Xτ-T——τ-T时间人体显热散热量的冷负荷计算系数,见课本附录2-15。

2.2.8房间3总的冷负荷(静坐)

Q3=607+106+52.92+45=811 w

总的湿负荷W3=1×68=68g/h。

2.2.9散湿量计算

2.2.9.1二层中餐厅散湿量:人散湿(轻劳动)263×184=48392g/h;食物散湿D=0.012φn=0.012×0.93×263=2.935kg/h。

2.2.9.2三层西餐厅散湿量:人散湿196×184=36064g/h;食物散湿D=0.012φn=0.012×0.93×196=2.187 kg/h。

2.2.10其余房间按面积热指标估算,得出冷负荷和湿负荷列于表1-7

3.集中空调装置系统的划分原则

3.1室内参数(温湿度基数和精度)相近以及室内热时比相近的房间可合并在一起,这样空气处理和控制要求比较一致,容易满足要求。

3.2朝向、层次等位置上相近的房间宜组合在一起,这样风道管路不止和安装较为合理,同时也便于管理。

3.3工作班次和运行时间相同的房间采用同一系统,这样有利于运行和管理,而对个别要求24小时运行或间歇运行的房间可单独配置空调机组。

3.4对洁净度等级或噪声级别不同的房间,为了考虑空气过滤系统和消声要求,宜按各自的级别设计,这对节约投资和经济运行都有好处。

3.5产生有害气体的房间不宜和一般房间和用一个系统。

3.6根据防火要求,空调系统的分区应与建筑防火分区相对应。

此外,当空调风量特别大时,为了减少与建筑配合的矛盾,可根据实际情况把它分成多个系统,如纺织厂、体育馆等。

4.系统形式的选择

在工程上应考虑建筑物的用途和性质、热湿负荷特点、温湿度调节和控制的要求、空调机房的面积和位置、初投资和运行维修费用等许多方面的因素,选定合理的空调系统。

4.1各种系统形式的分类

4.1.1按空气处理设备的设置情况分类、

4.1.1.1集中系统集中系统的所有空气处理设备(包括风机、冷却器、加湿器、过滤器等)都设在一个集中的空调机房内。

4.1.1.2半集中系统除了集中空调机房外,办集中系统还设有分散在被调房间的二次设备(末端装置),其中多半设有冷热交换装置(亦称二次盘管),它的功能主要是在空气进入被调房间之前,对来自集中处理设备的空气作进一步处理。

4.1.1.3全分散系统(局部机组)这种机组把冷、热源和空气处理、输送设备(风机)集中设置在一个箱体内,形成一个紧凑的空调系统。可以按照需要,灵活而分散的设置在空调房间内,因此局部机组不许集中的机房。

4.1.2按负担室内负荷所用的介质种类分类

4.1.2.1全空气系统是指空调房间的室内负荷全部由经过处理的空气来负担的空调系统。由于空气的比热较小,需要用较多的空气量才能达到消除余热余湿的目的,因此要求有较大断面的风道或较高的风速。

4.1.2.2全水系统空调房间的热湿负荷全靠水作为冷热介质来负担。由于水的比热比空气大的多,所以在相同条件下只需较小的水量,从而使管道所占的空间减小许多。但是,仅靠水来消除余热余湿,并不能解决房间的通风换气问题。因而通常不单独采用这种方法。

4.1.2.3空气-水系统随着空调装置的日益广泛使用,大型建筑物设置空调的场合愈来愈多,全靠空气来负担热湿负荷,将占用较多的建筑空间,因此可以同时使用空气和水来负担空调的室内负荷。

4.1.2.4制冷剂系统这种系统是将制冷系统的蒸发器直接放在室内来吸收余热余湿。这种方式通常用于分散安装的局部空调机组,但由于冷剂管道不便于长距离输送,因此这种系统不宜作为集中式空调系统来使用。

4.1.3根据集中式空调系统处理的空气来源分类

4.1.3.1封闭式系统他所处理的空气全部来自空调房间本身,没有室外空气补充,全部为再循环空气。因此房间和空气处理设备之间形成了一个封闭环路。封闭式系统用于密闭空间且无法(或不需)采用室外空气的场合。这种系统冷、热消耗量最省,但卫生效果差。当室内有人长期停留时,必须考虑空气的再生。这种系统应用于战时的地下蔽护所等战备工程以及很少有人进出的仓库。

4.1.3.2直流式系统他所处理的空气全部来自室外,室外空气经处理后送入室内,然后全部排出室外,因此与封闭系统相比,具有完全不同的特点。这种系统适用于不允许采用回风的场合,如放射性实验室以及散发大量有害物的车间等。为了回收排出空气的热量或冷量用来加热或冷却新风,可以在这种系统中设置热回收设备。

4.1.3.3混合式系统从上述二种系统可见,封闭式系统不能满足卫生要求,直流式系统经济上不合理,所以两者都只在特定场合下使用,对于绝大多数场合,往往需要综合这两者的利弊,采用混合一部分回风的系统。这种系统既能满足卫生要求,又经济合理,故应用最广。

4.2由系统形式比较选出风机盘管系统用于本次设计

4.2.1从风机盘管的结构特点来看,它的优点是:不止灵活,各房间可以独立调节室温,房间不住人时可方便的关掉机组(关风机),不影响其它房间,从而比其它系统较节省运转费用。此外,房间之间空气互不串通。又因风机多档变速,在冷量上能由使用者直接进行一定的调节。

4.2.2选用的风机盘管的型号

4.2.2.1二层中餐厅:选用三洋Ecoi中央空调,室外机,HP=24;

组合型号:SPW-CR2304DDXCH8,HP=12;

直流变频室外机(主):SPW-CR1154DDXH8,HP=12;

定速室外机(子):SPW-CR1154DDCH8,HP=12;

制冷量:Q=70.1KW;

最多可以连接室外机的数量:40。

4.2.2.2三层西餐厅:选用三洋Ecoi中央空调,室外机,HP=20;

组合型号:SPW-CR1904DDXCH8;

直流变频室外机(主):SPW-CR904DDXH8;

定速室外机(子):SPW-CR904DDCH8;

制冷量:Q=57.7KW;

最多可以连接室外机的数量:33.

