Issue Error Code: 04 04F2 00

Red Box during SPE SPS replace script

Message 0x00001509.0x3011:

At this point the SPS-CC-B should be powered down but

an unexpected power condition has been detected on SPS-0-B,SPS-1-B.

Please power up SPS-0-B,SPS-1-B as soon as possible or the DAE could power down.

Please call the EMC Support Center,

They will help you to locate the correct SPS.

(FIs ile: procalls.sl, Line: 7)

Environment Product: Symmetrix DMX800

Enginuity: 567x

Cause Error Code: 04 04F2 02 indicates SPS battery end-of-life (The SPS should be checked using emc64887 if it i Change SPE SPS replace script

Resolution

CE is replacing SPS B. This is the SPE SPS located on DA-1A. 8C,COND,,SPSI showed 0100- internal fault

During the script:

1. Step C: Prompt_User_to Power_Down_SPS - CE turns off SPE SPS B and answers Yes to question

2. Step D: Verify SPS is powered down then fails with the above red box.

3. Have CE verify that the only amber LED on any SPS is that of SPE SPS B and ensure that SPS SPE

4. PSE issues 8C,COND,,SPSI on DA-1A AND 16A

5. DA-1A still shows internal fault 0100 and DA-16A shows 0002 normal

6. 8C,POWR,,SPSI on DA-2A shows its DAE SPS are OK, however 8C,POWR,,SPSI on DA-15A fails b

power off top switch/Mux and now DA-15A cannot monitor the DAE SPS relating to it.

7. 9B,A will show the expected 0479 on DA-15A due to the above issue.

8. If the above checks are OK then OK for PSE to resume from failed step and skip step.

9. Script will then complete sucessfully.

Issue System destage and DU event occurs when switching off the faulty SPS for Sys replacement

Directors go to DD.

Error code: 28 04F1 55

Error code: 28 04F1 01

Error code: 28 04F1 02

Error code: 03 FEC0 00

Error code: 03 FEC0 01

Error code: 03 FEBA 00

Error code: 03 FEBA 10

Environment Product: Symmetrix DMX800

Hardware: Power Components

RS232 Switch

Standby Power Supply (SPS)

Product: RMS

Cause When an Standby Power Supply (SPS) for the card cage SPE is switched off, 04 the DA that monitors the SPS through the direct connect RS232 cable. DA-1a m

SPS-A. 0F41.55 indicates AC power loss. 0479.20 indicates the SPS cable is m

In this customer incident, SPS-A was reported faulty. When it was switched off f

04F1.55, but without 0479.20 and was immediately followed by 04F1.02, indica

the SPS on the other side. As a result of detecting a power issue on both sides,

sequence for power shutdown. Seconds later, FEBA and FEC0 errors logged on

WARNING! Always verify the cable connections before turning OFF any SP

The DC power output cable from SPS-A must go to PS-1 while the one from SPS

power cables were miswired so that the cable from SPS-A went to PS-2 while th

PS-1. Switching off the faulty SPS-A caused the Symmetrix to detect loss of AC

power to the PS on the other side. The weakening batteries in the faulty SPS we

power output and the PS-2 failure was immediately reported (04F1.02). Howeve

were subsequently reported.

Change Replace SPS Power Component script.

CE switches off power to the failed SPS during power component replacement.

Resolution Having logged 0F41.55, but without 0479.20 when the SPS for the card cage SP DC power output cables between the two SPS units being miswired. If the direct

between the FEBEs and the SPS units are miswired, the Symmetrix will also en

when the SPS is switched off. However, it will still log 0479.20.

Correct the cabling issue. The DC power output cable from SPS-A must go to P

PS2.

Notes Note: Error code 28 0479 20 does not apply to this solution.

Although the FEBA event is decoded to be "A/C failed again after A/C restore," i

comes from the FEBE board which monitors the 12V output of PS1 and PS2. Te

DC power output cable from SPS to the PS for SPE unplugged, switching the SP

events. Logging of the FEBA should indicate only that the DC power to the PS c

DC power could come from the batteries in the SPS.

Notes

(Employees

Symptom: Error code: 04F2

and

Partners)

Product Symmetrix, Symmetrix DMX800

Requested

5/25/2013 2:28 PM

Publish Date

External

Primus

Source

Primus/Webtop

emc215745

solution ID

Issue Error code: FEDD

AC power unplugged.