4.3风机盘管系统新风量确定原则

在处理空气时,大多数场合要利用相当一部分回风,所以,在夏、冬季节混入的回风量愈多,使用的新风量愈少,就愈显得经济。但实际上,不能无限制地减少新风量,一般规定,空调系统中的新风占送风量的百分数不应低于10%。

确定新风量的依据有下列三个因素:

4.3.1在人长期停留的空调房间内,新鲜空气的多少对健康有直接影响。可根据《工业通风》课程中确定全面通风量的基本原理,按消除二氧化碳所需的新鲜空气量来确定。在实际工作中,一般可按规范规定来确定。

4.3.2补充局部排风量

当空调房间内有排风柜等局部排风装置时,为了不是车间产生负压,在系统中必须有相应的新风量来补偿排风量。

4.3.3为了防止外界环境空气(室外的或相邻的空调要求较低的房间)渗入空调房间,干扰空调房间内温湿度或破坏室内洁净度,需要在空调系统中用一定量的新风来保持房间正压(即室内大气压力高于外界环境压力)。

4.3.4必须指出,在冬夏季室外设计计算参数下规定最小新风百分数,是出于经济方面考虑。多数情况下,在春、秋过渡季节中可以提高新风比例,从而利用新风所具有的冷量或热量以节约系统的运行费用。

4.4风机盘管机组新风供给方式

4.4.1靠渗入室外空气(浴厕机械排风)以补给新风,机组基本上处理在循环空气。这种方案初投资和运行费经济,但卫生条件较差,且无组织的渗透风影响,造成室内温度厂不均匀,因而此种方式之适用于室内人少的场合。

4.4.2墙洞引入新风直接进入机组,新风口做成可调节的,冬、夏季按最小新风量运行,过度季尽量多采用新风。这种方式虽然新风得到比较好的保证,但随着新风负荷的变化,室内参数将直接受到影响,故这种系统用于要求不高的建筑物。

4.4.3由独立的新风系统供给室内新风,即把新风处理到一定参数,也可承担一部分房间负荷。这种方案即提高了系统的调节和运转的灵活性,且进入风机盘管的供水温度可适当提高,水管的结露现象可得到改善。

4.4.4对于餐厅,设计时应注意新风与排风均匀性。按规定一、二、三、四级旅馆中的餐厅、宴会厅、多功能厅的新风量分别为30、25、20、15m3/(h﹒人)。

5.设计房间的送风系统

5.1送风系统的分类

空调送风系统可分为两类:低风速全空气单(双)风道送风方式和风机盘管加新风系统中的送新风方式。较大面积的公用场所,如商场、交易大厅、宴会厅、影剧院和体育馆等,多采用第一种送风方式,而写字间和宾馆饭店中的一、二、三级客房等较小面积的空调房间,则多采用第二种送风方式。

5.2采用风机盘管加新风空调方式新风系统划分

无论是写字间、客房新风系统还是公用场所各厅室新风系统,应以楼层和房间使用功能按中小规模划分新风区域。最大新风量不宜超过4000m3/h。以防止由于风系统区域过大使系统风量过大,输配距离过长所带来的三种弊病:

5.2.1主干风管断面过大,须占用较大的建筑空间;

5.2.2空间输配用电过大;

5.2.3系统风量的沿途漏损增大。

5.3送风系统应设置风量调节装置

5.3.1送风系统宜采用双速电机驱动的风机或并联双风机。因为,无论是公用场所或客房,每天人流量

的高峰时间和低谷时间均不同。在人流量小时不但可减少新风量,而且还可减少循环风量。

5.3.2新风系统必须设置随季节变化的风量调节装置。以便节省空气处理能耗。5.4送风温度与送风温差5.4.1送风温度。夏季为了防止送风口附近产生结露现象,一般应使送风干球温度高于室内空气的露点温度2~3℃。

5.4.2送风温差。空调系统夏季的送风温差,应根据送风方式、风口类型、安装高度、气流路线长度、贴附情况等因素确定。在满足舒适或工艺要求的前提下,送风温差应尽量大;一般舒适性空调的送风温差,宜根据以下原则确定:

送风高度H≤5m 送风温差Δts≤10℃;

送风高度H>5m 送风温差Δts≤15℃。

5.5送风方式和送风口形式

本设计中选用风口形式见表1-8

5.5.1一般应遵循原则

5.5.1.1室内对温湿度的要求无严格要求时,宜采用百叶风口或条缝型风口进行侧送;当室内允许波动范围≥±1℃时,测送气流易贴附;当室温允许波动范围≤0.5℃时,侧送气流应贴附。

5.5.1.2当空调房间内的工艺设备对侧送气流又一定阻挡或单位面积送风量过大,致使工作区的风速超出要求范围时,不应采用侧送。

5.5.1.3当建筑层高较低、单位面积送风量较大,且有吊平顶可供利用时宜采用圆型、方型或条缝型散流器进行下送,或采用孔板下送。

5.5.1.4当单位面积送风量很大,而工作区有需要保持较低风速或对区域温差有严格要求时,应采用孔板送风。

5.5.1.5室温允许波动范围等于或大于1℃的高大厂房或层高很高的公共建筑,宜采用喷口送风。喷口送风时的送风温差宜取8~12℃,送风口高度宜保持6~10m。

5.5.1.6当送风量很大,无法安排过多的送风口,或需要直接向工作区送风时,宜采用旋流风口送风。

5.5.1.7当室内的散热量较大,且产热设备的上部带排热装置时,宜采用地板下送风。

5.5.1.8侧送风口的设置,宜沿房间平面中的短边分布;当房间的进深很长时,宜采用双侧对送,或沿长边布置风口。

5.5.1.9设计贴附侧送流型时,宜采用水平与垂直两个方向均能进行调节的双层百叶风口。双层百叶仅供调节气流流型之用,不能用以调节送风量。因此,在风口之前(顺气流方向)应装置对开式风量调节阀。

5.5.2此次餐厅设计应遵循的原则

5.5.2.1常用送回风方式有两种,即只设送风道而不设回风道方式和设有送、回风道的送回风方式。低风速全空气方式虽然占空间较大,但餐厅、宴会厅、多功能厅的建筑往往有较高的空间可利用,管道布置不致有困难,宴会厅系统新风百分比较大,采用全空气系统可以在过渡季节充分利用室外空气的自然冷量。

5.5.2.2餐厅、宴会厅、多功能厅的送回风方式大多采用上送下回,或上送侧(下)回,对冬季送热风时常因层高较大而不易使气流下降时,可在设计中采用平顶风口调节装置等措施,以使冬季送热风时有较大射程。对于高度不大而下部难以设回风口的用上回方式。送风口采用散流器的较多,但也可采用双层百叶送风口,或条缝型风口。某些宴会厅或国际会议厅也有用侧墙喷口送风方式的实例。总之,餐厅宴会厅建筑装修的艺术要求较高,送风口形式必须照顾到与建筑装修的密切配合。

5.6经济风速。低风速送风道的经济风速可按表1-2选取。餐厅、宴会厅空调区域内的气流速度一般不大于0.25m/s(不吹动宴会时用的蜡烛火)。

表1-2经济风速

5.7送回风的消声措施

降低系统的噪声,在空调设计中是至关重要的。对于组合式空调机组来说,可在机组的功能段中加设“消声段”,而在空调机组的出风管道上加装消声弯头、消声器和消声管。但对紧靠餐厅、宴会厅、多功能厅安装的柜式空调机组,除在出风管上必须设置消声弯头和在各连接处采用软连接外,还需采用必要的消声措施。

6.参考文献

6.1北京市建筑设计研究院,建筑设备专业设计技术措施,北京,中国建筑工业出版社,1997

6.2陆耀庆主编,实用供热空调设计手册,北京,中国建筑工业出版社,1993

6.3于国清主编,建筑设备工程cad制图于识图,上海,机械工业出版社,2005

6.4 赵荣义、范存养、薛殿华、钱以明主编,空气调节,北京,中国建筑工业出版社,1981

6.5何耀东、何青主编,中央空调,北京,中国冶金工业出版社,2005

7.小结

此次设计为期两周,在这短短的两周里我学到了很多的东西。设计不同于课本的学习,从设计中学到的东西是课本中学不到的,当然没有课本这个基础,是无法做好设计的。做设计的同时对课本知识也有了更深的理解。

设计中当然会遇到问题,我们并没有被问题吓倒,查资料、问老师、各尽所能。刘老师耐心仔细的讲解,使迷茫的我们茅塞顿开。我们也被老师丰富的经验和深厚扎实的学术修养所折服。老师的耐心和严谨的治学精神使我们倍受鼓舞。在炎热的天气里感到心情轻松。

设计中另一个收获就是同学们的团队合作精神,和班级同学间的那份友爱,有的同学遇到问题,小组则共同探讨,在愉悦的氛围里解决问题,既学到了知识,又增进了同学间的感情,小组成员间互相探讨,使得每个人对设计都有了一定的认识,进一步熟悉了专业。

总之,在设计中我学到了很多,为以后的工作和学习奠定了基础。当然这与老师的悉心指导、同学之间的探讨是分不开的。我再次感谢老师,感谢同学。

暖通空调设计毕业设计说明书

摘要 本设计为哈尔滨望江集团办公楼空调系统工程设计。哈尔滨望江集团办公楼属中小型办公建筑,本建筑总建筑面积4138m2,空调面积2833m2。地下一层,地上八层,建筑高度33.9m。全楼冷负荷为191千瓦,全楼采用水冷机组进行集中供给空调方式。 此设计中的建筑主要房间为办公室,大多面积较小,且各房间互不连通,应使所选空调系统能够实现对各个房间的独立控制,综合考虑各方面因素,确定选用风机盘管加新风系统。在房间内布置吊顶的风机盘管,采用暗装的形式。将该集中系统设为风机盘管加独立新风系统,新风机组从室外引入新风处理到室内空气焓值,不承担室内负荷。风机盘管承担室内全部冷负荷及部分的新风湿负荷。风机盘管加独立新风系统由百叶风口下送和侧送。水系统采用闭式双管同程式,冷水泵三台,两用一备;冷却水泵选三台,两用一备。 在冷负荷计算的基础上完成主机和风机盘管的选型,并通过风量、水量的计算确定风管路和水管路的规格,并校核最不利环路的阻力和压头用以确定新风机和水泵。 依据相关的空调设计手册所提供的参数,进一步完成新风机组、水泵、热水机组等的选型,从而将其反应在图纸上,最终完成整个空调系统设计。 关键词:风机盘管加独立新风系统;负荷;管路设计;制冷机组:冷水机组

Abstract The design for the Harbin Wangjiang Design Group office building air conditioning system. Harbin Wangjiang Group is a small and medium-sized office building office buildings, the total floor area of building is 4138m2, air-conditioned area is 2833m2. There are eight floor of the building, building height is 33.9m. Cooling load for the entire floor, 191 kilowatts, the whole floor using Central Cooling Chillers to focus on the way . This design of the main room of the building for office, most of them is very small, and the rooms are not connected, the selected air-conditioning system should be able to achieve independent control of each room, considering the various factors to determine the selection of fan-coil plus fresh air system. Arrangement in the room ceiling fan coil units, using the dark form of equipment. Set the focus on fan-coil system, plus an independent air system, fresh air from the outdoor unit to deal with the introduction of a new wind to the indoor air enthalpy value, do not bear the load of indoor. All bear the indoor fan-coil cooling load and part of its new rheumatoid load. Fan-coil plus an independent air system sent by the Venetian and the under side air delivery. Closed water system with a dual-track program, three cold-water pump, dual-use a prepared; cooling pumps three elections, one prepared by dual-use. In the cooling load calculation based on the completion of the selection of host and fan coil units, and air volume, the calculation of water, the wind pipe and water pipes to determine the specifications of the road and check the resistance to the most disadvantaged and the loop to determine the pressure head new fans and pumps. Based on the relevant manuals provided by air-conditioning design parameters, and further completion of the new air units, water pumps, hot water units, such as the selection, which will be reflected in their drawings, the final design of the entire air-conditioning system Key words: PAU+FCU systems; load; pipeline design; refrigeration machine; Chillers

家用空调设计计算说明书

制冷系统课程设计说明书 热能与动力工程专业 目录 一、 设计工况 ............................................ 3 二、 压缩机选型 .......................................... 3 三、 热力计算 ............................................ 5 1、循环工况: ......................................... 5 2、 热力计算: ........................................ 6 四、蒸发器设计计算 (7)

1、设计工况: (7) 2、计算过程: (8) 3、风机的选择 (18) 4、汇总 (18) 五、冷凝器换热计算 (19) 第一部分:设计计算 (19) 一、设计计算流程图 (19) 二、设计计算 (19) 3、计算输出 (25) 第二部分:校核计算 (25) 一、校核计算流程图 (25) 二、计算过程 (26) 六、节流装置的估算和选配 (27) 七、空调电器系统 (28)

一、设计工况 3KW机组,半封闭压缩机,风冷冷凝器,风冷蒸发器,毛细管,制冷剂R22,蒸发温度5℃,过热度20℃,冷凝温度50℃,过冷度5℃ 二、压缩机选型 1、选型条件:制冷量3kW,制冷剂R22,蒸发温度5℃,过热度20℃,冷凝温度50℃,过冷度5℃。 2、选型结果:使用压缩机选型软件select 6,选择型号为DKM-75的半封闭往复式压缩机。 a.其基本参数如下:制冷量3.15kW,输入功率1.06kW,cop为 2.97,电流(400V)2A,质量流量18.9g/s,放热 3.65kWb. b.其技术参数:

空调系设计说明.