Environment Product: Symmetrix DMX800

Product: Symmetrix DMX801

Product: Symmetrix DMX-4 950

Product: Symmetrix DMX-3 950

Enginuity: 5670 All

Enginuity: 5671

Enginuity: 5771 All

Enginuity: 5772

Enginuity: 5773

SPS to SPE power cord is held in place by a retaining bail.

Cause RMS power plug pulled out.

Change Slide out the RMS SPE enclosure on the rails.

Replacing one of the Standby Power Supplies (SPSs) for the Storage Process

Replacing one of the SPSs in a Disk Array Enclosure (DAE).

Resolution When performing a maintenance activity which requires the SPE to be extended the SPSs that supports the SPE, or one of the SPSs in a DAE, check that the ba

secure. Make this check before moving the SPE or replacing an SPS and after.

procedure script and perform a health check after the procedure has been comp

disconnected during maintenance, ensure that the bail is put back in place. The b

at the furthest slot in the cable from the end of the plug. In other words, the bail

reachable slot away from the end of the cord to ensure a tight locked connection

If the system does not have any bails installed (early DMX800 systems were shi

to accidently unplug the SPS cables while moving the SPE or replacing an SPS.

Notes

(Employees

Fact: Product: Symmetrix DMX RMS

and

Partners)

Product Symmetrix DMX800, Symmetrix Enginuity 5670, Symmetrix Enginuity 5671, Symmetrix DMX Series, Symmetrix DMX801, Symmetrix DMX-3 950, Symmetri

Symmetrix Enginuity 5773

Requested

5/25/2013 2:16 PM

Publish Date

External

Primus

Source

Primus/Webtop

emc194707

solution ID

Issue Red Box: During Card Cage (CC) Standby Power Supply (SPS) replacement Error code: 04 0479 xx

Error Code: 04 04F2 xx

Message 0x00001509.0x3011:

Red Box: During CC-SPS-x replacement script

Red Box: At this point the SPS-CC-x should be powered down but

an unexpected power condition has been detected on SPS-0-B,SPS-1-B.

Please power up SPS-x-x,SPS-x-x, (etc) as soon as possible or the DAE could p

Environment Product: Symmetrix DMX800

Enginuity: 5671

Enginuity: 5670

Cause One of the Card Cage SPS (CC-SPS-x) powers the RS-232 Mux switch. When SPS, and the "Mux switch" loses power, all SPSs connected to that RS-232 Mux

the director. The Red Box occurs after the script checks the status of all the SPS

cannot communicate to the SPS with the Mux powered off.

Change SPS Replacement

Resolution Irrespective of this problem the script should be used as it will help detect other and could help prevent a potential DL

If you are going to replace both of CC_SPSs, after replacement of first one, alw

"Environmental" or call PSE LAB to check PS1 and PS2, as you could have a m

(found in a case where we had a undetectable error on PS2 and after removing

Should the script fail finish replacement of the Card Cage SPS Manually (CC-SP

Power Supply and SPS are working and have no other errors. The CE can then

Notes Card Cage SPSs (CC-SPSs) are also Known as SPE SPSs; SPS located on bo and SPS located on bottom/right of Card Cage is on use of PS1 (rear view) Product Symmetrix Enginuity 5670, Symmetrix Enginuity 5671, Symmetrix, Symmet

Requested

5/25/2013 1:53 PM

Publish Date

External

Primus

Source

Primus/Webtop

emc146126

solution ID

Impact SymmWin Environmental script must be run prior to every SPS replacement an

Environment Product: Symmetrix DMX-800

Product: Symmetrix DMX 1000

Product: Symmetrix DMX 2000

Product: Symmetrix DMX 3000

Enginuity: 5671

This statement does not apply: Enginuity: 5670

Change SPS Replacement

Power Supply Replacement

Resolution Before the SPS replacement or power supply replacement is performed, the Sy If the Environmental test determines that power related issues exist besides the

replacing, contact the PSE Lab prior to any power supply replacement.

Notes Due to SPS units in the field getting older, Engineering has requested that the before proceeding with any SPS replacements.

Product Symmetrix, Symmetrix DMX Series, Symmetrix Enginuity 5671

Requested

5/25/2013 4:39 PM

Publish Date

External

Primus

Source

Primus/Webtop

emc245194

solution ID

There are no SRs Linked To This Article