民强商业大厦空调系统设计说明 概述 珠海民大以位于珠海香洲区翠前南路,是集商业、办公、酒店等诸多功能于一体城市综合体,共17层,总建筑面积21000平方米 一、商场水冷螺杆式机组系统说明 一层、二层为银行营业和商场,三层至四层为酒楼餐厅或洗浴按摩中心或卡拉OK歌厅,五层为西餐厅或健身中心,空调空调面积约4800平方米。整个空调系统采用二台日立公司高效螺杆(RCUF200WZP)+麦克维尔公司吊顶新风柜和风机盘管提供冷源,吊顶新风柜负责提供新鲜空气,风机盘管负责提供各区域所需冷量,每台风机盘管单独控制,冷量灵活调配,以后业态改变或空间大需变化时容改造,增加热量表就可进行单独计费,无需更改风管,冷却塔为方形横流冷却塔,系统分层计费方式采用超声波热量表,每层一个,如有需要可在各层单独可增加,集中监控管理系统对机房螺杆机、水泵、冷却塔、新风柜、风机盘管进行监控,根椐区域温度设定要求智能化管理控制,在监控室监控制冷系统和各层区间温度,从而降低能能耗,并统计出各区实际使用冷量,进行精准计费,在管理专用电脑实现远程管理,大大降低管理人员人数 空调水系统 1、设备布置 制冷主机设在地下室冷冻机房内,冷却塔设置在综合楼的屋顶。 2、冷冻水系统 冷冻水系统为两管制闭式循环系统,冷冻水循环泵设在地下室的制冷机房,冷冻水膨胀水箱设在综合楼的顶层天面,由给排水的供水管道向膨胀水箱补水。 3、冷却水系统 冷却水循环泵设在地下室的制冷机房,冷却塔设在综合楼的屋顶。由给排水的供水管道向冷却塔补水。 4、冷凝水系统: 根据各建筑,各层的功能不同,冷凝水就近集中排入污水系统,或由立管集中收集至首层排入污水系统。 5、空调方式 各建筑各层均采用水冷式空调机,气流组织按功能及装修要求采用上(侧)送下(侧)回。 6、空调新风及排风 1)新风从外墙防水百页新风口进来,经风柜降温处理后送到各空调区,通过对开多叶调节阀调节新风量。 2)排风量由门窗缝隙及楼梯口正压排出室外或卫生间等处排风机排出室外。 7、空调自动控制 本工程的空调控制采用就地控制+集中智能控制。 1)、抄表维护方便:超声波热量表数据自动采集,分月、分年自动统计和

美的家用空调的营销策略分析报告

毕业设计(论文)题目美的家用空调的营销策略分析届:专业: 学生:学号: 指导老师:职称: 2014年 11月 24 日

美的家用空调营销策略分析 [摘要] 随着中国经济的快速发展,人们生活水平不断提高,极大的促进了中国空调产业的繁荣。据统计2014年中国空调产量和销量分别达到了 9670万台和10600万台,已成为中国国民经济持续繁荣的重要产业之一。中国空调市场如此巨大,给各大空调生产厂家带来无限机遇。美的集团是以家电制造业为主的大型综合性企业集团,2013年9月18日在深交所上市,旗下拥有小天鹅、威灵控股两家子上市公司。美的集团作为电器龙头在寻找与把握机遇的同时,终始顽强的面对着来自各方面的激烈竞争。本文先是回顾国外对市场营销的研究现状,研究思路、研究方法等营销理论,确定本文的研究路线图。接着分析中国空调行业的宏观环境,包括人口环境、经济环境、政治法律环境、自然环境、社会环境和科技环境。为了美的空调在中国空调行业能够继续取得良好的成绩,立足于中国空调市场,本文最后着力于美的空调的产品、渠道、价格和促销等几个重要营销要点,结合其市场定位,优化了美的空调的营销策略 [关键词]美的集团家用空调营销策略

Analysis of household air conditioner marketing strategy of beauty [Abstract] With the rapid development of China's economy, people life level unceasing enhancement, greatly promoted the prosperity of China's air conditioning industry. According to statistics, in 2014 China's air-conditioning production and sales reached 96.7 million and 106 million respectively, has become one of the important industry of the national economy continued to boom in China. China's air conditioner market is so great, to each big air conditioning manufacturers bring unlimited opportunities. Midea group was mainly used for household appliance manufacturing in large-scale comprehensive enterprise group, listed on the Shenzhen stock exchange on September 18, 2013, which owns the whistling, welling holding subsidiaries of listed companies. Midea group as well as the electric faucet in the search for and seize the opportunities, always stubborn in the face of intense competition from all sides. This paper first reviews the research on marketing status quo, research ideas, research methods such as marketing theory, determine the research road map. Then analysis the macro environment of China's air conditioning industry, including population environment, economic environment, political law environment, natural environment, social environment and technology environment . To Midea air-conditioning air-conditioning industry in China can continue to achieve good results, China based air conditioning market, finally, the paper focus on the beautiful air conditioning products, channel, price and promotion etc. Several important marketing points, combined with its market orientation, optimize the beautiful air conditioning's market strategy [Key words] Midea group Home air conditioning The marketing strategy

系统概要设计说明书规范

KTV点歌系统概要设计说明书

1. 引言 1.1目的 选歌系统是为某KTV唱吧开发的视频歌曲点唱软件。该软件能方便顾客进行选歌,帮助系统管理员管理歌曲的播放,提高KTV歌曲点唱的效率和准确率。 本文档为该系统的概要设计说明书,详细阐述了对用户所提出需求的设计方案,对系统中的各项功能需求、技术需求、实现环境及所使用的实现技术进行了明确定义。同时,对软件应具有的功能和性能及其他有效性需求也进行了定义。 1.2项目背景 ●系统名称:选歌系统 ●项目提出者:某KTV唱吧 ●项目开发者: ●项目管理者: ●最终用户:某KTV唱吧 1.3术语定义 实现环境:系统运行的目标软件、硬件环境。 实现技术:系统所采用的软件技术或体系结构。 实现语言或工具:实现系统最终采用的编程语言或工具包,如Delphi、VB、PB、Java、Ada等。 参考资料 1)新余电视点播系统; 2)某KTV唱吧《视频点歌系统计划任务书》; 本项目所参照的文件有: 3)康博工作室,《Visual Basic 新起点》,机械工业出版社,2000

2. 系统概述 2.1系统需求 2.1.1系统目标 本软件是为某KTV唱吧开发的视频点歌系统软件。该软件用于提高点歌系统的工作效率。随着人们业余生活的丰富,休闲活动的多种多样,人们更多的喜欢选择KTV这种形式的娱乐方式。且随着计算机普及,点歌系统越来越智能化,人性化;一个好的音乐唱吧必须要拥有一个方便、快捷、准确的点歌系统,因此,急需一个软件系统解决这些问题。本软件应能结合当前选歌播放手工操作的流程以及将来业务发展的需要,对视频点歌系统中歌曲信息、歌手信息、最新排行榜等等的查询、更新提供完全的计算机管理。 2.1.2性能需求 数据精确度 数量值:精确到小数后一位; 时间值:精确到日,并以yyyy/mm/dd的形式表示; 价格值:精确到分,并以.XX的形式表示。 时间特性 页面响应时间:不超过10秒 更新处理时间:不超过15秒 数据转换与传输时间:不超过30秒。 适应性 1) 开发基于的平台要考虑向上兼容性,如操作系统,数据库等要考虑更高版本的兼容 性。 2) 当需求发生变化时系统应具有一定的适应能力,要求系统能够为将来的变更提供以 下支持:能够在系统变更用户界面和数据库设计,甚至在更换新的DBMS后,系统的现有设计和编码能够最大程度的重用,以保护现阶段的投资和保证软件系统能够在较少后续投入的情况下适应系统的扩展和更新。在设计中最好列出针对变更所需要重新设计的模块部分

空调课程设计说明书——@蚂蚁微关注

环境与市政工程学院 课程设计说明书 题目:空调课程设计 姓名: __学号:__ 专业:建筑环境与设备工程班级:_09级1班_____ 2012年9月14日

目录 1.设计目的 (2) 2.设计原始资料 (2) 2.1设计概况 (2) 2.2室外设计参数 (2) 2.3室内设计参数 (2) 2.4土建资料 (3) 3.空调方案 (3) 4.空调负荷计算 (3) 4.1夏季冷负荷计算 (3) 4.2冬季热负荷计算 (8) 4.3计算结果 (9) 5.风机盘管选型及计算 (10) 6.水力计算 (10) 6.1冷冻水水力计算 (10) 6.2冷凝水水力计算 (11) 7.气流组织 (12) 参考文献 (13)

1.设计目的 培养学生运用《通风与空气调节工程》课程学习中所掌握的理论和技术知识解决实际工程问题,进一步其提高设计计算、制图、使用设计参考资料和规范的能力。通过课程设计的训练,使学生掌握空调系统的设计原理和方法,巩固所学理论知识,并运用这些知识解决实际工程问题。 2.设计原始资料 2.1设计概况 设计地点:沈阳市 设计题目:沈阳市中联建业别墅空气调节系统设计 建筑概况:沈阳市中联建业别墅共四层,各层层高均为3.3米,窗高1.8米。 2.2室外设计参数 按照《暖通空调规范实施手册》中规定的室外计算计算参数是按全年少数时间不保证室内室内温湿度标准而制定的,查得沈阳市室外设计参数(见表1-1)。 表1-1 室外设计参数 2.3室内设计参数 按照《采暖通风与空气调节设计规范》的规定,对于舒适性空调,所有房间均采用表1-2所示室内设计参数。 表1-2 室内设计参数 3.空调方案

空调系统设计说明书_范文

设计总说明 本设计为上海市某办公楼空调通风系统设计。该办公楼属大型办公建筑,总建筑面积约为55000㎡。地下两层,地上二十八层,建筑总高度为99.6m。地下两层为车库及设备用房,地上二十八层均为办公用房。该建筑的主要功能间有办公室、会议室、接待室等。全楼冷负荷为3080千瓦,全楼采用风冷热泵机组进行集中供给空调方式。 本建筑位于上海市。上海市地处我国东部沿海地区,东经121°43′,北纬31°16′。属于亚热带季风气候区,四季分明,夏热冬冷,春秋短暂,但由于地处沿海,雨季较为分散,以夏季雨量最大。夏季空调室外日平均温度30.4℃,办公室室内温度26℃,湿度65%,室内风速v ≤0.3 m/s;冬季办公室室内温度20℃,湿度40%,室内风速v≤0.2 m/s。 设计的依据主要有同济大学浙江学院毕业设计(论文)任务书《上海市某办公楼空调通风系统设计》、采暖通风与空调设计规范GBJ19—87、HV AC暖通空调节设计指南、高层民用建筑设计防火规范GB50045—95(2005版)、GB 50189-2005 公共建筑节能设计标准、简明通风设计手册等。 考虑该大厦为办公楼,空调的运行时间主要在上班时间,所以计算负荷时本设计取的时间为6—18时。此设计中的建筑主要房间为办公室,大多面积较小,且各房间互不连通,应使所选空调系统能够实现对各个房间的独立控制,综合考虑各方面因素,确定选用风机盘管加新风系统。在房间内布置吸顶式风机盘管,嵌入暗装的形式。将该集中系统设为风机盘管加独立新风系统,新风机组从室外引入新风处理到室内空气焓值,不承担室内负荷。风机盘管承担室内全部冷负荷及部分的新风湿负荷。风机盘管加独立新风系统由百叶风口下送和侧送。水系统采用闭式双管异程式,冷水泵四台,三用一备。 在冷负荷计算的基础上完成主机和风机盘管的选型,并通过风量、水量的计算确定风管路和水管路的规格,并校核最不利环路的阻力和压头用以确定风机和水泵。 通风设计方面,地下室为车库及设备用房,设计成机械送排风为主,自然进排风为辅的方式,其换气每小时不小于6次;卫生间排风设计为排风扇机械排风到外阳台,排风量按每小时不小于10次的换气量计算;考虑到办公室吸烟问题,也采用排风扇机械排风到外阳台,排风量为送风量的80%。电梯前室及楼梯间设计加压送风。 该设计按照建筑结构及其要求制定空调方案,力求能够满足使用的要求,即能够满足办公舒适性。此外还要从空调设计的科学合理性和经济性,以及建筑整体的美观度考虑。中央空调在现代建筑中越来越多的应用,技术也越来越成熟先进。能够有效的管理,一次性投资,后期使用方便,并且不占用建筑的有效空间。本文就是对中央空调的设计到选型,到校核计算的一个说明。从使用性到科学性再到经济性上做到好的结合。方案选择是整体考虑以及设计的总体思想,计算部分是整个设计的基础,绘图部分是与设计施工相联系的实际的走管和安装。三个部分相依相承,都与整个工程密不可分。各个部分都要保证科学合理,正确无误,经济适用。 本设计是真实性课题的典例。其中,有理论的分析计算,有中央空调方案的选择论证,有实际的绘图安装。是一个完整的工程设计实例。设计计算主要有冷负荷的计算,送风量的计算,管路的计算等。冷负荷的计算确定了各个房间的空气状况和调节条件,以及整个工程的负荷量。是确定室内空调调节方案的主要数据。也是选择冷水机组最主要的参考数据。送风量和管路的计算是面向实际设备和管路的数据资料。都是整个设计的基础。 在上面主要阶段完成以后还要对一些具体细节的问题加以论证思考并列出解决方案。比如管

中央空调设计手册

暖通空调系统设计手册 目录 第一章设计参考规范及标准 (5) 一、通用设计规范: (5) 二、专用设计规范: (5) 三、专用设计标准图集: (5) 第二章设计参数 (6) 一、商业和公共建筑物的空调设计参数ASHRAE (6) 二、舒适空调之室内设计参数日本 (7) 三、新风量 (8) 1、每人的新风标准ASHRAE (8) 2、最小新风量和推荐新风量UK (9) 3、各类建筑物的换气次数 UK (9) 4、各场所每小时换气次数 (9) 5、每人的新风标准UK (10) 6、考虑节能的基本新风量(1/s人)(日本) (10) 7、办公室环境卫生标准日本 (11) 8、民用建筑最小新风量 (11) 第三章空调负荷计算 (15) 一、不同窗面积下,冷负荷之分布% (15) 二、负荷指标(估算)(仅供参考) (15) 三、空调冷负荷法估算冷指标。空调冷负荷法估算冷指标(W/M2空调面积)见下表 (16) 四、按建筑面积冷指标进行估算建筑面积冷指标 (17) 五、建筑物冷负荷概算指标香港 (18) 六、各类建筑物锅炉负荷估算W/M3℃ (19) 七、热损失概算W/M3℃ (19) 八、冷库冷负荷概算指标 (20) 第四章风管系统设计 (21) 一、通风管道流量阻力表 (21) 1、缩伸软管摩擦阻力表 (21) 2、镀锌板风管摩擦阻力表 (21) 二、室内送回风口尺寸表 (24) 1、风口风量冷量对应表 (24) 2、不同送风方式的风量指标和室内平均流速ASHRAE (24) 三、室内风管风速选择表 (25) 1、低速风管系统的推荐和最大流速m/s (25) 2、低速风管系统的最大允许速m/s (25) 3、通风系统之流速m/s (25) 四、室内风口风速选择表 (26) 1、送风口风速 (26) 2、以噪音标准控制的允许送风流速m/s (26)

在线交易二手市场系统概要设计说明书

在线交易二手市场系统概要设计说明书概要设计说明书 信息与电气工程学院 软工1401 ** 201422******

1.引言 1.1编写目的 此概要设计说明书实现一个简易的基于校园网在线交易二手市场系统,对交易管理系统的总体设计、接口设计、界面总体设计、系统出错处理设计以及系统安全数据进行了说明,在以后的软件测试以及软件维护阶段也可参考此说明书,以便于了解在概要设计过程中所完成的各模块设计结构,或在修改时找出在本阶段设计的不足或错误。 1.2背景 A.待开发软件系统名称为: 在线交易二手市场; B.任务提出者:** 开发者:** C.使用用户能在校园网上进行交易的系统。 D. 按照《在线交易二手市场系统需求分析说明书》为基础来具体细化系统所具备的所有功能及功能的实现方法和接口。 1.3 开发环境 Visual Studio 2010 Mircosoft sql server 2008 Express

PowerDesigner 15.1 1.4定义 本系统:基于校园网的在线交易二手市场系统设计与实现 1.5参考资料 《基于校园网在线交易二手市场需求分析说明书》 《项目计划表》 《校园网在线交易二手市场系统_数据库模型》 2.总体设计 2.1设计目标 基于校园网的在线交易二手市场主要实现以下目标: ⑴为师生提供展示商品及表现学校形象的平台。 ⑵为用户提供商品信息查看、在线商品订购、商品浏览等功能。 ⑶采用动态网页技术,使页面中展示的商品信息更具时效性、先进性。 ⑷提供客户互评及客户给商品评论功能,收集用户对商品的意见及看法。 ⑸提供后台管理页面,简化了用户信息、商品信息、订单信息等系统数据的维护操作。 2.2运行环境

美的空调营业推广策划

策划委托人美的集团 策划公司赤壁营销策划公司联系电话****** 策划完成时间2011年8月20日

策划执行时间2011年10月1日——2011年10月7日 前言 为迎接2011年度“十一”黄金周的到来,现由赤壁营销策划公司接受美的集团营销部的委托,承担2011年度“十一”黄金周美的空调营业推广促销活动的策划工作。由于连续7天的国家假日会为消费者市场增加比往常更多的人流量,从而带来更多的购买潜力。为应征这样一个特殊时期的到来,全国空调市场的各个厂家商家都开始了一波一波的促销热潮。为把握购物高潮,作为行业头三的美的空调为避免被其他竞争者超越,必须要做好今年“十一”黄金周的营业推广的促销活动筹备。本策划力求从各种营业推广方式入手,提出一整套本年度“十一”黄金周的美的空调促销技术

方案。 目录?内容摘要 ?今年空调市场环境分析 ?企业SWOT分析 ?营销目标及战略方针

?行动技术方案及营销活动预算 ?效果评估及风险控制 一、内容摘要: 本公司计划重点在下半年的“十一”黄金周采用营业推广的方式进行促销,增加美的空调的销售量,提高利润率,减轻商家库存压力,有力地抵抗竞争对手的威胁。 二、美的空调2011年所处的空调市场环境介绍: 空调行业经过多年的充分竞争,品牌集中度较高。随着市场竞争的不断成熟,行业格局日趋稳定。2011年1~4月龙头品牌市场占有率稳中有升。前四家市场占有率合计超69%。格力、美的累积总销量均超1200万台,市场占有率分别为28.9%和28.7%,双寡头销量合计占据半壁以上江山。格力、美的增速超行业平均,累积同比增长分别为59.8%和47.6%。

暖通初步设计说明书

暖通空调初步设计说明书 摘要:地下三层,地上十层,框剪结构,空调形式为冰蓄冷,冷辐射吊顶。 1 设计依据 1.1上级批文详见总论部分; 1.2甲方提供的设计任务书; 1.3建筑专业提出的平面图和剖面图; 1.4室外计算参数(北京地区) 夏季空调计算干球温度33.2℃ 夏季空调计算日平均温度28.6℃ 夏季空调计算湿球温度26.4℃ 夏季通风计算干球温度30.0℃ 夏季空调计算相对湿度78 % 夏季大气压力99.86Kpa 夏季平均风速 1.9 m/s 冬季空调计算干球温度-12℃ 冬季通风计算干球温度-5℃ 冬季空调计算相对湿度45 % 冬季大气压力102.04 Kpa 冬季平均风速 2.8 m/s 1.6国家主要规范和行业标准 (1)《采暖通风与空气调节设计规范》GB50019-2003; (2)《高层民用建筑设计防火规范》GB50045-95(2001版); (3)《民用建筑热工设计规范》GB50176-93; (4) 全国民用建筑工程设计技术措施《暖通空调·动力》; (5) 《民用建筑隔声设计规范》GBJ118 1.7 2004年5月19日由中船重工集团组织的《科技研发大厦空调方案研讨会》专家组意见。 2 设计范围

本工程为船舶科技研发大厦,总建筑面积为33928平方米,预留建筑面积为5494平方米,建筑高度为33.99米。地下二﹑三层为停车库及设备用房,层高3.6米;地下一层主要为餐厅﹑厨房﹑多功能厅及档案室,层高5米;首层至八层主要为办公及会议室,首层层高为5.0米,其余为3.9米。 设计范围为采暖、通风、空调、防排烟及冷热源设计。冷冻机房冷却水系统由给排水专业设计。 3 设计原则 满足国家及行业有关规范﹑规定的要求,利用国内外先进的空调技术及设备,创建健康舒适的室内空气品质及环境。 4 空调设计

空调毕业设计说明书

……………………. ………………. ………………… 山东农业大学 毕 业 设 计 题目:南京实验楼集中空调系统设计 院 部 水利土木工程学院 专业班级 建筑环境与设备工程2010级3班 届 次 2010 学生姓名 孙晴 学 号 20103496 指导教师 王萌 二O 一四年六月十四日 装 订 线 ……………….……. …………. …………. ………

目录 一. 设计资料及说明 (1) 二. 空调设计方案分析 (2) 三. 负荷计算 (4) 四.空气处理过程设计 (12) 五. 房间气流组织方案设计 (14) 六. 水系统的水力计算 (15) 七.风系统的水力计算 (17) 八. 冷热源的设计和布置 (19) 九.空调设备明细表 (20) 十.空调系统消声减振的设计方案 (22) 十一.空调系统控制和调节 (24) . . . 参考文献 (24) 致谢词 (25) 附录(附件) (26)

南京实验楼集中空调系统设计 作者:孙晴 10建环3班 指导老师:王萌 设计内容简介: 对南京实验楼集中空调系统进行了设计。该实验楼共三层,建筑总面积6738.24m2,其功能包括:实验室、教室、办公室。该中心总冷负荷880.83kw,总热负荷744.02kw。基于冷负荷、湿负荷、热湿比及其功能区特点,并考虑到经济性和可行性,确定出了该实验楼的具体所适用的空调系统方案,并针对此方案进行了水管风管的布置、水力计算、设备选型及设备布置及对设备的消声减振的设计。

1 设计说明及资料 1.1原始资料 1.1.1 设计地区:江苏南京 1.1.2 建筑资料:该实验楼为五层建筑,第一、二、三层有实验室,内厅,卫生间等,第四层有实验室,教室,办公室,卫生间等。第五层有教室,卫生间。现以提供各层结构平面图等。每层层高除二层为5.4m外均为4.5m,吊顶3m(局部可低)1.1.3 室内设计参数 表1-1-1 1.2 室外气象资料和围护结构资料 1.2.1室外气象资料 表1-2-1 1.2.2围护结构资料 外窗-------普通玻璃,传热系数为3.6 w/m2.℃

设计方案说明(格力空调)

第一部分:设计方案说明 格力小型中央空调系统设计方案 一、工程概况 本方案中住宅的建筑室内面积约为多m2空调使用面积约为m2。设有客厅、餐厅、主卧室、次卧、书房。 本工程设计:主机采用格力数码多联家用中央空调机组。 1.电控系统:由主机电控部分、末端内机电控部分、主机与室内机联网控制部分组成。 2.控制方式:各房间室内机就地独立自动控制,主机在电脑控制下自动运行,全部室内机末端可与主机联动。 二、设计参数 (一) 室外气象参数: 夏季空调室外计算干球温度 T=36.5℃ 夏季空调室外计算湿球温度 Ts=27.3℃ 冬季干球温度 T=2.0℃ 冬季空调室外计算相对湿度Ф=82% 大气压力夏季 991.2hPa 冬季 973.2hPa (二)室内设计参数: 三、设计依据 (一)设计采用规范 1.《采暖通风与空气调节设计规范》。GBJ19-87(2001年版) 2.《户用和类似用途冷水热泵机组》国家标准(GB/T18430.2-200119-87) 3.《家用中央空调实用技术手册》(交通出版社) (二)业主要求 1.业主单位提供的建筑平面图; 2.主机与室内机均采用格力产品 3.空调主机按全负荷的计算。 4.空调内外机连接采用紫铜管,冷凝水管采用蓝色UPVC管。 四、设计思想 (一)优化系统设计,确保运行稳定可靠。 (二)室内温度可在一定范围内随意调控,控制器为格力标配的液晶显示智能温控器,其特点为:1.超小型外观设计,大液晶数字显示室内温度。

2.室内自动恒温控制,24小时定时开/关功能。 (三)系统噪音最小化。 (四)尽量提高安装高度,融入装饰之中 (五)降低初投资和运行费用 五、主机、末端选型 经计算总冷负荷为17.5KW,根据使用功能分配要求,考虑到空调区域的使用功能不同,不具有同时使用负荷高峰的可能性(如客厅与卧室一般使用会交替)。总负荷峰值按总末端负荷70%计算.故主机负荷为12kw. 制冷机的选型采用珠海格力空调设备有限公司生产的数码多联家用中央空调一台,型号为GMV-R120W/H,总制冷/制热量为12KW/13KW,制冷/制热用电功率为3.5KW/3.6KW。主机电源为220V、50Hz。脑板的控制下根据负荷变化,自动无级工作保证空调区域温度稳定。 六、空调氟系统及气流组织设计 1.铜管系统 (1)铜管系统: 空调内外机连接采用铜管,闭式循环系统;其管路走向由设计人员、施工人员根据现场具体情况与业主、装修及各施工单位共同协商确定、详见空调平面布置图。 (2)冷凝水系统 空调冷凝水依就近排入卫生间旁通地漏的原则,其管路布置根据现场具体情况与业主、装修单位共同确定。凝结水管路必须保证顺水流方向的斜度1/100,以保证凝结水能自然流畅。 (3)保温材料 冷(热)水路系统管道保温密闭,采用材料为橡塑福乐斯,外缠扎带。 2.气流组织 气流组织决定房间空调效果,本设计采用侧送下回风方式(详见空调方案设计图)。由施工人员根据现场具体情况与业主、装修单位共同确定,其开口及表面美饰由装修单位处理。 七、施工说明与其它注意事项 (一)在工程施工过程中,施工人员应多协调业主、装修及各工种,及时解决工程问题,做到气流组织合理,装修美观,空调安装方便,达到业主与设计要求;并保质、保量,按期完成工程内容。 (二)空调铜管系统管道保温连接处不能有缝隙,保温材料无破损。 (三)冷凝水管路必须保证凝结水自流畅通。

家用空调设计计算说明书模板

家用空调设计计算 说明书

制冷系统课程设计说明书 热能与动力工程专业 目录 一、 设计工况 .................................................................................... 4 二、 压缩机选型 ................................................................................ 4 三、 热力计算 (6) 1、循环工况:............................................................................. 6 2、 热力计算: ............................................................................ 7 四、蒸发器设计计算 . (8)

文档仅供参考 1、设计工况: (8) 2、计算过程: (9) 3、风机的选择 (19) 4、汇总 (19) 五、冷凝器换热计算 (20) 第一部分:设计计算 (20) 一、设计计算流程图 (20) 二、设计计算 (21) 3、计算输出 (27) 第二部分:校核计算 (28) 一、校核计算流程图 (28) 二、计算过程 (29) 六、节流装置的估算和选配 (30) 七、空调电器系统 (31)

一、设计工况 3KW机组,半封闭压缩机,风冷冷凝器,风冷蒸发器,毛细管,制冷剂R22,蒸发温度5℃,过热度20℃,冷凝温度50℃,过冷度5℃ 二、压缩机选型 1、选型条件:制冷量3kW,制冷剂R22,蒸发温度5℃,过热度20℃,冷凝温度50℃,过冷度5℃。 2、选型结果:使用压缩机选型软件select 6,选择型号为DKM-75的半封闭往复式压缩机。 a.其基本参数如下:制冷量3.15kW,输入功率1.06kW,cop 为2.97,电流(400V)2A,质量流量18.9g/s,放热3.65kW b. b.其技术参数:

系统概要设计说明书(数据库设计书)

[招生管理系统] 概要设计说明书 [V1.0(版本号)] 拟制人______________________ 审核人______________________ 批准人______________________ [二零零八年十月二十二日]

概要设计说明书 1.引言 1.1编写目的 本说明书交给各个被调研单位审核,并经领导层讨论通过后,软件开发小组成员将以这本说明书为框架开发新的系统。 1.2背景 a.待开发软件系统的名称: 基于XML的网上招生管理系统 b.本项目的任务提出者: 石河子大学 c.本项目开发者 d.本项目用户 石河子大学招生办 1.3定义 [列出本文件中用到的专门术语的定义和外文首字母组词的原词组。] 1.4参考资料 《软件工程》 2.总体设计 2.1需求规定 2.1.1功能规定

2.1.2系统功能 能对各招生子单位进行管理 能添加、修改、删除、考生信息 能对考生进行分类管理 能将考生信息导出至网上信息发布子系统 能根据各分类统计考生信息 能添加新的管理员 能修改管理员的密码 2.1.2.1精度 由于采用数据库技术并且用户的应用领域对数据精确度的要求不高,所以这点在系统中表现得比较少,但是用户数据的安全性与正确性是完全保证的,所以对用户的使用没有多大的障碍。 2.1.2.2时间特性要求 本系统的数据库较小,所以程序在响应时间,数据更新处理时间上性能是比较突出的。而且也正由于数据量相对较少,故在数据传输时间和系统运行时间上表现的较让人满意。 2.1.2.4可靠性 由于系统较小只保留一定程度上的可靠性。 2.1.2.5灵活性 由于系统较小只保留一定程度的灵活性。 2.1.3输入输出要求 2.1.4数据管理能力要求

中央空调设计说明书

第1章工程概况 第1章工程概况 1.1建筑概况 星城酒店广东省汕头市,总建筑面积为19595㎡,地上9层,地下一层,总建筑高度为34.3m。其中地下一层主要为休闲运动场所,一层为餐厅、会议室、办公室等,二层主要为桑拿中心,三层以上为客房。 1.2 计算参数 1.2.1 室外计算参数 表1.1 广州市夏季室外气象参数 大气压力(Pa)空调室外计算干球温度(℃)空调室外计算湿球温度(℃) 室外平均风速(m/s)100287 33.4 27.7 2.7 1.2.2 室内计算参数 表1.2 各空调房间室内计算参数 房间名称 夏季新鲜空气量噪声标准温度(℃) 湿度(%) m3/h·人dB(A) 客房25 50~65 30 < 45 乒乓球室、壁球室、桌 球室、美容美发、棋牌 室、投影室、健身房、 阅览室、银行 25 55~65 30 < 50 餐厅、会议室、茶室25 55~65 25 < 45 1.2.3 其他设计参数 表1.3 照明功率密度值(W/㎡) 建筑类别房间类别照明功率密度 酒店 餐厅13 中庭、大厅15 银行18 其他11

广东石油化工学院本科毕业设计:星城酒店空调工程设计 表1.4 不同类型房间人均占有的使用面积(㎡/人) 建筑类别房间类别人均占有的使用面积㎡ 酒店 客房10 餐厅 2 运动场所 5 其余 2 1.3 主要设计依据 1.3.1建筑与暖通空调工程制图标准 1、房屋建筑制图统一标准(GBJ 1—86); 2、采暖通风与空气调节制图标准(GBJ 114—88)。 1.3.2 通用设计规范 1、采暖通风与空气调节规范(GBJ 19—87); 2、民用建筑节能设计标准(JGJ 26—95); 3、民用建筑热工设计规范(GB 50176—93); 4、民用建筑设计通则(JGJ 37—87); 5、建筑设计防火规范(TJ 36—79); 1.3.3专用设计规范 1、办公建筑设计规范(JGJ 67—89); 2、综合医院建筑设计规范(JGJ 49—88); 1.3.4暖通空调工程施工及验收规范 1、通风与空调施工及验收规范(GB 50243—97); 2、压缩机、风机、泵安装工程施工及验收规范(JBJ 29—96); 3、制冷设备、空气分离设备安装工程施工及验收规范(GB 50274—98); 4、制冷设备安装工程施工及验收规范(GBJ 66—84)。

空调系统设计说明

中央空调系统设计说明 一、项目概况。该建筑为酒店型会所,共三层,空调面积约3500平米,以平均冷负荷指标170 W/㎡,得标准进行空调设计。 二、设计依据。根据甲方提供得建筑功能平面图。 《采暖通风与空气调节设计规范》(GB50019-2003) 《通风与空调工程施工及验收规范》(GB50243-2002) 设备厂家得安装说明手册 三、设计范围 各功能房间得夏季制冷、机房布置等设计。采用设计方案:冷水机组+风机盘管+冷冻水泵。设备置于设备间,膨胀水箱高位定压。 四、设计参数 夏季室外空气调节计算干球温度36℃,湿球温度27℃。夏季室内设计温度26±2℃ 五、项目分析及方案设计 单位面积冷负荷设计为约170w/㎡,本项目空调面积约3500平方米。 5、1一层系统 一层为高层高式大空间,采用高静压盘管风机。分区控制各个区域,容易针对性控制温度以达到节能目得。前台大厅约230w/㎡,餐厅约230w/㎡,咖啡厅约200w/㎡,KTV包房及棋牌娱乐室约260w/㎡,客房每个房间负荷约180w/㎡,走廊空间约80w/㎡。送风方式按各分区特点配合室内装饰选择合适得送风方式。 5、2二层系统 二层为客房与会议室,均采用静音型风机盘。会议室单位冷负荷约260w/㎡,客房每个房间负荷约180w/㎡,送风采用侧送风得方式。走廊空间80w/㎡,采用静压箱集中送风方式。5、3三层全部为客房,均采用静音型风机盘。客房每个房间负荷约180w/㎡,送风采用侧送风得方式。走廊空间80w/㎡,采用静压箱集中送风方式。 六、送风口形式:采用铝合金双层百叶风口,以单层百叶铝合金风口作为回风口。最终具体选用情况,与装修公司紧密配合选择。 七、系统控制。 7、1主机机组得运行、管理均由微电脑控制系统完成,操作简单,仅需管理人员在季节变化需要启动时打开电源、总阀及分区控制阀门;机组根据负荷自动启动/停止压缩机,使机组既运行在最佳经济点,又节约用户能源。机组得各项保护功能齐全,具备故障自检系统,自动平衡压缩机得磨损,冬季自动防冻等功能。 7、2室内机风机盘管由线控器分别控制,根据装饰设计配合放置在光源开关处。 八、冷冻水系统。 本系统以水作为载冷剂进入房屋,安全,环保、无任何潜在使用危险,也不会出现一点泄漏就造成全系统瘫痪得问题。冷冻水系统经过室外主管进入各空调区域。冷冻水系统管道:DN≥50MM采用无缝钢管,DN<50MM采用PPR管。风机盘管与冷冻水支管间采用橡胶软接头,阀门采用铜闸阀。系统最低点设立排污阀,局部最高点设自动排空阀。 九、冷凝水排水系统,采用U-PVC管,通过卫生间就近排放。 十、主机设备。 冷水机组设备采用水冷螺杆机组,该类型机组最大优点在于技术成熟、性能稳定、能效比高。设备放置于单独得设备间,基础由建设方根据我方提供得基础图预制。冷却塔采用角型横冷式冷却塔,放置于设备间屋顶。屋顶承压结构由我方提供基础图及设备循环重量,建设方据

相关文档